No 50 amp shore power - troubleshooting help please?

Left the campground in GA this morning and landed at friends house in VA earlier this evening.
Plugged into their 50 amp service, and no shore power inside coach.
My surge protector indicators show correct wiring on line 1 and on line 2 at their box, and surge indicators are lit.
Only getting 99 or 100 Volts on the AC Line Meter inside the coach. I didn't include full commentary here, but it seemed that "inverter" was flashing on the Xantrex RC7 GS while plugged into shore power
Switched to Generator power, and shows 118 V on the AC Line Meter that is plugged into outlet inside entry to coach.
Xantrex RC7 GS display indicates "System Status: Float Charging", with generator running.
What am I missing?
Any help is appreciated.
__________________

__________________
2005 Monaco Windsor 40PDQ
05MoWi is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-17-2020, 10:55 PM   #2
Senior Member
 
Skip426's Avatar


 
Join Date: Apr 2011
Location: Powell River, B.C.
Posts: 19,128
When you ran the gen set did everything ;120 volt inside the RV; work?

Is your surge guard between the auto transfer switch and the coach , or just in the shore line?

100 volts is low for shore power , my surge guard will shut down at 109/107.
Have you got the surge guard manual .
How about the Xantrex? it may be looking for higher voltage too.
__________________

__________________
99DSDP 3884, Freightliner, XC, CAT 3126B, 300 HP /ALLISON 3060
2000 Caravan toad, Remco & Blue Ox.
Skip426 is offline   Reply With Quote
Old 05-18-2020, 04:36 AM   #3
YC1
Senior Member
 
YC1's Avatar


 
Holiday Rambler Owners Club
Join Date: Jun 2011
Posts: 7,482
Leaving out clues can be an issue but I will take a stab at it.

You need a voltmeter to be sure the post is providing the proper power.

That power goes to a transfer switch that is automatic. The switch could have loose connections or could have failed.

Running the generator may be supplying the proper voltages and the transfer switch defaults to that position so may work in that mode.

Between the shoreline post and transfer switch is often a hose reel and there can be a source but more often it is the transfer switch versus the reel.

If you were running the generator with your air conditioners running (high load), then plugged into shoreline and did not turn off the AC's before transferring the load you could have arced the transfer panel contacts.

Transfer panels are not magical nor very complex and do are not pricey. But you must be careful poking around in there if not competent with a voltmeter,
__________________
Myron & Deborah
08 HR Endeavor 40 SKQ
2012 Ford Edge Limited FWD 3.5L
Aluminator tow bar, Demco base plate
YC1 is online now   Reply With Quote
Old 05-18-2020, 07:37 AM   #4
Senior Member
 
RamiDav's Avatar
 
Join Date: Jan 2016
Posts: 1,418
As stated your transfer sw is most likely the culprit and Monaco used a lot of Iota
switches in your coaches time frame .
Those switches were recalled because of problems and fires .
So if you have an Iota sw you should look into replacing it whether it's your
current :-) problem or not .
Unfortunately both Monaco and Iota went bankrupt so you are on your on .

Ray
RamiDav is offline   Reply With Quote
Old 05-18-2020, 10:45 AM   #5
Senior Member
 
Ljwt330's Avatar
 
Join Date: Jan 2018
Location: Capistrano Beach, California
Posts: 1,806
All good advice, above. However, I'd suggest some step by step diagnosis first.


Obviously you know how to use a volt meter and we don't know what type of surge protector you have or where it's located. It doesn't sound like it is an EMS type, however, which would shut down incoming low power to the coach.



If this was my problem, given the information, here's how I'd proceed:
1) Measure the voltage at the shore outlet, both lines. This may be the issue.


2) If outlet voltage is good, repeat the measurement at the transfer switch. Measure the shore power (cord) inlet lugs. If low, check that all lugs are clean and tight. If still low, the issue is the cord/connection to outlet. If good, measure at the outlet to coach lugs. If low, clean and tighten lugs. If still low, shore contacts are issue. If good, that puts you back to the panel.


3) Inside the panel, measure voltage at incoming lugs. If not same as at transfer switch outlet, issue with wiring to panel. Clean and tighten all lugs. If good, measure voltage at main circuit breaker. If low, replace CB.


4) The inverter is also a clue. You appear to be measuring the coach AC voltage from an outlet. The inverter has a pass-through circuit that allows shore power to go directly through to the coach outlets. As mentioned, that circuit may need to detect a higher line voltage that you are getting, but if you follow the steps, that will be known. The fact that you get full voltage when on gen power means that the pass through circuit is working.



Following the above steps will allow you to find the area of the problem quickly and you will not have to necessarily do all the steps.
__________________
Larry, Eileen, and Finley
2004 Alpine 36FDDS
Third motor home, first Alpine, no need for another.
Ljwt330 is offline   Reply With Quote
Old 05-19-2020, 04:22 PM   #6
Junior Member
 
Monaco Owners Club
Join Date: Mar 2015
Posts: 1
I did just that, I was on 30 amp shore power and wanted to run both air conditioners so I started the generator while still plugged into shore power. cooked the transfer switch on the AC side. The generator side still worked and powered everything.
The Popes is offline   Reply With Quote
Old 05-20-2020, 10:06 PM   #7
Junior Member
 
Join Date: Jan 2020
Posts: 17
Thanks to all for your input on troubleshooting the 50 amp service issue.
With a voltmeter, I was able to determine that the post was not providing the proper power, as it had an open ground. We repaired, and all was good again.
I've got a lot to learn, still, but with the help of the good folks on this forum, I'm learning....
Thanks, again !
Be safe. Be well.
__________________

__________________
2005 Monaco Windsor 40PDQ
05MoWi is offline   Reply With Quote
Reply

Tags
power, shore power



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Converter going bad when on 50 amp shore, but not 30 amp shore Loraura RV Systems & Appliances 10 10-07-2017 02:21 PM
Plugging into shore power trips shore power breaker BFF Travel Supreme Owner's Forum 8 07-28-2017 10:53 PM
Troubleshooting... no shore power bobk3d Class A Motorhome Discussions 12 04-02-2017 10:24 PM
Shore Power help please check4pulse iRV2.com General Discussion 5 05-27-2013 09:07 PM
30-amp dog-bone with 50-amp shore power jeeprubi RV Systems & Appliances 11 02-14-2008 03:10 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 03:16 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2020, vBulletin Solutions, Inc.
×