I am trying to figure out why I can not get roof A/C to work on 50amp post power but both A/c units work on generator power. Never had a problem before and both A/C's worked fine till this point. I checked breakers in bedroom and fuses and found nothing. 2007 Monaco coach. Anyone had a similar situation? I can run the microwave and other 110 and 12v outlets. Thanks Steve
__________________
2007 Monaco Knight-source engineering front & rear sway bars, Bilstiens, X- braces, Safe-T-plus, Watts link (front)
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
05-15-2022, 11:17 AM
|
#2
|
Senior Member
Join Date: Oct 2014
Posts: 7,882
|
Steve,
From the ATS (automatic transfer switch) onward through wiring and main 120 VAC breaker box shore power and generator are EXACTLY the same.
So the issue is either with the shore power itself, any protection device you have on on the "shore power IN" side of the ATS.
I would start by verifying with a voltmeter that the shore power outlet is good. If you need the "how to check" let us know.
Next and also easy is, with all power off to check connections in your ATS.
__________________
Brett Wolfe
Ex: 2003 Alpine 38FDDS. Ex: 1997 Safari Sahara. Ex: 1993 Foretravel U240
|
|
|
05-15-2022, 11:18 AM
|
#3
|
Senior Member
Join Date: Apr 2011
Location: Powell River, B.C.
Posts: 31,500
|
OK have you confirmed 120 volts at each hot leg at the post ?
Your microwave maybe operating off your inverter and the post power is dead or circuit breaker tripped there .
Have you asked your neighbors about power supply ?
EDIT: I see Brett , posted while I was typing , sorry about the duplication , but your description points to shore power not getting into coach systems .
__________________
99DSDP 3884, Freightliner, XC, CAT 3126B, 300 HP /ALLISON 3060
2000 Caravan toad, Remco & Blue Ox.
|
|
|
05-15-2022, 11:23 AM
|
#4
|
Senior Member
Monaco Owners Club
Join Date: Jun 2014
Posts: 14,608
|
X3 on checking transfer switch.
__________________
Jim J
2002 Monaco Windsor 38 PKD Cummins ISC 350 8.3L
2005 Jeep Grand Cherokee w/5.7 Hemi
|
|
|
05-15-2022, 05:29 PM
|
#5
|
Member
Monaco Owners Club
Join Date: Feb 2020
Posts: 43
|
so, I failed to mention I have used this post at my home for 2+years-never a problem-I have always used a Hughes 50amp surge protector. While electronics is like eating for others, I would starve to death. If you would help me, tell me what I need to check to go forward. I did purchase a new transfer switch almost a year ago but have not installed-I did check to make sure the exsiting transfer switch lugs were tight and no signs of heat or burning. Thanks
__________________
2007 Monaco Knight-source engineering front & rear sway bars, Bilstiens, X- braces, Safe-T-plus, Watts link (front)
|
|
|
05-15-2022, 05:58 PM
|
#6
|
Moderator Emeritus
Ford Super Duty Owner
Join Date: Aug 2000
Location: Bryan, TX when not traveling.
Posts: 22,948
|
Check the transfer switch, but first you have to find it. Tap it with a plastic handle and see if it will release.
Ken
__________________
Amateur Radio Operator (KE5DFR)|No Longer Full-Time! - 2023 Cougar 22MLS toted by 2022 F150, 3.5L EcoBoost Tow Max FX4 Lariat Travel with one Standard Schnauzer and one small Timneh African Gray Parrot, retired mechanical engineer
|
|
|
05-15-2022, 06:15 PM
|
#7
|
Senior Member
Join Date: Jul 2014
Posts: 35,446
|
Can you do a test without the surge guard device.
Do you have a cord reel ? It may be bad.
|
|
|
05-16-2022, 11:05 AM
|
#8
|
Senior Member
Join Date: Apr 2011
Location: Powell River, B.C.
Posts: 31,500
|
You checked the connections in the transfer switch for tightness , so you know exactly where they are .
Do you have a multi meter to check for 120/240 volt in and out of the switch or a non contact 120 volt power tester .
Can you post a picture of your transfer switch ( cover off ) and we'll be able to tell you exactly where to check with the meter to confirm power flow through it .
__________________
99DSDP 3884, Freightliner, XC, CAT 3126B, 300 HP /ALLISON 3060
2000 Caravan toad, Remco & Blue Ox.
|
|
|
05-16-2022, 11:23 AM
|
#9
|
Senior Member
Join Date: Oct 2014
Posts: 7,882
|
Suggest you spend 30 seconds checking your shore power outlet with your voltmeter. Would hate to see you tear into your coach only to find out it is a shore power issue:
Two outer straights are the HOTS (L1 and L2)
The center straight is the NEUTRAL
The center round is the GROUND
So:
From either outer straight to either center= 120 VAC
Center straight to center round= 0 VAC
Outer straight to outer straight= 240 VAC
If those check out, do the same test at the "shore power IN" side of the ATS and then at the OUT side of the ATS
Generally colors are as follows, though they could be different:
Black is HOT
Red is the other HOT
White is NEUTRAL
Green is GROUND
So either black or red to green or white= 120 VAC
Green to white= 0 VAC
Black to red= 240 VAC
__________________
Brett Wolfe
Ex: 2003 Alpine 38FDDS. Ex: 1997 Safari Sahara. Ex: 1993 Foretravel U240
|
|
|
05-16-2022, 11:30 AM
|
#10
|
Senior Member
Join Date: Apr 2011
Location: Powell River, B.C.
Posts: 31,500
|
Here's a diagram to go with Brett's description.
__________________
99DSDP 3884, Freightliner, XC, CAT 3126B, 300 HP /ALLISON 3060
2000 Caravan toad, Remco & Blue Ox.
|
|
|
05-17-2022, 06:11 PM
|
#11
|
Member
Monaco Owners Club
Join Date: Feb 2020
Posts: 43
|
Brett- I checked power at the post as you mentioned and all is fine 120 and 240. plugged in the surge protector(hughes 50amp) and checked across the ATS red and black 240v and 120 on l1 and l2. Unplugged the surge protector and hooked coach direct to the pole-no change. Went to the breaker panel in the rear bathroom, shut off all breakers and reset-no change. Switched mode on controller to fan only high manuel-no go. All works fine on generator power. What next?
__________________
2007 Monaco Knight-source engineering front & rear sway bars, Bilstiens, X- braces, Safe-T-plus, Watts link (front)
|
|
|
05-18-2022, 06:15 AM
|
#12
|
Senior Member
Join Date: Jun 2011
Location: FL
Posts: 11,452
|
Do you have a panel (EMS), that shows for example 50 amp or 30 amps when adapted down for a 30 amp service?
It is possible your EMS load shedding device is confused. Of course I do not know your setup so providing that information will help.
IF you have this there is a circuit board behind the AC breaker panel. Lots of things in there to hurt you so no jewelry and one hand in your lap while taking measurements.
The circuit board passes power through relays and when on 30 amp service they will unload devices to help prevent overloading the 30 amp service.
If the device is confused for some reason it might be unloading devices and your AC's could be at the top of the list to unload.
Here is a bunch of files with pictures that might help you sort it out. Look at the pictures of the AC breaker panel and let us know if you have something like it.
https://1drv.ms/u/s!Aqrv2TUdbV6xjl_O...H0evI?e=ijJU07
__________________
Certified Senior Electronic Technician, Telecommunications Engineer, Telecommunications repair Service Center Owner, Original owner HR 2008
.
|
|
|
05-18-2022, 06:39 AM
|
#13
|
Senior Member
Join Date: Jul 2008
Location: Pennsylvania
Posts: 2,799
|
Do yourself a favor
1. Unplug
2. Turn off your Chassis, and house switches and inverter
3. Wait 30 minutes.
4. Turn on all your switches
5. Plug in
See it fixes everything
Believe me, this simple move can do wonders
__________________
2020 Winnebago Horizon 42Q (XCL chassis)
2022 Jeep Wrangler Sahara Unlimited
99 Storm 30H, 04 Southwind 32 VS, 07 Ellipse 40FD
|
|
|
05-18-2022, 06:55 AM
|
#14
|
Senior Member
Monaco Owners Club
Join Date: Jun 2011
Location: CA
Posts: 4,486
|
My 06 came with an Intelliec EMS. The main board is within the circuit breaker panel. It has 'intellitec' printed on the cover.
Not sure what an 07 Knight came with. Post a picture of your circuit breaker cover. There is a 'reboot' procedure, if they are similar.
__________________
Bill & Brigitte
06 Windsor PEQ, Cummins 400 ISL
2014 Honda CRV or 2012 Jeep
|
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|