RV News RVBusiness 2021 Top 10 RVs of the Year, plus 56 additional debuts and must-see units → ×
RV Trip Planning Discussions

Go Back   iRV2 Forums > THE OWNER'S CORNER FORUMS > Monaco Owner's Forum
Click Here to Login
Join iRV2 Today

Mission Statement: Supporting thoughtful exchange of knowledge, values and experience among RV enthusiasts.
Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on iRV2
 
Thread Tools Search this Thread Display Modes
 
Old 02-14-2019, 04:51 PM   #1
Senior Member
 
Join Date: Nov 2018
Location: Tampa, Florida
Posts: 107
Power Fluctuations

How much should the power fluctuate on my readout?

Typically it's between 117 and 122.

I had the microwave going while the dryer was on. I turned on the air fryer and glanced at the readout and it said 105. I instantly shut off the dryer.

Should it go that low? I seem to remember something about 110-125.

Any thoughts?

I can't imagine this thing couldn't handle those three items. What if I'd had the AC on?

With only the air fryer going I'm showing 112.

Thanks.Click image for larger version

Name:	1550184648276.jpeg
Views:	25
Size:	75.6 KB
ID:	235033
__________________
03 Monaco Windsor, just in front of:
a Dodge Durango, or on occasion, a Toyota Prius
SegwayGuy is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 02-14-2019, 04:59 PM   #2
Senior Member
 
Join Date: Jul 2018
Posts: 3,173
Was that the voltage on BOTH legs of the 50 amp service? I ask because if the voltage on the "other" leg rises proportionately to the voltage drop on the lower-voltage leg, it indicates a compromised neutral connection (which could be anywhere, not just on your side of the pedestal).


FWIW, you were probably drawing 30-35 amperes on that leg. To see the voltage drop relative to the load you experienced, I'd also guess that the wiring to the pedestal is under-size or has corroded terminations, or that the service in the park/CG is heavily loaded.
__________________
2005 Four Winds Majestic 23A
ďTo the world you may be one person; but to one person you may be the world.Ē - Dr Suess
Solo_RV_Guy is offline   Reply With Quote
Old 02-14-2019, 05:18 PM   #3
Senior Member
 
96 Wideglide's Avatar
 
Holiday Rambler Owners Club
Join Date: Aug 2010
Posts: 7,156
I'm guessing all three of those appliances are fed from the same leg of your 50A shore power.
__________________
Ben & Sharon
2008 43' Holiday Rambler Scepter PDQ
96 Wideglide is offline   Reply With Quote
Old 02-14-2019, 07:48 PM   #4
Senior Member
 
RamiDav's Avatar
 
Join Date: Jan 2016
Posts: 1,565
Many RV parks don't have enough capacity to maintain voltage when there is
very much demand .
I doubt you have a problem , the problem is most likely the park power .

I have a Progressive Industries HW50C EMS . I think everyone should have one .
It samples the power before passing it to the RV . The little read out window tells
me the volts and amps on each leg . It will also kill the power if it drops to 104 or
rises to 132 . It protects in many other ways too such as frequency off , spikes and
open neutral .

https://www.rvupgradestore.com/Progr...p/emshw50c.htm

Ray 03 Windsor
RamiDav is offline   Reply With Quote
Old 02-14-2019, 08:07 PM   #5
Senior Member
 
Join Date: Nov 2018
Location: Tampa, Florida
Posts: 107
I found out the park power is old and sub par.

I have a built in surge protector which is supposed to test the power coming in.

I'd like to learn more about this area. I hated to see that meter go down to 105. That can't be great for the appliances.
__________________
03 Monaco Windsor, just in front of:
a Dodge Durango, or on occasion, a Toyota Prius
SegwayGuy is offline   Reply With Quote
Old 02-14-2019, 08:08 PM   #6
Senior Member
 
Jim_HiTek's Avatar
 
Join Date: Nov 2011
Location: Full time RV'er
Posts: 3,386
Rule of thumb is appliances are usually rated between +/- 10% of 120 Volt AC. (There hasn't been a US power supplier of 110 volt since the '20's so I often wonder why manufacturers still use it occasionally to rate their devices. Probably to skirt some difficult regulation of some kind).

Anyway, try to keep your incoming line voltage at between 108 to 132.

Now, if you see your line voltage drop when you turn on some appliance, that can mean several things. Starting at your rig, you could have a poor connection in the input box in the power bay. Your power cord could have a connection going bad (I've had this happen in the head of a 30 amp cord), the socket you plug into (shore power) might have a contact sprung making poor contact. The circuit breaker in the parks power tower might be bad or the wire clamp loosened up.

All of these things can be checked by feeling for heat nearby. Electrical connections should not be hot. Neither should circuit breakers or power cords. Warm maybe, but not significantly hotter then nearby areas. There's other stuff to know, but I'm tired.

If it was me, I'd start looking for a bad connection. Your cords power head is a prime suspect. Meanwhile, minimize your power consumption and check tomorrow.
__________________
'02 Winnebago Journey DL, DSDP, 36' of fun.

Visit my RV Travel & Repair Blog at : https://chaos.goblinbox.com
Jim_HiTek is offline   Reply With Quote
Old 02-14-2019, 08:21 PM   #7
Senior Member
 
Join Date: Nov 2018
Location: Tampa, Florida
Posts: 107
Quote:
Originally Posted by Jim_HiTek View Post
Rule of thumb is appliances are usually rated between +/- 10% of 120 Volt AC. (There hasn't been a US power supplier of 110 volt since the '20's so I often wonder why manufacturers still use it occasionally to rate their devices. Probably to skirt some difficult regulation of some kind).

Anyway, try to keep your incoming line voltage at between 108 to 132.

Now, if you see your line voltage drop when you turn on some appliance, that can mean several things. Starting at your rig, you could have a poor connection in the input box in the power bay. Your power cord could have a connection going bad (I've had this happen in the head of a 30 amp cord), the socket you plug into (shore power) might have a contact sprung making poor contact. The circuit breaker in the parks power tower might be bad or the wire clamp loosened up.

All of these things can be checked by feeling for heat nearby. Electrical connections should not be hot. Neither should circuit breakers or power cords. Warm maybe, but not significantly hotter then nearby areas. There's other stuff to know, but I'm tired.

If it was me, I'd start looking for a bad connection. Your cords power head is a prime suspect. Meanwhile, minimize your power consumption and check tomorrow.
I couldn't wait till tomorrow. I checked the post, box, breaker, cord head and surge protector. Nothing is even warm. There is slightly more heat in the surge protector but not even luke warm. The other connections are as cool as the night air. It's about 63 right now.

The mystery continues...
__________________
03 Monaco Windsor, just in front of:
a Dodge Durango, or on occasion, a Toyota Prius
SegwayGuy is offline   Reply With Quote
Old 02-15-2019, 07:35 AM   #8
Senior Member
 
K7JV's Avatar
 
Join Date: Jul 2006
Posts: 1,546
Higher than rated voltages can be a problem for electronics, like TV's, microwave controls, etc. Lower than rated voltages can be a problem for motors, like AC units, etc..

In my home state there are government rules that I believe require the electric utility to provide 120 VAC, plus or minus 5%. So that means 114 volts to 126 volts. But what happens beyond their point of service is purely a function of the quality and condition of the installed conductors and devices.

The posts above are pretty much right on. Many older RV parks were built to serve much smaller and much more basic RV's than what is commonplace, today. As a result, their service conductors may not be even close to doing the job with today's "all the comforts of home" coaches.

This summer, in an older park in the northeast corner of Nevada, I actually saw 102 volts on one leg on our coach. The entire reason for that low voltage was the overloading of the parks system by a large number of RV's, and it was in the upper 90's for temperature. It ultimately cost me a control board for our front heat pump unit. Low voltage to AC motors results in higher currents, and I'm suspecting that the contacts on the relay for the fan motor couldn't handle the high current that it was experiencing and the result was a fan that wouldn't turn off. New board, all is good. Thankfully it was the board that failed, and not the fan motor.
__________________
Jim & Angie, Boise, ID
2006 Monaco Dynasty Countess III
2017 GMC Acadia Denali
K7JV is offline   Reply With Quote
Old 02-15-2019, 07:49 AM   #9
Senior Member
 
RonLC's Avatar


 
Join Date: Jul 2015
Location: Punta Gorda, FL
Posts: 1,056
Perhaps the OP might consider adding a Hughes Autoformer or similar voltage regulator.
__________________
Ron & Peggy (aka GM of Universe)
2019 Renegade Verona LE 40 LTS (Freightliner M2-106 chassis)
2017 Buick Enclave/AF1
2004 Blue Bird M380 (sold)
RonLC is offline   Reply With Quote
Old 02-15-2019, 08:32 AM   #10
Registered User
 
Monaco Owners Club
Join Date: Mar 2018
Location: Blairsville, GA & WPB, FL
Posts: 3,993
Send a message via ICQ to Ivylog
My EMS shuts my rig down/disconnects at 107-108V. The further you are from the transformer feeding the CG the lower the voltage, especially when everyone else is using a lot of power. Moving closer to the transformer will help.
Ivylog is offline   Reply With Quote
Old 02-15-2019, 08:51 AM   #11
Senior Member
 
Join Date: Nov 2018
Location: Tampa, Florida
Posts: 107
Quote:
Originally Posted by RonLC View Post
Perhaps the OP might consider adding a Hughes Autoformer or similar voltage regulator.
I would consider this. What are the details of this device, how does it work? What are the benefits?
__________________
03 Monaco Windsor, just in front of:
a Dodge Durango, or on occasion, a Toyota Prius
SegwayGuy is offline   Reply With Quote
Old 02-15-2019, 12:54 PM   #12
Senior Member
 
RonLC's Avatar


 
Join Date: Jul 2015
Location: Punta Gorda, FL
Posts: 1,056
Quote:
Originally Posted by SegwayGuy View Post
I would consider this. What are the details of this device, how does it work? What are the benefits?
Probably more than you want to know:

https://hughesautoformers.com/

https://en.wikipedia.org/wiki/Autotransformer

The reason I have one is that some parks have low voltage especially in times of heavy use in hot weather where everyone is running their A/C.

Mine is hard wired inside the bay (out of sight) where the power cord reel is located. They will work outside by the power post too but if one "walked off" it would be expensive.
__________________
Ron & Peggy (aka GM of Universe)
2019 Renegade Verona LE 40 LTS (Freightliner M2-106 chassis)
2017 Buick Enclave/AF1
2004 Blue Bird M380 (sold)
RonLC is offline   Reply With Quote
Old 02-15-2019, 05:12 PM   #13
Senior Member
 
96 Wideglide's Avatar
 
Holiday Rambler Owners Club
Join Date: Aug 2010
Posts: 7,156
I carry a Hughes Autoformer for sites that have questionable power. One such park I am heading to in a few weeks, in AZ. I have found the voltage on one of the two legs get's very low when I put any kind of load on it. I chalk it up to all the pedestals being daisy chained together, and if I have half a dozen 30A travel trailers on either side of me, the power load is high, on one leg.
Had one electrician tell me my theory is possible !
__________________
Ben & Sharon
2008 43' Holiday Rambler Scepter PDQ
96 Wideglide is offline   Reply With Quote
Reply

Tags
power



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Voltage fluctuations on house batteries Affinityfan RV Systems & Appliances 8 03-02-2015 08:35 PM
Oasis again...big temperature fluctuations danleininger Newmar Owner's Forum 9 08-30-2014 07:57 AM
Onan 10KW Diesel Has Frequency Fluctuations notlost Class A Motorhome Discussions 7 05-05-2014 12:09 AM
Voltage fluctuations on dash voltmeter bosshawg MH-General Discussions & Problems 7 03-14-2013 07:35 PM
Engine temperature fluctuations Higgins Cummins Engines 6 05-10-2008 05:59 AM


All times are GMT -6. The time now is 01:46 AM.