Old 07-31-2021, 10:14 AM   #1
Senior Member
 
Chef Guy's Avatar
 
Join Date: May 2008
Posts: 242
Temperature and pressure relief valve

I had to replace a very leaky temperature and pressure relief valve from my Atwood Water heater model GC10A-E. The dealer I bought it from sold me the identical one except for the length of the temperature probe. The OEM was longer by a couple of inches than the replacement. Everything else was identical (pressure rating and temperature rating). Does anyone know if the length of this little white probe will be a safety issue or any other issue? The heater does not leak anymore from this valve and it seems to be working okay, but I am a little bit gun shy and only turn the heater on for 30 minutes at a time. The electric stopped working years ago but the propane gas always worked great. Thanks👍
Chef Guy is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-31-2021, 11:30 AM   #2
Senior Member
 
Join Date: Aug 2019
Location: Eastern outskirts of Dallas, TX
Posts: 520
No issue as long as the end of the probe isn’t bound against the tank in some way. Easy to test -

1. remove the new P&T
2. Take a piece of wire and measure the length of the new P&T from the end of the probe to the top of the threads (what would be seen when the T&P is installed) on the body of the T&P
3. Using the wire with your thumb at the measured point at the threads, insert the wire into the port on the water heater at the same angle as the valve is screwed in, up to the point that your thumb hits the boss that the valve screws into.
4. If the wire doesn’t bottom out, your good to go.

How much longer is the probe anyway?
MrMark52 is offline   Reply With Quote
Old 07-31-2021, 11:46 AM   #3
Senior Member
 
Chef Guy's Avatar
 
Join Date: May 2008
Posts: 242
Mr. Mark

The newer probe is shorter, not longer.
Chef Guy is offline   Reply With Quote
Old 07-31-2021, 12:12 PM   #4
Senior Member
 
Join Date: Nov 2015
Posts: 18,370
Not all 3/4" NPT T&P Relief Valves are the same

Temp probe for Atwood use a 4" temp probe

Shorter probe should not be used as it may not reach into the water
Must be in the water to properly sense temperatures

Water Heater Tank has by design an Air Pocket on top of water to help control pressure increases
The Pressure sensing is via the Air Pocket
The Temperature Sensing is via the probe being in the water

4" probe is shortest that should be used

Atwood 90028
Or match up one from Local Hardware
3/4" NPT with 4" probe
Temp/Press are universal-----210*F/150psi
__________________
Is it time for YOUR Medication or Mine?
Dodge 3500 w/Tractor Motor & NUWA 5vr
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Old 07-31-2021, 01:18 PM   #5
Senior Member
 
Chef Guy's Avatar
 
Join Date: May 2008
Posts: 242
Quote:
Originally Posted by Old-Biscuit View Post
Not all 3/4" NPT T&P Relief Valves are the same

Temp probe for Atwood use a 4" temp probe

Shorter probe should not be used as it may not reach into the water
Must be in the water to properly sense temperatures

Water Heater Tank has by design an Air Pocket on top of water to help control pressure increases
The Pressure sensing is via the Air Pocket
The Temperature Sensing is via the probe being in the water

4" probe is shortest that should be used

Atwood 90028
Or match up one from Local Hardware
3/4" NPT with 4" probe
Temp/Press are universal-----210*F/150psi
Old biscuit,

Mine uses the 1/2” NPT. Will that make a difference? The parts guy told me that it should be okay, but he also told me about some oceanfront property in Nevada he was interested in selling too! I have an email into Dometic, who own Atwood now, so hopefully they will reply soon. 🙏
Chef Guy is offline   Reply With Quote
Old 07-31-2021, 02:12 PM   #6
Senior Member
 
Join Date: Nov 2015
Posts: 18,370
Atwood 1/2" T&P uses a 4" probe also
*Same as 3/4" just smaller threads/body

2006 was last year Atwood used the 1/2" T&P
__________________
Is it time for YOUR Medication or Mine?
Dodge 3500 w/Tractor Motor & NUWA 5vr
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Old 08-01-2021, 06:47 AM   #7
Senior Member
 
Join Date: Jul 2000
Posts: 3,247
Chef Guy. Tell us how you survived the big fire.
__________________
Moisheh
2008 Dynasty 42' Diamond IV
1988 Bluebird PT38
2009 Silverado Toad
moisheh is offline   Reply With Quote
Old 08-01-2021, 09:42 AM   #8
Senior Member
 
Chef Guy's Avatar
 
Join Date: May 2008
Posts: 242
Quote:
Originally Posted by moisheh View Post
Chef Guy. Tell us how you survived the big fire.
Moisheh,

I am presently in Cochrane, AB (Wild Rose Country) chauffeuring my wife back and forth to Calgary while she judges a 4 day dog show, but as far as the fires are concerned they are still burning up the province of BC. There has been all day smoke here since arriving, from the BC fires, and there appears no let up in site.

We were never that close to the town of Lytton that had burned to the ground, although it was just a 3 hour drive north from our house.

As far as the new pressure temperature probe, it seems to be working so far, or rather the thermostat is working and keeping the temp steady at 140 degrees with no leaks.

I am going to try and call Dometic again once we get back home just to verify that the shorter probe either will work or not work. I expect that I will have to order the longer probe part as called for in the specs.

But it was probably one of the easier re and re’s I have done on this coach. Wish all repairs were this easy🤗
Chef Guy is offline   Reply With Quote
Old 08-01-2021, 08:43 PM   #9
Senior Member
 
Join Date: Nov 2015
Posts: 18,370
2006 vintage
Uses Common DC to operate Electric & Propane
Yellow wire from Circuit Board goes to DC Relay that when using Electric closes to allow AC to Element
*Bad DC Relay
*Bad AC wires to/from relay
*Bad Element

Unfortunately both the DC Relay and Element are located under the cover on backside of WH Tank
*access can be difficult

T-stat Opens at 140*F/Closes at 110*F for reheat
ECO (hi temp t-stat) Opens at 180*F/triggers FAULT Light which locks out heater functions. ECO self resets at 150*F but OWNER has to reset Lockout by turning switch off/back on (electric or gas)

Thermal Fuse (in clear tubing on brown wire) blows at 190*F due to flame blow back (dirty/obstructed burner assembly)
One time fuse...shuts down all heating functions
__________________
Is it time for YOUR Medication or Mine?
Dodge 3500 w/Tractor Motor & NUWA 5vr
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Old 08-13-2021, 07:15 AM   #10
Senior Member
 
Chef Guy's Avatar
 
Join Date: May 2008
Posts: 242
Update on correct information from water heater manufacturer

Quote:
Originally Posted by Old-Biscuit View Post
Not all 3/4" NPT T&P Relief Valves are the same

Temp probe for Atwood use a 4" temp probe

Shorter probe should not be used as it may not reach into the water
Must be in the water to properly sense temperatures

Water Heater Tank has by design an Air Pocket on top of water to help control pressure increases
The Pressure sensing is via the Air Pocket
The Temperature Sensing is via the probe being in the water

4" probe is shortest that should be used

Atwood 90028
Or match up one from Local Hardware
3/4" NPT with 4" probe
Temp/Press are universal-----210*F/150psi
Old Biscuit,

I finally heard back from Dometic technical department after first touching base with them a couple of weeks ago and they assured me that the shorter probe on the Watts temperature pressure relief valve will not be an issue as long as the temperature and pressure ratings are the same, which they are.

So, anyone replacing the longer OEM probe with the shorter Watts temp/pressure probe should not be concerned. Just match the pressure and temperature ratings and you should be fine.

My OEM probe measured a good 4" while the newer one is half that length.

End of thread!
__________________
2006 HR Endeavor PDQ
formerly 2008 Suzuki Grand Vitara 4WD
now 2007 Honda CR-V
Chef Guy is offline   Reply With Quote
Old 08-13-2021, 11:36 AM   #11
Senior Member
 
Join Date: Aug 2019
Location: Eastern outskirts of Dallas, TX
Posts: 520
Quote:
Originally Posted by Chef Guy View Post
Old Biscuit,

I finally heard back from Dometic technical department after first touching base with them a couple of weeks ago and they assured me that the shorter probe on the Watts temperature pressure relief valve will not be an issue as long as the temperature and pressure ratings are the same, which they are.

So, anyone replacing the longer OEM probe with the shorter Watts temp/pressure probe should not be concerned. Just match the pressure and temperature ratings and you should be fine.

My OEM probe measured a good 4" while the newer one is half that length.

End of thread!
That is correct ChefGuy! But good you “heard it from the horses mouth”!

Thanks for posting back your findings!
MrMark52 is offline   Reply With Quote
Old 08-13-2021, 11:44 AM   #12
Senior Member
 
Join Date: Nov 2015
Posts: 18,370
Temp sensing is via the Probe
Probe MUST be submerged in the water in order to sense water temp

Press sensing is via the internal of T&P Valve
Press is sensed in the Air Pocket area

210*F/150 psi ratings are standard for water heaters

A 2" probe MAY work....provided water level is maintained at/near the T&P Port level
Water level fluctuates depending on pressure in the tank
That is why a 4" probe is used.......

But Dometic tech gave the big OK..........
Hummmmm wonder why OEM is 4" probe when 2" is OK
__________________
Is it time for YOUR Medication or Mine?
Dodge 3500 w/Tractor Motor & NUWA 5vr
US NAVY---USS Decatur DDG-31
Old-Biscuit is offline   Reply With Quote
Old 08-13-2021, 12:00 PM   #13
Senior Member
 
Chef Guy's Avatar
 
Join Date: May 2008
Posts: 242
Quote:
Originally Posted by Old-Biscuit View Post
Temp sensing is via the Probe
Probe MUST be submerged in the water in order to sense water temp

Press sensing is via the internal of T&P Valve
Press is sensed in the Air Pocket area

A 2" probe MAY work....provided water level is maintained at/near the T&P Port level
Water level fluctuates depending on pressure in the tank
That is why a 4" probe is used.......

But Dometic tech gave the big OK..........
Hummmmm wonder why OEM is 4" probe when 2" is OK
Overkill by the OEM? Who knows....I do know that I am always able to get cold or hot water out of the water heater through the pressure temperature relief valve whether or not it is turned on or has not been used for several days, so I suspect that the air pocket is not low enough to prevent water from even the smaller probe from making contact. Escaping water has to be higher than any part of the probe's length as it has to escape at the top of the valve, not the bottom...and cold water doesn't expand like hot.

The Watt's valves are also available almost anywhere, unlike the OEM which is special order.
__________________
2006 HR Endeavor PDQ
formerly 2008 Suzuki Grand Vitara 4WD
now 2007 Honda CR-V
Chef Guy is offline   Reply With Quote
Old 08-13-2021, 12:28 PM   #14
Registered User
 
Monaco Owners Club
Join Date: Nov 2017
Posts: 1,493
Quote:
Originally Posted by Old-Biscuit View Post
Temp sensing is via the Probe
Probe MUST be submerged in the water in order to sense water temp

Press sensing is via the internal of T&P Valve
Press is sensed in the Air Pocket area

210*F/150 psi ratings are standard for water heaters

A 2" probe MAY work....provided water level is maintained at/near the T&P Port level
Water level fluctuates depending on pressure in the tank
That is why a 4" probe is used.......

But Dometic tech gave the big OK..........
Hummmmm wonder why OEM is 4" probe when 2" is OK
Biscuit for the win Think about it.

Mine was leaking a bit more than it should. I took it out and put it in my ultrasonic cleaner. That fixed it right up and restored proper functionality. It was 22 years old and I figure it's still got lots of life left in it
BobJones is offline   Reply With Quote
Reply

Tags
temperature, valve



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
2013 Sightseer 33C...where is the hot water tank drain plug and pressure relief valve threadbear Winnebago Industries Owner's Forum 4 10-11-2016 04:52 PM
Water heater pressure relief valve leaking? Benny367 Class A Motorhome Discussions 13 09-27-2011 06:29 PM
pressure relief valve question made2care Travel Trailer Discussion 3 05-20-2011 05:14 PM
Water Heater Pressure Relief Valve traveler of california Winnebago Industries Owner's Forum 7 11-30-2010 08:41 AM
Pressure Relief Valve?? Firewall-Vac Ball Downsizer Monaco Owner's Forum 4 09-29-2010 09:09 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 01:07 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2021, vBulletin Solutions, Inc.