Old 11-24-2018, 08:49 PM   #1
Member
 
dalemschultz's Avatar
 
Monaco Owners Club
Join Date: Apr 2017
Location: Soap Lake, Washington
Posts: 71
Traveling and the generator won’t stay running

Howdy!

We’re on out snowbird trip from Central Washington to Florida for the Winter. Things were peachy until Arizona. One morning the generator (Oman 10k) would not continue running after starting for 5 seconds. Multiple tries, same result. Feels like the software is sending a shutdown code. The code is a 1-3, or a 1-4. According to the Oman manual, a code 13 is called “Under Voltage”. “The corrective action is: Turn OFF the line circuit breaker on the operator’s console. If the genset now runs, run it with fewer connected loads.” I don’t see where that circuit breaker is on the console. I did switch off the breaker on the generator to see if that did the trick, but still no running more than 5 seconds. Anybody have this happen before. Please tell me there’s a simple fix! We’re in Texas and I’d love to be able to use the generator. Many thanks

Dale
dalemschultz is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 11-24-2018, 10:57 PM   #2
Senior Member
 
Join Date: Jul 2014
Posts: 28,607
Checked the oil level, coolant level and fan belt ?
twinboat is online now   Reply With Quote
Old 11-25-2018, 01:08 AM   #3
Senior Member
 
Monaco Owners Club
Join Date: Mar 2011
Posts: 820
They are referencing your main 120v breaker panel when they say Operator’s Console. The line circuit breaker is the input breaker. I assume it is a double breaker on yours, probably marked 50A.
By doing that you are removing the output load. If it continues to show the same error condition, the error is before the main breaker wiring in the generator itself, the transfer switch, and any power monitoring system like a Progressive EMS (if it is wired after the transfer switch).
It is always a good idea to tighten down the input and output legs in the transfer switch periodically as loose connections can create additional resistance, and heat, all the way up to a fire.
You need to remove all power sources (disconnect shore power and turn generator off) before opening the transfer switch for safety.
__________________
Paul Whittle
2005 Monaco Signature 45'
525 HP/1850 Ft Lb ISX-15/6-Speed Allison 4000
pwhittle is offline   Reply With Quote
Old 11-25-2018, 04:52 AM   #4
Senior Member
 
nodine's Avatar
 
Monaco Owners Club
Join Date: Jan 2003
Location: Knoxville, TN, USA
Posts: 3,842
Quote:
Originally Posted by twinboat View Post
Checked the oil level, coolant level and fan belt ?
Definitely do what twinboat suggests.

If you turn off the main breaker on the generator and it still does not remain running then the problem is internal to the generator.

Bob
__________________
Bob and Pam
2022 Quantum JM31
2020 Chevy Sonic
nodine is offline   Reply With Quote
Old 11-25-2018, 06:38 AM   #5
Senior Member
 
RamiDav's Avatar
 
Join Date: Jan 2016
Posts: 1,754
When my Onan 7.5 exhibited those same symptoms it was a broken
fan belt .
Replaced the belt and no more problem .

Ray
RamiDav is offline   Reply With Quote
Old 11-25-2018, 07:28 AM   #6
Senior Member
 
Winnebago Owners Club
Freightliner Owners Club
Join Date: May 2013
Location: Springfield, IL
Posts: 1,068
If you switch off the circuit breaker located on your generator it is now without any load. If you start it and it runs for a moment or two and shuts down the problem is with the generator itself. It can be something as simple as
(1) The circuit breaker itself is defective and not really shutting of the load requirement. This requires 2 people to test: With the generator circuit breaker in the off position place your volt meter leads on each of the wires exiting the CB and have 2nd person start generator. If voltage is recorded the CB could be bad so to rule this out place leads on incoming side of CB and have 2nd person start generator again. If you have power coming to CB then the CB is bad, if no voltage you'll need to look at the generator.
(2) Check oil level and coolant level as their is an automatic shutdown on the Onan when sensors are reading a low level with either. If the levels are full then it could be a faulty sending sensor but before you go there let's check one more thing - the fan belt. Not easy but grab hold of it with your hand and pull on it. If it comes off in your hand you have found the problem. If you can stretch it more than 1/4" you have a loose belt that is not maintaining adequate friction on all pulleys so you will need to tighten the tension by loosening and moving the main pulley outward to apply tension and tighten the bolts. Start generator again with CB in off position. If generator now runs without stopping now switch on the generator CB. If it still runs you should have power and you're ready to go.
(3) IF all the above doesn't correct the problem you'll need Onan to check it out. Depending on your route through TX there are several locations where you can get it checked out (especially along I-10).

Hope all goes well and your travels go smooth the rest of your journey - Richard
__________________
2011 Itasca Ellipse 42QD; 2012 Buick La Crosse; Retired US Army MSG (20 years AFS); Retired! Retired!
rrtribble is offline   Reply With Quote
Old 11-25-2018, 09:57 AM   #7
Senior Member
 
JohnBoyToo's Avatar
 
Monaco Owners Club
Join Date: May 2012
Location: DFW, Tex-US
Posts: 6,196
Obviously you have over a 1/4 tank of fuel ???
__________________
'11 Monaco Diplomat 43DFT RR10R pushed by a '14 Jeep Wrangler JKU. History.. 5'ers: 13 Redwood 38gk(junk!), 11 MVP Destiny, Open Range TT, Winn LeSharo, C's, popups, vans, tents...
JohnBoyToo is offline   Reply With Quote
Old 11-25-2018, 10:45 AM   #8
Senior Member
 
Join Date: Nov 2009
Posts: 208
Dale, I've had the same problem a couple of times. A couple of things to try, after making sure oil level is ok.

1) Hold the boost switch down when starting gen and continue holding it down while gen runs a bit. If you really have low battery voltage this should get you thru it until running gen charges batteries.

2). Problem could be fuel has lost prime. Hold gen start switch in off position for two minutes, you should hear fuel pump running, it might even change pitch when system is cleared of air.

3) Also you could start main drive motor and then try starting gen after a couple of minutes, if low battery voltage is the problem, main alternator on motor will have battery voltage higher in a minute or so.

Let us know, added info will help us all.
Larry
larry koenn is offline   Reply With Quote
Old 11-25-2018, 10:56 AM   #9
Senior Member
 
distaff's Avatar
 
Join Date: Dec 2009
Posts: 1,863
I just referred to the Onan service manual (models HDKCA, HDKCB, HDKCC, HDKCD, and HDKCG) and it describes level 1 and level 2 codes. Level 1 codes are a series of blinks followed by a pause - for example blink, blink, pause, blink, blink, pause etc..

There is no 1-4 or 1-3 listed, and if you are saying you have either a series of three or four blinks, and you couldn't tell, you need to go back and get it to show you again. Do this by pressing the prime/stop button for three to four seconds (until the light comes on), then press it three times in five seconds and the blinks will start again and run for 5 minutes.

If you get a code 3 you need to momentarily press the stop button to get the secondary code.

BTW changing a fan belt can be a real trial. I had my stator bearings replaced this year and the tech expressed amazement when I told him I had replaced the belt in a field a few years earlier. He told me they pull the unit and dismount the engine to change belts on my model.
__________________
Paul
2006 Patriot Thunder C13 Allison 4000
2010 Ford Flex Ecoboost AWD
distaff is offline   Reply With Quote
Old 12-03-2018, 05:16 PM   #10
Member
 
dalemschultz's Avatar
 
Monaco Owners Club
Join Date: Apr 2017
Location: Soap Lake, Washington
Posts: 71
Onan 10k generator

To clarify, I did see a series of 3 blinks and pressed stop once to see the second level of blinking codes, which was blink-pause-blink, blink, blink. I referred to that as a “1-3”, when on page 4-4 of my manual that’s a “CODE NO. 13”, Under Voltage. The coolant level seems fine and the oil level is on the lower end of nominal. The fan belt? I can’t even see it. There’s a Cummins shop not too far from here and since this one’s over my head and tools, think I’ll have to take her in. I think all of your ideas were very helpful and I very much appreciate all of you offering your experience and knowledge. I’ll send a note as to what Cummins finds regarding the generator.

Thank you so much,

Dale
__________________
Dale & Brooke & Phoenix
2009 Monaco Camelot 42KFQ
2013 Gecko Green Jeep Wrangler
dalemschultz is offline   Reply With Quote
Old 12-03-2018, 05:38 PM   #11
Senior Member
 
Windecker's Avatar
 
Join Date: Dec 2011
Location: Logan Indiana (Near Cincinnati Ohio)
Posts: 731
Have personally seen this and is easy to correct.
In our case, the shut down signal came at 5 seconds after startup and is doing so because line voltage is low on one or both legs.

I checked the brushes which is easy to do if you know what you are looking at, brushes worn out is all. Roughly $25.00 from Onan and 20 minutes work, done. They are on the oil access cover side of the genset (on the 10K and 12.5K), front lower side. Some gensets have access panels, maybe 6 inches by 4 inches or so to access them, others you have to access them from the oil access hatch. A broken brush wire will do the same thing.

Before sending it to Onan, I would check that as it is something you don't need special equipment to do and is easy.

Once the brush wears to about 1/2 inch or less, it is worn out. There are 2.
Windecker

Quote:
Originally Posted by dalemschultz View Post
To clarify, I did see a series of 3 blinks and pressed stop once to see the second level of blinking codes, which was blink-pause-blink, blink, blink. I referred to that as a “1-3”, when on page 4-4 of my manual that’s a “CODE NO. 13”, Under Voltage. The coolant level seems fine and the oil level is on the lower end of nominal. The fan belt? I can’t even see it. There’s a Cummins shop not too far from here and since this one’s over my head and tools, think I’ll have to take her in. I think all of your ideas were very helpful and I very much appreciate all of you offering your experience and knowledge. I’ll send a note as to what Cummins finds regarding the generator.

Thank you so much,

Dale
__________________
RV #5 1999 Monaco Signature Slide ISM 11 450
RV #6 2005 Monaco Executive 43PBQ Detroit Series 60
Honda Fit, Odyssey or Cargo trailer in tow.
Windecker is offline   Reply With Quote
Old 12-03-2018, 05:53 PM   #12
Senior Member
 
Windecker's Avatar
 
Join Date: Dec 2011
Location: Logan Indiana (Near Cincinnati Ohio)
Posts: 731
I googled around a little and came up with this clip on Onan Generator brushes. This is a different model and accessed differently but essentially the same inspection and replacement technique.

I did not look up the part number so if you do wind up needing brushes, have that number looked up. I just wanted to use this as information of what a new brush will look like:
https://apelectric.com/generator-par...kaAitJEALw_wcB

I am one of the lucky ones that got to replace a broken fan belt as well which will throw out a few different codes BUT in our case, the engine would run for a minute or two before shutting down.

When one of my two brushes wore out, it would shut down at 5 seconds every time regardless of temperature or whatever.
Hope this helps.
Windecker

Quote:
Originally Posted by dalemschultz View Post
To clarify, I did see a series of 3 blinks and pressed stop once to see the second level of blinking codes, which was blink-pause-blink, blink, blink. I referred to that as a “1-3”, when on page 4-4 of my manual that’s a “CODE NO. 13”, Under Voltage. The coolant level seems fine and the oil level is on the lower end of nominal. The fan belt? I can’t even see it. There’s a Cummins shop not too far from here and since this one’s over my head and tools, think I’ll have to take her in. I think all of your ideas were very helpful and I very much appreciate all of you offering your experience and knowledge. I’ll send a note as to what Cummins finds regarding the generator.

Thank you so much,

Dale
__________________
RV #5 1999 Monaco Signature Slide ISM 11 450
RV #6 2005 Monaco Executive 43PBQ Detroit Series 60
Honda Fit, Odyssey or Cargo trailer in tow.
Windecker is offline   Reply With Quote
Old 12-03-2018, 06:40 PM   #13
Member
 
dalemschultz's Avatar
 
Monaco Owners Club
Join Date: Apr 2017
Location: Soap Lake, Washington
Posts: 71
Thank you Windecker! Very useful. I’ll take a look tomorrow. The hours on the Genset are only 320. Is it possible for the brushes to be worn by then?

Thanks a million!

Dale
__________________
Dale & Brooke & Phoenix
2009 Monaco Camelot 42KFQ
2013 Gecko Green Jeep Wrangler
dalemschultz is offline   Reply With Quote
Old 12-03-2018, 07:40 PM   #14
Senior Member
 
Windecker's Avatar
 
Join Date: Dec 2011
Location: Logan Indiana (Near Cincinnati Ohio)
Posts: 731
Oh boy, should not be, they should go thousands of hours. Can easily be a broken brush wire or stuck brush though. Once you gain access to them you can lightly pull on the brush wires and see if one sort of just comes out un attached. They typically break close to where they attach to the brush itself.

If you do remove the brush block assembly, take a look at the slip rings. That is on the rotating part of the genset and is what the brushes are making contact with. The slip rings should be shinny where the brushes ride. If not that means they are arcing which is caused by a stuck or otherwise incorrectly working brush.

At such little hours though, almost has to be a broken brush wire or brushes are not your problem.

Good luck with it.
Windecker
Oh and the access panel is larger than I said earlier, more like 9 x 6 or so.
__________________
RV #5 1999 Monaco Signature Slide ISM 11 450
RV #6 2005 Monaco Executive 43PBQ Detroit Series 60
Honda Fit, Odyssey or Cargo trailer in tow.
Windecker is offline   Reply With Quote
Reply

Tags
generator, travel



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Generator won't stay running CdnCruiser RV Systems & Appliances 10 07-06-2014 11:39 AM
Generator won't stay running LarryWeaver Class A Motorhome Discussions 6 11-29-2011 12:22 PM
Generator won't stay running racer26 MH-General Discussions & Problems 13 09-13-2011 06:31 PM
Diesel Generator won't stay running Mike-N-Sally Winnebago Industries Owner's Forum 8 01-01-2010 12:08 AM
Onan Generator won't stay on while traveling Darrell & Mel RV Systems & Appliances 5 11-12-2007 05:05 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 05:35 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2021, vBulletin Solutions, Inc.