Old 06-17-2021, 05:23 PM   #1
Junior Member
 
Monaco Owners Club
Mid Atlantic Campers
Join Date: Mar 2021
Location: Everett, PA
Posts: 28
URGENT: Onan 12.5k Won't Stay Running / fuel pump issue

Hi All - need some help with an Onan 12.5kw Generator - trying to leave for a trip in 3 days but can't keep it running and kind of need it.

First: Rig is 2007 Beaver Marquis on Roadmaster S-Series
Second: Generator is a Kubota powered Onan 12.5 QD
Third: Code the Genset is spitting is 36
Fourth: Fuel is well past 1/2 tank. Added more anyways.
Fifth: Changed air, fuel filters and oil already

Here is the issue, if cold, it will start and run for an hour or so and dies. Won't start again - try priming - no go. Went in for a tune up to see if it was a filter problem. Started, ran for an hour or so and died.

Went back to the truck repair place and we hunted down the issue to fuel pump on the genset losing power after an hour or so. We gave the fuel pump 12v directly and the generator started right up.

Their best guess is a (1) bad fuel pump relay (heating up), but don't know where it is (not on the front/rear run boxes, assuming in the genset somewhere), (2) a bad control board (but can't figure out where it is either - help?) Assuming same as the relay? it is under the black panel on the top front side of the generator but not clear? Or (3) potentially a bad fuel pump that is drawing more current than it should.

I'm hoping that one of you wonderful folks on this forum knows these things better we do - we looked through the Onan Manual and the Beaver schematics and no real solution to a fuel pump relay or circuits (there is a diagram in the Onan book, but it doesn't tell me where the board would be or if there is a removable relay, etc).

Would love any advice on how to get closer to a solution here and what parts I might need to order or hunt down given that I have little time left before we get moving.

Thanks big time in advance. Will keep paying it forward on this forum.

Anand
__________________
2007 Beaver Marquis Lapis 45' CAT C15
2019 Jeep JLU Sport TOAD
2014 Thor Palazzo 33.3 (SOLD)
anand is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-17-2021, 05:50 PM   #2
Senior Member
 
Monaco Owners Club
Join Date: Jun 2010
Location: Willard .Missouri
Posts: 192
Had a issue with are generator on are coach the water temper sensor went bad causing that kind issue you are having
oh no is offline   Reply With Quote
Old 06-17-2021, 05:56 PM   #3
Senior Member
 
Mile Marker 42's Avatar
 
Join Date: May 2013
Location: S. California
Posts: 1,379
Could potentially be a faulty code and apparently the only way to clear codes is to remove power. I'd go under and disconnect power for 30 mins and wire brush cable ends and mounting studs. Then reconnect. Hold down start button for 60 seconds and restart. See what happens. Worked on my 7500 QD.
__________________
2003 Monaco Knight 36ft PST Triple Slide- 315 ISC
2007 Jeep Grand Cherokee 3.0 Diesel 4x4
2- 2013 Yamaha VXR's 70MPH+. 2019 Sun Tracker 18ft Pontoon w/ 75hp Mercury
Mile Marker 42 is offline   Reply With Quote
Old 06-17-2021, 05:58 PM   #4
Junior Member
 
Monaco Owners Club
Mid Atlantic Campers
Join Date: Mar 2021
Location: Everett, PA
Posts: 28
Quote:
Originally Posted by oh no View Post
Had a issue with are generator on are coach the water temper sensor went bad causing that kind issue you are having
Thanks, will look at that - I'd assume that would be a different code and wouldn't explain why the set would keep running when we put hot 12v on the pump - it should still stop, no? Or does a failed water-temp sensor get the control board to stop the fuel pump?
__________________
2007 Beaver Marquis Lapis 45' CAT C15
2019 Jeep JLU Sport TOAD
2014 Thor Palazzo 33.3 (SOLD)
anand is offline   Reply With Quote
Old 06-18-2021, 05:50 AM   #5
Senior Member
 
Monaco Owners Club
Join Date: Jun 2010
Location: Willard .Missouri
Posts: 192
Yes on the water sensor shutdown the motor .
oh no is offline   Reply With Quote
Old 06-18-2021, 07:51 AM   #6
Senior Member
 
markpj23's Avatar
 
Join Date: May 2010
Location: Florida
Posts: 319
Control Board

Had the same issue on our 2009 Beaver. Around 2006 I was told Onan made a change to their control board so that the 12v supplied to the fuel pump was fed from the control board instead of through a relay. It would work for a while then quit. Was a heat issue with the board as I recall.


I had a tech replace the fuel pump - no change. Finally went to a Cummins dealer who found the tech bulletin and installed the updated control board to fix the problem. Might be worth looking into this through Cummins tech support.


If short on time you can just use the workaround already done - wire 12v to the fuel pump directly when you need to run the genset. I would be sure to disconnect the 'normal' fuel pump wire when running the temp 12v connection.
__________________
Mark
'07 Essex (Sold)
'21 Jeep GC dinghy
markpj23 is offline   Reply With Quote
Old 06-18-2021, 08:29 AM   #7
Senior Member
 
Monaco Owners Club
Join Date: Jan 2017
Location: Utopia, TX
Posts: 500
Is there any chance you have gen start/stop enabled on your inverter? There could be a setting in the inverter that shuts the gen off after a certain state of charge is reached.
I had a devil of a time figuring this out on mine... dang near bought a new control board in desperation...
If the gen is shutting itself down due to some error condition, it should be logging a meaningful error message.
Edit: never mind. Just noticed the part where you said "run for an hour or so and dies. Won't start again - try priming - no go. ". If it was the inverter shutting it down, you would be able to restart it.
Cheers,
Walter
__________________
2003 Monaco Dynasty 42 Regal.
wamcneil is offline   Reply With Quote
Old 06-18-2021, 08:36 AM   #8
Senior Member
 
Monaco Owners Club
Join Date: Sep 2013
Posts: 2,503
The control board is a common $800 problem. It intermittently will stop supplying power to the fuel pump. Some folks simply wire a switch to 12 volts and the fuel pump turn it on when starting the generator. I have AGS Automatic Generator Start which I use frequently and couldn’t figure out a reliable way to run the fuel pump, so I bought the control board from Cummins. Problem solved.

Without AGS I would do the switched 12 volt workaround.
__________________
2014 Newell 2020P 45'8" ISX 600 HP
hypoxia is online now   Reply With Quote
Old 06-18-2021, 06:29 PM   #9
Junior Member
 
Monaco Owners Club
Mid Atlantic Campers
Join Date: Mar 2021
Location: Everett, PA
Posts: 28
Thanks / Solved!

Thank you for all of the responses - it may still be a overheating control board issue, but cleaned all of the pins on the connector to controller board and the 10 pin remote connector. Also replaced the fuel pump relay which was hot to the touch after 10 minutes of running. Not sure which of these worked but it ran like a champ after that.
__________________
2007 Beaver Marquis Lapis 45' CAT C15
2019 Jeep JLU Sport TOAD
2014 Thor Palazzo 33.3 (SOLD)
anand is offline   Reply With Quote
Reply

Tags
fuel, fuel pump, onan, pump



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Onan 5500 Generator won't stay running DLMCGOV RV Systems & Appliances 7 01-31-2023 07:35 AM
Urgent Question Needs Urgent Answer Volunteer Cummins Engines 23 02-12-2017 02:07 PM
Onan Generator won't stay running Car54 Class A Motorhome Discussions 38 07-12-2015 02:44 AM
5KW CCK Onan won't stay running Childeric Vintage RV's 18 06-17-2015 07:19 PM
Onan 10K Won't Stay Running Doc Mark Newmar Owner's Forum 4 09-30-2011 09:31 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 05:11 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.