50A power and amperage readings for a 2001, Excel RLE Limited

Sorry about a long post in advance.....I'm more verbal, visual and touch it kind of guy, really hate to write.

I stated in the "cheater box" discussion that I would be taking amperage readings of various systems and equipment on my unit. As not to be Off Topic, I posted some information there that might relate and will do the same here. These readings are from MY unit and suspect that they might relate to other Excel's as well and that is why I decided to share this information. Just never thought when I started it would take on a life of its own.


Several weeks ago, what started out to be a simple project of determining which input leg to use to install a POWER INLET on my unit, ended up with other questions I had no answers for. A question about the CHEATER BOX was asked on the Excel Owners Forum: "Anyone use electrical plug cheater box? The one that you plug in a 20 amp and 30 amp plug and it gives you 50 amp service". This question lead me to others and a week of projects ranging from exploring my breaker panel, installing the Inlet, taking amperage reading multiple times in different places and moving circuits___ you get the ideal.

I find the term 50A is as general a term as I used to use when saying 30A.
Being new to the 50 amp service requirements of my Excel, the terms 50A available, 50A service, 50A 120/240v service, 30A to 50A adapters, AUTOFORMER, SURGE PROTECTIONand CHEATER BOX I, like most, initially found this confusing. What is SHORE POWER? I don't have a boat.

After a lot of reading, the 50A 120/240v service isn't that much different than my stick built. It has two power input legs, a neutral and a ground. Each leg provides power to various breakers that feed different circuits that make up the outlets, refrigerator, air conditioner, etc.

But there are differences. In general, a stick built is designed to have a consistent power input and a relatively balanced load. My unit with the panel that is installed and would guess, speaking in general terms, other units providing 50A 120-240v service that the panels aren't designed to be balanced in the same manner. As RV'ers we face the challenges of having to deal with a variable power input, 30A or 50A 120/240v with a consistent to variable load (and don't forget the 50A from the cheater box). When I stated.... the panels aren't designed to be balanced in the same manner....what I discovered on my panel was that the black input leg provided power to breakers # 1,2, 5,6 and 7. The red leg serviced breakers 3 and 4.

After checking the breakers to determine which circuits they provided power to, I discovered that the black leg provided power to all the circuits that I normally use. The red, serviced the washer-dryer and a single rear outlet that included a ceiling fan. As we wouldn't be installing a W/D in our unit, this means that the entire load was on the black. IMO it's helpful to know what's on each leg and what each circuit or item has as a load demand when determining how we deal with or without the 50A 120-240v service our units require. Enter the cheater box discussion again. Without knowing my units demands, I would have been providing 30A to a 50A or greater demand and 20A to a circuit that had none. I'm sure this would have given me a sense of extra power, if I had chose to use it at the time. Regardless without the 50A 120-240V service available and by whatever means I hook up to the pedestal, load management is still required and that was a different project.
__________________________________________________ _______________________________________________

Amperage readings. What did it all mean?

I tried to run the equipment that would give me a base line for amperage use. With the A/C, WH, Refrig, entertainment area operating and items we might use on a "normal" trip. This included 4.5amps from the converter to run 60% of the lights and the Charge wizard in normal mode. Had an amperage reading of 30.5 amps on my black input leg, 0 amps on the red and 30.5 amps on the neutral. With the microwave on, readings increased to 41.5amps. Add the coffee maker, another 10 amps, or the hair dryer, another 8 amps. One thing about determining a load, there is a constant, intermittent and occasional demand. Guess it could be possible to reach the 50 amp on a single leg input for a short period. When the DW makes me use the onboard vacuum system, there's more in overload than the additional 8 amps.

What I did to "balance the load" was to move the WD and Rear outlet to the black leg and installed the Water heater and Microwave to the red leg. By doing this I have 18.9amps on the black and 22.6 amps on the red with the above equipment running. The white, neutral, read 7.6 amps compared to the 41.5 amps as before.

As demands change, so would the amperage on each leg. By making the changes I did, it gives me a little cushion on the black leg when the hair dryer comes on and the coffee pot is doing its thing. As mentioned, it's impossible to balance a system that has 5 circuits on one leg and 2 on the other. With my figures, with a W/D installed, it would still be possible to transfer a constant 10-20A load to the red leg and be within limits of the breaker and giving the black leg a little more capacity. Having just two breakers available is what limits my red leg from carrying more amperage.

Using the figures from the above test, if I was connected to a 50 amp service at the pedestal, one leg would read 18.9 amps and the other 22.6 amps. IMO the pedestal and my unit's breaker panel would perform better and safely within its limits.

If connected to a 30 amp service at the pedestal, with a 30 to 50 adapter, the demand would still be 41.5 amps for the duration of the Microwave operation. Thus I can't run a higher amperage load on my unit, by attempting to balance the load, as nothing has changed, the equipment and demand is still there. It also doesn't change how I should adjust to having 30 amp service.

__________________________________________________ ____________________________________________

Amperage by number:

I thought about what I should be running on shore power when connected to a 30 amp service but can say I never knew where the line was that I shouldn't cross. Like most, tried to conserve and run gas on the WH or refrig when I thought I needed to. Have seen many times amperage and load charts for various equipment and items that has been posted on the .net or in articles and never thought much about them. Do they really relate to my unit or my needs? Well, must admit, after spending a day checking my amperage use, I will say they do.

Here's a link to RV CONVERTER AND AMP DRAW. It will provide information that should be useful. Found that most of the readings listed were within the range of what I recorded. Found my reading for major items, like the A/C or WH to be in the middle of the range. Even though I took readings of my coffee maker, toaster etc, will not list them as they were close to those listed in the link and mfg vary.

I will list the following as they relate to my unit:

____The individual AC loads were taken after the item has been running for at least 15 minutes and read at the output of the circuit breaker. The DC load for the converter was taken with the unit plugged into the Splitter that was connected to it power source. (As I'm only concerned with AC amperage, the amp draw for various items does not relate to the load/amperage of the battery.)___

Norcold 814___ 4.0 amps
Atwood WH, GC6AA9E___ 11 amps
Coleman Series 8535 Air Cond___ 11 amps
Maxum RV2000 Vac___ 8 amps

For those with the Progressive converter and using the CHARGE WIZARD, the information below is provided to add to the information in the above link.

Converter, with Wizard in Storage Mode: .3 amps____ in Normal Mode: .8 amps___ in Boost Mode: 2.2 amps

When this series of test were taken, the batteries were fully charged and the Wizard was in Storage Mode with a draw of .3 amps. As loads were put on the converter, because the batteries were fully charged, the Wizard stayed in the Storage Mode and the Converter increased its output to meet the demand. Taking the .3 amp draw into account and subtracting it from the reading, this was my amp usage by load on the converter:

Water pump:___ .4
Water heater on gas:___ .4
Furnace fan:___ 1.8
Fluorescent lights (2):___ .6
Four fluorescent lights:___ 1.2
80% of units lighting:___ 3.5
TV booster, 80% lighting and furnace fan:___ 6.4

It took about 30 minutes to complete the above test. When the demands were removed from the converter, it read .3 amps, still in Store Mode. I'm sure this isn't a "real life" test of the system but did give me an indication that the converter will carry the load as required and change its amperage as demand changes. It also showed that during the heating season, I need to add at least 6.4 amps to my figures when determining Load Usage for lighting and heat using the furnace.

__________________________________________________ _____________________________________________


Bruce asked in the "cheater box" discussion:___ As for additional loads besides HW and refrig, don't forget you're built in battery charger. Particularly if you arrive at a CG after some time in the boonies.

___Using a spare battery that was already low and load testing it until it read 11.9v; I installed it as the second battery bank. The Wizard analyzed the battery and changed to Boost mode. At which time the battery recorded 14.4v on the meter and an amp draw of 2.2 amps at the converter. Checked the amperage after 30 minutes and the reading was 1.9 amps. IMO the 2.2 amps should be the max draw of the converter while boosting, the draw duration will depend upon the batteries state of charge before cycling to the Normal mode at .8 amps.

__________________________________________________ ______________________________________________


What I did ...determining circuits and load at the service panel.

These test and procedures were done with the face of the breaker panel removed. Extreme CAUTION must always be exercised when working on any 120v circuit. I DO NOT SUGGEST or ENCOURAGE that anyone should do the following. It is only stated as a procedure that I followed in determining my circuit and amperage loads. DO NOT perform any test or procedure regardless of the maintenance task that you do not feel comfortable with or have no knowledge of. DO NOT perform any procedure or test while riding in a car or use while in the shower. With that said:

.....Performed an amperage reading of the black and red input legs with equipment running.
.....Determined which breaker was on each leg. This required the removal of an input leg and checking the breakers. Power, at the pedestal, was removed and applied at various times to complete this step.
.....Determined which items or circuits were on each breaker. The Air Cond, WH, microwave, W/D and GFI each had their own 20 amp breaker.
.....Performed an amperage reading of each breaker to determine its load.
.....Performed an amperage reading of the utility items we might use, i.e. the coffee maker, toaster, central vacuum, converter etc to determine their load. This was done using the item plugged into the Line Splitter.
.....I swapped several circuits to different legs to help balance the load.
..... Performed an amperage reading of the black and red input legs with equipment running.
.....I relabeled the panel to change or add addition information.

A description of MY PANEL: there are 2 columns of breakers. On the RIGHT, there is a 50A ganged breaker which is the input, Main or disconnect depending on how you prefer to name it. The GFI breaker is installed below, my #7. On the LEFT, there are three, double circuit breakers, meaning two circuits per breaker. These are my breakers 1 to 6. As stated: # 1, 2, 5, 6, and 7 are on the black leg and # 3 and 4 on the red.

The following test equipment was used to determine which circuits were "live" and for taking the amperage readings. IDEAL AUTOMATIC METER, AC LINE SPLITTER AND NON-CONTACT VOLTAGE DETECTOR. I would suggest the Ideal Meter to anyone in need of an easy to use, multifunction meter.


Here are a few links that made this Topic shorter:

120-240 VOLT POWER TOPICS
RV ELECTRIC SERVICE
50A TESTER

Wish to thank the following for the information that they share with us all:

RVtechLibrary.com____great resource. On my favorites list.
myrv.com____for electrical information
KOA, RV Maintenance Tips
And various manufactures that provide information on their products.

and to ChiefJohn, who has seen several versions of this. Yes it has gotten longer. I still hate to write!

__________________________________________________ ______________________________________________


Still need to conserve and manage the load as required. Now have a little more information to do it.

If you managed to get this far....hope that something helped.
Chris
__________________
2000 Alpenlite, 29 ft Valhalla - 2014 F350
Workshop is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-10-2008, 11:30 AM   #2
Senior Member
 
Workshop's Avatar
 
Join Date: Sep 2007
Posts: 1,334
50A power and amperage readings for a 2001, Excel RLE Limited

Sorry about a long post in advance.....I'm more verbal, visual and touch it kind of guy, really hate to write.

I stated in the "cheater box" discussion that I would be taking amperage readings of various systems and equipment on my unit. As not to be Off Topic, I posted some information there that might relate and will do the same here. These readings are from MY unit and suspect that they might relate to other Excel's as well and that is why I decided to share this information. Just never thought when I started it would take on a life of its own.


Several weeks ago, what started out to be a simple project of determining which input leg to use to install a POWER INLET on my unit, ended up with other questions I had no answers for. A question about the CHEATER BOX was asked on the Excel Owners Forum: "Anyone use electrical plug cheater box? The one that you plug in a 20 amp and 30 amp plug and it gives you 50 amp service". This question lead me to others and a week of projects ranging from exploring my breaker panel, installing the Inlet, taking amperage reading multiple times in different places and moving circuits___ you get the ideal.

I find the term 50A is as general a term as I used to use when saying 30A.
Being new to the 50 amp service requirements of my Excel, the terms 50A available, 50A service, 50A 120/240v service, 30A to 50A adapters, AUTOFORMER, SURGE PROTECTIONand CHEATER BOX I, like most, initially found this confusing. What is SHORE POWER? I don't have a boat.

After a lot of reading, the 50A 120/240v service isn't that much different than my stick built. It has two power input legs, a neutral and a ground. Each leg provides power to various breakers that feed different circuits that make up the outlets, refrigerator, air conditioner, etc.

But there are differences. In general, a stick built is designed to have a consistent power input and a relatively balanced load. My unit with the panel that is installed and would guess, speaking in general terms, other units providing 50A 120-240v service that the panels aren't designed to be balanced in the same manner. As RV'ers we face the challenges of having to deal with a variable power input, 30A or 50A 120/240v with a consistent to variable load (and don't forget the 50A from the cheater box). When I stated.... the panels aren't designed to be balanced in the same manner....what I discovered on my panel was that the black input leg provided power to breakers # 1,2, 5,6 and 7. The red leg serviced breakers 3 and 4.

After checking the breakers to determine which circuits they provided power to, I discovered that the black leg provided power to all the circuits that I normally use. The red, serviced the washer-dryer and a single rear outlet that included a ceiling fan. As we wouldn't be installing a W/D in our unit, this means that the entire load was on the black. IMO it's helpful to know what's on each leg and what each circuit or item has as a load demand when determining how we deal with or without the 50A 120-240v service our units require. Enter the cheater box discussion again. Without knowing my units demands, I would have been providing 30A to a 50A or greater demand and 20A to a circuit that had none. I'm sure this would have given me a sense of extra power, if I had chose to use it at the time. Regardless without the 50A 120-240V service available and by whatever means I hook up to the pedestal, load management is still required and that was a different project.
__________________________________________________ _______________________________________________

Amperage readings. What did it all mean?

I tried to run the equipment that would give me a base line for amperage use. With the A/C, WH, Refrig, entertainment area operating and items we might use on a "normal" trip. This included 4.5amps from the converter to run 60% of the lights and the Charge wizard in normal mode. Had an amperage reading of 30.5 amps on my black input leg, 0 amps on the red and 30.5 amps on the neutral. With the microwave on, readings increased to 41.5amps. Add the coffee maker, another 10 amps, or the hair dryer, another 8 amps. One thing about determining a load, there is a constant, intermittent and occasional demand. Guess it could be possible to reach the 50 amp on a single leg input for a short period. When the DW makes me use the onboard vacuum system, there's more in overload than the additional 8 amps.

What I did to "balance the load" was to move the WD and Rear outlet to the black leg and installed the Water heater and Microwave to the red leg. By doing this I have 18.9amps on the black and 22.6 amps on the red with the above equipment running. The white, neutral, read 7.6 amps compared to the 41.5 amps as before.

As demands change, so would the amperage on each leg. By making the changes I did, it gives me a little cushion on the black leg when the hair dryer comes on and the coffee pot is doing its thing. As mentioned, it's impossible to balance a system that has 5 circuits on one leg and 2 on the other. With my figures, with a W/D installed, it would still be possible to transfer a constant 10-20A load to the red leg and be within limits of the breaker and giving the black leg a little more capacity. Having just two breakers available is what limits my red leg from carrying more amperage.

Using the figures from the above test, if I was connected to a 50 amp service at the pedestal, one leg would read 18.9 amps and the other 22.6 amps. IMO the pedestal and my unit's breaker panel would perform better and safely within its limits.

If connected to a 30 amp service at the pedestal, with a 30 to 50 adapter, the demand would still be 41.5 amps for the duration of the Microwave operation. Thus I can't run a higher amperage load on my unit, by attempting to balance the load, as nothing has changed, the equipment and demand is still there. It also doesn't change how I should adjust to having 30 amp service.

__________________________________________________ ____________________________________________

Amperage by number:

I thought about what I should be running on shore power when connected to a 30 amp service but can say I never knew where the line was that I shouldn't cross. Like most, tried to conserve and run gas on the WH or refrig when I thought I needed to. Have seen many times amperage and load charts for various equipment and items that has been posted on the .net or in articles and never thought much about them. Do they really relate to my unit or my needs? Well, must admit, after spending a day checking my amperage use, I will say they do.

Here's a link to RV CONVERTER AND AMP DRAW. It will provide information that should be useful. Found that most of the readings listed were within the range of what I recorded. Found my reading for major items, like the A/C or WH to be in the middle of the range. Even though I took readings of my coffee maker, toaster etc, will not list them as they were close to those listed in the link and mfg vary.

I will list the following as they relate to my unit:

____The individual AC loads were taken after the item has been running for at least 15 minutes and read at the output of the circuit breaker. The DC load for the converter was taken with the unit plugged into the Splitter that was connected to it power source. (As I'm only concerned with AC amperage, the amp draw for various items does not relate to the load/amperage of the battery.)___

Norcold 814___ 4.0 amps
Atwood WH, GC6AA9E___ 11 amps
Coleman Series 8535 Air Cond___ 11 amps
Maxum RV2000 Vac___ 8 amps

For those with the Progressive converter and using the CHARGE WIZARD, the information below is provided to add to the information in the above link.

Converter, with Wizard in Storage Mode: .3 amps____ in Normal Mode: .8 amps___ in Boost Mode: 2.2 amps

When this series of test were taken, the batteries were fully charged and the Wizard was in Storage Mode with a draw of .3 amps. As loads were put on the converter, because the batteries were fully charged, the Wizard stayed in the Storage Mode and the Converter increased its output to meet the demand. Taking the .3 amp draw into account and subtracting it from the reading, this was my amp usage by load on the converter:

Water pump:___ .4
Water heater on gas:___ .4
Furnace fan:___ 1.8
Fluorescent lights (2):___ .6
Four fluorescent lights:___ 1.2
80% of units lighting:___ 3.5
TV booster, 80% lighting and furnace fan:___ 6.4

It took about 30 minutes to complete the above test. When the demands were removed from the converter, it read .3 amps, still in Store Mode. I'm sure this isn't a "real life" test of the system but did give me an indication that the converter will carry the load as required and change its amperage as demand changes. It also showed that during the heating season, I need to add at least 6.4 amps to my figures when determining Load Usage for lighting and heat using the furnace.

__________________________________________________ _____________________________________________


Bruce asked in the "cheater box" discussion:___ As for additional loads besides HW and refrig, don't forget you're built in battery charger. Particularly if you arrive at a CG after some time in the boonies.

___Using a spare battery that was already low and load testing it until it read 11.9v; I installed it as the second battery bank. The Wizard analyzed the battery and changed to Boost mode. At which time the battery recorded 14.4v on the meter and an amp draw of 2.2 amps at the converter. Checked the amperage after 30 minutes and the reading was 1.9 amps. IMO the 2.2 amps should be the max draw of the converter while boosting, the draw duration will depend upon the batteries state of charge before cycling to the Normal mode at .8 amps.

__________________________________________________ ______________________________________________


What I did ...determining circuits and load at the service panel.

These test and procedures were done with the face of the breaker panel removed. Extreme CAUTION must always be exercised when working on any 120v circuit. I DO NOT SUGGEST or ENCOURAGE that anyone should do the following. It is only stated as a procedure that I followed in determining my circuit and amperage loads. DO NOT perform any test or procedure regardless of the maintenance task that you do not feel comfortable with or have no knowledge of. DO NOT perform any procedure or test while riding in a car or use while in the shower. With that said:

.....Performed an amperage reading of the black and red input legs with equipment running.
.....Determined which breaker was on each leg. This required the removal of an input leg and checking the breakers. Power, at the pedestal, was removed and applied at various times to complete this step.
.....Determined which items or circuits were on each breaker. The Air Cond, WH, microwave, W/D and GFI each had their own 20 amp breaker.
.....Performed an amperage reading of each breaker to determine its load.
.....Performed an amperage reading of the utility items we might use, i.e. the coffee maker, toaster, central vacuum, converter etc to determine their load. This was done using the item plugged into the Line Splitter.
.....I swapped several circuits to different legs to help balance the load.
..... Performed an amperage reading of the black and red input legs with equipment running.
.....I relabeled the panel to change or add addition information.

A description of MY PANEL: there are 2 columns of breakers. On the RIGHT, there is a 50A ganged breaker which is the input, Main or disconnect depending on how you prefer to name it. The GFI breaker is installed below, my #7. On the LEFT, there are three, double circuit breakers, meaning two circuits per breaker. These are my breakers 1 to 6. As stated: # 1, 2, 5, 6, and 7 are on the black leg and # 3 and 4 on the red.

The following test equipment was used to determine which circuits were "live" and for taking the amperage readings. IDEAL AUTOMATIC METER, AC LINE SPLITTER AND NON-CONTACT VOLTAGE DETECTOR. I would suggest the Ideal Meter to anyone in need of an easy to use, multifunction meter.


Here are a few links that made this Topic shorter:

120-240 VOLT POWER TOPICS
RV ELECTRIC SERVICE
50A TESTER

Wish to thank the following for the information that they share with us all:

RVtechLibrary.com____great resource. On my favorites list.
myrv.com____for electrical information
KOA, RV Maintenance Tips
And various manufactures that provide information on their products.

and to ChiefJohn, who has seen several versions of this. Yes it has gotten longer. I still hate to write!

__________________________________________________ ______________________________________________


Still need to conserve and manage the load as required. Now have a little more information to do it.

If you managed to get this far....hope that something helped.
Chris
__________________
2000 Alpenlite, 29 ft Valhalla - 2014 F350
Workshop is offline   Reply With Quote
Old 01-10-2008, 11:54 AM   #3
Senior Member
 
ChiefJohn's Avatar
 
Winnebago Owners Club
Join Date: Nov 2006
Location: Anywhere, USA
Posts: 2,472
Outstanding!! "Rockin" could not have done better -- for what that's worth.

Seriously, Chris I appreciate your discussion on our Excel 50amp electrical systems. I'm sure we'll be referring to this topic frequently.
John
__________________
John & Marilyn Yoder, Sophie & Misha (Bichons)
2008 Vectra 40TD, WIT-151980 FMCA F265880
ChiefJohn is offline   Reply With Quote
Old 01-10-2008, 12:23 PM   #4
Senior Member
 
Ecker's Avatar
 
Join Date: Feb 2004
Location: South Carolina
Posts: 770
"Anyone use electrical plug cheater box? The one that you plug in a 20 amp and 30 amp plug and it gives you 50 amp service".
-------------------------------------------------
One important fact often overlooked in the cheater discussion is that putting a 20 and 30 amp together does not give 50 amp IF the pedestal is wired to code. Code requires that the two circuits be fed by a 40 amp single pole breaker at the main. Thus if the box is to code and one actually pulls 50 amp you may go dead and since the main is padlocked (or should be) there will be no way to reset.
__________________
Ecker
Ecker is offline   Reply With Quote
Old 01-10-2008, 12:29 PM   #5
Senior Member
 
Texas Boomers Club
Join Date: Jul 2000
Location: Cypress, Texas USA
Posts: 8,854
HERE is a thread where we just about beat the 50A subject to death.

Most 50 amp rigs use the 2nd leg to feed the 2nd A/C (if so equipped) in addition to the W/D that you mention.

Rusty
RustyJC is offline   Reply With Quote
Old 01-10-2008, 12:39 PM   #6
Administrator in Memoriam
 
Hitchhiker's Avatar


 
Appalachian Campers
Join Date: Jan 2000
Location: Buladean, NC
Posts: 8,126
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by ecker:
"Anyone use electrical plug cheater box? The one that you plug in a 20 amp and 30 amp plug and it gives you 50 amp service".
</div></BLOCKQUOTE>

I carry one but can rarely use it becauise most of the 20 amp receptacles are on a GFCI. I think I used it once in a park with old wiring.
__________________
'11 GMC Acadia SLT AWD
'11 GMC Sierra 1500 4x4 Extended Cab
Hitchhiker is offline   Reply With Quote
Old 01-10-2008, 01:49 PM   #7
Senior Member
 
Newmar Owners Club
Join Date: Sep 2006
Location: Franklin, Michigan
Posts: 1,306
Remember that if your coach has an EMS (Energy Management System), a cheater cord will not work.
__________________
Scott Crompton
Newmar TBD
Sue (DW):Celia 18, Alec 17, Isis (Abyssinian)
JavaJelly is offline   Reply With Quote
Old 01-10-2008, 02:45 PM   #8
Senior Member
 
LarryGodby's Avatar
 
Excel Owners Club
Join Date: Apr 2007
Location: Colorado
Posts: 537
Man Chris you make me want to go out there and tear into the circuits and check stuff out.

Thank you so much for the information, that will be a post to keep, maybe this might be a best practices post.

I know last weekend when I was looking at all the amp draw it seemed funny that the 2nd leg read zero, we did not have the W/D going. I am going to have to see what the dryer draws and see if I can move some lines around, I doubt we will have a 2nd AC in our 33. Never need it in the mountains and I don't go east of the Mississippi much in the heat of the summer.
__________________
Larry & Patty Godby Guard Dogs are Jo Jo & Shadow
"Stars & Stripes" 2000 F-350 CrewCab LB 4x4 -"Freedom" 2003 33 RSE
Colorado Excel Club
LarryGodby is offline   Reply With Quote
Old 01-11-2008, 02:26 AM   #9
Senior Member
 
MakinSmoke's Avatar
 
Excel Owners Club
Join Date: Mar 2007
Location: Big Pine Key, FL
Posts: 1,424
Thanks Chris. Very nice job, even I understood.
__________________
Member # 47, "squirt", Smart Cabriolet The Newest Family Addition
The Wagon, Excel L36CLO, Overkill, Volvo 610, Venture Out, Cudjoe Key, FL
MakinSmoke is offline   Reply With Quote
Old 01-11-2008, 06:28 AM   #10
Senior Member
 
Workshop's Avatar
 
Join Date: Sep 2007
Posts: 1,334
As a general note, I don't own or plan to use a "cheater box".

Larry, I felt the same way after reading it once it was posted.

It would be interesting to know what a washer/dryer does to the amp load to use as a future reference. Being concerned about a long post and bringing down the server, I didn't include some information and thought it could be added later.

Since you indicated that you might move a circuit, I will list mine as they presently are, plus list the AMPERAGE SIZE of the breaker and EQUIPMENT or CIRCUIT on each.

BLACK WIRE OR LEG: LOAD, 21 amps on 120v, possible 36 amps with appliances, or 17 amps on gas, plus add appliance load

Breaker # 1: 20 amps__Air conditioner: 10-12 amps Fan only: 3 amps

Breaker # 2: 20 amps
__Bedroom outlets
__Entertainment area: 3 amps (TV, DVD/VCR, total of 4 outlets)
__Refrigerator: 4 amps, on 120v...... .4 amps on 12v and gas.
__Three storage compartment outlets, which powers the converter (.3 to possible 8 amps,
3 amp might be average ?) and the House vacuum: 8 amps

Breaker # 5: 20 amps__Single rear outlet and ceiling fan: ? During the winter will possibly use this outlet for the small electric space heater, 10-13 amps, when needed as it will give me 20 amps without other equipment on the circuit.

Breaker # 6: 20 amps__Washer/Dryer: not installed

Breaker # 7: 20 amps__GFI outlets. Kitchen (2), Sofa/Dinette (2), Bath (1), Utility compartment (1) and outside receptacle (1). Hair dryer, coffer maker, toaster. For possible load 15 amps was figured, which is variable and not always there.

RED WIRE OR LEG: LOAD, 11 amps on 120v, possible 22amps with appliances, or 0 amps on gas, plus add appliance load

Breaker # 3: 20 amps__Water Heater: 11 amps, on 120v..... .4 amps on 12v and gas

Breaker # 4: 20 amps__Microwave: 11 amps


Hope this additional information helps.
__________________
2000 Alpenlite, 29 ft Valhalla - 2014 F350
Workshop is offline   Reply With Quote
Old 01-11-2008, 04:00 PM   #11
Senior Member
 
Sunny's Avatar
 
Join Date: Sep 2000
Location: Prattville, AL USA
Posts: 202
Workshop
I have 1? what size Gen do you have?

Tom
__________________
2001 Sunnybrook 33 BWS

2015 Chevy 2500 6.0L 4.10
Sunny is offline   Reply With Quote
Old 01-11-2008, 04:48 PM   #12
Senior Member
 
Workshop's Avatar
 
Join Date: Sep 2007
Posts: 1,334
<BLOCKQUOTE class="ip-ubbcode-quote"><div class="ip-ubbcode-quote-title">quote:</div><div class="ip-ubbcode-quote-content">Originally posted by Sunny:
Workshop
I have 1? what size Gen do you have? </div></BLOCKQUOTE>

Tom, if you are asking if I have a generator, the answer is no. Unit came equiped for a LP generator setup, and an exterior remote gen plug. Decided to use one of the small Hondas if I need one, as I like the front storage for batteries, tools and storage.

The question about the washer/dryer amps was just for inquiring minds like mine. With it being a 20A breaker, just wondered how much of that it used either for the washer or dryer.

Thanks, Chris
__________________
2000 Alpenlite, 29 ft Valhalla - 2014 F350
Workshop is offline   Reply With Quote
Old 01-11-2008, 05:31 PM   #13
Senior Member
 
HB Phil's Avatar
 
Excel Owners Club
Join Date: Feb 2007
Posts: 298
Thanks Chris,

I'll be sure to check the leg/load balance on mine and get things as equally distributed as possible according to my loads.
__________________
2007 Excel 30RKE
HB Phil is offline   Reply With Quote
Old 01-14-2008, 04:01 PM   #14
Senior Member
 
rockintom's Avatar
 
Excel Owners Club
Join Date: Dec 2006
Location: Fulltime TX Escapee
Posts: 8,898
Chris,

You are amazing. Some real great stuff you worked up there! I'm wondering if PI has changed the loads on the legs to be more equal in the later model units.

Please tell me how long I can run my inverter tonight with my 2 group 27 bats with a 478 watt draw. The bats start fully charged and I don't want to go below a 46.5% charge level before recharging! Answer must be in the number of beers!!! Just funnin'....take the night off, so you don't blow a fuse!

You are a great assest to our forum, buddy!
Tom
__________________
2012 Excel L33ft. GKE named Charm as in 3 times is a Charm. Love Fulltiming. Bullet '14 Chevy D/A 3500 LB CC DRW Summit White - Ebony Interior. Check out our blog at: https://claphamstravels.blogspot.com
rockintom is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Mystery 50A breaker Sixpack98 Monaco Owner's Forum 5 06-14-2008 04:32 PM
50A Cheater box Roam America Travel Trailer Discussion 7 02-21-2008 09:23 PM
50a Voltage Boosters Robin_M MH-General Discussions & Problems 2 09-11-2007 07:01 AM
30 to 50A Service Conversion The Clock Meister Winnebago Industries Owner's Forum 5 01-03-2007 12:31 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 10:33 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2023, vBulletin Solutions, Inc.