2012 31RSE Winslow - SH 35 Suburban furnace cycling on high limit switch. Have replaced limit switch, cleaned fan, replaced burner, propane regulator (wc set at 11in.) rerouted ducts. Temperature at bathroom register reaches 180 degrees after about five minutes. High limit switch opens then closes in about a minute, repeat. Draw on fan motor 6.5 amps. The basement door is open to insure return air is not the problem and none of the ducts are restricted. HELP PLEASE
rick gorman is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 08-14-2020, 05:55 PM   #2
Senior Member
 
Join Date: Nov 2015
Posts: 13,470
180*F at bathroom register....How are you measuring that air temp?
**SH 35 uses a 160*F High Temp Limit Switch


Basement door open?
So furnace is pulling in OUTSIDE air vs RETURN Air from INSIDE the trailer
Furnance should pull Inside air thru Return Air Path


'Limiting' (operating on High Limit)
Overfiring due to HIGH LP System Pressure or oversized/damaged burner orifice
Obstructed Return Air Path....minimum of 55 sq inch

Restricted Duct(s).....
*rerouted ducts? Four 4" minimum required with at least 56 sq inch
Motor maps 6.5A----SH35 with 3" motor 8.2 amp draw with 375 CFM Discharge
**motor running slow/air flow low/12VDC Voltage Low??


Heat Exchanger obstructed/low air flow thru it....
Heat Exchanger can be cleaned but must be completely removed from furnace/everything disconnect........hgih pressure air blown thru OR even run water thru it/drain/blow out with air
__________________
Is it time for YOUR Medication or Mine?
Dodge 3500 w/Tractor Motor & NUWA 5vr
US NAVY---USS Decatur DDG-31
Old-Biscuit is online now   Reply With Quote
Old 08-14-2020, 09:13 PM   #3
Junior Member
 
Join Date: Mar 2019
Posts: 10
Good information and questions, I also wondered why the limit switch was not tripping sooner, as I looked at the furnace, the limit switch is located at the front of the furnace and as the fan blows the air past the heat exchanger itís almost a direct passage through the heat exchanger through that center duct and past the limit switch, that center duct does not get nearly as hot as the one above or below it.
I changed five of the ducts in order to eliminate sharp turns, my thinking on the return air was to keep the basement door open to make sure the furnace was getting enough return air, the duct temp measured with a digital probe with the door open or closed is the same. Changing the ducts to allow better airflow did make a difference. It used to cycle on the high limit switch after about 3 to 4 minutes of operation and then after three times it would go into lock out so Iím making improvements but there is still something thatís not right, i have checked voltage, but will check again, do you think 6.5 amps indicates a problem? Donít have a way to measure cfm, the bathroom register that gets the hottest (180) and the shortest duct (18Ē) seems to have great air flow. 🙂
__________________
RG 2012 Excel 31 RSE Winslow
rick gorman is offline   Reply With Quote
Reply

Tags
ace, furnace



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Furnace fan 2002 Alpine (Suburban gas furnace) dlmoo1 Alpine Coach Owner's Forum 5 01-21-2020 10:31 PM
Suburban NT-45S Furnace or Furnace motor Ronbstewart Monaco Owner's Forum 7 05-25-2018 08:15 PM
Furnace problem may not be in the furnace! turkeychuckt MH-General Discussions & Problems 3 02-03-2010 03:26 PM
Finally on the road and problems - furnace and water! Loralie Excel Owner's Forum 4 02-09-2009 03:38 AM
Furnace nutensteve Monaco Owner's Forum 17 01-01-2009 08:27 AM


All times are GMT -6. The time now is 04:50 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2020, vBulletin Solutions, Inc.