On 30AMP power for 13 days, until...
We've had to extend our stay in SC, because of the nasty weather up north. I almost feel ashamed for enjoying a 79 degree day, when they are going to be getting 5-9 inches of snow at home. That's another story though.
We had a water leak at the WH the other night and the felt under the cabinets was wet. I got everything mostly dry and wanted to run the A/C, so it would draw out more moisture. It ran for 3 hours and then the pedestal breaker tripped. I reset it and it tripped again, in less than a minute. When I checked further, I could smell a bit of smoke.
I found that one pin on the GFCI/surge suppressor and one pin of the power cord plug had gotten pretty hot. I called the CG and told them the plug on the pedestal was smoking. The maintenance guy was here in less than a minute!
He replaced the 30AMP receptacle and the breaker. I'm not real sure what the problem was, since I only had the A/C and the converter pulling power. I guess it was a faulty receptacle.
Attached are a pic of the surge plug and a couple of the inside of the same surge/gfci. You can see how hot it was, by looking at the partially melted wire nut on the ground wire..
__________________
2015 Excel Winslow 37SDF 38' fifth wheel
2007 Excel Limited 33RKE 35' fifth wheel
2015 Ford F350 Platinum DRW Crew Cab 6.7PSD
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
03-04-2015, 05:33 PM
|
#2
|
Senior Member
Excel Owners Club
Join Date: Dec 2006
Location: Fulltime TX Escapee
Posts: 8,901
|
Looks pretty common for a 30 amp plug that has a loose tired/loose female receptacle creating high resistance thus overheating. This is pretty common on 30 amp plugs that have been taxed to the max. Are you sure you only had the only the A/C and converter on? No refer or the WH on electric? If you only had the AC/converter on....you probably had a tired/loose connection at the receptacle. I hate dealing with the puny 30A circuits.
__________________
2012 Excel L33ft. GKE named Charm as in 3 times is a Charm. Love Fulltiming. Bullet '14 Chevy D/A 3500 LB CC DRW Summit White - Ebony Interior. Check out our blog at: https://claphamstravels.blogspot.com
|
|
|
03-04-2015, 06:53 PM
|
#3
|
Senior Member
Excel Owners Club Mid Atlantic Campers Coastal Campers
Join Date: Nov 2011
Location: Beaufort, SC
Posts: 540
|
I forgot about the refer being on, but the WH was off. That was it.. Would it be worth asking the CG to pay for my replacement parts?
__________________
2015 Excel Winslow 37SDF 38' fifth wheel
2007 Excel Limited 33RKE 35' fifth wheel
2015 Ford F350 Platinum DRW Crew Cab 6.7PSD
|
|
|
03-04-2015, 07:08 PM
|
#4
|
Senior Member
Join Date: Apr 2010
Location: Joplin MO
Posts: 435
|
Good Luck with that one!! I can hear the reply now-you probably had too many things on and overloaded our supply line (or something to that effect). I know just an old cynic.
__________________
2006 - 33' Excel/5thWheel/Limited/2015 Dodge Laramie/3500 Cummings Diesel/Crew Cab/ DRW/Retired Navy
|
|
|
03-04-2015, 08:46 PM
|
#5
|
Senior Member
Excel Owners Club
Join Date: Dec 2006
Location: Fulltime TX Escapee
Posts: 8,901
|
Quote:
Originally Posted by EMD_Driver
I forgot about the refer being on, but the WH was off. That was it.. Would it be worth asking the CG to pay for my replacement parts?
|
I don't think that's gonna happen.....this is a common occurrence on 30 amp especially on older cord plug in and less than new park pedestals.
Don't everyone go getting picky on me and my numbers, but here's something to think about.
A/C- 14-16 AMP draw
Converter depending on rate of charge/load- 5-10 AMPS
Refer on electric with heating element on- 5-8 AMPS
Pretty soon you're maxing out a poor old 30 AMP circuit.
Another problem that occurs often is that many folks overload and trip the 30 AMP breakers. When this happening over and over again it makes the breaker "soft" (weaker) and then they trip at less then 30 AMP draw. Over time they get weaker and weaker and frustrating to deal with. Did I say I hate 30 AMP???!!! rockin'
50 AMP breakers are much harder to trip, but if you try....you can do it.
The park I work at in OR, we get some Prevosts that should be using 100 AMP service and we only have 50 AMP service. They try running the 4 roof A/Cs and then try to run something like a microwave. Yeah right........
The park is trying to get the corp. to approve a row of 10 sites for 100 AMP service. The cost is unbelievable, so no....we haven't seen them yet! Hard to justify with such a short RVing season and temps that rarely get into the 90's.
__________________
2012 Excel L33ft. GKE named Charm as in 3 times is a Charm. Love Fulltiming. Bullet '14 Chevy D/A 3500 LB CC DRW Summit White - Ebony Interior. Check out our blog at: https://claphamstravels.blogspot.com
|
|
|
03-04-2015, 09:37 PM
|
#6
|
Junior Member
Join Date: Feb 2014
Posts: 16
|
A 50 amp power supply is actually allowing you to pull 100 amps total, a double 50 amp breaker is giving you two legs of 50 amps.
Each leg can carry 50 amps total, most trailers are all using 110- 120 volt appliances connected to one of the two legs in the trailers breaker box.
The trailer manufacturer connects all the required power loads between the two 50 amp legs when you use a 50 amp power cord.
If you use a 50 amp to 30 amp cord adaptor the adaptor is connecting the trailers two power legs from the trailer breaker box together so it can be plugged into the parks 30 amp single leg power supply that only has a total of 30 amps.
|
|
|
03-04-2015, 10:01 PM
|
#7
|
Senior Member
Join Date: Jul 2014
Location: Graham, WA
Posts: 357
|
Quote:
Originally Posted by rockintom
The park I work at in OR, we get some Prevosts that should be using 100 AMP service and we only have 50 AMP service.
|
What park do you work at in Oregon?
__________________
Rob & Cathy
2011 F350 6.7 SRW LB CC
2014 Excel 34ike
|
|
|
03-04-2015, 10:23 PM
|
#8
|
Senior Member
Excel Owners Club
Join Date: Jan 2001
Location: Whitney, Texas, USA
Posts: 2,284
|
"Work"?.....
__________________
Russell
'13 Excel Winslow 34IKE
'16 GMC Sierra 3500HD
|
|
|
03-04-2015, 10:44 PM
|
#9
|
Senior Member
Excel Owners Club
Join Date: Dec 2006
Location: Fulltime TX Escapee
Posts: 8,901
|
Quote:
Originally Posted by Rob17
What park do you work at in Oregon?
|
For 5 summer seasons I worked @ Portland-Fairview RV Park in Fairview, OR. (east of Portland about 12 miles). Worked about 12 to 14 hrs. a week as a night host. We took last summer off to travel and sight see some more. I think we are gonna do the same this year. However, we may not travel as much as it gets real expensive and as all retired folks know.....we are on a "fixed" income! rockin'
Rob, Why do you ask?
I see you are in Graham, WA....we just missed you last summer as we stayed at the Elks in Puyallup, WA. We may be passin' that way again this summer. Don't you owe us a Happy Hour? That's what I thought!!! I can do a safety inspection on your ol' Excel!!!
__________________
2012 Excel L33ft. GKE named Charm as in 3 times is a Charm. Love Fulltiming. Bullet '14 Chevy D/A 3500 LB CC DRW Summit White - Ebony Interior. Check out our blog at: https://claphamstravels.blogspot.com
|
|
|
03-04-2015, 11:27 PM
|
#10
|
Senior Member
Join Date: Jul 2014
Location: Graham, WA
Posts: 357
|
Quote:
Originally Posted by rockintom
Rob, Why do you ask?
We may be passin' that way again this summer. I can do a safety inspection on your ol' Excel!!!
|
That's what I was wondering.
__________________
Rob & Cathy
2011 F350 6.7 SRW LB CC
2014 Excel 34ike
|
|
|
03-05-2015, 05:06 AM
|
#11
|
Senior Member
Damon Owners Club Workhorse Chassis Owner
Join Date: Mar 2009
Posts: 24,024
|
That is the most common failure on 30 amp outlets.. Your photos showed two views of a 20 amp GFCI outlet, do not know why,, NOTE that a GFCI outlet like that is not a surge progector nor is a Surge protector a GFCI, though you can put both in the same box.
But that is the most common failure.. Clean and polish that pin well before re-connecting.
I keep spare 30 amp plugs on hand (And a 30 amp outlet end as well) cause in some parks I have to use 30 amps.. and I've had to replace and end or 3.
__________________
Home is where I park it!
|
|
|
03-05-2015, 05:56 AM
|
#12
|
Senior Member
Winnebago Owners Club
Join Date: Feb 2014
Posts: 962
|
I had the same experience at a campground on the panhandle of Fla this summer.
I have a progressive Surge/EMS that tells me if the Ground or Power connection is bad, and it tells me how many amps my Rv is using- it really works- It interrupts the flow of electricity before low amperage damages anything.
|
|
|
03-05-2015, 06:13 AM
|
#13
|
Senior Member
Winnebago Owners Club Freightliner Owners Club
Join Date: Mar 2007
Location: Home on the hill in Georgia
Posts: 2,742
|
I've got a couple of old 30amp cords around that look just like the one you pictured. Ones that I replaced on previous 30amp coaches. Was going to buy new plugs and make them into extension cords but you know how that goes.
__________________
Jerry Potter, Taz
1999 Coachman Catalina Sport
[SIGPIC][/SIGPIC]
|
|
|
03-05-2015, 06:38 AM
|
#14
|
Registered User
Monaco Owners Club
Join Date: Oct 2009
Location: Varies Depending on The Weather
Posts: 8,517
|
Quote:
Originally Posted by EMD_Driver
I found that one pin on the GFCI/surge suppressor and one pin of the power cord plug had gotten pretty hot. I called the CG and told them the plug on the pedestal was smoking. The maintenance guy was here in less than a minute!
He replaced the 30AMP receptacle and the breaker. I'm not real sure what the problem was, since I only had the A/C and the converter pulling power. I guess it was a faulty receptacle.
Attached are a pic of the surge plug and a couple of the inside of the same surge/gfci. You can see how hot it was, by looking at the partially melted wire nut on the ground wire..
|
The GFCI receptacle in your photos does NOT have the surge suppressor capability. They are two separate devices that perform different functions and are not commonly found in the same unit.
http://ra.panamax.com/pdf/gfci.pdf
The burnt pin on your 30 amp male plug is your Load Pin. Like others have posted that usually occurs when the female receptacle has gotten old and worn out.
However, I also agree with Rockintom that you were most likely pulling too many amps for the condition of the receptacle.
Is your rig 50 amp or 30 amp?
Dr4Film ----- Richard
|
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|