Issue with Fuel Gauge/Generator

Hey y”all,

I have recently acquired a 2001 Forest River Class A (34 ft) on a workhorse chassis. The generator in question is an Onan Marquis Gold 5500.

When I purchased it from the guy he mentioned the fuel gauge is stuck on Full, and that he couldn’t seem to get the generator working - not sure if it’s related). He mentioned that he had attempted to have the fuel gauge repaired twice in the past few years with both attempts being unsuccessful so he “gave up” and simply calculated his mileage and how much to pump for each journey basically.

It’s not “the end of the world” by any means for us to have a faulty fuel gauge but I am starting to believe it is effecting the generator. I could be entirely wrong, and I actually hope I am entirely wrong, as I was told the following from a friend:

“Well there has to be an interlock switch a set of contacts that has to be closed for it to enable if the fuel float isn’t working then it’s probably not closing the switch it and therefore your generator won’t turn on. It Doesn’t-go by what the needle says on the gauge itself inside the RV”

As of now if I go to start my generator it tries to turn on, it blows exhaust out and all but the moment I take my finger off the start button (on the generator itself as the inside RV button doesn’t seem to work) it just cuts out and dies.

My friend also advised there may be a way to bypass the switch to test the generator, but I would need a wiring diagram and I have not the slightest clue where to obtain one. If anybody does have a schematic of the float / generator would be highly appreciated as well.

I guess all in all I was hoping for some general advice on what to check / if the above information makes sense AKA is it possible that the reason my generator isn’t working simply due to the faulty fuel gauge (that’s stuck reading Full)?
NovaScotiaRV is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 05-02-2022, 07:44 AM   #2
Senior Member
 
Workhorse Chassis Owner
Join Date: Jun 2006
Location: Northwestern Montana
Posts: 3,505
The thing to do first is to make sure you have above a quarter tank of fuel, put in 20 gallons or so to be sure you have fuel in the tank.
The fuel pickup line within the fuel tank does not reach all the way to the bottom of the tank. This is done to insure the generator does not consume all the onboard fuel and leave you stranded. The fuel gauge being on full all the time is not an issue in running or starting the generator, and should be addressed as a separate issue.
__________________
Dieselclacker
dieselclacker is offline   Reply With Quote
Old 05-02-2022, 11:46 AM   #3
Member
 
Join Date: May 2022
Posts: 40
Thanks. That’s exactly what I thought but somebody local tried telling me otherwise. I appreciate your reply on the matter.

Addressing the fuel gauge issue is still something I want to do. If anybody has any advice on where to start I’m all ears!
NovaScotiaRV is offline   Reply With Quote
Old 05-04-2022, 07:33 AM   #4
Senior Member
 
Join Date: May 2005
Posts: 678
I would suggest replacing the fuel pump in the fuel tank especially if the MH has a lot of miles behind it. The fuel pump comes with a new fuel gauge tank unit. Since some fuel pumps in earlier chassis have failed at around 75,000 miles, you would be avoiding a roadside engine failure and eliminating the fuel gauge tank unit as the reason for the gauge failure. As Dieselclacker stated, the generator starting issue is affected by fuel level and certainly not by the fuel pump.
__________________
04 Southwind 37C W22

DIY Rear Panhard Rod
exrench is offline   Reply With Quote
Old 05-04-2022, 07:43 AM   #5
Senior Member
 
jacwjames's Avatar
 
Monaco Owners Club
Join Date: Jun 2014
Posts: 13,138
Get a copy of the generator manual. Not sure on your specific model but in my case I have a 7.5KW diesel generator, and have the ability to get fault codes from my generator. If there is a problem it will point me in the right direction as to what is wrong.

In my case I just press the stop side of the switch for ~5 seconds and it will give me a two part blink code if there is a problem. It will also tell me if there are no faults with a different blink code.
Again, not sure if your model generator does this or not.
__________________
Jim J
2002 Monaco Windsor 38 PKD Cummins ISC 350 8.3L
2005 Jeep Grand Cherokee w/5.7 Hemi
jacwjames is offline   Reply With Quote
Old 05-09-2022, 12:14 PM   #6
Junior Member
 
Join Date: Feb 2022
Posts: 20
Many of the Onan generators will stop running if there is no power generation. Will fire up while cranking but will immediately stop if you let go and no power is detected. Depends on which Marquis model you have. My 1992 Marquis will keep running even if no power is generated. New models will not. Might be time to drop your genset and do some serious maintenance. New plugs and a carb rebuild at the very least. One issue that's common on the newer Marquis is a belt the connects the engine to the generator. If broke, it will not keep running. On older models if can be a slip ring that needs to be cleaned. On all models it can be a faulty regulator.

As others have indicated, there is no connection between the engine fuel system and the generator. The generator has its own fuel pump and pickup tube in the gas tank. Nothing about your fuel gauge could affect your generator.
92LandYacht is offline   Reply With Quote
Old 05-09-2022, 12:27 PM   #7
Senior Member
 
Skip426's Avatar


 
Join Date: Apr 2011
Location: Powell River, B.C.
Posts: 28,828
It would be interesting to know what the previous repair attempts on the fuel gauge involved .
As mentioned by exrench, the tank sending unit is on the side of the fuel pump in the tank .

If the sender or the pump assembly has already been replaced then wiring or dash unit have to be tested.

Cummins Onan should provide wiring info for your gen set .

Or you can check out this site for just about any manual you may need.

www.myrvworks.com/manuals/
__________________
99DSDP 3884, Freightliner, XC, CAT 3126B, 300 HP /ALLISON 3060
2000 Caravan toad, Remco & Blue Ox.
Skip426 is offline   Reply With Quote
Old 05-10-2022, 05:39 AM   #8
Junior Member
 
Join Date: Feb 2022
Posts: 20
Here's a web site that's been very helpful on older Onan generators:

https://www.smokstak.com/forum/forum...-generators.1/

No mater what, you will need to know the generator model number and serial number.
92LandYacht is offline   Reply With Quote
Old 05-10-2022, 06:03 AM   #9
Senior Member
 
Tilted Kilt's Avatar
 
Winnebago Owners Club
Join Date: Apr 2020
Location: Georgia
Posts: 223
If you do your own work, check the gas gauge for voltage, it should vary with the fill level. Disconnect a wire to see if it drops to empty, if not it's mechanically stuck. Mine gets wonky after I (over) fill the tank but eventually straightens itself out. The advice to keep a 1/4 tank or better for your genset should be followed, otherwise it will never start. Changing the fuel filter isn't a bad idea and cleaning the carb might help. For me having a reliable genset is priceless. Another thing I noticed about my W24 is pressure in the gas tank, somehow, I think it effects the gauge and once in a while my "check engine" light comes on. Opening the gas cap slowly and keeping it really clean has helped with the gauge and the light. I think the float gets less of a pounding, but I can't confirm that, I just know it works for me. I have a 05 Adventurer on a W24 chassis, 75-gal tank and 7000-watt Onan genset. I hope you get this stuff squared away, especially the genset.
Tilted Kilt is offline   Reply With Quote
Old 05-10-2022, 06:41 AM   #10
Senior Member
 
Join Date: Jul 2017
Posts: 1,285
I doubt the problems are related. For the genset you should be able to run it independently from the fuel tank by disconnecting the fuel line near the genset and using a jerry can of fuel to feed it. I'm not sure about that one but lots have the fuel pump right at the genset so you could disconnect the line there to feed it from the jerry can and eliminate the fuel issue. I have run older Onan's that way so I don't think there is any electrical interlock on them. You would need the schematics to know for sure though and with them it should be easy to figure out how to bypass it.
For the fuel gauge check your grounds, if you have a bad ground typically they read over full.
__________________
98 Monaco Windsor
2015 Rubicon Toad
Craig1960 is offline   Reply With Quote
Old 05-11-2022, 04:44 AM   #11
Senior Member
 
Tilted Kilt's Avatar
 
Winnebago Owners Club
Join Date: Apr 2020
Location: Georgia
Posts: 223
Someone is confused about the problems being related, there are two separate issues, the gas gauge doesn't work and the genset doesn't work. Before you do the jerry can trick just check for fuel at your generator. You were given good advice about fuel levels in your gas tank and a link to get manuals for your generator, I would follow that good advice before you start taking your coach apart.
Tilted Kilt is offline   Reply With Quote
Old 05-11-2022, 06:18 AM   #12
Senior Member
 
Join Date: Nov 2020
Location: South Dakota
Posts: 408
Quote:
Originally Posted by Tilted Kilt View Post
Someone is confused about the problems being related, there are two separate issues, the gas gauge doesn't work and the genset doesn't work. Before you do the jerry can trick just check for fuel at your generator. You were given good advice about fuel levels in your gas tank and a link to get manuals for your generator, I would follow that good advice before you start taking your coach apart.
__________________
2004 Rexhall Roseair. 3955ET 370
bduemig is offline   Reply With Quote
Old 05-11-2022, 07:18 PM   #13
Member
 
Join Date: May 2022
Posts: 40
Thanks for the advice everyone. I’ve been busy as heck dealing with more urgent matters (leaks) and haven’t had a chance to get to this yet. I can confirm that the RV has barely any gas in it (as the previous owner only put 20L of gas in it he said for me and thinks it’s near empty — something I thought he would of mentioned earlier but it is what it is).

So, first thing I’m going to do when I have time to is fill the tank at least half way to see if it’s as easy as that. If this isn’t a fix, then I will dig deeper. There are less then 40 hours on this generator for an ‘01 model, and only 18 thousand miles on the MH itself.. also seems that everything was extremely well kept (that I can see anyway) around the gen.. so it very well could be the lack of fuel itself.

I appreciate everyone’s comments.
NovaScotiaRV is offline   Reply With Quote
Old 05-27-2022, 08:09 PM   #14
Senior Member
 
Chaffeekid's Avatar
 
Join Date: Dec 2011
Location: Chaffee, MO.
Posts: 503
When you press the bottom of the start switch do you hear a clicking sound. This is the start switch at the generator.
That clicking is the fuel pump priming or pumping gas into the carb. If you don’t hear anything you have a bad fuel pump. It is located under the generator and s easy to change. Just did it on mine. I paid 22 bucks for the pump and 18 for the associated filter on Amazon just search for your generator fuel pump.
__________________
MGySgt USMC(R) 1961-1991
2004 Winnebago Brave 34D
2019 Jeep Wrangler unlimited Amateur Call N0LZS
Chaffeekid is offline   Reply With Quote
Reply

Tags
fuel, generator



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Faulty Fuel Gauge.......is Scan Gauge a good alternative? DGBPokes Spartan Motorhome Chassis Forum 9 07-06-2015 08:43 PM
Fuel Gauge Versus Remaining Diesel Fuel lavamanz Freightliner Motorhome Chassis Forum 16 01-30-2012 07:11 AM
Fuel Gauge & Volt Gauge not working Deerhunter Freightliner Motorhome Chassis Forum 9 07-20-2010 02:22 PM
Onan fuel pickup vs. Caoch fuel gauge JWatkins Winnebago Industries Owner's Forum 5 01-13-2008 05:20 PM
temp gauge & fuel gauge indicators antlerz MH-General Discussions & Problems 9 02-16-2006 05:34 PM