Old 06-17-2021, 08:16 AM   #1
Junior Member
 
Donfleming's Avatar
 
Monaco Owners Club
Join Date: Dec 2020
Posts: 3
2 A/Cís on 50 amp

I have 3 ac units that run fine on my generator but my understanding was you could only run 2 on a 50 amp shore power. I have a Hughes 50 amp that shows 112 on leg 1 and 108 on leg 2 so I think it will kick me off if anything runs below 104 volts is their anything I can do? Itís going to be 2 hot 🥵 to run on 1 Ac all the time. Thanks Don
Donfleming is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-17-2021, 08:21 AM   #2
Community Moderator
 
Lt Dan's Avatar


 
Tiffin Owners Club
Join Date: Sep 2013
Location: DFW, Texas
Posts: 10,121
Yes, you can run all three A/Cs on 50 amp service, I do it all the time. My three 15k units draw 12amps each and you have 100 amps total on a 50 amp service (two legs of 50 each). Your voltage readings are low and that's a supply problem with the park power. The EMS will kick off below 104 volts but on decent supply you should never see voltage that low. You may have seen that you can only run two units on 30 amp service and that is correct.
__________________
2017 Phaeton 40IH XSH Maroon Coral - Power Glide Chassis with IFS
Previously '15 Tiffin Allegro RED 38QRA and '06 Itasca Sunrise 35A
'16 Jeep JKU Wrangler Sahara or '08 Honda Goldwing
Lt Dan is offline   Reply With Quote
Old 06-17-2021, 08:23 AM   #3
Senior Member
 
Mr_D's Avatar
 
Country Coach Owners Club
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 37,593
You can easily run 3 heat pumps on a 50 Amp service.
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft, HWH Active Air
Charter Good Sam Lifetime Member, FMCA, SKP
RV'ing since 1957, NRA Benefactor Life, towing '21 Jeep JLU Rubicon Ecodiesel
Mr_D is offline   Reply With Quote
Old 06-17-2021, 08:23 AM   #4
Senior Member
 
Busskipper's Avatar
 
Join Date: Sep 2007
Location: Grasonville, MD -- Golden, CO
Posts: 6,106
Quote:
Originally Posted by Donfleming View Post
I have 3 ac units that run fine on my generator but my understanding was you could only run 2 on a 50 amp shore power. I have a Hughes 50 amp that shows 112 on leg 1 and 108 on leg 2 so I think it will kick me off if anything runs below 104 volts is their anything I can do? Itís going to be 2 hot 🥵 to run on 1 Ac all the time. Thanks Don
Should be no Problem on shore power - a 50 amp service gives you 100 amps of 120, so more than enough power if the pedestal is wired correctly.

Best of Luck,
__________________
Busskipper
Location - Grasonville, Maryland - and/or - Superior, Colorado
2005 Travel Supreme 42DS04 - GX470 Toad
Busskipper is offline   Reply With Quote
Old 06-17-2021, 08:25 AM   #5
Senior Member
 
Join Date: Oct 2014
Posts: 2,995
Two somewhat unrelated questions.


Low voltage is almost always a park of power company issue. Very little you can do about it other than trying another site or another CG.


Can you run 2 roof A/C's on one leg of your 50 amp service (that is really the question). The answer is absolutely, unless loads are not properly divided. Said another way the let with the two A/C's should not have many other heavy amp draws-- they should be on the other leg.
__________________
Brett Wolfe
Ex: 2003 Alpine 38FDDS. Ex: 1997 Safari Sahara. Ex: 1993 Foretravel U240
wolfe10 is online now   Reply With Quote
Old 06-17-2021, 11:14 AM   #6
Senior Member
 
gnvrvin's Avatar


 
Join Date: Aug 2017
Location: Burien, Wa
Posts: 590
Is it a Hughes autformer?
Is it not boosting your voltage up?
Ours does a good job of doing so
__________________
Greg and Vicki R.
2004 Country Coach Intrigue "Sweet Serenade"
40' Tag Axle Quad slide CCI #11811
16 Jeep Wrangler, Airforce One
gnvrvin is offline   Reply With Quote
Old 06-18-2021, 07:36 AM   #7
Senior Member
 
SKP Kirk's Avatar
 
Join Date: May 2010
Location: Part-time out of Mesquite, TX
Posts: 1,091
Quote:
Originally Posted by Donfleming View Post
I have a Hughes 50 amp that shows 112 on leg 1 and 108 on leg 2 so I think it will kick me off if anything runs below 104 volts is their anything I can do?
You could just take the Hughes out and plug into the power panel directly and hope that your air conditioners don't fail today. Low voltage to an alternating current motor will cause it to draw more current and if the circuit breaker doesn't trip it will run but get hotter than it should. If the motor runs that way long enough it will shorten the life of the motor and while it may not fail today, someday it will. I worked in electrical service for 40 years and have made many repairs that were needed because of low voltage supplies.

The best answer is to first talk to the RV park to see if they can resolve your power problems. It may be that the park just doesn't have a large enough power feed to supply all of the RV air conditioners currently operating without their voltage dropping off. If so, the only fix would be to rewire the entire RV park. You may be able to move to a different site if the problem is just where you are, but that may not help you if it is the entire park. That would leave you with only the use of your onboard generator as the only good answer.
__________________
Good Travelin! Kirk
Full-time 11 years, now part-time.
Kirk & Pam's Great Adventure!
SKP Kirk is offline   Reply With Quote
Old 06-18-2021, 07:41 AM   #8
Senior Member
 
PandS's Avatar
 
Join Date: Jun 2015
Posts: 897
We have been full timing for a bit over 3 years now, and have experienced low voltage problems many times in multiple locations during that period. 50 AMP service with insufficient voltage = useless. We purchased a Hughes Autoformer, which will boost voltage up to 10%. Problem solved.


I don't know what genset you have, but we can only power 2 A/C's using our Onan 8KW, unless we shut off the battery charger, and water heater. Also would have to shut one down to cook or use the microwave.


Hope you can find a way to keep cool until you can get an Autoformer. We got ours at Camping World. Not cheap, but worth every penny. -Paul
__________________
2017 Ventana 4369
towing a 2013 Honda CRV
PandS is offline   Reply With Quote
Old 06-18-2021, 07:52 AM   #9
Senior Member
 
twojayhawks's Avatar
 
Join Date: Jul 2015
Location: Lenexa KS
Posts: 1,537
I also run three with no issues under extreme conditions. You should set fan speed to high instead of auto and that will help even more. I have yet to experience conditions where I needed three units for very long. If I did I'd start driving north
__________________
Bill & Kelli 2015 Dutch Star 4366
2002 Safari Zanzibar 3906
1995 Fleetwood Bounder 36JD
twojayhawks is offline   Reply With Quote
Old 06-18-2021, 08:33 AM   #10
Junior Member
 
Donfleming's Avatar
 
Monaco Owners Club
Join Date: Dec 2020
Posts: 3
Thanks for all the information. I do have a Autoformer so I am able to monitor on my app. I’m going to talk to the park today. I have a 10k generator so that saves the day. From all your help it seems I might just need to find another park ��. Thanks again guys.
Donfleming is offline   Reply With Quote
Old 06-18-2021, 05:31 PM   #11
Senior Member
 
CWSWine's Avatar
 
Fleetwood Owners Club
Freightliner Owners Club
Join Date: Feb 2017
Location: Manhattan (Little Apple) Kansas
Posts: 1,529
Quote:
Originally Posted by PandS View Post
We have been full timing for a bit over 3 years now, and have experienced low voltage problems many times in multiple locations during that period. 50 AMP service with insufficient voltage = useless. We purchased a Hughes Autoformer, which will boost voltage up to 10%. Problem solved.


I don't know what genset you have, but we can only power 2 A/C's using our Onan 8KW, unless we shut off the battery charger, and water heater. Also would have to shut one down to cook or use the microwave.


Hope you can find a way to keep cool until you can get an Autoformer. We got ours at Camping World. Not cheap, but worth every penny. -Paul

Thank you for the tip. I have 3 15K AC and only could run two on the 8000W generator. I just shut off the battery charger and fired up all three and worked just fine. Two on the generator will keep the temps around 74 to 76 with outside temps at 102 and 105 but nice to be able to run all three.
__________________
2017 Newmar LE 4037 - 2020 Jeep Rubicon
1994 Airstream Excella 28 Foot Project Update
2017 Ram 2500 Gas Payload 3174
CWSWine is online now   Reply With Quote
Old 06-19-2021, 08:25 AM   #12
Senior Member
 
PandS's Avatar
 
Join Date: Jun 2015
Posts: 897
Just be sure to monitor the voltage of your batteries. If you run with the charger off, they will need to be monitored.


Glad I could be of help.= Paul
__________________
2017 Ventana 4369
towing a 2013 Honda CRV
PandS is offline   Reply With Quote
Old 06-19-2021, 08:32 AM   #13
Senior Member
 
CWSWine's Avatar
 
Fleetwood Owners Club
Freightliner Owners Club
Join Date: Feb 2017
Location: Manhattan (Little Apple) Kansas
Posts: 1,529
Quote:
Originally Posted by PandS View Post
Just be sure to monitor the voltage of your batteries. If you run with the charger off, they will need to be monitored.


Glad I could be of help.= Paul

I haven't mess with anymore but I did find if you turn off the charger using the button on the Magnum control head while using AGS and the AGS shuts off and restarts the charger defaults to on when the generator restarts.
__________________
2017 Newmar LE 4037 - 2020 Jeep Rubicon
1994 Airstream Excella 28 Foot Project Update
2017 Ram 2500 Gas Payload 3174
CWSWine is online now   Reply With Quote
Old 06-19-2021, 08:43 AM   #14
Senior Member
 
2cyber71's Avatar
 
Join Date: Jul 2008
Location: Pennsylvania
Posts: 821
Below 108 volts for an extended period of time will damage your AC unit.
I set my auto-Gen at 108 for that reason.
As soon as it dips below 108 my Gen kicks in
I rather burn diesel than have a AC Unit go bad.
Just my opinion.
I’m not sure you can adjust your auto-Gen unit settings.
__________________
2020 Winnebago Horizon 42Q
Maxum Chassis, 450 ISL
99 Storm 30H, 04 Southwind 32 VS, 07 Ellipse 40FD
2cyber71 is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
"NORCOLD & DOMETIC RECALLS" & Service Manuals Norcold & Dometic "007" RV Systems & Appliances 89 07-18-2019 04:41 PM
Generator Maintenance & MANUALS Onan & Generac & PARTS "007" RV Systems & Appliances 34 07-06-2019 02:09 AM
February "Celebrity Classic" Meal Signups Madame Boomer Texas Boomers 29 02-06-2018 06:55 PM
2011 RV chassis Mods & parts & Tech info new & old chassis "007" Ford Motorhome Chassis Forum 4 09-27-2011 07:26 AM
50 amp to 30 amp to 20 amp?? fansill MH-General Discussions & Problems 5 05-15-2011 01:36 AM