Old 06-16-2018, 09:13 AM   #15
Senior Member
 
Sweetbriar's Avatar
 
Thor Owners Club
Ford Super Duty Owner
Join Date: Jul 2011
Posts: 3,795
I have also run both 13.5K BTU roof A/C's off 30 amps. Water heater on propane and a full charge on the battery bank before switching on A/C #2 (limit power demand of the converter). Fridge is residential. Highest steady power demand I've measure has been 24 amps.
__________________
2006 Hurricane 31D built on a 2006 Ford F53
Sweetbriar is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-16-2018, 09:23 AM   #16
Senior Member
 
Mr_D's Avatar
 
Country Coach Owners Club
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 37,725
Our '02 DSDP had two 13.5 heat pumps. Ran both of them on 30 amp regularly with no problems other than having to watch how much other stuff we tried to run.
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft, HWH Active Air
Charter Good Sam Lifetime Member, FMCA,
RV'ing since 1957, NRA Benefactor Life, towing '21 Jeep JLU Rubicon Ecodiesel
Mr_D is offline   Reply With Quote
Old 06-16-2018, 07:59 PM   #17
Senior Member
 
Join Date: Nov 2005
Posts: 3,968
We have 2 Coleman 13,500 btu Mach 8 air conditioners on our 2013 Winnebago Adventurer. The maximum draw in the cooling mode is 14.1 amps at startup. If you have similar AC units and stagger the startup you should be able to run both on a 30 amp service. We run both of ours regularly on a 30 amp service with no problems.

Some older units draw more at startup and when running, so I would say it depends on the age and model AC units you have.
__________________
Hikerdogs
2013 Adventurer 32H
Hikerdogs is offline   Reply With Quote
Old 06-16-2018, 09:14 PM   #18
Senior Member
 
Join Date: Apr 2016
Posts: 446
On my coach I can not run two air conditioners which are also heat/pumps with 30 amp. I need 50 amps. I would think you are taking a chance of burning up an electric motor.
__________________
2002 Gulf Stream Scenic Cruiser 38'
Neway Freightliner chassis, 2018 Buick Envision Ess.
3126-E Caterpillar 330 hp
RayChez1 is offline   Reply With Quote
Old 06-17-2018, 05:15 AM   #19
Senior Member
 
scbwr's Avatar
 
Join Date: Jul 2013
Location: North Ridgeville, OH
Posts: 2,455
I'm a newbie to motorhomes, but I'm surprised that no one has mentioned energy management systems. Don't many motorhomes have energy management systems that control AC use to avoid problems? Therefore, it would depend on whether the OP's coach has an energy management system.
I'm certainly interested in hearing what experienced owners have to say about this.
__________________
Retired but busier than ever!
2012 Newmar Bay Star 3302
5 Star Tune, SumoSprings, Roadmaster Steering Stabilizer, Blue Ox Avail
Brake Buddy, 2015 Chevy Malibu
scbwr is offline   Reply With Quote
Old 06-17-2018, 09:06 AM   #20
Senior Member
 
Bloodyhell's Avatar
 
Join Date: Jun 2012
Posts: 210
The EMS in my coach tells me that my two A/C heat pump units use 24 amps together. The seasonal spot where we keep it when we’re not traveling has a 30 amp service and that really has very little effect on anything in practice. Occasionally it will shed the water heater or the refrigerator when we are using them with the microwave or the coffeemaker, but there is no real discernible effect. The campground has offered to upgrade our service, but we haven’t had them bother with it.
Bloodyhell is offline   Reply With Quote
Old 06-17-2018, 10:20 AM   #21
Senior Member
 
Join Date: Apr 2016
Posts: 446
It is true that some of these gasoline motor homes have smaller air conditioning units with smaller motors to save, they are called energy management systems. But most of your top end coaches have the heavier units and do require 50 amps.
You got to be careful when an electric motor is not getting enough amps, it will start to drag and eventually something has to give. Usually it will kick the circuit breaker, but at the same time it is causing damage to the motor.
__________________
2002 Gulf Stream Scenic Cruiser 38'
Neway Freightliner chassis, 2018 Buick Envision Ess.
3126-E Caterpillar 330 hp
RayChez1 is offline   Reply With Quote
Old 06-21-2018, 06:28 AM   #22
Senior Member
 
JLWoodward's Avatar
 
Join Date: Nov 2016
Posts: 377
Ray. My class A coach will run on 30 amp. Ems refers to coach system that will shed other loads and not let both ac units start at same time if theirs not enough amps. Usually if I’m on 30 amp I run water heater and fridge off of the propane. The late model class A’s do have higher amp loads. Some have three ac’s. Floor radiant heat, etc, etc. not sure one of those could run off of 30 amp but in theory their load shed ems systems should all work in same way and protect system from overload by shedding loads to keep under 30 amp.
JLWoodward is offline   Reply With Quote
Old 06-21-2018, 08:51 AM   #23
Senior Member
 
OLYLEN's Avatar
 
Monaco Owners Club
Join Date: Jan 2008
Location: Olympia, Wa
Posts: 2,772
Yes I did it all the time, BUT, watch the voltage. Problem is as more other RVs next to you use power many times the voltage drops. As voltage drops amp draw goes up and according to specs below 108 volts you run the risk of AC damage. I use a Kill-a-Watt volt meter to see voltage and have in the high use hot afternoon or evening run the Gen to have both AC's run.

LEN
__________________
2004 Clss C 31' Winnebgo
OLYLEN is offline   Reply With Quote
Old 06-21-2018, 08:59 AM   #24
Senior Member
 
Join Date: Oct 2014
Location: Port Orchard, WA
Posts: 4,217
Quote:
Originally Posted by critterair2 View Post
Coach has 50A service but on our 5 week planned trip we have one CG that only has 30A service. We have 2 AC units 13,500 each. Hot water heater I can run off propane. Will 30A run both AC units at the sane time? Only other draw would be tv's. We can deal w/o microwave for one night if we need to or shut off one AC unit while micro is in use.
We have personally done exactly what you describe above on 30 amps with no issues, on multiple occasions. As stated, we will generally shut down one AC unit if using the microwave, or the coffee pot, but other than that, we've even run the water heater (accidentally) on electric at the same time and not had a problem. We have two 15k btu heat pumps.

Hope this helps!
__________________
Scot & Laura Kellersberger, U.S. Army (ret)
Newmar 4 wheel drive Dutch Star 3891, SOLD
Now RV'ing on the water in a Trawler!
Hit_the_Rhod is offline   Reply With Quote
Old 06-21-2018, 01:40 PM   #25
Senior Member
 
Bob Hyatt's Avatar
 
Tiffin Owners Club
Join Date: Apr 2018
Location: Pelham (Birmingham) AL
Posts: 400
Quote:
Originally Posted by critterair2 View Post
Coach has 50A service but on our 5 week planned trip we have one CG that only has 30A service. We have 2 AC units 13,500 each. Hot water heater I can run off propane. Will 30A run both AC units at the sane time? Only other draw would be tv's. We can deal w/o microwave for one night if we need to or shut off one AC unit while micro is in use.
I was just in a CG with the same issue. 30A. I have a 13.5K BTU rear A/C and a 15.0K BTU front unit. We ran them both with no problems. But I can set the power system to tell it there is only 30a available and it will figure out what to do, except (apparently) when the electric option on the water heater kicks on and both of the A/Cs are running. But with the water heater on propane, we had zero problems with 2 A/Cs running + TVs, Lights (LEDs everywhere in coach) and such. Used the microwave a couple of times but can not say for sure what else was running or was shut off automatically. The WH tripped the 30a breaker once before I set it to propane only.

You should not have much of a problem, and it was pretty hot this past week in Central Alabama where we were...
__________________
Bob Hyatt
2018 Tiffin Allegro 32SA
Bob Hyatt is offline   Reply With Quote
Old 06-21-2018, 01:49 PM   #26
Member
 
Join Date: Mar 2018
Posts: 38
Spoke with manufacturer, was hoping I could isolate the batteries so they wouldn't charge until I wanted them to. That way I could run lights and fridge off the batteries, hot water heater on propane and all 30A would run is tv's, AC units and microwave. Obviously I can load shed those 3 items as needed. May just run genny during hot part of day and one AC unit at night. May turn AC unit to like 55 degrees so it comes on and stays on instead of cycling.
critterair2 is offline   Reply With Quote
Old 06-22-2018, 07:52 AM   #27
Senior Member
 
JLWoodward's Avatar
 
Join Date: Nov 2016
Posts: 377
Quote:
Originally Posted by critterair2 View Post
Spoke with manufacturer, was hoping I could isolate the batteries so they wouldn't charge until I wanted them to. .

Seems like this should be possible via a switch controlled contactor installed on output of charger Line to batteries.
JLWoodward is offline   Reply With Quote
Old 06-22-2018, 09:06 AM   #28
Senior Member
 
Bob Hyatt's Avatar
 
Tiffin Owners Club
Join Date: Apr 2018
Location: Pelham (Birmingham) AL
Posts: 400
Quote:
Originally Posted by critterair2 View Post
Spoke with manufacturer, was hoping I could isolate the batteries so they wouldn't charge until I wanted them to. That way I could run lights and fridge off the batteries, hot water heater on propane and all 30A would run is tv's, AC units and microwave. Obviously I can load shed those 3 items as needed. May just run genny during hot part of day and one AC unit at night. May turn AC unit to like 55 degrees so it comes on and stays on instead of cycling.
My EMS control panel lets me turn the charger off with the push of a button, although it is smart enough to figure out it can't run a heavy-duty bulk charge while two A/C units are running.
__________________
Bob Hyatt
2018 Tiffin Allegro 32SA
Bob Hyatt is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Use of 50A Surge Protector with 30A Pigtail for 30A Shore Power hugh37 Newmar Owner's Forum 9 07-08-2016 01:14 PM
Is it possible to convert a 30A coach to 50A? D-n-Tyke Class A Motorhome Discussions 9 01-10-2011 10:38 PM
30A to 50A Step Up Transformer? Houdini52 5th Wheel Discussion 53 12-04-2010 08:06 PM
Power Monitor showing 50A service when on 30A service Yoda2405 RV Systems & Appliances 3 10-26-2010 03:08 AM
Intellitec Power Monitor shows 50A when on 30A Power Yoda2405 Winnebago Industries Owner's Forum 0 10-22-2010 08:54 PM