05-14-2016, 09:04 PM
|
#15
|
Senior Member
Join Date: Aug 2001
Location: North America somewhere
Posts: 32,318
|
Just an aside to your 30A RV; NEVER plug your RV into a 3-prong home electric dryer receptacle! It is 220VAC on that one leg. You will ruin your RV electrics, at least the majority of it.
__________________
2000 Winnebago Ultimate Freedom USQ40JD , ISC 8.3 Cummins 350, Spartan MM Chassis. USA IN 1SG 11B5MX,Infantry retired;GS Life member,FMCA " My fellow Americans, ask not what your country can do for you, ask what you can do for your country. John F. Kennedy
|
|
|
 |
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
05-14-2016, 09:44 PM
|
#16
|
Senior Member
Tiffin Owners Club Freightliner Owners Club
Join Date: Apr 2012
Posts: 2,079
|
I am assuming that he is going to use a 30 amp power cord and put a 50 amp plug on the end of it. I for one never ever advocate putting a 30 amp cord or service on 50 amp breaker. You should never have a breaker that will handle more current than the wiring that is attached to it. It is dangerous and a possible fire hazard.
__________________
2005 Allegro Bus 38DP
2012 Enclave tow vehicle
No Dogs, No cats.
|
|
|
05-15-2016, 01:33 AM
|
#17
|
Senior Member
Join Date: Oct 2011
Location: Central, SC
Posts: 762
|
Quote:
Originally Posted by Ray,IN
Just an aside to your 30A RV; NEVER plug your RV into a 3-prong home electric dryer receptacle! It is 220VAC on that one leg. You will ruin your RV electrics, at least the majority of it.
|
Ray, you a right and wrong. Yes it will ruin lots of things in your RV, but there is not a hot leg with 220. There are 2 hot legs out of phase instead of one hot and one neutral. If you test from the ground to either hot leg you should get 120 and across the two hots, 240.
1997 Tiffin Allegro Bus 37', Cat 3126
|
|
|
05-15-2016, 04:41 AM
|
#18
|
Senior Member
Join Date: Aug 2001
Location: North America somewhere
Posts: 32,318
|
Quote:
Originally Posted by rssnape
Ray, you a right and wrong. Yes it will ruin lots of things in your RV, but there is not a hot leg with 220. There are 2 hot legs out of phase instead of one hot and one neutral. If you test from the ground to either hot leg you should get 120 and across the two hots, 240.
1997 Tiffin Allegro Bus 37', Cat 3126
|
Thanks for catching my mistake. That's what I get for overthinking.
gemini5362, It's perfectly OK to run 30A circuit from a 50A breaker when the 30A circuit is protected by a 30A breaker, which is true in this instance. It's no different than your house attached to the power grid.
__________________
2000 Winnebago Ultimate Freedom USQ40JD , ISC 8.3 Cummins 350, Spartan MM Chassis. USA IN 1SG 11B5MX,Infantry retired;GS Life member,FMCA " My fellow Americans, ask not what your country can do for you, ask what you can do for your country. John F. Kennedy
|
|
|
05-15-2016, 05:35 PM
|
#19
|
Senior Member
Fleetwood Owners Club Workhorse Chassis Owner
Join Date: Feb 2000
Location: Lewisburg, TN, USA
Posts: 2,819
|
Quote:
Originally Posted by gemini5362
I am assuming that he is going to use a 30 amp power cord and put a 50 amp plug on the end of it. I for one never ever advocate putting a 30 amp cord or service on 50 amp breaker. You should never have a breaker that will handle more current than the wiring that is attached to it. It is dangerous and a possible fire hazard.
|
By that thinking one should never plug a phone charger in to a standard wall outlet - the outlet is protected by a 15A breaker, but the charger is only 1A or so.
__________________
Alan Hepburn - Lewisburg, TN
2007 Bounder 35E being pushed by a 2020 Jeep Gladiator Sport S or a 2022 Jeep Wrangler Unlimited (JLU) Sport S
|
|
|
 |
|