Old 07-14-2017, 05:54 AM   #43
Senior Member
 
triplewide's Avatar
 
Join Date: Mar 2015
Location: Greensboro, NC
Posts: 2,738
Is the pedestal GFI protected?

Sounds like you have a 30 amp to 50 amp adapter with the ground prong removed. It is plugged in to a 30 amp 3 prong receptacle, Hot, Neutral, and Ground.

Does the breaker servicing the 30 amp receptacle have a "test" or "reset" button? If so it is probably GFI protected. Some different brands:

https://www.amazon.com/Cutler-Hammer...mp+GFI+breaker

https://www.amazon.com/QO130GFI-Squa...mp+GFI+breaker

https://www.amazon.com/Siemens-QF130...mp+GFI+breaker

https://www.amazon.com/GE-THQL1130GF...mp+GFI+breaker


A GFCI monitors the amount of current flowing from hot to neutral. If there is any imbalance, it trips the circuit. It is able to sense a mismatch as small as 4 or 5 milliamps, and it can react as quickly as one-thirtieth of a second.

With the ground prong removed from the adapter it does not provide equipment ground to the RV. It will still trip if current through the hot leg does not return through the neutral, providing protection from shock between hot leg and earth ground.

If it is GFI, motor loads may cause it to trip. Refrigerators in s&b homes are a common cause. Original post indicates a residential frig in the RV. If the frig is powered directly from 120 volt panel it may be the culprit. 1-3 hours between shutdowns - could be the frig compressor kicking in at those intervals.

Maybe running the frig off your inverter would work, if possible.
__________________
1998 Min Winnie, 2000 Winbago Journey, 2015 ACE 29.3
2016 Thor Miramar 34.2
triplewide is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-14-2017, 07:35 AM   #44
Senior Member
 
bobgio's Avatar
 
Fleetwood Owners Club
Join Date: May 2015
Location: Wakefield, MA
Posts: 160
Thank you all for a great thread. Triplewide, Great stuff. Yes I have the dogbone 50 to 30 attached to an adapter with the ground prong removed and then to a 30A adapter all taped up and attached tightly. Since that configuration the pedestal breaker has not tripped. Neither has the GFI tripped that is on the pedestal. I am now sitting in the rain and cannot do too much more troubleshooting. At least I have power in the coach. Question: If I have an opportunity to detach from the pedestal and run the gennie for a few hours and it does not trip a Coach breaker would that tell me the problem is with the Pedestal? I would like to find out before I move on in two weeks to another CG with 50A and discover I have a problem in the coach.
__________________
2015 Fleetwood Bounder 33C
F53 Roadmaster Trac Bar
bobgio is offline   Reply With Quote
Old 07-14-2017, 08:39 AM   #45
Senior Member
 
hohenwald48's Avatar
 
Join Date: Jan 2017
Location: Titusville, FL
Posts: 5,160
I don't think I'd be opening the coach door from the outside in bare feet with the ground removed.
__________________
When seconds count, the police are only minutes away.
2023 Grand Design 2600RB, 2022 F-350 King Ranch tow vehicle, Titusville, FL when not on the road
hohenwald48 is offline   Reply With Quote
Old 07-14-2017, 09:03 AM   #46
Senior Member
 
Sbrownstein's Avatar
 
Ford Super Duty Owner
Join Date: Dec 2010
Posts: 1,799
Seems to me you have never tripped your 50 amp breaker in the RV. I am very surprised that the pedestal has a GFCI, normally they don't. If you had said that from the beginning (I think I looked) it would have been a different conversation. Personally I hate GFCIs as while they do protect you, they are prone to all kinds of spurious trips.

Disconnect and run the genny. Chances are you can do that while still connected (most transfer switches have the genny set as priority) but it is safer to disconnect first.
__________________
Scott Brownstein
Palm Island, Florida
2015 Georgetown 335DS
Sbrownstein is offline   Reply With Quote
Old 07-14-2017, 11:45 AM   #47
Senior Member
 
8TiresRollin's Avatar
 
Join Date: Nov 2016
Location: Calgary, AB
Posts: 206
Send a message via Skype™ to 8TiresRollin
"Could be a continuation of a bonded generator connection however."

The generator neutral ground should be grounded at the generator on the generator side of the transfer switch. That way it does not affect the system when you are plugged into shore power as the generator is isolated through the transfer switch. With the ground pin removed I would be cautious without the ground due to safety issues. A GFCI breaker works by comparing how much current is flowing back through the neutral compared to what is going out on the Line. If the difference is >3-5mA (as stated earlier) then the breaker trips as the difference will be flowing via the ground wire back to the pedestal. Hence the term "Ground Fault" breaker. So by removing the ground pin from the circuit you create a safety issue as you have stopped the flow of current through the ground. Check with a voltmeter the difference between something metal on your coach and the metal box on the pedestal. DO NOT TOUCH BOTH AT THE SAME TIME with your person. That is how plumbers used to get killed with metal drain pipes decades back when they cut them. If you see a potential (IE measured voltage between the two) then immediately turn off the pedestal breaker and disconnect your shore power. You have a serious problem. I still say you have either a bad connection in the neutral somewhere or a faulty appliance or piece of equipment that is the problem. The GFCI is just doing it's job. Try that voltmeter, with that ground as is for now, but like I said don't touch both the motorhome and the pedestal at the same time.
Don't know what makes me say this - but check that adapter 50-30A as sometimes they can have issues as well. See if some other friendly camper can lend you theirs for a few minutes and see if that makes a difference.
__________________
Barry & Cindy
2008 Dutch Star 4304, Cider color
Cummins ISL 425, 2013 Passat TDI Toad
8TiresRollin is offline   Reply With Quote
Old 07-15-2017, 04:15 AM   #48
Senior Member
 
triplewide's Avatar
 
Join Date: Mar 2015
Location: Greensboro, NC
Posts: 2,738
Your pedestal has GFI and your RV breakers is probably not. Your pedestal is tripping and your RV is not. Removing the ground prong on your adapter stops the tripping. I think these details indicate that the pedestal is/was tripping due to ground fault not over current.

Your RV circuit breakers that feed the frig and any other motor loads are probably not GFI and therefore will not trip when on geny.

In the future, if you are in a park that does not have GFI pedestal breakers you probably will not have an issue.

If you could get the current park to install a non GFI breaker, you could determine if it is over current or ground fault causing the tripping. Park may not be willing to do this.

A way to test:

Turn off your frig.
Replace the altered adapter with a good one.
Turn power on, wait 1-3 hours, see if breaker trips.
If it does you know it is not the frig.
If it doesn't, turn the frig on, if it trips you know for sure whats up.
__________________
1998 Min Winnie, 2000 Winbago Journey, 2015 ACE 29.3
2016 Thor Miramar 34.2
triplewide is offline   Reply With Quote
Old 07-15-2017, 04:56 AM   #49
Senior Member
 
Busskipper's Avatar
 
Join Date: Sep 2007
Location: Grasonville, MD -- Golden, CO
Posts: 6,222
Quote:
Originally Posted by bobgio View Post
Thank you all for a great thread. Triplewide, Great stuff. Yes I have the dogbone 50 to 30 attached to an adapter with the ground prong removed and then to a 30A adapter all taped up and attached tightly. Since that configuration the pedestal breaker has not tripped. Neither has the GFI tripped that is on the pedestal. I am now sitting in the rain and cannot do too much more troubleshooting. At least I have power in the coach. Question: If I have an opportunity to detach from the pedestal and run the gennie for a few hours and it does not trip a Coach breaker would that tell me the problem is with the Pedestal? I would like to find out before I move on in two weeks to another CG with 50A and discover I have a problem in the coach.
I'm not into all this Electro Speak - BUT - if it works on the Genny then the "PROBLEM" IMHO is not in the Coach.

? so ask the Park electrician Why/How can it work when you supply your own power and disconnect from His?

I'm no Rocket Scientist, but that sure seems to follow MY logic.

So again - they need to FIX the Electric on the Pedestal.

? Only other explanation is the 50 - 30 might be wired incorrectly or be Faulty.

Best of Luck,
__________________
Busskipper
Location - Grasonville, Maryland - and/or - Superior, Colorado
2005 Travel Supreme 42DS04 - GX470 Toad
Busskipper is offline   Reply With Quote
Old 07-15-2017, 08:31 AM   #50
Senior Member
 
imUrlaub's Avatar
 
Tiffin Owners Club
Join Date: Jul 2017
Posts: 123
This last comment makes sense and is the kind of logical approach a home owner or consumer can follow. As a supplement, the wire bypassed isn't the ground conductor it is the grounding conductor and they are different! The grounding conductor on an appliance cord for instance is that third part of the plug usually rounded. When you have a 2 wire receptacle then one gets an adapter so it can be used. Not all appliances have them. But, if an appliance has exposed metal parts then the cord will usually have that third prong. The idea is that if a fault occurs the current will get shunted to ground. The fault will cause a short of voltage to ground causing very high and brief current as the breaker trips. This is the same principle as a GFCI. The GFCI will sense the load of the appliance as the current traveling from the ungrounded conductor (hot) to the grounded conductor (neutral). When a fault happens because a user becomes a conductor the the GFCI senses a load imbalance between the grounded conductor and the grounding conductor (you) and trips at 3-5 ma. When the grounding wire was interrupted at the source the fault was not allowed to ground and no trip. This isn't a wiring issue. I suspect a faulty capacitor, used to start single phase motors like your refrigerator, heating blower, AC, etc. Your generator can handle this since it isn't tied to ground.
imUrlaub is offline   Reply With Quote
Old 07-15-2017, 08:34 AM   #51
Senior Member
 
Sbrownstein's Avatar
 
Ford Super Duty Owner
Join Date: Dec 2010
Posts: 1,799
Generally your generator is bonded to ground. The difference here is that when you are using your generator there is no GFCI involved. Frankly I am surprised that the pedestal had a GFCI and if the OP had mentioned that to start, this would have been a much shorter thread.
__________________
Scott Brownstein
Palm Island, Florida
2015 Georgetown 335DS
Sbrownstein is offline   Reply With Quote
Old 07-15-2017, 09:13 AM   #52
Senior Member
 
imUrlaub's Avatar
 
Tiffin Owners Club
Join Date: Jul 2017
Posts: 123
Quote:
Originally Posted by Sbrownstein View Post
Generally your generator is bonded to ground. The difference here is that when you are using your generator there is no GFCI involved. Frankly I am surprised that the pedestal had a GFCI and if the OP had mentioned that to start, this would have been a much shorter thread.


Ground so far as the coach is concerned but unless you have a bond to earth the tires act as insulation.
imUrlaub is offline   Reply With Quote
Old 07-15-2017, 09:22 AM   #53
Senior Member
 
Join Date: Jul 2014
Posts: 35,348
There have been at least 3 posts in recent months about State CGs having GFCI breakers on there 30 amp service and then tripping.

That is why I asked that question in post #2. If that question would have been answered, this post may have been helpful in finding a fix.

With 3 questions about 30 amp GFCIs, on this fourm alone, it seems to be a trend of State parks doing this. There must be a fix, besides cutting the ground pin off the plug.
twinboat is offline   Reply With Quote
Old 07-15-2017, 09:28 AM   #54
Senior Member
 
imUrlaub's Avatar
 
Tiffin Owners Club
Join Date: Jul 2017
Posts: 123
Quote:
Originally Posted by twinboat View Post
There have been at least 3 posts in recent months about State CGs having GFCI breakers on there 30 amp service and then tripping.

That is why I asked that question in post #2. If that question would have been answered, this post may have been helpful in finding a fix.

With 3 questions about 30 amp GFCIs, on this fourm alone, it seems to be a trend of State parks doing this. There must be a fix, besides cutting the ground pin off the plug.


That is a good comment. Generally, GFCI's of the 220v variety seem rare to me but then I don't have the experience of other RV'ers here. In a former life, I designed and implemented bot single phase and three phase high load GFCI's in the field. They were expensive to build and maintain. They also needed to be replaced a lot.
imUrlaub is offline   Reply With Quote
Old 07-15-2017, 11:00 AM   #55
Senior Member
 
hohenwald48's Avatar
 
Join Date: Jan 2017
Location: Titusville, FL
Posts: 5,160
A couple of questions -

(1) Is the GFCI the problem or is it simply an indication of a wiring problem within the coach or the adapters being used?

(2) Regardless of the answer to (1), why does it take an hour or more for the GFCI to trip? Seems it should trip instantly when connected.
__________________
When seconds count, the police are only minutes away.
2023 Grand Design 2600RB, 2022 F-350 King Ranch tow vehicle, Titusville, FL when not on the road
hohenwald48 is offline   Reply With Quote
Old 07-15-2017, 11:06 AM   #56
Senior Member
 
Sbrownstein's Avatar
 
Ford Super Duty Owner
Join Date: Dec 2010
Posts: 1,799
GFCIs can trip for lots of reasons and only some are dangerous. That reefer has an inverter driven compressor and GFCIs are known for nuisance tripping when voltage and current are out of sync. Once every 3 hours could merely be the compressor starting at high speed. Who knows?
__________________
Scott Brownstein
Palm Island, Florida
2015 Georgetown 335DS
Sbrownstein is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Use of 50A Surge Protector with 30A Pigtail for 30A Shore Power hugh37 Newmar Owner's Forum 9 07-08-2016 01:14 PM
Is it possible to convert a 30A coach to 50A? D-n-Tyke Class A Motorhome Discussions 9 01-10-2011 10:38 PM
30A to 50A Step Up Transformer? Houdini52 5th Wheel Discussion 53 12-04-2010 08:06 PM
Power Monitor showing 50A service when on 30A service Yoda2405 RV Systems & Appliances 3 10-26-2010 03:08 AM
Intellitec Power Monitor shows 50A when on 30A Power Yoda2405 Winnebago Industries Owner's Forum 0 10-22-2010 08:54 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 04:01 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.