Question Capacitor specifications for Coleman Mach model 6636-871

From the circuit diagram sticker - it says the run capacitors for the compressors are supposed to be 30uF/370V...


Can someone tell me what YOUR unit or schematic indicates for the starter capacitors?


One of my compressors just hums and draws 50A when it tries to start, the other pulls a LOT of power during startup - so much that the inside fan almost stop but once started, it runs well!


I've measured the resistance over both the run and start coils and they seem fine - measuring thru start to run coil gives me roughly the total of the resistance the two - so that seems fine... My meter is not able to measure any resistance to ground (open circuit as one would hope to find)


I tried swapping the compressor / circuit feeding it and get the same result so in my mind - there's got to be something going on in the compressor.


With summer heat around the corner in Florida - I would LOVE to get the second compressor/cooling circuit up and running as the ONE is barely keeping up.


Any insight/suggestions is appreciated!
__________________
1999 P12 Winnebago Vectra Grand Prix 37B
anders_g is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 04-08-2021, 01:09 PM   #2
Senior Member
 
153stars's Avatar
 
Join Date: Mar 2019
Location: Braidwood Il.
Posts: 2,808
I searched your model it lists three of the caps specs but only start kit . I couldn't share link for PDF for some reason. I just googled the model start capacitor. Found spare parts page.The start capacitors may have the pcr on them like a hard start cap and don't want to publish spec. because there's no circuit to take it back out.
I would ask anyone if they have added a Supco hard start to one.
I take it this is a basement air some owners may not have their model memorized and not know they can possibly help you. I know there have been at least one rebuild threads on similar basement are.
Not that's it's a lot of help.I can tell you many dual caps are the start is about four times the run side but I'm surprised the run caps are 30uf but they are big compressors for 120v.
__________________
95 Monaco Crown Royale
M11 400hp, 4060 trans.
Aquahot, Generac Guardian7.5k
153stars is offline   Reply With Quote
Old 04-08-2021, 01:20 PM   #3
Junior Member
 
Join Date: Jan 2021
Posts: 24
Question

Correct - this is the 2ton double two-circuit basement model (mine has the "cold vent" pointing to the "left/rear" when you look at it from the front)


That is correct - it has three capacitors, one for the inside blower (i think), then two sets of capacitors (one for each compressor) containing of one run capacitor plus a starting capacitor with a PTCR "switch" (variable resistor that is low ohm when cold and "cut out"/high resistance once current has warmed it up..


Its a shame you can't reach inside the compressor and "spin it" to see if it was locked up or something like that..


Much appreciated!
__________________
1999 P12 Winnebago Vectra Grand Prix 37B
anders_g is offline   Reply With Quote
Old 04-08-2021, 06:26 PM   #4
Senior Member
 
153stars's Avatar
 
Join Date: Mar 2019
Location: Braidwood Il.
Posts: 2,808
It sounds like you could substitute a supco hard start directly . They normally stack on the run side cap because of circuit that takes start cap back out prevents from being properly charged when needed. I supposed could draw power instead. Is the issue you can't find the right cap" the search I did show a part # possibly aftermarket" or are they ridiculously priced to just test it. I'm assuming swapping circuits didn't mean swapping caps as your suspecting it.
I have found spades completely cooked or just plain loose in HVACs , chillers. Not a big fan of them in high current use. I know these are not the easiest ACs to to work on, hope its just the cap.
This comes up as a hard start kit listed to fit you model probably slightly larger cap than stock but smaller than most supco hard starts at triple the price. Also not a fan these caps compared to can type. We have used hard start kits in many ACs and gotten far more life out of mostly large window / wall slide in units that are all over our plant now. Every so many years you can't find same dimension unit any longer then you have to alter the through wall installation.
https://parts.unitedrv.com/products/...pacitor-w-ptcr
__________________
95 Monaco Crown Royale
M11 400hp, 4060 trans.
Aquahot, Generac Guardian7.5k
153stars is offline   Reply With Quote
Old 04-08-2021, 06:37 PM   #5
Senior Member
 
Xmcdog's Avatar
 
Join Date: Dec 2019
Location: Nova Scotia
Posts: 1,419
Sounds like a stuck compressor. A hard start kit may work. Worth a try.
Otherwise you are looking at a replacement compressor or unit.
Good luck
__________________
Jeff and Annette Smith
04 Glendale Titanium 24E29 Fifth
2011 GMC Diesel 2500 HD
Xmcdog is offline   Reply With Quote
Old 04-08-2021, 08:43 PM   #6
Junior Member
 
Join Date: Jan 2021
Posts: 24
This might sound silly - but, what would happen if you add TWO hardstart kits, JUST for testing to see if a stuck compressor might come back to life?
__________________
1999 P12 Winnebago Vectra Grand Prix 37B
anders_g is offline   Reply With Quote
Old 04-08-2021, 08:49 PM   #7
Senior Member
 
Ray Lenning's Avatar
 
National RV Owners Club
Join Date: Sep 2018
Posts: 128
Here is a part list but it doesn't call out the start capacitor capacity . Just calls the a start device .
Attached Files
File Type: pdf Colman Mack Parts.pdf (530.7 KB, 7 views)
File Type: pdf 6535heatpump.pdf (1.00 MB, 5 views)
__________________
Ray & Melinda
2005 National Dolphin 5355 (MEPAW) , Koni FDS shocks, Safe-T-Plus , Rear track bar , Sumo springs . She tows a 2006 Tacoma 4X4
Ray Lenning is offline   Reply With Quote
Old 04-09-2021, 03:42 AM   #8
Senior Member
 
153stars's Avatar
 
Join Date: Mar 2019
Location: Braidwood Il.
Posts: 2,808
I can't remember if the Supco 5 or 6 is largest for 120v comp. but I can't imagine any larger or two will do anything else. If your not on 30 or 50 amp cord start your genny. Replace the run as well it gives a little kick, get decent quality no need for OEM they don't make them. Should be able to get both for $30-$40



Quote:
Originally Posted by anders_g View Post
This might sound silly - but, what would happen if you add TWO hardstart kits, JUST for testing to see if a stuck compressor might come back to life?
__________________
95 Monaco Crown Royale
M11 400hp, 4060 trans.
Aquahot, Generac Guardian7.5k
153stars is offline   Reply With Quote
Old 04-09-2021, 04:44 AM   #9
Junior Member
 
Join Date: Jan 2021
Posts: 24
Exclamation

Heeey now! That's a great idea too.. I'll turn the RV around and use the shortest possible shore cord DIRECTLY to the A/C! My outlet box is actually mounted on the outside wall within a foot or two from the electric meter with a 100A service so I can't get much cleaner/stronger power than that


I'm going to get my second COVID 19 shot this afternoon so i probably won't get out there until tomorrow to test this ;-)


I'll let y'all know how it goes!! Thanks :-)
__________________
1999 P12 Winnebago Vectra Grand Prix 37B
anders_g is offline   Reply With Quote
Old 04-10-2021, 10:48 AM   #10
Senior Member
 
153stars's Avatar
 
Join Date: Mar 2019
Location: Braidwood Il.
Posts: 2,808
When you say you swapped controls to compressor you probably didn't swap start car did you? If start cap is dead it's not gonna want bump over. Just making sure your not on a 50' 16ga cord.
Don't draw FLA locked rotor amps too much before getting/trying a new cap.
I don't how well you can inspect connections inside but I have run across many bad spades on high amp side.
__________________
95 Monaco Crown Royale
M11 400hp, 4060 trans.
Aquahot, Generac Guardian7.5k
153stars is offline   Reply With Quote
Old 04-10-2021, 10:59 AM   #11
Junior Member
 
Join Date: Jan 2021
Posts: 24
Iím waiting for the Supco 6 to be delivered. When I ďswappedĒ / I basically swapped the two compressors leads so that everything controlling #1 instead controlled #2.

Whenever I test, I donít think Iíve left it longer that 0.5-1 second. The plan is:
* Good power
* All caps replaced
* Supco added to both compressors

Iíll try that one the sun gets lower

The unit is encapsulated so if this doesnít work, Iím going to pull it. Hopefully the nit has service valves (Iíd like to check the working circuit anyway)

Thank You !

Quote:
Originally Posted by 153stars View Post
When you say you swapped controls to compressor you probably didn't swap start car did you? If start cap is dead it's not gonna want bump over. Just making sure your not on a 50' 16ga cord.
Don't draw FLA locked rotor amps too much before getting/trying a new cap.
I don't how well you can inspect connections inside but I have run across many bad spades on high amp side.
anders_g is offline   Reply With Quote
Old 04-10-2021, 02:53 PM   #12
Junior Member
 
Join Date: Jan 2021
Posts: 24
I just got my delivery of the SPP6's but just as I got home - a storm has moved in.. I'll have to check it in the morning... Just FYI; the SP6 has a Cap of 160uF in it
__________________
1999 P12 Winnebago Vectra Grand Prix 37B
anders_g is offline   Reply With Quote
Old 04-11-2021, 05:26 PM   #13
Junior Member
 
Join Date: Jan 2021
Posts: 24
We had storms come thru overnight and this morning so I'm just back from being outside... Both compressors are withing +-0.1 ohm of each other both on start and run coil... I replaced both RUN and START caps on both circuits (I know, stoopid - don't touch it if it works!) and added the SPP6. The first compressor came on nicely.. When the second tried to kick in - it just hummed for a few seconds (1-3) and then shut off and tried again in about 30 seconds. After two of those cycles I pulled the nine pin connector that comes from the vehicle/thermostat to shut the whole thing down...


Sat and scratched my head for a while, took a walk-a-bout and when I got back, about an hour later - and plugged the 9 pin connector back in - everything is DEAD!?


I don't get the green OR red LED.. I checked supply power - beautiful 120volt even when i started the waterheater...


Checking the board - i found that it is the 6535C320 and found it here:
https://www.rvcomfort.com/pdf_documents/6535c3209.pdf


It tells me everything about how to convert a prior version of this board this this version (that PO must have had done)... Does anyone know what the pins in the 9 pin connector are? Knowing what I do now - i am going to push on WITHOUT the control board to see if I can just get the compressor to start - wired with JUST inbound power, run/start cap AND the SPP6... (That'll be next weekend)
__________________
1999 P12 Winnebago Vectra Grand Prix 37B
anders_g is offline   Reply With Quote
Old 04-11-2021, 05:53 PM   #14
Senior Member
 
Ray Lenning's Avatar
 
National RV Owners Club
Join Date: Sep 2018
Posts: 128
Anders , check my post above , the second file has the pin out for the connector .
__________________
Ray & Melinda
2005 National Dolphin 5355 (MEPAW) , Koni FDS shocks, Safe-T-Plus , Rear track bar , Sumo springs . She tows a 2006 Tacoma 4X4
Ray Lenning is offline   Reply With Quote
Reply

Tags
cat, coleman



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Alternative thermostat for 6636-3441 FiveOhRanger RV Systems & Appliances 4 06-07-2020 07:09 PM
Coleman Mach Basement Air Unit Capacitor Repair AKIQPilot Winnebago Industries Owner's Forum 30 08-17-2019 02:25 PM
start capacitor coleman mach a/c bdba673 RV Systems & Appliances 8 04-21-2014 10:01 AM
Coleman Mach Air conditioner Capacitor and wiring treetop Travel Trailer Discussion 7 06-25-2012 08:15 PM
Coleman Mach 3 Start Capacitor Burns Up A440 RV Systems & Appliances 13 08-16-2009 10:41 AM


All times are GMT -6. The time now is 08:12 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2021, vBulletin Solutions, Inc.