Old 12-09-2017, 10:26 AM   #43
Senior Member
 
hohenwald48's Avatar
 
Join Date: Jan 2017
Location: Titusville, FL
Posts: 5,164
Quote:
Originally Posted by Quincy View Post
Just an observation here. If that is the case (and I have no reason to doubt you) then when the ground and common are brought to the MH panel that would bind them also.

Q
The reasons for only bonding neutral and ground in the service entrance are pretty complicated. Suffice it to say that bonding in a location other than service entrance equipment is not allowed in the NEC. If you're interested in why I'm sure you can Google it and find plenty of reading.

An RV panel is NOT considered to be service entrance equipment when the RV is plugged in to shore power.

Generators and inverters are a little different and a bit more complicated.
__________________
When seconds count, the police are only minutes away.
2023 Grand Design 2600RB, 2022 F-350 King Ranch tow vehicle, Titusville, FL when not on the road
hohenwald48 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 12-09-2017, 12:10 PM   #44
Member
 
Join Date: Apr 2017
Posts: 38
If the power goes out with 15 Amp, it means most often the power cord is not able to give the load and the voltage will drop below the threshold thus switching off the internal systems. It restores automatically since the load is gone. You will need a better power cord with thicker wires. The standard extension cords are often not capable to carry the full 15 Amps without the voltage dropping.

Just the refrigerator and some light should not draw that much but probably the charger is kicking in and drawing a lot of amps. If you have a Magnum remote panel you should be able to switch off the charger (there is a switch on that panel) that way it will work, if there are no other appliances using anything.
erald is offline   Reply With Quote
Old 12-09-2017, 12:19 PM   #45
Senior Member
 
Join Date: Jan 2015
Location: Oroville, CA
Posts: 3,133
Twinboat has the neutral / ground-bonding thing down pat. Read all about it:https://www.mikeholt.com/mojonewsarc...s~20020521.htm
__________________
Bill, Kathi and Zorro; '05 Beaver Patriot Thunder
2012 Sunnybrook Harmony 21FBS (SQEZINN)
2007 Jeep Grand Cherokee Overland
cruzbill is offline   Reply With Quote
Old 12-10-2017, 04:38 AM   #46
Senior Member
 
Join Date: Nov 2017
Location: Citra, Florida
Posts: 1,396
Quote:
Originally Posted by cruzbill View Post
Twinboat has the neutral / ground-bonding thing down pat. Read all about it:https://www.mikeholt.com/mojonewsarc...s~20020521.htm
Sounds like Hohenwald48 has a pretty good handle on it also. I do not know about 47 or 49 although I think they could learn allot from 48.

Q Please note the above is intended to be a bit funny not a poke at 48... or 47 and 49 either .
Quincy is offline   Reply With Quote
Old 12-10-2017, 06:03 AM   #47
Senior Member
 
Join Date: May 2017
Posts: 235
Quote:
Originally Posted by Kiawah View Post
When people reference 50amps, it is actually two legs of 120vac each being fused at 50 amps, which happen to be 'out of phase'. Most RV's now adays just use those two legs separately, providing up to 100 amps of 120vac. The wire is actually 4 wires: 2 legs @120vac (red and black), a neutral (white), and a ground (bare or green).

A 30 amp power plug at a campground, is 30 amps @ 120vac. A 15/20 amp plug is 15or 20 amps @ 120vac.

When you connect a 50 amp coach thru a dongle to 30 amp plug, then a 30 amp to 20 amp plug converter........all of the circuits are technically able to try and draw power from that garage socket of 15/20 amps. Obviously if you turn too much on, they will blow the house circuit breaker protecting the wiring.

You cannot necessarily take a 30amp house dryer plug, and use it for your coach, reason being is it may be two legs each at 120vac (or 240vac), without a neutral, but an earth ground. If an electrician rewires both the socket and the wire at your breaker box, they can make it work. However you can't just change the socket end. The electrician needs to make it 30amp leg, neutral, and ground........as opposed to two 30 amp legs, and ground. You can do serious damage to your coach if this is not done correctly, and burn up expensive coach electrical items.

My refrigerator uses 1 amp when compressor is running, 8 amps when it shifts to defrost cycle. You charger/converter (some people incorrectly call it the inverter) can easily consume up to 10 amps or so, if you don't have it configured to throttle back it's charge current. An A/C can typically consume about 15 amps.


I am trading in my C Class for an A Class. Next week We are picking up our 2018 Thor Hurricane 29 M. It has 2 a/c units and 50 amp service.

We plan to store the new coach at our house, in the same place we stored our C. We have a 30 amp receptacle already in place. Will we be able to plug our new coach into that 30 amp outlet (using an adapter) and just manage our power usage?
__________________
Val
2018 Thor Hurricane 29 M
2018 Chevy Equinox Tow Vehicle
KeysVal is offline   Reply With Quote
Old 12-10-2017, 06:10 AM   #48
Senior Member
 
Monaco Owners Club
Holiday Rambler Owners Club
Join Date: Oct 2012
Location: Carpentersville, IL
Posts: 233
15 amp residential circuit

Interesting responses from a wide variety of folks.

I've tried a number of time to do this, plugging into the house 15 amp circuit, and every time, it would blow the circuit breaker in my home after a few minutes.

All I was interested in doing was to keep the fridge going for around 12-15 hours before our departure. - Ended up having it run on gas, which I wasn't too comfortable with, but it ended up working OK.
__________________
Steve & Maryann Nowak
'98 Holiday Rambler Imperial 38WDS
'16 Subaru Outback LTD, '07 Infiniti G Cpe
FMCA # F26083
fluffyms is offline   Reply With Quote
Old 12-10-2017, 06:33 AM   #49
Senior Member
 
Winemaker2's Avatar
 
Join Date: Nov 2006
Location: Western NY
Posts: 6,150
Quote:
Originally Posted by KeysVal View Post
I am trading in my C Class for an A Class. Next week We are picking up our 2018 Thor Hurricane 29 M. It has 2 a/c units and 50 amp service.

We plan to store the new coach at our house, in the same place we stored our C. We have a 30 amp receptacle already in place. Will we be able to plug our new coach into that 30 amp outlet (using an adapter) and just manage our power usage?
Absolutely OK... just manage your load.
If you have an energy mgmt system EMS it should adjust to 30A setting automatically or you can set it manually.
__________________
Don & Marge
'13 Newmar Ventana 3433 - '14 CR-V TOAD
'03 Winnebago Adventurer 31Y - SOLD
Winemaker2 is offline   Reply With Quote
Old 12-10-2017, 08:12 AM   #50
Senior Member
 
Scottybdivin's Avatar


 
Newmar Owners Club
Join Date: Jun 2012
Location: Spicewood Texas (West of Austin)
Posts: 4,514
Quote:
Originally Posted by fluffyms View Post
Interesting responses from a wide variety of folks.

I've tried a number of time to do this, plugging into the house 15 amp circuit, and every time, it would blow the circuit breaker in my home after a few minutes.

All I was interested in doing was to keep the fridge going for around 12-15 hours before our departure. - Ended up having it run on gas, which I wasn't too comfortable with, but it ended up working OK.
Your 15A plug is more than likely a GFCI protected plug. Many large RV's have the same issue. Otheres do not. Read this from another poster in a related thread.

Quote:
HOW DO WE PREPARE FOR GFCI ISSUES?
The two most common situations where GFCI outlets trip are when plugging in shore power or wiring up to an electrical panel. We can conclude there is an incompatibility when we consider the sensitivity of the outlets and that they were designed to protect you from a single appliance being plugged in. What happens is an electrical panel and/or the AC wiring can cause the GFCI to detect a discrepancy between line and neutral, as if there was a ground leak, even though there is not. These outlets were not really designed to have anything plugged down line from them, aside from the appliance and maybe an extension cord. Furthermore, your RV or boat likely has GFCI outlets located inside. Standard GFCI outlets tend to trip when they have other standard GFCI outlets down the line from them. If you need to energize an entire RV, boat, or electrical panel, I would recommend staying away from inverters that only have outlets. Inverters with a 3-wire AC hardwire terminal block option are designed and much better suited for these types of installations. These types of inverters with AC hardwire capability will often come with GFCI outlets as an option as well. I do not recommend altering the GFCI outlets or bypassing the ground prong as this can lead to other problems or hazards. Inverters with outlets only are suitable for plugging devices directly in or energizing a single 15-20 Amp circuit. Referring to how a GFCI outlets work and the purpose of ground fault protection is the most effective tool in preventing issues. Do not expect GFCI’s to do something they were not designed for.

I hope you have a better understanding of how GFCI functions, why it is important, and the limitations of these outlets. Feel free to comment below and if you have any questions contacting us at 800-367-3019 or info@donrowe.com.
__________________
Scotty and Kristen, Airedales Dagny and Wyatt
2007 Newmar Mountain Aire 4528, 450 HP ISM, Allison 4000, 8 Lifeline AGM's
2019 F250 King Ranch 4x4 Powerstroke - SOLD
2022 F350 DRW King Ranch 4 x 4
Scottybdivin is offline   Reply With Quote
Old 12-10-2017, 12:26 PM   #51
Senior Member
 
hohenwald48's Avatar
 
Join Date: Jan 2017
Location: Titusville, FL
Posts: 5,164
Quote:
Originally Posted by erald View Post
If the power goes out with 15 Amp, it means most often the power cord is not able to give the load and the voltage will drop below the threshold thus switching off the internal systems. It restores automatically since the load is gone. You will need a better power cord with thicker wires. The standard extension cords are often not capable to carry the full 15 Amps without the voltage dropping.
True. Fat cords are your friend. The fatter (and shorter) the better.
__________________
When seconds count, the police are only minutes away.
2023 Grand Design 2600RB, 2022 F-350 King Ranch tow vehicle, Titusville, FL when not on the road
hohenwald48 is offline   Reply With Quote
Reply

Tags
single



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Single branch circuit transfer switch? TDroma iRV2.com General Discussion 7 07-15-2016 04:39 PM
Replaced Norcold N841 (single wide) with a Frigidaire residential refrigerator vito.a RV Systems & Appliances 4 10-03-2015 11:44 AM
Diagram on connecting coach & chassis batteries deaudlebug RV Systems & Appliances 2 03-27-2015 09:28 PM
Single female looking for another single female to go on Mexico RV Caravan trip Paul Beddows Solo RV'ers 0 05-23-2014 11:41 PM
open circuit in colman pop-up 12V circuit 04Sundancer Pop Up, Tent Trailer and Teardrop Topics 6 09-20-2011 07:26 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 10:05 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.