I have been following this thread as I have exactly the same issue with my Dometic NDR1292 as the OP. I also did as Old Biscuit suggested and direct wired the heaters bypassing the board. My freezer stays around zero and fridge temps are mostly in the 40's, with an overnight dip down to 39. It's been over 24 hours now.
Jimmy, i'm curious as to the outside where you're at? I'm in the Florida Keys and it's about about 90. Sounds like your fridge cooled down nicely bypassing the board and mine didn't...so my cooling unit is bad? Thanks
|
0*F in freezer is very good
40's ? 42*F or lower is acceptable in food compartment but borderline
Two questions:
Are BOTH heater elements operating?
Both have to function in order to generate enough heat to turn the ammonia into a vapor in sufficient quantities
Is the 'LAT' switch ON?
(Low Ambient Temp...located beneath top decorative panel where control panel is......next to Climate Control Switch)
LAT.....keeps light in food compartment ON generating heat.
Used when outside air temps are 50*F or below.
Above 50*F it just causes HEAT which has to be removed.