Quote:
Originally Posted by Time machine
Howdy folks…
I am at the RV now and am still not getting power. I have checked the wet bay and there is no gfci there, nor can I find any in the coach itself.
I have reset the breaker panel (in the pic below). And also included some pics of the inverter.
Currently I have an extension cord from the house through the rv window to get some heat in here lol.
Thanks again for your tips! Looking forward to reading more suggestions.
Cheers
|
&
Quote:
Originally Posted by Time machine
Alright folks, here is the latest…
I plugged the 30A (with a “downsizer”) to the outdoor gfci plug at the house. I noticed today that as soon as I plugged it in it tripped the gfci…
So I went in the motorhome and turned off all of the breakers. Went back and plugged the motorhome back into the outdoor gfci and this time it did not trip the breaker…. So I went in the unit, through the breakers back on and this time it tripped the 15A breaker in the house that feeds the outdoor gfci…
I noticed on the breaker panel in the basement of the house that there was a 20A breaker for a different outlet, however in order to reach that outlet, I’ll have to use an extension cord that will plug into the 30A plug from the motorhome (not the one beside the breakers in the picture above) but the cable I would use to get shore power.
|
At Time machine: (1998 Coachmen Santara 37)
Let me first say, you definitely have a serious issue, in the RV to cause a 15A house breaker to trip. A GFCI breaker tripping, is more common, as they are testing for voltage leak.
It takes only 5 mA (0.005 A) of current leakage from the hot wire to the ground to cause a GFCI to trip.
A 15A house breaker tripping is quite another.
I suspect that somewhere in the RV (and who knows where right now) a Romex wire is damaged (chaffed), shorted to ground, or mis-wired by the previous owner. You could also have a shorted out refrigerator 120V heating element.
It is clear the Previous Owner did some custom wiring. Why?
The photo you posted of the RV 120V breaker panel, with the Nema 6-30 plug is not factory.
That plug is not supposed to be there. We have that exact same panel in our RV.
The previous owner also installed the Intellitec with Charge Wizard converter to charge the house batteries. It is a very nice up grade for an older coach. Have have one ourselves.
Now, to the nitty gritty:
You stated that when you turned off all of the breakers in the RV, the house outlet did not trip. So,
1) You have determined you have power at the house receptacle, and that the power stays on when the RV is plugged in. That means that the RV 30A shore cord accepts power, and that power is most likely reaching the RV main breaker panel.
2) Once you turned on the breakers in the RV, and power was supplied down stream of the breaker, your homes house breaker tripped. That means that at least 1 of the 5 breaker feeds has the problem.
What to do next?
A) Turn off all of the RV breakers
the 30 Amp main, #1 15Amp bed/kitchen, #2 20 Amp A/C (that is the roof air conditioner), #3 15 Amp Micro (microwave), #4 15 Amp Galley (kitchen), and #5 15 Amp GFI (ground fault interrupt)
B) Reset your home's 15 Amp breaker.
C) Unplug the RV's shore cord and verify you have power coming out of that outlet by plugging in a lamp (and turn it on), or a 120V A/C Tester. You can buy them at Lowe's for about $7.00
https://www.lowes.com/pd/Southwire-A...ter/1001005712
D) Leave the lamp, or tester plugged in to the outlet, then plug in the RV shore cord. Verify the lamp is on, or the tester still reads correctly.
E) Go into the RV and turn on only the 30 Amp Main breaker.
F) Exit the RV and check to see if the lamp stayed on, or tester still reads good. If the lamp went out, or the tester reads nothing, you have a problem in the RV main breaker panel.
If the lamps is on, or the tester reads fine, proceed to (G)
G) Go back into the RV and turn on the next breaker, breaker #1 - Bed/Kitchen.
H) Exit the RV and check to see if the lamp stayed on, or tester still reads good. If the lamp went out, or the tester reads nothing, you have isolated the problem to somewhere in the #1 circuit.
If the lamps is on, or the tester reads fine, repeat this procedure for each circuit one-by-one.
Using this method, you can determine which RV circuit has a problem. Then it is down to trouble shooting everything plug into that one circuit. IE refrigerator, TV, microwave, antenna amplifier, converter.
If you find that unplugging an appliance from the 120V outlet cures the breaker tripping, you have found that problem.
If everything is unplugged, and the breaker still trips, you know that somewhere in the wiring, the Romex is damaged, and will need to be repaired/replaced.
Good hunting!