Front A/C-Heat Pump

I have an 2020 encore 325ss coachmen with airxcell 45000 series heat pumps (2). The rear one works fine. Yesterday the front one failed. When I turn on the front one, both units quit. Have to go out to the pole and flip the breaker. The minute the front unit is turned on, same thing happens. The breaker itself does not flip either on the pole or the panel in the coach. We had a surge protector put in a few weeks ago and this is our first trip since then. We are traveling across the country to Washington state from Maine and the heat is killing us. Anyone have any insight? Is it the surge protector or AC unit itself?
Thanks,
Tony
TonyCicoria is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-13-2021, 07:32 PM   #2
Senior Member
 
Xmcdog's Avatar
 
Join Date: Dec 2019
Location: Nova Scotia
Posts: 1,633
Hi Tony,
Sorry to hear you are having problems. Have you tried running the front unit on its own? Have you checked the amp draw on both units. Also check supply voltage. I would also check the capacitors. Good luck
__________________
Jeff and Annette Smith
04 Glendale Titanium 24E29 Fifth
2011 GMC Diesel 2500 HD
Xmcdog is offline   Reply With Quote
Old 06-13-2021, 10:56 PM   #3
Senior Member
 
DRM901's Avatar
 
Tiffin Owners Club
Texas Boomers Club
Join Date: Feb 2018
Location: North Texas
Posts: 590
I'm pretty sure the AC is pulling too many amps and tripping the circuit. That normally means the compressor is locked or the start capacitor is bad. Capacitors are dirt cheap; compressors are very expensive, and normally can't be replaced.

So your choice. Are you feeling lucky?

To replace the capacitor, get the specs. Normally stamped on it. (To save money, you don't need to buy the part from Airxcel. Any capacitor that matches will work fine. I think around $15.)
__________________
2014 Tiffin Allegro Bus 37AP
DRM901 is offline   Reply With Quote
Old 06-14-2021, 03:40 AM   #4
Senior Member
 
Shutterbug57's Avatar
 
Tiffin Owners Club
Join Date: May 2019
Posts: 491
Quote:
Originally Posted by TonyCicoria View Post
We are traveling across the country to Washington state from Maine and the heat is killing us. Anyone have any insight? Is it the surge protector or AC unit itself?
Thanks,
Tony
Not sure where you are at this point or your route, but we have a great RV Tech at our campground in Batesville Indiana (about half way between Indianapolis & Cincinnati). He stays busy in the campground, but is usually able to see you in a day or two. If you cannot figure your issue out on your own, or don’t want to, it may be worth a detour. (Chicago to Indianapolis (I65), to Batesville (I74), to Cincinnati (I74), then Cleveland (I71)).

The campground is Indian Lakes which has KOA and Thousand Trails components. Check your PMs for details on the RV Tech.
__________________
2011 Tiffin Phaeton 36QSH
2019 Ford Expedition Max as the TOAD
Shutterbug57 is offline   Reply With Quote
Old 06-14-2021, 08:45 AM   #5
Senior Member
 
SKP Kirk's Avatar
 
Join Date: May 2010
Location: Part-time out of Mesquite, TX
Posts: 1,093
While it is possible that there is a problem with your air conditioner, I would consider that to be unlikely. I would suspect that your front air conditioner is a much larger (more BTU's) than the rear and for that reason would expect that it would draw more current than the rear one.
Quote:
When I turn on the front one, both units quit. Have to go out to the pole and flip the breaker.
Have you tried operating the front a/c while the rear is off? Are you connected to a 30A power pedestal or a 50A and is your power cord 30/50a? Based on your first statement it would seem that you are overloading the circuit breaker on the power pole or that the circuit breaker there is weak and needs to be replaced.
Quote:
The breaker itself does not flip either on the pole or the panel in the coach.
I do not understand this part? Above you say that you reset it at the pole. If that circuit breaker is tripping, it would not move the actuator handle to the off position but most do move slightly. To reset any circuit breaker you move the handle to the off position, then close it again.
Quote:
We had a surge protector put in a few weeks ago and this is our first trip since then. ............... Is it the surge protector or AC unit itself?
If you are resetting the circuit breaker at the power pole to get power back, then your new surge protector plays no part in it. If the power goes away, but will turn back on after a few minutes without you doing anything, that would indicate some fault being detected by your power protection device. If yours is the full power protection type of surge protector it will also interrupt the power if the supply voltage should fall below 108V or so. It does that because low voltage will cause damage to an electric motor if it is allowed to run on low voltages for an extended period. While there are other types of fault that those protectors interrupt, low voltage would be the one that is most common when using an air conditioner.
__________________
Good Travelin! Kirk
Full-time 11 years, now part-time.
Kirk & Pam's Great Adventure!
SKP Kirk is offline   Reply With Quote
Old 06-15-2021, 08:19 AM   #6
Junior Member
 
Join Date: May 2021
Posts: 6
Thank you all. I was able to get a camping world in ND to look at it. They said the compressor is seized. They found oil and freon on the coils, indicating a leak which lead to the compressor seizing...amperage draw exceeded 50A due to that, which shut down the circuit through the surge protector. They said it needed a new unit...which they didn't have to replace it.
TonyCicoria is offline   Reply With Quote
Old 06-15-2021, 08:54 AM   #7
Dom
Senior Member
 
Join Date: Apr 2018
Posts: 643
Thanks for letting everyone know. All too often the OP just gets it diagnosed or fixed without letting is know, and we're all left wondering.
__________________
I came into this world with nothing, and I still have most of it left
Dom is offline   Reply With Quote
Reply

Tags
heat, pump



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
AC/HeatPump Hi-Low Switch JC2 RV Systems & Appliances 4 06-05-2007 01:05 PM
basement heatpump again cabindog Winnebago Industries Owner's Forum 4 03-14-2007 12:43 AM
Coleman Mach AC/Heatpump Fan Speed JC2 Winnebago Industries Owner's Forum 3 03-05-2007 05:04 PM
basement heatpump (freon) Ken & Joyce Winnebago Industries Owner's Forum 4 06-02-2006 01:16 PM