Generator Gas v Diesel
Hi y'all, long time no see. Major family illness. Getting better. Looking to get back to traveling. Thinking of stepping down from steep step Diesel pusher to low entry Gas model.
Question: Why do gas RVs have only the wimpy Onan 5500? On our first RV, that generator couldn't power AC and a Microwave at the same time. Would miss that big 6500 if we step down.
Thank you, graciously
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
11-15-2022, 09:28 AM
|
#2
|
Senior Member
Ford Super Duty Owner
Join Date: Mar 2009
Location: Oregon
Posts: 2,758
|
I have no problem with the 5500 with two A/C and microwave.
__________________
2016 Bounder 34T Anniversary Edition
|
|
|
11-15-2022, 10:17 AM
|
#3
|
Senior Member
Join Date: Jul 2014
Posts: 35,446
|
Quote:
Originally Posted by Bookmon
Hi y'all, long time no see. Major family illness. Getting better. Looking to get back to traveling. Thinking of stepping down from steep step Diesel pusher to low entry Gas model.
Question: Why do gas RVs have only the wimpy Onan 5500? On our first RV, that generator couldn't power AC and a Microwave at the same time. Would miss that big 6500 if we step down.
Thank you, graciously
|
Must have been something wrong with the generator or wiring.
Seen a few incidents where the main 30 amp supply was wired to the 20 amp generator breaker.
|
|
|
11-15-2022, 11:05 AM
|
#4
|
Senior Member
Join Date: Oct 2014
Posts: 145
|
All running at same time? Wow! Thank you.
|
|
|
11-15-2022, 11:08 AM
|
#5
|
Senior Member
Join Date: Oct 2014
Posts: 145
|
Quote:
Originally Posted by twinboat
Must have been something wrong with the generator or wiring.
Seen a few incidents where the main 30 amp supply was wired to the 20 amp generator breaker.
|
Thank you. Wonder if that was part of it. Have a used '96 Dutchman Class A. Shortly after purchase, pulled into a shopping center to heat some lunch. Had 1 AC going. Fried that 5500.
Replaced with a Generac. (Big mistake). Still Can not run both.
|
|
|
11-15-2022, 03:26 PM
|
#6
|
Moderator Emeritus
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 27,713
|
I suspect that was a 30A coach.
A 5500 watt generator can easily supply the power for two a/c (about 1400W each) and a microwave (another 1200W or so) and still have capacity left over. But the branch circuit wiring in the coach may not be designed to actually allow that. It never is in a 30A shore power coach, and more than a few with 50A wiring still come up short.
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is West Palm Beach, FL
|
|
|
11-15-2022, 06:01 PM
|
#7
|
Senior Member
Join Date: Oct 2014
Posts: 145
|
Quote:
Originally Posted by Gary RVRoamer
I suspect that was a 30A coach.
A 5500 watt generator can easily supply the power for two a/c (about 1400W each) and a microwave (another 1200W or so) and still have capacity left over. But the branch circuit wiring in the coach may not be designed to actually allow that. It never is in a 30A shore power coach, and more than a few with 50A wiring still come up short.
|
So, what is the path to solving this issue? Another response alluded to this discrepancy. Thank you for reply
|
|
|
11-15-2022, 06:33 PM
|
#8
|
Senior Member
Winnebago Owners Club Fleetwood Owners Club Holiday Rambler Owners Club
Join Date: Dec 2011
Location: North East Florida
Posts: 2,028
|
Probably has a lot to do with physical size. There isn't a lot of room in most coaches to cram in a larger generator. Since most people manage just fine with 2 a/c's in a gas coach with a 5.5kW there wouldn't be much incenitive to design and build a larger generator that most coach builders wouldn't sell because they are trying to hit a certain price point.
__________________
2019 Horizon 42Q
Cummins L-9 450 HP
Maxum Chassis / IFS with Tag
|
|
|
11-15-2022, 06:45 PM
|
#9
|
Senior Member
Join Date: Jul 2014
Posts: 35,446
|
The path to making it work is to wire it to run one A/C on the 20 amp circuit and the rest of the RV on the 30 amp circuit
A 30 amp circuit will easly power 1 A/C, the fridge, the converter/charger, TVs and microwave.
How do I know, I have a 30 amp RV.
|
|
|
11-15-2022, 06:51 PM
|
#10
|
Senior Member
Join Date: Mar 2019
Posts: 5,702
|
Quote:
Originally Posted by chuckftboy
Probably has a lot to do with physical size. There isn't a lot of room in most coaches to cram in a larger generator. Since most people manage just fine with 2 a/c's in a gas coach with a 5.5kW there wouldn't be much incentive to design and build a larger generator that most coach builders wouldn't sell because they are trying to hit a certain price point.
|
The Onan 7000 was a $900 option on ours to replace the Onan 5500 but there really was no need for us. Two 15K BTU A/C's, a microwave, a fireplace, and other stuff and our Onan 5500 can easily handle the needed simultaneous loads.
An Onan 5500 can supply 45 amps which is about 1.5 30-amp pedestals. Our Onan 5500 has two 30-amp breakers and the manufacturer split the loads up fairly well. For example, one A/C is on one breaker and the other A/C is on the other breaker.
I did install Micro-Air's EasyStart "soft start" units and they really reduce the peak power needed by the roof units to get started up. I can run both A/C's on a 30-amp pedestal plus other smaller loads.
An Onan 7000 can supply 58 amps, which is slightly more than one leg of a 50-amp pedestal.
Ray
__________________
2020 Forest River Georgetown GT5 34H5
2020 Equinox Premier AWD 2.0L/9-speed
|
|
|
11-15-2022, 07:48 PM
|
#11
|
Senior Member
Join Date: Sep 2021
Posts: 1,877
|
+ 1 for the advice above on hard start Capacitors, they certainly help but I agree with all the other advice it's a how things are wired issue. I have a big diesel Cat genny and the way it's wired I can pop the breaker that is actually on the generator itself by running too much on the 20 amp circuit. It's annoying but the biggest offender is the inverter trying to grab big amps for the battery charger...I often forget to just turn it off.
__________________