Even if you could play contortionist and get that temp sensor installed w/o dropping the genset what happens if your back to step 1?
Perhaps you need to really get a close look at the water pump, belt hoses and such. Maybe the impeller on the water pump disintegrated or the fan belt is glazed and slipping.
__________________
Robert & Deb
07 Discovery 39v FWS Full Timers, Henniker NH
1K solar - 05 Jeep Grand Cherokee
mchero is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 09-04-2020, 10:34 PM   #44
Junior Member
 
Join Date: Jun 2020
Posts: 26
Well guys, I figured out how to get the sensor out. Drilled a small hole in the shroud next to it so that I could get the proper angle for a drill bit. I stuff some paper towers down the thermostat housing below the temp sensor to catch debris, then drilled out the broken piece. Cleaned out the sensor hole with a bottle brush, pulled out the paper towels (now soaked in water from sitting in the thermostat housing) which grabbed all the little metal shavings on its way out. Installed the new temp sensor, and went to fire it up. Of course now it decides to not crank at all. The fuel pump works (clicks as it primes the line), but no turn over.
So I check the battery connections, the negative terminal is a little dirty, so I loosen to it to clean it and SNAP! No more negative terminal 🤦*♂️ How can one person have so much bad luck with a generator???? Luckily, a new neighbor pulled in and was willing to help and between the two of us we came up with a ghetto temporary fix. Then the generator fired right up and ran fine with both AC’s cranked for 30 or 40 minutes. That’s all the time I had left to test if before I had to start packing things up to move out. Maybe it’s fixed? Maybe not. I’ll report back after I’ve had a chance to test it some more.
Dan4Governor is offline   Reply With Quote
Old 09-10-2020, 12:15 PM   #45
Senior Member
 
edge68474's Avatar
 
Join Date: Oct 2017
Posts: 1,937
WOW!!! I feel for you my friend. Well, maybe now somehow it is fixed. Best of luck. What a process, huh. I will still be watching. Thank you for updating us.
__________________
Larry & Sheree & KD the CAT
2009 Holiday Rambler Admiral 30SFS Lewis County, Wa.
USN 1964-68, USS LEXINGTON CVS-16
edge68474 is offline   Reply With Quote
Old 09-10-2020, 12:22 PM   #46
Member
 
Join Date: Jun 2020
Posts: 96
Maybe try putting a 8" fan in the generator bay.
SacRV is offline   Reply With Quote
Old 09-13-2020, 12:28 PM   #47
Senior Member
 
edge68474's Avatar
 
Join Date: Oct 2017
Posts: 1,937
Quote:
Originally Posted by SacRV View Post
Maybe try putting a 8" fan in the generator bay.

I am thinking of that also.
__________________
Larry & Sheree & KD the CAT
2009 Holiday Rambler Admiral 30SFS Lewis County, Wa.
USN 1964-68, USS LEXINGTON CVS-16
edge68474 is offline   Reply With Quote
Old 09-13-2020, 12:35 PM   #48
Senior Member
 
mchero's Avatar
 
Join Date: Mar 2006
Location: Full Time USA
Posts: 2,216
I still find it hard to believe an Onan shop tells you they don't know what's wrong with it.
__________________
Robert & Deb
07 Discovery 39v FWS Full Timers, Henniker NH
1K solar - 05 Jeep Grand Cherokee
mchero is offline   Reply With Quote
Old 09-13-2020, 03:18 PM   #49
Senior Member
 
jerichorick's Avatar
 
Winnebago Owners Club
Join Date: Jun 2013
Location: Full-timer/volunteer w/SOWERS
Posts: 3,958
Quote:
Originally Posted by Dan4Governor View Post
Okay so I’ve read a million threads here on what to fix on my Onan QD 8000 generator and can’t figure out what to do next. Here are the symptoms:

Generator overheats and shuts off (giving the 33 overheating error code) consistently after 30-40 minutes under moderate load (running one AC) if the outside temps are above 85 degrees. If cooler than 85 outside it will run one AC just fine indefinitely, but will overheat if I run both AC’s regardless of outside temps.

Here’s what I’ve done (following advise on this forum in other threads)

Changed oil and new oil filter
Flushed and changed coolant
New thermostat
New radiator camp
New air filter
New fuel filter
Generator is not on a slide so I just had Cummins diagnose and do new water pump and belt

They told me it was fixed and they load tested it (not good enough apparently) because nothing is any different. Exact same issues. Not even a little better (Cummins charged me $1,400!).

I’m at my wits end. I see people running their generators and ACs all day long in the campsites I’m visiting without issues so I know mine should be working better than this. Even the Cummins onan website says this model should run two AC’s and more without issue.

I don’t think it’s the temp sensor (although I have one on hand just in case) because normally it won’t run more than a minute if the sensor is bad, and since it runs longer, then shuts off when overheating that tells me the sensor is doing its job. Temp gun verifies 220 degrees at the water pump and thermostat housing, so it is definitely overheating.

Anything else I can do????
Thanks so much for your wisdom!
I'd go back to the shop and tell them to fix it. No more money. Don't be a victim to the big guys.
__________________
Rick & Melissa Young, 2011 Itasca Meridian 40U, Frtliner XCL, Cummins ISL 380HP/DEF, Allison 3000 MH, 2014 Honda CR-V, SMI AF1, Blue Ox, EEZ TPMS, TruCenter steering control
Servants On Wheels Ever Ready. Best job we ever paid to do . (full time volunteers)
jerichorick is offline   Reply With Quote
Old 09-13-2020, 03:41 PM   #50
Senior Member
 
mchero's Avatar
 
Join Date: Mar 2006
Location: Full Time USA
Posts: 2,216
I'm with Rick.
We don't know what's wrong....CYA! Just doesn't work for me.
__________________
Robert & Deb
07 Discovery 39v FWS Full Timers, Henniker NH
1K solar - 05 Jeep Grand Cherokee
mchero is offline   Reply With Quote
Old 09-13-2020, 04:56 PM   #51
Senior Member
 
Bobby F's Avatar
 
Join Date: Aug 2019
Location: MN
Posts: 2,810
I think they did know what was wrong, but the factory-approved fix was very costly and he was looking for alternatives.
__________________
------------------------------------

1993 Rockwood 28' Class C - Ford E-350 7.5L
Bobby F is offline   Reply With Quote
Old 09-14-2020, 03:43 AM   #52
Senior Member
 
triplewide's Avatar
 
Join Date: Mar 2015
Location: Greensboro, NC
Posts: 2,753
Quote:
Originally Posted by Dan4Governor View Post
Well guys, I figured out how to get the sensor out. Drilled a small hole in the shroud next to it so that I could get the proper angle for a drill bit. I stuff some paper towers down the thermostat housing below the temp sensor to catch debris, then drilled out the broken piece. Cleaned out the sensor hole with a bottle brush, pulled out the paper towels (now soaked in water from sitting in the thermostat housing) which grabbed all the little metal shavings on its way out. Installed the new temp sensor, and went to fire it up. Of course now it decides to not crank at all. The fuel pump works (clicks as it primes the line), but no turn over.
So I check the battery connections, the negative terminal is a little dirty, so I loosen to it to clean it and SNAP! No more negative terminal 🤦*♂️ How can one person have so much bad luck with a generator???? Luckily, a new neighbor pulled in and was willing to help and between the two of us we came up with a ghetto temporary fix. Then the generator fired right up and ran fine with both AC’s cranked for 30 or 40 minutes. That’s all the time I had left to test if before I had to start packing things up to move out. Maybe it’s fixed? Maybe not. I’ll report back after I’ve had a chance to test it some more.

I wonder if the terminal was the problem all along?
__________________
1998 Min Winnie, 2000 Winbago Journey, 2015 ACE 29.3
2016 Thor Miramar 34.2
triplewide is offline   Reply With Quote
Old 10-10-2020, 04:28 PM   #53
Senior Member
 
edge68474's Avatar
 
Join Date: Oct 2017
Posts: 1,937
Did this problem ever get resolved??
__________________
Larry & Sheree & KD the CAT
2009 Holiday Rambler Admiral 30SFS Lewis County, Wa.
USN 1964-68, USS LEXINGTON CVS-16
edge68474 is offline   Reply With Quote
Old 06-08-2021, 05:44 PM   #54
Junior Member
 
Join Date: Jun 2020
Posts: 26
Hey guys, I know some of you have been asking for an update, but it’s taken until now for the weather to be warm enough to really put it through the ringer. The good news is that everything appears to be working as it should. The last couple weeks it’s been in the 90’s with high humidity here in Oklahoma where I’m working on remodeling the interior of my motorhome, so I’ve been running AC’s a lot. I only have a 20 amp outlet to connect my RV to for this remodel, so to run both AC’s I need to use the generator or I’ll trip the circuit. I’ve been running the generator to run both AC’s the majority of the day as well as higher amperage power tools. The EMS is telling me I’m drawing upwards of 40ish amps consistently, and the genset doesn’t seem to mind at all. Hasn’t overheated since my fight with the temp sensor/negative battery cable.

So I’m gonna call it fixed, praise the Lord!
Thanks for all the help and friendly motivation. My guess is that the cause of the overheating was the corrosion in the radiator and coolant passages which had eaten away at the temp sensor as well, but the corrosion was also what was holding the temp sensor together, so when I replaced the radiator, and flushed the corrosion out with the Restore plus, the temp sensor finally bit the dust completely and needed replaced as well. I think the negative battery cable was just bad luck/me not being gentle with the generator after so much frustration. Note to self, take it REALLY EASY when removing/reconnecting those battery cables. That brass is very soft.
Dan4Governor is offline   Reply With Quote
Old 07-22-2021, 10:30 PM   #55
Senior Member
 
Holiday Rambler Owners Club
Join Date: Jun 2021
Location: AZ
Posts: 125
I myself is going through this same scenario , overheating code 33 . I too have also changed out the temp sensor , coolant , thermostat and still get a code 33 my only worry some is that this relay clicks and clicks right after the generator shuts down. Something also clicks in the back compartment where all the inverter components are ( breakers I'm assuming) . An i posted another thread on here when i first purchased the coach and quite a few people say stay away form cummins repair shops . So with that been said should i too just purchase a new radiator do all the flushes stated before or could my problem be something else? thanks in advance
Attached Thumbnails
Click image for larger version

Name:	IMG_2010 2.jpg
Views:	24
Size:	294.4 KB
ID:	336899  
RayAZ is offline   Reply With Quote
Old 07-23-2021, 10:24 PM   #56
Senior Member
 
Join Date: Apr 2018
Posts: 3,441
I admit to not reasing the whole thread. Did you check or change the fan belt in the rear?
shootist is offline   Reply With Quote
Reply

Tags
generator, heat, heating, overheating



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Generator Blues --- Help TEEGEE1997 Newmar Owner's Forum 11 06-11-2013 07:48 AM
Blues at the USPS.........this ever happened to you??????? araucano Full-Timers 8 04-09-2009 10:38 AM
I got those old injector blues............ SargeW Cummins Engines 5 09-16-2008 04:57 PM
Blues & Brews Festival in Laughlin, NV WWFan Toy Haulers Discussion 6 09-27-2005 06:54 PM
Is it related to the Moody Blues possibly? 56Nomad Toy Haulers Discussion 33 06-27-2005 05:48 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 09:41 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.