Old 07-02-2017, 02:24 AM   #15
Senior Member
 
Newmar Owners Club
Join Date: Jun 2016
Location: Katy, TX
Posts: 841
I store my motorhome at a covered storage facility not far away from my home, Each storage spot has a 15 amp outlet to use to keep the house batteries charged. I use a 50-amp to 15 amp adapter with a short 25 foot extension cord. The night before a weekend outing, I turn on my Norcold NX841 refrigerator on "electricity setting' so it is cold the next morning for all of the "stuff" we bring on our outings.
__________________
Mike & Cindy in Katy, TX
2016 Newmar Ventana LE 4037
2016 Jeep Wrangler Unlimited Sahara
fagnaml is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-02-2017, 09:26 AM   #16
Registered User
 
Newmar Owners Club
Appalachian Campers
Freightliner Owners Club
Join Date: Feb 2017
Location: Midlothian, VA
Posts: 4,774
I'll try next time with a shorter cord and also setting the incoming to 20A. But I also need to do a test for my own education and let the batteries run down until AGS kicks in and see how long they actually go. I have a hunch I can go days with my use and need to not worry about a few days at the house disconnected from power or generator. Kind of like validating the E on the car gas tank
NealC is offline   Reply With Quote
Old 07-02-2017, 09:41 AM   #17
Senior Member
 
Old Scout's Avatar
 
Join Date: Nov 2005
Posts: 7,396
Sounds like a good test for your AGS but most equipment has a menu item so you can set the voltage level you want your genset to start at. Need to make sure the house outlet you are trying to use is not GFI protected. Most modern surge equip wont let you use GFI protected plugs.... Something to do with the way the neutral and ground are treated within the GFI plug......?????
__________________
Old Scout
2015 IH45 Foretravel
2003 Alpine 40' MDTS [Sold]
New Braunfels, Texas
Old Scout is offline   Reply With Quote
Old 07-02-2017, 09:57 AM   #18
Registered User
 
Newmar Owners Club
Appalachian Campers
Freightliner Owners Club
Join Date: Feb 2017
Location: Midlothian, VA
Posts: 4,774
Quote:
Originally Posted by Old Scout View Post
Sounds like a good test for your AGS but most equipment has a menu item so you can set the voltage level you want your genset to start at. Need to make sure the house outlet you are trying to use is not GFI protected. Most modern surge equip wont let you use GFI protected plugs.... Something to do with the way the neutral and ground are treated within the GFI plug......?????
Yes, the outlet next to my front door on my house is in fact GFI and I was worried about that. Will use a different outlet from the garage next time.

I know I can test the AGS but I want to get a field test of how long the batteries actually last before it gets to that point. Confidence in the system through testing it real world...kind of like keeping an iPhone on a charger all the time vs. letting the batteries cycle and actually see how long you can go.
NealC is offline   Reply With Quote
Old 07-02-2017, 07:32 PM   #19
Senior Member
 
Join Date: Feb 2016
Posts: 691
Mine doesn't like a gfi plug at all. Tried it at home and at storage and it would trip it (the house gfi) every time...sometimes immediately, other times after a few hours. Wasn't an amp issue I am sure of....something about the neutral and ground and imbalance I believe. I have never got it to work on a gfi
gtsum2 is offline   Reply With Quote
Old 07-03-2017, 06:24 AM   #20
Senior Member
 
Scottybdivin's Avatar


 
Newmar Owners Club
Join Date: Jun 2012
Location: Spicewood Texas (West of Austin)
Posts: 4,511
Quote:
Originally Posted by gtsum2 View Post
Mine doesn't like a gfi plug at all. Tried it at home and at storage and it would trip it (the house gfi) every time...sometimes immediately, other times after a few hours. Wasn't an amp issue I am sure of....something about the neutral and ground and imbalance I believe. I have never got it to work on a gfi
Same for me. I have turned the SHORE setting down to 15A or below and it still trips a GFI immediately. Next time I am faced with that, I am going to try connecting smart battery charger to the house batteries instead.
Scottybdivin is offline   Reply With Quote
Old 07-03-2017, 07:05 AM   #21
Senior Member
 
JohnBoyToo's Avatar
 
Monaco Owners Club
Join Date: May 2012
Location: DFW, Tex-US
Posts: 6,196
To the original poster, NealC,
your coach is new enough to have the 'smartest' converter/inverter so you shouldn't have to set the amp limit down manually (IMHO), it should automatically 'know' the amps in and will shed load if needed.

Different coach, but I too wanted to know and had to 'prove' the ags worked on for me, so I could possibly stop using the extension cords..
I had two 50 amp extension cords that I would use when loading up at the house and they were like fighting anacondas to lay out, etc... !

the temp level test test was very easy last summer when it was 105 degrees outside - as soon as it sensed I had set the temp setting to a low temp, it fired up the genny...

The next test was setting the volts to as high as it would set, 12.2 volts, and turning on all the lights (before I swapped to LED's) and inverter for the res fridge... it actually took a while before the ags started then genny, but after that I trusted the AGS and no longer use the extension cords at home...

At the storage facility I did get a heavy gauge outdoor extension for the batteries only... good luck !
__________________
'11 Monaco Diplomat 43DFT RR10R pushed by a '14 Jeep Wrangler JKU. History.. 5'ers: 13 Redwood 38gk(junk!), 11 MVP Destiny, Open Range TT, Winn LeSharo, C's, popups, vans, tents...
JohnBoyToo is offline   Reply With Quote
Old 07-03-2017, 07:55 AM   #22
Registered User
 
Newmar Owners Club
Appalachian Campers
Freightliner Owners Club
Join Date: Feb 2017
Location: Midlothian, VA
Posts: 4,774
Quote:
Originally Posted by JohnBoyToo View Post
To the original poster, NealC,
your coach is new enough to have the 'smartest' converter/inverter so you shouldn't have to set the amp limit down manually (IMHO), it should automatically 'know' the amps in and will shed load if needed.

Different coach, but I too wanted to know and had to 'prove' the ags worked on for me, so I could possibly stop using the extension cords..
I had two 50 amp extension cords that I would use when loading up at the house and they were like fighting anacondas to lay out, etc... !

the temp level test test was very easy last summer when it was 105 degrees outside - as soon as it sensed I had set the temp setting to a low temp, it fired up the genny...

The next test was setting the volts to as high as it would set, 12.2 volts, and turning on all the lights (before I swapped to LED's) and inverter for the res fridge... it actually took a while before the ags started then genny, but after that I trusted the AGS and no longer use the extension cords at home...

At the storage facility I did get a heavy gauge outdoor extension for the batteries only... good luck !
Good info and you are correct, it does sense the incoming amps because this was a problem on the factory pickup, they had an issue where the coach was only seeing 30A so the EMS was shedding causing the issues I had. I think it was the GFI outlet as the main problem, second may be a low quality ext cord.

The anaconda comment made me laugh! Funny!
NealC is offline   Reply With Quote
Old 07-03-2017, 08:27 AM   #23
Senior Member
 
Join Date: Jul 2014
Posts: 35,349
Quote:
Originally Posted by JohnBoyToo View Post
To the original poster, NealC,
your coach is new enough to have the 'smartest' converter/inverter so you shouldn't have to set the amp limit down manually (IMHO), it should automatically 'know' the amps in and will shed load if needed.
!
The load sheading system does not actually sense amps, it samples incoming voltage.

If it sees 240 volts, a standard RV 50 amp service, it assumes that it is 50 amp service.

It if sees 120 volts, a standard 30 amp RV service, it assumes 30 amp service. Once it sees it's 120 volts, it defalts to 30 amp service. You can then manually change it to a lower amp rating, 20, 15, 10......

An actuall " amp test " would require increasing the load until the supply breaker tripped, back at the outlet.
twinboat is online now   Reply With Quote
Old 07-03-2017, 08:37 AM   #24
Senior Member
 
Busskipper's Avatar
 
Join Date: Sep 2007
Location: Grasonville, MD -- Golden, CO
Posts: 6,222
Quote:
Originally Posted by NealC View Post
Good info and you are correct, it does sense the incoming amps because this was a problem on the factory pickup, they had an issue where the coach was only seeing 30A so the EMS was shedding causing the issues I had. I think it was the GFI outlet as the main problem, second may be a low quality ext cord.

The anaconda comment made me laugh! Funny!
One of these for when you have 30 amp and it's not close -

https://www.amazon.com/Camco-55501-P...c+cords+30+amp

Then one of these for 120 - 50 ' - 10 ga -

https://www.amazon.com/Lighted-Exten...0%2Bgauge&th=1

If you are any further the line drop will pretty much suck up the voltage so fire up the generator. 30' of 50 amp + 30' of 30 amp + 50' of 15 amp - should handle most everything.

Just incase you didn't get the pressure regulator - it would be in my hook up compartment of on the end of my hose.

https://www.amazon.com/Camco-40055-B...J6AW825J9HFDBS

Think you are ready to get out on the Road,
__________________
Busskipper
Location - Grasonville, Maryland - and/or - Superior, Colorado
2005 Travel Supreme 42DS04 - GX470 Toad
Busskipper is offline   Reply With Quote
Old 07-03-2017, 08:44 AM   #25
Registered User
 
Newmar Owners Club
Appalachian Campers
Freightliner Owners Club
Join Date: Feb 2017
Location: Midlothian, VA
Posts: 4,774
Quote:
Originally Posted by Busskipper View Post
One of these for when you have 30 amp and it's not close -

https://www.amazon.com/Camco-55501-P...c+cords+30+amp

Then one of these for 120 - 50 ' - 10 ga -

https://www.amazon.com/Lighted-Exten...0%2Bgauge&th=1

If you are any further the line drop will pretty much suck up the voltage so fire up the generator. 30' of 50 amp + 30' of 30 amp + 50' of 15 amp - should handle most everything.

Just incase you didn't get the pressure regulator - it would be in my hook up compartment of on the end of my hose.

https://www.amazon.com/Camco-40055-B...J6AW825J9HFDBS

Think you are ready to get out on the Road,
Thanks for the links. Can't leave yet, have to wait for another load of amazon deliveries this week
NealC is offline   Reply With Quote
Old 07-03-2017, 09:32 AM   #26
Senior Member
 
computerguy's Avatar
 
Join Date: Jul 2010
Location: FT on the Road
Posts: 3,831
I use a 50 to 30 and a 30 to 20/15 adapter. Plug into the house with a 25' extension cord. Hardly and voltage loss as far as I can tell as it is showing 119v on my EMS. Set the amps allowed down to 15 and I can run my small AC (13.5k)no problem. Have to make sure you keep the amp draw low if you use the adapter and an extension cord.
I am running my residential refer off my solar/inverter and leave the breaker from the panel to the inverter/converter/charger off.
__________________
I don't subscribe to threads I reply to so will not see your reply to my comment. Drop me a direct message if you want a reply from me.
Cheers!
computerguy is offline   Reply With Quote
Old 07-03-2017, 09:38 AM   #27
Senior Member
 
BFlinn181's Avatar
 
Gulf Streamers Club
Join Date: Jan 2012
Location: Cincinnati
Posts: 19,925
Quote:
Originally Posted by twinboat View Post
The load sheading system does not actually sense amps, it samples incoming voltage.

If it sees 240 volts, a standard RV 50 amp service, it assumes that it is 50 amp service.

It if sees 120 volts, a standard 30 amp RV service, it assumes 30 amp service. Once it sees it's 120 volts, it defaults to 30 amp service. You can then manually change it to a lower amp rating, 20, 15, 10......

An actuall " amp test " would require increasing the load until the supply breaker tripped, back at the outlet.
I too wondered at "sensing amps."

An RV has many electrical appliances and connections. To supply power to the RV through a 15 amp GCFI outlet is just asking for it to trip. They are designed to protect an individual from getting shocked. An RV, doesn't have a true ground connection like a home with a rod buried in the soil. Somewhere the neutral and ground are tied together. This could cause an imbalance between the hot lead and neutral, so the GCFI is likely to trip.

In a campground pedestal, the 50 amp and 30 amp outlets aren't GCFI protected, only the 15 amp outlet since it is more likely to be used for 'domestic' use, not provide power for an RV.
__________________

Bob & Donna
'98 Gulf Stream Sun Voyager DP being pushed by a '00 Beetle TDI
BFlinn181 is offline   Reply With Quote
Old 07-03-2017, 09:59 AM   #28
Senior Member
 
JohnBoyToo's Avatar
 
Monaco Owners Club
Join Date: May 2012
Location: DFW, Tex-US
Posts: 6,196
Quote:
Originally Posted by twinboat View Post
The load sheading system does not actually sense amps, it samples incoming voltage.

If it sees 240 volts, a standard RV 50 amp service, it assumes that it is 50 amp service.

It if sees 120 volts, a standard 30 amp RV service, it assumes 30 amp service. Once it sees it's 120 volts, it defalts to 30 amp service. You can then manually change it to a lower amp rating, 20, 15, 10......

An actuall " amp test " would require increasing the load until the supply breaker tripped, back at the outlet.
you are correct of course.. I was thinking shedding load on the back end and typed amps... sometimes my help is not help, but I still try to help...
__________________
'11 Monaco Diplomat 43DFT RR10R pushed by a '14 Jeep Wrangler JKU. History.. 5'ers: 13 Redwood 38gk(junk!), 11 MVP Destiny, Open Range TT, Winn LeSharo, C's, popups, vans, tents...
JohnBoyToo is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
50 AMP coaches, avoid 30 AMP and use GEN instead? NealC Just Conversation 8 06-12-2017 07:36 AM
LLC & Insurance, Finance & More? For those who use it! WyoFree Class A Motorhome Discussions 6 08-14-2016 05:29 PM
50 amp down to 15 amp for use in shed steelbreezzz Just Conversation 21 05-25-2015 06:32 AM
What does everyone use for a shower caddy..if you use anything? StansCustoms Alpine Coach Owner's Forum 9 07-19-2011 06:37 PM
Wondering if I can use a 50 amp converter cord with my 30 amp service? luke_vardanian Travel Trailer Discussion 12 11-10-2008 03:34 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 05:36 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.