Old 06-29-2017, 07:49 PM   #1
Registered User
 
Newmar Owners Club
Appalachian Campers
Freightliner Owners Club
Join Date: Feb 2017
Location: Midlothian, VA
Posts: 4,774
How to use 50 to 15 amp

So I'm at my house and figured I'd plug in to the 110 and use a 50 to 15 adapter. I am not sure what it should do for me but I expect it would run the 12v stuff. I think the EMS didn't like it but I have nothing on. I bypassed the EMS in the power bay but still nothing. Heard a few things cycle on then off. Then went to unplug and the extension cord was hot.

What use is 50 to 15 and how should I be using it?
NealC is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-29-2017, 07:56 PM   #2
Senior Member
 
Podivin's Avatar
 
Winnebago Owners Club
Join Date: Dec 2015
Location: Jacksonville, Fl
Posts: 3,542
The 12 volt stuff should always run, unless your batteries are run down, or turned off.

The technology in yours is WAY beyond what's in mind, but if I'm not too mistaken you've got a fancy control panel in there somewhere. In that panel I believe you'll find where you can tell the EMS what power source you're connected to (50 amp, 30 amp, 20 amp). My GUESS is that it's set to 50 amp and isn't managing the power correctly. Change the settings and see if it's better behaved.
__________________
2013 Winnebago Sightseer 36V
Podivin is offline   Reply With Quote
Old 06-29-2017, 08:15 PM   #3
Senior Member
 
BFlinn181's Avatar
 
Gulf Streamers Club
Join Date: Jan 2012
Location: Cincinnati
Posts: 19,925
When my RV is in the driveway, I plug my 50 amp shore cord into a 50>30 amp adaptor, then a 30>15 amp adaptor that fits in an outdoor outlet (15 amp breaker) My EMS monitors amps used. I can operate my RV refrigerator, converter/charger, even a TV or couple of small fans if needed. No A/C, if I wanted to use the microwave I'd turn off everything else so not to overload the circuit.

A heated wire or connection means resistance is present. I'd use a larger gauge extension cord and make sure all prongs and connections are clean and shiny.
__________________

Bob & Donna
'98 Gulf Stream Sun Voyager DP being pushed by a '00 Beetle TDI
BFlinn181 is offline   Reply With Quote
Old 06-29-2017, 08:17 PM   #4
KEH
Senior Member
 
KEH's Avatar
 
National RV Owners Club
Freightliner Owners Club
Join Date: Oct 2014
Posts: 121
Quote:
Originally Posted by Podivin View Post
The 12 volt stuff should always run, unless your batteries are run down, or turned off.

The technology in yours is WAY beyond what's in mind, but if I'm not too mistaken you've got a fancy control panel in there somewhere. In that panel I believe you'll find where you can tell the EMS what power source you're connected to (50 amp, 30 amp, 20 amp). My GUESS is that it's set to 50 amp and isn't managing the power correctly. Change the settings and see if it's better behaved.
Smart advice. Need to select your incoming power amperage.
__________________
2002 National RV Tradewinds LTC 7390
Cummins 350 ISC
Freightliner XC, Generac QUIETPACT 75D
Fulltimer's - Class of 2014
KEH is offline   Reply With Quote
Old 06-29-2017, 08:29 PM   #5
Senior Member
 
Busskipper's Avatar
 
Join Date: Sep 2007
Location: Grasonville, MD -- Golden, CO
Posts: 6,222
Quote:
Originally Posted by NealC View Post
So I'm at my house and figured I'd plug in to the 110 and use a 50 to 15 adapter. I am not sure what it should do for me but I expect it would run the 12v stuff. I think the EMS didn't like it but I have nothing on. I bypassed the EMS in the power bay but still nothing. Heard a few things cycle on then off. Then went to unplug and the extension cord was hot.

What use is 50 to 15 and how should I be using it?
15 amps is like Boondocking - will handle the batteries - maybe the refrig - Be sure the A/C is Off - Hot water heater is 13 amps, so use the gas setting if plugged into 15. Often if the batteries are low this will be a heavy draw and you will need to dial back your charger on 15.

When in doubt just fire up the genny - you should have some sort of meter that will tell you what you are using.

Hope that helps,
__________________
Busskipper
Location - Grasonville, Maryland - and/or - Superior, Colorado
2005 Travel Supreme 42DS04 - GX470 Toad
Busskipper is offline   Reply With Quote
Old 06-29-2017, 08:36 PM   #6
Senior Member
 
Mr_D's Avatar
 
Country Coach Owners Club
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 37,725
I have a 50 to 15 amp adapter, bought it from Home Depot but it's not normally stocked, had to order it. Use it all the time at the stick house, but last time out I forgot I had been running the gen and all three heat pumps to cool the rig off. Kept blowing the breaker at home till I remembered to turn off the heat pumps!
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft, HWH Active Air
Charter Good Sam Lifetime Member, FMCA,
RV'ing since 1957, NRA Benefactor Life, towing '21 Jeep JLU Rubicon Ecodiesel
Mr_D is offline   Reply With Quote
Old 06-29-2017, 08:40 PM   #7
Senior Member
 
BFlinn181's Avatar
 
Gulf Streamers Club
Join Date: Jan 2012
Location: Cincinnati
Posts: 19,925
50 amp RV service is two hot legs of 120, one line of neutral, and a ground. Each leg is 50 amps, so you actually could use up to 100 amps when plugged in to a 50 amp outlet. When adaptors are used from 15 or 30 amps to 50, the single hot leg is split into the 2 legs of the 50 amp plug. Without this split, half of your breaker panel would be dead. The current is limited by the smallest breaker in the circuit, so if you're only plugged into a 15 amp home outlet, when you try to draw more, the breaker will trip. Likewise, if a 50 amp RV is plugged into a 30 amp outlet, when your try to exceed 30 amps, the breaker will trip.
__________________

Bob & Donna
'98 Gulf Stream Sun Voyager DP being pushed by a '00 Beetle TDI
BFlinn181 is offline   Reply With Quote
Old 06-29-2017, 08:45 PM   #8
Moderator Emeritus
 
Spk64's Avatar


 
Newmar Owners Club
Join Date: Apr 2014
Location: Southern Indiana
Posts: 19,417
How to use 50 to 15 amp

I found the charger alone pulls quite a bit when first plugged in on our unit. Once it hits float it is better. I also store in the winter plugged into a 15 amp socket. So if you have any other loads it will be pulling a lot on a 15 or 20 amp circuit.
Also too small a cord with any length will pull the voltage down and EMS will kick it out.
__________________
Steve
2002 Newmar Mountain Aire 4095
Spk64 is offline   Reply With Quote
Old 06-29-2017, 08:54 PM   #9
Senior Member
 
saddlesore's Avatar


 
Foretravel Owners Club
Join Date: Apr 2016
Location: Home is Where WE PARK IT...
Posts: 6,054
Quote:
Originally Posted by Spk64 View Post
I found the charger alone pulls quite a bit when first plugged in on our unit. Once it hits float it is better. I also store in the winter plugged into a 15 amp socket. So if you have any other loads it will be pulling a lot on a 15 or 20 amp circuit.
Also too small a cord with any length will pull the voltage down and EMS will kick it out.
Yup, had that issue at the S&B with 15a. Called the electrician and installed RV pedestal with 50/30/20 at the concrete pad & another one in the garage for friends who sometimes park in front while visiting... ended all the issues.
__________________
Retired truckdriver,
'02 Foretravel... "This Shack will do"
being pushed by an '06 Scion xB
SKP's of Box Elder, South Dakota
saddlesore is offline   Reply With Quote
Old 06-29-2017, 09:21 PM   #10
Senior Member
 
Join Date: Jan 2015
Location: Oroville, CA
Posts: 3,133
Check your inverter remote panel and see if you can select 20a service.
__________________
Bill, Kathi and Zorro; '05 Beaver Patriot Thunder
2012 Sunnybrook Harmony 21FBS (SQEZINN)
2007 Jeep Grand Cherokee Overland
cruzbill is offline   Reply With Quote
Old 06-30-2017, 11:54 AM   #11
Senior Member
 
Join Date: May 2016
Posts: 430
Quote:
Originally Posted by BFlinn181 View Post
When my RV is in the driveway, I plug my 50 amp shore cord into a 50>30 amp adaptor, then a 30>15 amp adaptor that fits in an outdoor outlet (15 amp breaker) My EMS monitors amps used. I can operate my RV refrigerator, converter/charger, even a TV or couple of small fans if needed. No A/C, if I wanted to use the microwave I'd turn off everything else so not to overload the circuit.

A heated wire or connection means resistance is present. I'd use a larger gauge extension cord and make sure all prongs and connections are clean and shiny.
I do the same as you when in my driveway except I dont have an outdoor plug anywhere at my house so I bought one of those plugs that screws into a light bulb socket. and plug my 15 amp adapter into that. I use it to power the fridge and lights and keep the batteries charged is all.
__________________
1998 fleetwood pace arrow 34 foot
bobbelcher is offline   Reply With Quote
Old 06-30-2017, 12:33 PM   #12
Senior Member
 
Scottybdivin's Avatar


 
Newmar Owners Club
Join Date: Jun 2012
Location: Spicewood Texas (West of Austin)
Posts: 4,514
When possible, run your 50A cord all the way to the source and adapt there.
Scottybdivin is offline   Reply With Quote
Old 06-30-2017, 12:43 PM   #13
Senior Member
 
WillandJane's Avatar
 
Join Date: May 2015
Location: San Jacinto, CA
Posts: 411
Quote:
Originally Posted by BFlinn181 View Post
50 amp RV service is two hot legs of 120, one line of neutral, and a ground. Each leg is 50 amps, so you actually could use up to 100 amps when plugged in to a 50 amp outlet. When adaptors are used from 15 or 30 amps to 50, the single hot leg is split into the 2 legs of the 50 amp plug. Without this split, half of your breaker panel would be dead. The current is limited by the smallest breaker in the circuit, so if you're only plugged into a 15 amp home outlet, when you try to draw more, the breaker will trip. Likewise, if a 50 amp RV is plugged into a 30 amp outlet, when your try to exceed 30 amps, the breaker will trip.


......I am glad someone said it was 120v....I always turn up an eye when I hear 110. [emoji4]

WDK
WillandJane is offline   Reply With Quote
Old 06-30-2017, 12:53 PM   #14
Senior Member
 
Monaco Owners Club
Join Date: Sep 2014
Posts: 4,569
I have new a new plug and connector on my 30amp RV cord. It reaches to a 15Amp outlet I installed right next to my breaker box. Nothing gets hot when I run the 13,5k AC unit non-stop. I suspect the first place to get hot would be the adapter as they get older. I do have my converter on it's own breaker and keep it turned off.
__________________
1996 Tioga Class C
2007 Monaco Diplomat 40 PDQ
TOAD 2012 Cadillac SRX 4
okcnewbie is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
50 AMP coaches, avoid 30 AMP and use GEN instead? NealC Just Conversation 8 06-12-2017 07:36 AM
LLC & Insurance, Finance & More? For those who use it! WyoFree Class A Motorhome Discussions 6 08-14-2016 05:29 PM
50 amp down to 15 amp for use in shed steelbreezzz Just Conversation 21 05-25-2015 06:32 AM
What does everyone use for a shower caddy..if you use anything? StansCustoms Alpine Coach Owner's Forum 9 07-19-2011 06:37 PM
Wondering if I can use a 50 amp converter cord with my 30 amp service? luke_vardanian Travel Trailer Discussion 12 11-10-2008 03:34 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 08:48 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.