HVAC - Help - Low too low - High too high
Class A diesel, replaced compressor, did evac and recharged BUT.
The low side is just 15 lbs and the high side is 325 lbs on a 82dg F day. Fan runs on the condenser coil.
But the book low should be 40-50 lbs and high should be 276-345
If I try to put in more to raise the low I can get all the way to 400lbs and just 28lbs on the low side.
Even with bad numbers I get nice cold air at 46 dg F, full flow no icing.
Any Ideas?
__________________
2007 Country Coach Tribute 260 Sequoia
40' DP w/Cat400, F494513, Lithium Battery & Solar
Live next to Yosemite
|
|
|
 |
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
05-05-2021, 05:00 PM
|
#2
|
Senior Member
Grand Design Owners Club
Join Date: Jul 2017
Posts: 471
|
Step one is to charge the system by weight , then see what pressures you have. It is also important to have balanced the refrigeration oil level. I’m guessing an R134 system , and a correct charge is critical. Much more so than the older R12 systems. If the charge weight is correct , the most common thing that will cause low/low & high /high is a restriction - as expansion valve or drier. Occasionally a compressor failure will stop up the condenser tubes with particulate. Low heat dissipation, as in poor airflow across the condenser , or overcharging, will typically cause both sides to be high. If there is a restriction you will detect a temp change where it is.
Charlie
__________________
2019 310GK-R
2017 RAM DRW - sold
2020 RAM Longhorn DRW
|
|
|
05-05-2021, 05:04 PM
|
#3
|
Senior Member
Join Date: Nov 2017
Location: Oakhurst, CA
Posts: 851
|
Quote:
Originally Posted by cfowler55
Step one is to charge the system by weight , then see what pressures you have. It is also important to have balanced the refrigeration oil level. I’m guessing an R134 system , and a correct charge is critical. Much more so than the older R12 systems. If the charge weight is correct , the most common thing that will cause low/low & high /high is a restriction - as expansion valve or drier. Occasionally a compressor failure will stop up the condenser tubes with particulate. Low heat dissipation, as in poor airflow across the condenser , or overcharging, will typically cause both sides to be high. If there is a restriction you will detect a temp change where it is.
Charlie
|
There is no specification for the refill amount. This is a DP not a ford clsss C.
__________________
2007 Country Coach Tribute 260 Sequoia
40' DP w/Cat400, F494513, Lithium Battery & Solar
Live next to Yosemite
|
|
|
05-05-2021, 05:07 PM
|
#4
|
Senior Member
Monaco Owners Club
Join Date: Nov 2015
Posts: 2,147
|
There should be specs for the fill amount and oil also despite being a class A. Mine was by the dryer on the front firewall. If all else fails reach out the manufacturer
__________________
Steven & Laurie
2006 Moncaco Executive Ranier
Detrioit Series 60 (515HP), Allison 4000 series
|
|
|
05-05-2021, 05:30 PM
|
#5
|
Senior Member
Join Date: Nov 2008
Posts: 3,472
|
Correct, EVERY vehicle AC unit has a specified number of ounces for a correct fill. For example my Phaeton takes 32oz for a correct refill after being evacuated for at least one hour.
I would suspect you have a clogged receiver dryer based on the information given.
__________________
2013 Tiffin Phaeton 40QBH
2016 Chevrolet Equinox LTZ AWD V6
|
|
|
05-06-2021, 09:44 AM
|
#7
|
Member
Join Date: Sep 2020
Posts: 93
|
Quote:
Originally Posted by gpounder
Class A diesel, replaced compressor, did evac and recharged BUT.
The low side is just 15 lbs and the high side is 325 lbs on a 82dg F day. Fan runs on the condenser coil.
But the book low should be 40-50 lbs and high should be 276-345
If I try to put in more to raise the low I can get all the way to 400lbs and just 28lbs on the low side.
Even with bad numbers I get nice cold air at 46 dg F, full flow no icing.
Any Ideas?
|
Im assuming you mean 15psi on the low side gauge? IF the compressor is coming on, I would continue to add a couple more oz's of refrigerant to get the psi up to 45psi.
IF compressor is NOT running or cycling, you may need to jumper the low pressure cut off switch to force the compressor to continue running and pulling in refrigerant. I've also put the bottom half of can of R134 in a warm container of water to help speed the process up.
__________________
2011 Fleetwood Discovery 40G
Freightliner XC Chassis
|
|
|
05-06-2021, 10:01 AM
|
#8
|
Senior Member
Monaco Owners Club Ford Super Duty Owner
Join Date: Dec 2008
Location: Kingsville TX
Posts: 1,696
|
Low side is wrong,along with high side being wrong, you have a restriction, evac, remove reciever drier, check it for restriction, and also check the expansion valve for debris, expansion valve might have a screen in it, should be NO metal particles anywhere in the lines if there is compressor is gone, clogging up the receiver/drier.
|
|
|
05-06-2021, 10:02 AM
|
#9
|
Senior Member
Damon Owners Club
Join Date: Apr 2020
Location: Clovis NM
Posts: 4,385
|
Quote:
Originally Posted by SC182
Im assuming you mean 15psi on the low side gauge? IF the compressor is coming on, I would continue to add a couple more oz's of refrigerant to get the psi up to 45psi.
IF compressor is NOT running or cycling, you may need to jumper the low pressure cut off switch to force the compressor to continue running and pulling in refrigerant. I've also put the bottom half of can of R134 in a warm container of water to help speed the process up.
|
With the high side being too high in pressure, he certainly doesn’t to make it worse with more Freon. It sounds like there’s a restriction in the system. This is precisely why most laymen shouldn’t do AC work.
__________________
2006 Damon Daybreak 3276 35'with 5 Star Tuner. 3 200 Amp Lithium batteries and 2000 watt PSW inverter/charger. 2013 Elantra on a Master Tow dolly.
Retired USAF
|
|
|
05-06-2021, 10:02 AM
|
#10
|
Senior Member
Country Coach Owners Club
Join Date: Jan 2006
Location: Northern California
Posts: 5,718
|
46 degrees in the chute at 75 degrees ambient temp?
Call it good, until it is not.
That is what I do with a 30 degree differential.
__________________
Dean
1995 38' CC Magna #5280
C8.3L 300hp Cummins, 31,000lbs
Gillig Bus Chassis 05 Jeep Wk
|
|
|
05-08-2021, 11:20 AM
|
#11
|
Senior Member
Join Date: Nov 2017
Location: Oakhurst, CA
Posts: 851
|
Update
I finally found a label with the fill quantity, 5 LBS for R134A.
So I evacuated the system and did a refill to the specification.
High side is normal now, about 200psi
Low side still at 15 psi, very low by the book.
But I get real cold air, 45 degrees on a 75 degree day, no signs of icing on the coil.
So it is working. Note the low pressure switch is not stopping the system so that is leading me to think the switch is up front on the dryer and my gauges are in the back just 2 ft from the compressor. Is the long hose affecting the low side reading?
If the system was somehow clogged causing a low reading would I get still get nice cold air?
__________________
2007 Country Coach Tribute 260 Sequoia
40' DP w/Cat400, F494513, Lithium Battery & Solar
Live next to Yosemite
|
|
|
05-08-2021, 12:35 PM
|
#12
|
Senior Member
Join Date: May 2016
Posts: 733
|
In my opinion, no. I would definitely not add more refrigerant, and assuming you are testing on a relatively high outside temperature day and given a good temp drop, coil sweating over the entire area, good hi-side pressure, I would button it up and go with it.
__________________
Marvin (and Eileen) - Weekend RVer On A Budget
1997 34’ Gas Bounder / F53 Chassis | Towing 1996 Ford Ranger on Acme Dolly
|
|
|
05-08-2021, 12:50 PM
|
#13
|
Senior Member
Entegra Owners Club
Join Date: Apr 2011
Location: Estero, FL
Posts: 2,432
|
45 lbs is waay too high! 15lbs is the right number to chase, particularly if the Schrauder valve is close to the compressor. As you can tell you’ve found the sweet spot!
__________________
Gary & Leigh
2019 Entegra Cornerstone 45Y,
2010 Seneca, 2011 & 2014 Anthem, 2017, 2018 Cornerstone(All Sold)
|
|
|
05-08-2021, 06:04 PM
|
#14
|
Senior Member
Join Date: Sep 2018
Posts: 287
|
You said low “by the book”. What book are you referencing? If you are expecting similar gauge readings that you see on a car, then you will be off.
The extremely long run of hose from the evaporator back to the compressor drops the low side pressures lower than an automotive system. If you are getting 15 to 20 on the low, 200 to 250 on the high, and the low cutout switch is not cycling the compressor, then you are right where you want to be.
You were very smart to evacuate the system and start over again. You had too much refrigerant in it, driving the high side pressure into compressor fail territory.
__________________
Richard Entrekin
99 Newell,Subie Outback toad
Inverness, Fl
|
|
|
 |