I think I got lucky
I had one of the low end Progressive Industries surge protectors with the lights that tell if the pedestal is wired properly and I used it like always. I plugged it in first to check the wiring before I plugged the coach in.
About 10 minutes after plugging in to the pedestal and I'm back inside, I hear a hum, a buzz, a sizzle, and I smelled a faint smell of electrical smoke. I hurried back outside and turned off the pedestal breaker. The Progressive Industries model SS-50 was smoking. I checked the pedestal with my multi-meter and the neutral was open. I went back inside to see what all got fried and thankfully nothing but the power strip that my daughter's game system was plugged into was hurt. I was stressing out for a while thinking about how much it was going to cost to replace an inverter/charger, two TVs, Samsung refer, water heater, microwave, etc.
I don't know if the PI SS-50 made any difference or not but I'm glad we didn't suffer any severe damage.
So now I'm shopping for some hard-wired protection. I'm leaning toward the TRC units and I'd like to have the remote display panel. It looks like there are two choices, the model 35550 and the 40240.
Do any of you have experience with either of these units or can you comment on the differences?
Thanks
__________________
1994 Holiday Rambler Navigator
300HP Cummins 8.3
Allison MD 3060
|
|
|
 |
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
08-01-2016, 01:23 AM
|
#2
|
Senior Member
Join Date: Nov 2015
Posts: 14,533
|
TRC.......
1 year limited warranty
Non-serviceable (throw away units)
Lack luster customer service dept.
Progressive Industries ......
LIFETIME warranty
Service..rebulidable/repairable units
Good customer service dept.
Choice is simple
|
|
|
08-01-2016, 01:47 AM
|
#3
|
Senior Member
Monaco Owners Club Winnebago Owners Club
Join Date: Sep 2011
Posts: 7,462
|
Quote:
Originally Posted by Old-Biscuit
TRC.......
1 year limited warranty
Non-serviceable (throw away units)
Lack luster customer service dept.
Progressive Industries ......
LIFETIME warranty
Service..rebulidable/repairable units
Good customer service dept.
Choice is simple
|
Could not agree more. Progressive Industries EMS HW50C or PT50C is the only way to go.
__________________
US Navy Vet, Liberty Tree Member of Oath Keepers, NRA & VFW Life Member, Alaska EMT.
2009 Safari Cheetah 40 SKQ
2009 Winnebago Chalet 231CR
|
|
|
08-01-2016, 06:34 AM
|
#4
|
Senior Member
Monaco Owners Club
Join Date: Jun 2014
Posts: 7,851
|
X3 on the Progressive Industries EMS HW50C
I went without one for +6 years, I guess I was lucky. Then parked at home and the coach plugged into a 20 amps plug to keep batteries charged. Had lightening strike the power pole that services our house. We lost a TV in the kitchen and I thought that was it. Then the next month we were getting ready to leave and I could get the AC to work even on generator. I found that the EMS system was fried, ~$450 to fix.
I got lucky and found an open box special on the Progressive unit for ~$200. Installed it and on one of our first outings I found reversed polarity at one campground and low voltage at another.
I invested in a 2nd display so that I can monitor the power while plugging in and after it shows OK I switch to the inner display which on can monitor throughout the day/night.
__________________
Jim J
2002 Monaco Windsor 38 PKD Cummins ISC 350 8.3L
2005 Jeep Grand Cherokee w/5.7 Hemi
|
|
|
08-01-2016, 06:42 AM
|
#5
|
Senior Member
Join Date: May 2013
Location: Chester, VA/Zephyrhills, FL
Posts: 1,185
|
Wouldn't leave home without my Progressive Industries surge protector. It has saved me 3 times at different campgrounds.
__________________
Tom and Gloria 2017 Newmar Ventana 4369, TOAD: 2015 GMC Canyon, Blue Ox Towbar, Baseplate and M&G Braking System
|
|
|
08-01-2016, 07:32 AM
|
#6
|
Senior Member
Thor Owners Club Ford Super Duty Owner
Join Date: Jul 2011
Posts: 3,217
|
I'm a bit partial to the cord end units. As soon as I plug in I can see if the power terminal is correct. The up side of the hardwired protection is you can install it after the shore power/generator transfer switch and use it to monitor the generator.
Failure rate is pretty low for either hardwired or cord end but for the hardwired type know and understand how to bypass if necessary just in case it does fail.
|
|
|
08-01-2016, 08:46 AM
|
#7
|
Moderator Emeritus
Monaco Owners Club Texas Boomers Club
Join Date: Nov 2015
Location: Central Texas
Posts: 12,703
|
is the HW50C permanently installed? If so where does it go? I normally check out the pedestal with a DVM before plugging into it. Nothing elaborate, just to make sure the voltages are there and correct.
__________________
Dennis and Katherine
2000 Monaco Dynasty
|
|
|
08-01-2016, 09:04 AM
|
#8
|
Senior Member
Join Date: Jun 2012
Location: AB
Posts: 7,587
|
Quote:
Originally Posted by barmcd
is the HW50C permanently installed? If so where does it go? I normally check out the pedestal with a DVM before plugging into it. Nothing elaborate, just to make sure the voltages are there and correct.
|
Mine is mounted in my electrical bay. It does not monitor the generator. I was told by my electrician installer that it my cause problems with the transfer switch if installed before the switch. See left side of the photo. Ignore the Green circle.
Mine has saved me more than a few times from shoddy power pedestals and low voltage issues.
__________________
2019 Unity LTV CB, pushed by a 2013 Honda CRV, BlueOx Baseplate, Aventa Bar & Patriot Brake
|
|
|
08-01-2016, 11:44 AM
|
#9
|
Senior Member/RVM #90
Monaco Owners Club
Join Date: Nov 2002
Location: Columbus, MS
Posts: 44,456
|
Quote:
Originally Posted by sdennislee
Could not agree more. Progressive Industries EMS HW50C or PT50C is the only way to go.
|
My vote also! 
__________________
Joe & Annette
Sometimes I sits and thinks, sometimes I just sits.....
2002 Monaco Windsor 40PBT, 2013 Honda CRV AWD
|
|
|
08-01-2016, 01:00 PM
|
#10
|
Community Moderator
Newmar Owners Club
Join Date: Feb 2011
Location: Point Pleasant Beach, NJ
Posts: 21,764
|
Quote:
Originally Posted by Old-Biscuit
TRC.......
1 year limited warranty
Non-serviceable (throw away units)
Lack luster customer service dept.
Progressive Industries ......
LIFETIME warranty
Service..rebulidable/repairable units
Good customer service dept.
Choice is simple
|
It's saved me several times.
__________________
Tony & Ruth........... FMCA#F416727
2016 London Aire 4519, Freightliner chassis, Cummins ISX, 2018 Jeep Wrangler Unlimited, Blue Ox Avail with AF1. TST 507 TPMS
|
|
|
08-01-2016, 03:38 PM
|
#11
|
Senior Member
Join Date: Oct 2011
Posts: 251
|
Mine is mounted after the transfer switch;so, covers pedestal and generator. Has worked fine for 5 years. Transfer switch is cheap compared to all the other electrical devices that could be damaged. I'm willing to sacrifice it to also get protection from generator malfunction. I've had some say the generator cannot cause problems, but that is not true.
__________________
2011 Monaco Knight 36', MaxForce 10, 350HP, 1150 lbs. Torque.
2008 Saturn Vue Toad, SMI Duo Brake, Roadmaster Sterling Tow Bar
San Antonio, TX Home Port
|
|
|
08-01-2016, 05:02 PM
|
#12
|
Senior Member
Monaco Owners Club Winnebago Owners Club
Join Date: Sep 2011
Posts: 7,462
|
Quote:
Originally Posted by wigginsjsr
Mine is mounted after the transfer switch;so, covers pedestal and generator. Has worked fine for 5 years. Transfer switch is cheap compared to all the other electrical devices that could be damaged. I'm willing to sacrifice it to also get protection from generator malfunction. I've had some say the generator cannot cause problems, but that is not true.
|
I had intended to move mine from the electric bay to down stream of of the transfer switch but read the FAQ page on Progressive Industries site and they say not to install after the transfer switch.
__________________
US Navy Vet, Liberty Tree Member of Oath Keepers, NRA & VFW Life Member, Alaska EMT.
2009 Safari Cheetah 40 SKQ
2009 Winnebago Chalet 231CR
|
|
|
08-01-2016, 05:18 PM
|
#13
|
Senior Member
Join Date: May 2013
Posts: 335
|
Wow. No one likes the TRC surge guard? It appears they do the same thing. Is the warranty the main reason the Progressive Industries units are preferred?
1994 Holiday Rambler Navigator
Cummins 6CTA
Allison MD3060
__________________
1994 Holiday Rambler Navigator
300HP Cummins 8.3
Allison MD 3060
|
|
|
08-01-2016, 05:23 PM
|
#14
|
Senior Member
Monaco Owners Club Winnebago Owners Club
Join Date: Sep 2011
Posts: 7,462
|
In addition to the warranty, I made my decision on the EMSHW50C being field serviceable if it took a hit and burned a board to save the coach.
__________________
US Navy Vet, Liberty Tree Member of Oath Keepers, NRA & VFW Life Member, Alaska EMT.
2009 Safari Cheetah 40 SKQ
2009 Winnebago Chalet 231CR
|
|
|
 |
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Thread Tools |
Search this Thread |
|
|
Display Modes |
Linear Mode
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|