Lost power from pedestal

Hooked to 50 amp pedestal, all running good. Awoke to generator starting, brownout alarm on. Shut off gen. Magnum showing 188 volt on line one, 44volts line two. Turned gen. back on, 118 volts both lines In am shut gen. off both l1 and l2 showing 34 and 40 volts. Re-started gen. everything running ok. Inverter checked out ok. Voltage at surge protector showing 121/118 no amps. draw at all. Shut power at ped. back on, ran thru 123 seconds back on still reading 118/119 volts, no amps. with gen. off. Today I will put spare surge protector on and recheck. After that where to go? Power cord and reel inside closet, then what? Getting a mobile tech here in so east Tn. not easy. Need help. Staying warm with gas furnaces. 2010 Monaco 42 SKQ
__________________
Steve Corsetti
2010 Monaco Diplomat
St Petersburg, FL
tranquility is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 12-18-2020, 05:40 AM   #2
Senior Member
 
Join Date: Jul 2014
Posts: 35,446
The lopsided voltage happens with a bad neutral connection on the 120/240 volt 50 amp service.

It won't happen with no load on it, but if the surge thing is showing good voltage and your seeing uneven voltage inside, the problem is inside, after the surge thing.

You will need to check every connection from the shore power plug, to the main breaker panel.

If the surge thing is shutting down the power, causing the generator to run, then its a problem before the surge thing.
twinboat is offline   Reply With Quote
Old 12-18-2020, 09:17 AM   #3
Moderator Emeritus
 
TXiceman's Avatar
 
Ford Super Duty Owner
Join Date: Aug 2000
Location: Bryan, TX when not traveling.
Posts: 22,948
Blog Entries: 21
Sounds like the pedestal has a bad or weak neutral. Do not connect to it until it is corrected.

Ken
__________________
Amateur Radio Operator (KE5DFR)|No Longer Full-Time! - 2023 Cougar 22MLS toted by 2022 F150, 3.5L EcoBoost Tow Max FX4 Lariat Travel with one Standard Schnauzer and one small Timneh African Gray Parrot, retired mechanical engineer
TXiceman is offline   Reply With Quote
Old 12-19-2020, 11:47 AM   #4
Moderator Emeritus
 
Gary RVRoamer's Avatar


 
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 27,713
Fully agree with the others. Bad neutral and potentially very damaging to your RV electrical gear. Need to determine if its the pedestal (e.g. a loose or corroded wire there) or your shore cord or wiring from it to the load center.
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is West Palm Beach, FL
Gary RVRoamer is offline   Reply With Quote
Old 12-19-2020, 12:04 PM   #5
Senior Member
 
Skip426's Avatar


 
Join Date: Apr 2011
Location: Powell River, B.C.
Posts: 31,500
Try re-positioning the cord reel , ( run the reel so it's internal contacts are in a different location say 90 degrees ) wouldn't be the first time the internal contacts have messed up.
__________________
99DSDP 3884, Freightliner, XC, CAT 3126B, 300 HP /ALLISON 3060
2000 Caravan toad, Remco & Blue Ox.
Skip426 is offline   Reply With Quote
Reply

Tags
power



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Checking power pedestal question Camper Ken MH-General Discussions & Problems 34 03-07-2013 11:59 AM
New Power Pedestal Product from PPL JC2 RV Systems & Appliances 0 04-30-2012 02:26 PM
Total Loads on a Power Pedestal? RustyTools RV Systems & Appliances 6 04-18-2009 04:50 AM
Test Power at the pedestal Workshop Excel Owner's Forum 7 01-13-2008 01:19 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 07:49 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.