Old 03-24-2018, 08:09 PM   #15
Senior Member
 
Luv2go's Avatar
 
Newmar Owners Club
Nor'easters Club
Appalachian Campers
Ford Super Duty Owner
Coastal Campers
Join Date: Dec 2007
Posts: 2,463
Progressive makes both hard wired and plug in units. I have a plug in Surge Guard and installed it at the end of a 9' Dryer pigtail I used in place of the long power cord. The pigtail happens to reach my 50A outlet in the RV tent where the coach is stored. This allows me to lock up the plug-in Surge Guard in the compartment when I need to. Note to get under and overvoltage protection you need their EMS units, not the SSP's.
__________________
Stewart, Brenda and kids
2008 Newmar Canyon Star 3410, now at a new home
2006 Roadtrek Versatile 210
Luv2go is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 03-24-2018, 08:26 PM   #16
Senior Member
 
powercat_ras's Avatar
 
Winnebago Owners Club
Solo Rvers Club
Join Date: May 2015
Posts: 1,834
In the real world, the L1 and L2 sides of a RV with a 50 Amp Shore Cable rarely if ever draw over 30 Amps each. This is why many RVs with a 50 Amp Service Panel and 50 Amp Shore Cable only have a 7,000 Watt Generator capable of output of 30 Amps each on L1 and L2, I would just size for the 3% voltage drop at 50 Amps and actual load will be less and actual real world voltage drop will be less.

If what you plan to ever park at your site has or might have the 12,500 Watt Generator then the RV maker designed the RV to actually draw 50 A each on both L1 and L2 in a real world worst case, and sized the generator to be able to deliver 50 A x 2. In that case IMHO you should oversize, incremental cost is quite small compared to the price you paid for your very deluxe RV.
__________________
Randy - Manhattan, Kansas
2015 Vista 27N
2020 Ford Escape Hybrid
[SIGPIC][/SIGPIC]
powercat_ras is offline   Reply With Quote
Old 03-25-2018, 03:10 PM   #17
Senior Member
 
mmorgan's Avatar
 
Join Date: Apr 2013
Location: Kaplan, LA
Posts: 308
Don’t worry about an 80 foot run for 50 amp service.

I just ran a 310 foot line to power up a new 50 amp circuit, used #4 copper that is working great.

I just went out to the coach and with no load I’m seeing 122 volts on each leg. I turned on all three air-conditioners, residential fridge stays on all the time and the electric water heater for a total draw of 36 amps......voltage dropped to 120 on each leg.

If I added Microwave and electric dryer would probably drop another one or two volts and still be well above safe minimum voltage levels.
__________________
Michael Morgan
Kaplan, LA.
2002 Dutch Star 3567
mmorgan is offline   Reply With Quote
Old 03-25-2018, 03:19 PM   #18
Senior Member
 
Scottybdivin's Avatar


 
Newmar Owners Club
Join Date: Jun 2012
Location: Spicewood Texas (West of Austin)
Posts: 4,514
I agree with previous post. Mine is about 95', which is at or beyond the limit. No problems running 2 or 3 AC's. I was was glad I ran 50A to it last summer when the AC went out in the house. We slept in the RV for almost a week while we had a new one installed. Otherwise it would have benn off to an RV Park or Motel.
__________________
Scotty and Kristen, Airedales Dagny and Wyatt
2007 Newmar Mountain Aire 4528, 450 HP ISM, Allison 4000, 8 Lifeline AGM's
2019 F250 King Ranch 4x4 Powerstroke - SOLD
2022 F350 DRW King Ranch 4 x 4
Scottybdivin is offline   Reply With Quote
Old 03-25-2018, 04:16 PM   #19
Senior Member
 
Join Date: Dec 2013
Location: Lake Havasu City, AZ & Plover, WI
Posts: 6,403
I would bury wire to the RV site and put your 50 amp recep. box there. Might cost a bit more to do, but would be the best for years to come. We've buried thousands of miles of direct burial wire in the business over the years. I suspect a local electrician will have a mini-sneaker to make the job easy.
__________________
2006 Monaco Executive 44 Denali
2013 43 QGP Allegro Bus ( SOLD )
2013 Avalanche
Crasher is offline   Reply With Quote
Old 03-25-2018, 04:23 PM   #20
Senior Member
 
HamboneTHW's Avatar
 
Join Date: Mar 2018
Location: Harlingen, TX
Posts: 938
Quote:
Originally Posted by Crasher View Post
I would bury wire to the RV site and put your 50 amp recep. box there. Might cost a bit more to do, but would be the best for years to come. We've buried thousands of miles of direct burial wire in the business over the years. I suspect a local electrician will have a mini-sneaker to make the job easy.
Crasher,

I've had plenty of experience. While it sucks, I really don't mind trenching. The issue for me is that this isn't our forever home. Just don't see the point. The extra 50' of extension cord might also come in handy down the road. A hardwired receptacle with hundreds of dollars in wire and a lot of trenching won't do much for me in a house that won't be ours in 3 years. The Navy sees it fit that we move often.
HamboneTHW is offline   Reply With Quote
Old 03-25-2018, 04:25 PM   #21
Registered User
 
Join Date: Aug 2014
Location: western NC mountains!
Posts: 4,106
I've run 200' foot, no problem.
MisterT is offline   Reply With Quote
Old 03-25-2018, 06:56 PM   #22
Senior Member
 
Join Date: Jan 2009
Posts: 5,399
Quote:
Originally Posted by HamboneTHW View Post
I used to do electrical work. I'm not a fan of trenching wire and I like the traditional braided 6/3 better than the weatherproof wire, so then you're talking PVC work as well. A black extension cord temporarily won't both me. This isn't our forever home, otherwise I might look into doing that. The Navy still moves me every 2 to 3 years.
I just finished installing 30 amp service out to the MH. I'd say it took two or three days to make the plans, locate and buy the materials (receptacle, 6 awg thwn wire, conduit, grounding rod, other misc items.), rent the ditch witch, and then do the 100+ foot install. All total, a bit over $500 with me doing all the work.

You only being there for a couple of years, the cord is the way to go!
__________________
03 Itasca Sunova, Workhorse P32 with the 8.1 and 4L85-E
Mudfrog is offline   Reply With Quote
Old 03-25-2018, 07:45 PM   #23
Senior Member
 
BigBillSD's Avatar
 
Join Date: Oct 2016
Location: San Diego
Posts: 923
Quote:
Originally Posted by Triangle Drifter View Post
Why do you need 50amp service from house to trailer? I assume you want to chill the fridge & possibly top off the battery bank.
+1 I just plug my coach into a 20 amp circuit to get the batteries topped off and the refrigerator cold the night prior to leaving. You only need the 50 amp to run the A/C. You didn't mention living in it outside the house. I've never seen a reason to need more than 20 amp service when loading the coach or working on it at home. -Bill
__________________
2006 Allegro Bus 40 QDP IFS, 8.9L Vmspec, 1.5kw Solar + 400w Suitcase, 2@ 50amp & a 30amp Victron Smart MPPT's, 712BMV, SBS, CerboGX, 8.7kw LiFePo4, RR, MS2812, Max Transit, eero 6+ Mesh WiFi, Roof Mounted Starlink In-Motion dishy
BigBillSD is offline   Reply With Quote
Old 03-26-2018, 05:18 AM   #24
Senior Member
 
Scottybdivin's Avatar


 
Newmar Owners Club
Join Date: Jun 2012
Location: Spicewood Texas (West of Austin)
Posts: 4,514
Quote:
Originally Posted by HamboneTHW View Post
Crasher,

I've had plenty of experience. While it sucks, I really don't mind trenching. The issue for me is that this isn't our forever home. Just don't see the point. The extra 50' of extension cord might also come in handy down the road. A hardwired receptacle with hundreds of dollars in wire and a lot of trenching won't do much for me in a house that won't be ours in 3 years. The Navy sees it fit that we move often.
In that case go buy 50' of 6-4 SO cable plus male / female ends. SO cable will be more durable and easy to carry. I made one when we first started RV'ing and have used it many times..
__________________
Scotty and Kristen, Airedales Dagny and Wyatt
2007 Newmar Mountain Aire 4528, 450 HP ISM, Allison 4000, 8 Lifeline AGM's
2019 F250 King Ranch 4x4 Powerstroke - SOLD
2022 F350 DRW King Ranch 4 x 4
Scottybdivin is offline   Reply With Quote
Old 03-26-2018, 10:11 AM   #25
Senior Member
 
HamboneTHW's Avatar
 
Join Date: Mar 2018
Location: Harlingen, TX
Posts: 938
Quote:
Originally Posted by Scottybdivin View Post
In that case go buy 50' of 6-4 SO cable plus male / female ends. SO cable will be more durable and easy to carry. I made one when we first started RV'ing and have used it many times..
Scotty,

I was definitely looking at that route, but the cheapest I've found 6/4 SO is $2.50-$3.00 a foot. So $125-$150 just for the cable then $15-$20 for each of the plug ends. Found an already fabricated cord in 6 AWG for $188 to the house with free shipping. I figured for the price difference, why not get it already assembled and done?
HamboneTHW is offline   Reply With Quote
Old 03-26-2018, 12:26 PM   #26
Senior Member
 
Luv2go's Avatar
 
Newmar Owners Club
Nor'easters Club
Appalachian Campers
Ford Super Duty Owner
Coastal Campers
Join Date: Dec 2007
Posts: 2,463
Quote:
Originally Posted by HamboneTHW View Post
Scotty,

I was definitely looking at that route, but the cheapest I've found 6/4 SO is $2.50-$3.00 a foot. So $125-$150 just for the cable then $15-$20 for each of the plug ends. Found an already fabricated cord in 6 AWG for $188 to the house with free shipping. I figured for the price difference, why not get it already assembled and done?
We have two 50A extension cords for the Canyon Star. One made from the shore power cord that came with the coach with a female end put on. That one is very flexible in cold temperatures. The second was purchased from one of the big RV stores for a very good price. It has a plastic jacket instead of rubber and gets very stiff in cold weather. If I could do it over I would spend the extra money and get one that is rubber like SO cord.
__________________
Stewart, Brenda and kids
2008 Newmar Canyon Star 3410, now at a new home
2006 Roadtrek Versatile 210
Luv2go is offline   Reply With Quote
Old 03-26-2018, 02:37 PM   #27
Senior Member
 
Join Date: Feb 2015
Posts: 1,951
Surge Guard now has a lifetime warranty also.
__________________
2015 Itasca Ellipse 42QD
2017 Jeep Wrangler Rubicon Hard Rock
2011 Harley Davidson CVO Street Glide
TXTiger is offline   Reply With Quote
Old 03-26-2018, 03:55 PM   #28
Senior Member
 
Scottybdivin's Avatar


 
Newmar Owners Club
Join Date: Jun 2012
Location: Spicewood Texas (West of Austin)
Posts: 4,514
Quote:
Originally Posted by HamboneTHW View Post
Scotty,

I was definitely looking at that route, but the cheapest I've found 6/4 SO is $2.50-$3.00 a foot. So $125-$150 just for the cable then $15-$20 for each of the plug ends. Found an already fabricated cord in 6 AWG for $188 to the house with free shipping. I figured for the price difference, why not get it already assembled and done?
I'm sure it has gone up in price in 6 years or so. I think I built mine for just over $100. I once ran mine over two chain link fences and hanging from some tree limbs when we we parked on the beach in Rotary Park beside Lake Havasu for a boat race.
Attached Thumbnails
Click image for larger version

Name:	IMAG0157.jpg
Views:	186
Size:	1.00 MB
ID:	196876  
__________________
Scotty and Kristen, Airedales Dagny and Wyatt
2007 Newmar Mountain Aire 4528, 450 HP ISM, Allison 4000, 8 Lifeline AGM's
2019 F250 King Ranch 4x4 Powerstroke - SOLD
2022 F350 DRW King Ranch 4 x 4
Scottybdivin is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Motorhome length versus campgrounds max length hstansel Class A Motorhome Discussions 10 05-20-2016 06:36 PM
Speed going up grades: max HP vs. max torque RTegarini Workhorse and Chevrolet Chassis Motorhome Forum 19 01-16-2016 09:16 PM
Buyer Beware!! RV Ins - Max payout of $3500 if hit by Uninsured or Hit & Run!!! TangoDancers National RV Owner's Forum 13 03-19-2010 03:46 PM
Tire Pressure (Max or not to Max) Experts? Always-RVing iRV2.com General Discussion 32 09-30-2009 08:46 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 01:10 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.