Maxing out 200 Amp Main?

Slightly puzzled here... and probably thinking too much

So my property had a mobile home on a separate meter, I've repurposed that cement pad and meter for my Class A.

The panel has a 200 Amp main GE THQMV2200 so does that mean my max load would be 4 friends with 50 Amp RVs blasting AC?

Simple math 4 x 50 = 200. Or does it?

It is often said a 50 Amp double pole can provide 50 Amps on each leg. Most I've seen on the PowerWatchdog app is 30 to 35 on each leg.

Using the logic a 50 Amp double pole can provide max 50 per leg does that mean a 200 Amp main is also providing 200 max per leg or 800 total?
KenZ71 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 08-15-2022, 06:47 AM   #2
Senior Member
 
Join Date: Jul 2014
Posts: 31,181
It provides 200 amps at 240 volts.

It can have 4 120/240 branch circuits at 50 amps each. That gives you a grand total of 400 Amps at 120 volts, not 800 amps.

Theexperts will soon be here to explain how the 200 amp breaker won't support 200 amps but 4 RV will never be drawing exactly 50 amps each.
twinboat is online now   Reply With Quote
Old 08-15-2022, 06:49 AM   #3
Senior Member
 
Join Date: Apr 2020
Posts: 720
As you note a typical RV with 50A power never actually pulls 50A from each leg. I bet two A/Cs, a microwave and an electric water heater all running at once will only pull a max of 35A and only on one leg as the A/Cs are usually on separate legs.

So figure 200/35 = 5 or maybe 6 RVs hooked up simultaneously. What are you trying to do, start an RV park?

David
DavidEM is offline   Reply With Quote
Old 08-15-2022, 06:51 AM   #4
Senior Member
 
Dutchstar411's Avatar


 
Newmar Owners Club
Join Date: Dec 2015
Location: Wellington, Florida
Posts: 1,399
Quote:
Originally Posted by KenZ71 View Post
Slightly puzzled here... and probably thinking too much

So my property had a mobile home on a separate meter, I've repurposed that cement pad and meter for my Class A.

The panel has a 200 Amp main GE THQMV2200 so does that mean my max load would be 4 friends with 50 Amp RVs blasting AC?

Simple math 4 x 50 = 200. Or does it?

It is often said a 50 Amp double pole can provide 50 Amps on each leg. Most I've seen on the PowerWatchdog app is 30 to 35 on each leg.

Using the logic a 50 Amp double pole can provide max 50 per leg does that mean a 200 Amp main is also providing 200 max per leg or 800 total?
A 200 amp main is just that, 200 amps max based on it's recommended setup. In a house you rarely use all of that at once so there are many breakers within the panel that would total more then 200 amps. But the main breaker of that panel should be 4 50amp breakers in unison. So two coaches running 50 amp service, (50 amps per leg,) would be the max for your setup. Larger coaches can run close to the 50 amps per leg so why stretch it. Especially if you have other breakers in use as well. Just my opinion.
__________________
Ted & Nancy with our fur kids Mr. Vincent & Miss Daisy
2015 Newmar Dutch Star 4018
2002 Newmar Dutch Star 3852
2020 Jeep Wrangler Rubicon
Dutchstar411 is offline   Reply With Quote
Old 08-15-2022, 07:32 AM   #5
Senior Member
 
KenZ71's Avatar
 
Join Date: Nov 2017
Location: Back Woods of NC
Posts: 835
Not looking to setup an RV Park but plan to setup to allow friends to visit. Say a pig roast with a few RVs - what is ideal setup given the 200 Amp main as the limiter?

DavidEM and Dutchstar411 have different opinions - that is what makes the world fun.

For now I'll go with a 2 x 50 and 1 x 30 then adjust as needed. Easy enough to run out to lowes for a couple more breakers and plugs or just tell visitors to boondock it 🤔😀

If anyone says consult a qualified electrician that is the trick. Can't find qualified "pros". We've all seen the posts where a pro sets up a plug that fries the RV

While renovating my home I had a couple pros tell me this box is safe. I kicked them out faster than you can say fire
Attached Thumbnails
Click image for larger version

Name:	IMG_20211113_113206.jpg
Views:	26
Size:	430.5 KB
ID:	373709  
KenZ71 is offline   Reply With Quote
Old 08-15-2022, 07:38 AM   #6
Senior Member
 
Dutchstar411's Avatar


 
Newmar Owners Club
Join Date: Dec 2015
Location: Wellington, Florida
Posts: 1,399
Quote:
Originally Posted by KenZ71 View Post
Not looking to setup an RV Park but plan to setup to allow friends to visit. Say a pig roast with a few RVs - what is ideal setup given the 200 Amp main as the limiter?

DavidEM and Dutchstar411 have different opinions - that is what makes the world fun.

For now I'll go with a 2 x 50 and 1 x 30 then adjust as needed. Easy enough to run out to lowes for a couple more breakers and plugs or just tell visitors to boondock it 🤔😀

If anyone says consult a qualified electrician that is the trick. Can't find qualified "pros". We've all seen the posts where a pro sets up a plug that fries the RV

While renovating my home I had a couple pros tell me this box is safe. I kicked them out faster than you can say fire
In theory, you could have 4 friends at 50 amp service, so adding 2 50's and 1 30 would be the bomb and very safe

As long as your wiring doesn't look like that picture you posted.
__________________
Ted & Nancy with our fur kids Mr. Vincent & Miss Daisy
2015 Newmar Dutch Star 4018
2002 Newmar Dutch Star 3852
2020 Jeep Wrangler Rubicon
Dutchstar411 is offline   Reply With Quote
Old 08-15-2022, 07:50 AM   #7
Senior Member
 
jacwjames's Avatar
 
Monaco Owners Club
Join Date: Jun 2014
Posts: 11,941
Playing it safe is the way to go.



If i run everything in my coach I can pull about 70 amps. As long as your visitors have some common sense you should be fine. If you start having problems and your visitors don't want to conserve you may have to force them to use a 50 to 30 dog bone to limit amperage.
__________________
Jim J
2002 Monaco Windsor 38 PKD Cummins ISC 350 8.3L
2005 Jeep Grand Cherokee w/5.7 Hemi
jacwjames is offline   Reply With Quote
Old 08-15-2022, 08:07 AM   #8
Senior Member
 
Talloaks's Avatar
 
Country Coach Owners Club
Join Date: Feb 2019
Location: Kalamazoo MI
Posts: 407
Quote:
Originally Posted by KenZ71 View Post
Slightly puzzled here... and probably thinking too much...

so does that mean my max load would be 4 friends with 50 Amp RVs blasting AC...

Simple math ...

Or does it...

It is often said ...

Using the logic ...

does that mean ...?
I picked out a few phrases from your post to illustrate the basis for my suggestion to you: why not wire it in accordance with code? Why not give your AHJ a call to become familiar with local requirements? The NEC provides you the answers to your questions in terms of utilization factors to apply for multiple connections to a campground electrical circuit.

Kudos to you for asking good questions. Unfortunately, the use of what seems like common sense combined with a minimal understanding of how electricity works, compounded by uninformed but confident advice from somebody on an online forum, leads to expensive equipment damage and possible injury, not to mention disappointment and bewilderment. Good luck.
__________________
John
2007 Country Coach Tribute; Cat C9 400; 2012 Ford Edge toad; Roadmaster Blackhawk 2 10,000 lb tow bar; Demco AF1 Braking System; 2007 BMW K1200LT Hannigan Trike Conversion; Member, IEEE, NFPA, PMI, NRC SRO (Ret).
Talloaks is offline   Reply With Quote
Old 08-15-2022, 08:38 AM   #9
Senior Member
 
Dutchstar411's Avatar


 
Newmar Owners Club
Join Date: Dec 2015
Location: Wellington, Florida
Posts: 1,399
Ken,

Hopefully, you can shop out your job by contacting a few electrical contractors and see what they suggest as to how THEY would build out your job based on your requirements. With their suggestions, you can decide on how you would proceed with your project.
__________________
Ted & Nancy with our fur kids Mr. Vincent & Miss Daisy
2015 Newmar Dutch Star 4018
2002 Newmar Dutch Star 3852
2020 Jeep Wrangler Rubicon
Dutchstar411 is offline   Reply With Quote
Old 08-15-2022, 08:52 AM   #10
Senior Member
 
Workhorse Chassis Owner
Join Date: Jul 2005
Location: USA
Posts: 3,473
This will require installation of a 100 amp subpanel.
Two 50s in the main panel and two 50s in the subpanel.
OP's water pump, if he has one, stays on the main panel, along with any other outdoor lighting fixtures and such. Good luck!!
__________________
TandW
TandW is online now   Reply With Quote
Old 08-15-2022, 08:54 AM   #11
Senior Member
 
Join Date: Jan 2009
Posts: 4,077
Quote:
Originally Posted by Dutchstar411 View Post
In theory, you could have 4 friends at 50 amp service, so adding 2 50's and 1 30 would be the bomb and very safe

As long as your wiring doesn't look like that picture you posted.
Might as well add a second 30 amp service, on the opposite leg the first is on.

Four 50s, on their own breakers, would be fine. Of course they'd bring the installation cost up.
__________________
03 Itasca Sunova, Workhorse P32 with the 8.1 and 4L85-E
Mudfrog is offline   Reply With Quote
Old 08-15-2022, 09:12 AM   #12
RRR
Senior Member
 
Ford Super Duty Owner
Join Date: Mar 2009
Location: Oregon
Posts: 2,493
Quote:
Originally Posted by KenZ71 View Post

While renovating my home I had a couple pros tell me this box is safe. I kicked them out faster than you can say fire
And please do tell us why you say this box is safe. Inquiring minds want to know.
__________________
2016 Bounder 34T Anniversary Edition
RRR is online now   Reply With Quote
Old 08-15-2022, 09:17 AM   #13
Senior Member
 
Rockwood27's Avatar
 
Winnebago Owners Club
Nor'easters Club
Workhorse Chassis Owner
Join Date: Jun 2012
Location: Freedom, NH
Posts: 1,315
Quote:
Originally Posted by KenZ71 View Post

...So my property had a mobile home on a separate meter, I've repurposed that cement pad and meter for my Class A.
One thing not stated here is whether or not you replaced the mobile home with a permanent home. If you have or are planning to, does your electric company allow for 2 separate services on your property?

Sent from my SM-A515U using iRV2 - RV Forum mobile app
__________________
Fran, Mary & Zoey (silver Cocker)
2017 Thor Axis 25.5 "RUV", Ford E-450, V10, 6 speed
2016 Chevy Sonic LTZ Auto Hatchback 4-down
Rockwood27 is offline   Reply With Quote
Old 08-15-2022, 09:51 AM   #14
Senior Member
 
Join Date: Aug 2022
Posts: 133
The main breaker is, and should be, a 200A breaker, not 4, 50A breakers as mentioned previously.

Whatís ideal? It depends.

Downstream of the main breaker you could have 4, 50A breakers feeding 4, 14-50 outlets, 4, 30A breakers feeding 4, TT-30ís and a dozen 15A breakers feeding various circuits.

Will you be able to have 8 RVís running full tilt boogie and 12 air compressors running simultaneously? No.
IAlreadyGot1 is online now   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Oil pressure gauge maxing and check eng and oil light buzzer reosw Cummins Engines 27 01-21-2021 06:12 PM
carry out satellite dish & directv receiver hr 44/200 mycoolbeans Technology: Internet, TV, Satellite, Cell Phones, etc. 13 07-20-2015 04:59 PM
Alternator 200 Amp vs 270 Amp Rehbergl Class A Motorhome Discussions 8 02-21-2014 08:40 PM
200 amp fuse no-go on Inverter? (as per Battery Store?) BadBoy MH-General Discussions & Problems 21 06-30-2010 10:24 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 10:35 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2022, vBulletin Solutions, Inc.