nEU Fault on my Automated Electrical Control System
We have been on 50 Amp Shore power for over two weeks. We live full time in our 2005 Fleetwood American Tradition. When I got home from work the refrigerator was blasting the NoCo alarm. thinking it just needed reset I went to the board to do that. It wouldnt reset. So I went back in to check things out and surprise...no 110 v lights. I started the generator and all powered up. I shut off the generator and went to the power bin. There was an nEU fault displayed on the Automated Electrical Control System. What is this fault and how do I fix it?
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
If all worked ok when you switched to generator but still had the issue on shore power I think you need to check the circuit breakers on the post 1st.
I think you have a 50 amp meaning 2 hot, 1 neutral and 1 ground wire.
Now your panel shows fault NEU which to me means neutral is your fault.
And that could only be an open neutral wire. White wire.
Hope this helps a bit for now until you tell us more.