Old 01-22-2019, 08:02 AM   #15
Senior Member
 
KanzKran's Avatar
 
Join Date: Sep 2018
Posts: 1,944
Quote:
Originally Posted by fishmaine View Post
Per twin boat above, turning out the idle adjustment screw on the carburetor may decrease the motor RPM which would typically cause a direct decrease in the output voltage level. I adjusted the idle in this manner to reduce the RPMs but there was no change...the generator still produced exactly 155 volts (although turning in the idle screw slightly did increase the voltage a little bit to about 160 volts)
Have you checked output frequency? That unit, according to the specs and manual, is a constant-speed design with the usual two windings for 120/240V output, or connected in parallel for 120V only. Engine speed is mechanically governed at 2571 rpm, with a speed increasing belt drive to a 3600 rpm generator. So if the voltage is way off, it's either a bad or loose neutral (if 120/240V), or the regulator is shot.
KanzKran is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-22-2019, 01:25 PM   #16
Senior Member
 
Domo's Avatar
 
Join Date: Sep 2018
Location: Fort Myers, FL
Posts: 1,687


Are those Canadian volts? If so, that's about 120 USVAC.

__________________
2008 Phaeton 36QSH, Safe-t-Plus, Quadra Bigfoot
2017 Jeep Cherokee Trailhawk w/ flat tow wiring mod.
Blue ox, BrakeMaster + BrakeAway, diode lights and charge.
Domo is offline   Reply With Quote
Old 01-22-2019, 01:30 PM   #17
Senior Member
 
Domo's Avatar
 
Join Date: Sep 2018
Location: Fort Myers, FL
Posts: 1,687


Are those Canadian volts? If so, that's about 120 USVAC.




BTW - the Voltage Regulator is what regulates the voltage (hence the name). The motor RPM is what regulates the power capable of being delivered. That's why you hear the motor rev up to deliver more power when your A/C (or other load) kicks on, however the voltage stay constant (yes, within design tolerance and phase of the moon changes).
__________________
2008 Phaeton 36QSH, Safe-t-Plus, Quadra Bigfoot
2017 Jeep Cherokee Trailhawk w/ flat tow wiring mod.
Blue ox, BrakeMaster + BrakeAway, diode lights and charge.
Domo is offline   Reply With Quote
Old 01-22-2019, 02:20 PM   #18
Member
 
fishmaine's Avatar
 
Newmar Owners Club
Workhorse Chassis Owner
Join Date: Jul 2018
Location: Maine/Arizona
Posts: 81
Hi all....I need to be on the road shortly so to resolve this issue quicker I went in to a local RV tech and he was able to quickly confirm that the voltage regulator on the generator was bad....his meter was reading $155 volts also. He also confirmed that our automatic transfer switch (ATS) was defective by connecting the shore power lines to the generator input site on the ATS and running 120 shore power through the generator side of the ATS...again no power in the RV. This confirmed that the ATS was not switching and damaged inside somehow...possibly by high voltage from the generator or maybe from the fact that the ATS had a slowly developing manufacturers defect (it was recalled several years ago - I have the IOTA 50-ITS 50R). The end result is that I will be buying and installing both a new Generac voltage regulator and a new automatic transfer switch. I am planning on getting the ESCO LPT50BRD ATS which is the historically recommended replacement for the IOTA. Both the voltage regulator and ATS are available on Amazon.....VR is $119, ESCO ATS is $177. Thanks once again for all your valuable help. The tests I conducted per your input gave me the knowledge to proceed with the repairs!
__________________
2004 Newmar Scottsdale on 2003 W-22 Workhorse Chassis, 8.1 Vortec, super short 30.5', AZ in winter & ME in summer. Half Of Life Is Just Showing Up
fishmaine is offline   Reply With Quote
Old 01-22-2019, 03:28 PM   #19
Senior Member
 
Join Date: Jul 2014
Posts: 35,415
Quote:
Originally Posted by Domo View Post


Are those Canadian volts? If so, that's about 120 USVAC.




BTW - the Voltage Regulator is what regulates the voltage (hence the name). The motor RPM is what regulates the power capable of being delivered. That's why you hear the motor rev up to deliver more power when your A/C (or other load) kicks on, however the voltage stay constant (yes, within design tolerance and phase of the moon changes).
Wrong.
Most gasoline powered RV generators are constant speed units. What you hear is the load increasing, not the RPMs.

Portable, inverter type generators varry engine speed depending on load.

Check out the specs below for a very popular Cummins-Onan 4000 watt RV generator.

It turns at 3600 RPMs for 60 Hertz.
It turns at 3000 RPMs for 50 Hertz.

If the generator speed changed up and down the HZs would be all over the place.

Check it out.Click image for larger version

Name:	Capture%2B_2019-01-22-17-16-44.jpeg
Views:	129
Size:	104.8 KB
ID:	232786
twinboat is online now   Reply With Quote
Old 01-22-2019, 04:17 PM   #20
Senior Member
 
Domo's Avatar
 
Join Date: Sep 2018
Location: Fort Myers, FL
Posts: 1,687
Quote:
Originally Posted by twinboat View Post
Wrong.
Most gasoline powered RV generators are constant speed units. What you hear is the load increasing, not the RPMs.

Portable, inverter type generators varry engine speed depending on load.

Check out the specs below for a very popular Cummins-Onan 4000 watt RV generator.

It turns at 3600 RPMs for 60 Hertz.
It turns at 3000 RPMs for 50 Hertz.

If the generator speed changed up and down the HZs would be all over the place.

Check it out.Attachment 232786
Well, thanks for the update!
__________________
2008 Phaeton 36QSH, Safe-t-Plus, Quadra Bigfoot
2017 Jeep Cherokee Trailhawk w/ flat tow wiring mod.
Blue ox, BrakeMaster + BrakeAway, diode lights and charge.
Domo is offline   Reply With Quote
Old 01-23-2019, 05:58 AM   #21
Senior Member
 
KanzKran's Avatar
 
Join Date: Sep 2018
Posts: 1,944
Quote:
Originally Posted by twinboat View Post
Wrong.
Most gasoline powered RV generators are constant speed units. What you hear is the load increasing, not the RPMs.

Portable, inverter type generators varry engine speed depending on load.

Check out the specs below for a very popular Cummins-Onan 4000 watt RV generator.

It turns at 3600 RPMs for 60 Hertz.
It turns at 3000 RPMs for 50 Hertz.

If the generator speed changed up and down the HZs would be all over the place.

Check it out.Attachment 232786
What he said about frequency.

Same as induction motors, frequency times 120 divided by number of poles is generator speed (60Hz x 120 / 2 = 3600 rpm). Most small generators are 2-pole, so they spin at 3600 rpm for 60Hz output (3000 rpm for 50Hz). Larger diesels are usually 4-pole, so they spin at 1800 rpm, and really large ones may be 6- or 8-pole and turn proportionately slower. Power plants at hydrodams have as many as 64 poles which would require 112.5 rpm to generate at 60Hz.
KanzKran is offline   Reply With Quote
Old 01-23-2019, 06:12 AM   #22
Senior Member
 
Join Date: Jul 2014
Posts: 35,415
There are some RV generators sets that belt drive the generator end.
Doing that, they can slow the engine RPMs down for less noise, but still turn the head at 3600 RPMs for 60 HZs. Very common in the gas, 2 cylinder, vertical engine models.
twinboat is online now   Reply With Quote
Old 01-23-2019, 07:44 AM   #23
Registered User
 
Join Date: Oct 2016
Posts: 2,078
Onan QD 8000 is a variable speed

Are there any inverter gas or propane generators in rvs?
lwmcguire is offline   Reply With Quote
Old 01-23-2019, 08:17 AM   #24
Senior Member
 
Join Date: Jul 2014
Posts: 35,415
Quote:
Originally Posted by lwmcguire View Post
Onan QD 8000 is a variable speed

Are there any inverter gas or propane generators in rvs?
We haven't seen fuel injected, gas generators in RVs yet. Carburators died in the early 80s.

Inverter generators of that size don't seem to be out there yet, although Honda has a eu7000 portable now.
twinboat is online now   Reply With Quote
Old 07-03-2019, 02:06 PM   #25
Senior Member
 
Trickdog's Avatar
 
Join Date: Nov 2017
Location: Frisco Texas
Posts: 136
I have the same model. You need to check HZ first before trying to adjust the voltage regulator according to the manual. You should be reading around 60HZ with the generator loaded if possible. You can get a decent meter on Amazon that will read HZ. Then there is a small adjustment screw on the voltage regulator. Mine would not adjust and had to buy a new one. Was around $200 if I remember correctly. I will see if I can find the manual and send it to you (PDF).
__________________
Trickdog,
2001 Coleman Pop-up, 2006 Fleetwood Pioneer, 2017 Coleman TQ toy hauler, 2008 Forest River Georgetown 373DS / KIA Forte TOAD, 2022 Keystone Cameo / 2022 Chevy 3500
Trickdog is offline   Reply With Quote
Old 07-03-2019, 02:28 PM   #26
Senior Member
 
Trickdog's Avatar
 
Join Date: Nov 2017
Location: Frisco Texas
Posts: 136
Quote:
Originally Posted by Trickdog View Post
I have the same model. You need to check HZ first before trying to adjust the voltage regulator according to the manual. You should be reading around 60HZ with the generator loaded if possible. You can get a decent meter on Amazon that will read HZ. Then there is a small adjustment screw on the voltage regulator. Mine would not adjust and had to buy a new one. Was around $200 if I remember correctly. I will see if I can find the manual and send it to you (PDF).
I PM'ed you with my email address. I can send you the service manual not the owners manual for your generator model. Handy to have.
__________________
Trickdog,
2001 Coleman Pop-up, 2006 Fleetwood Pioneer, 2017 Coleman TQ toy hauler, 2008 Forest River Georgetown 373DS / KIA Forte TOAD, 2022 Keystone Cameo / 2022 Chevy 3500
Trickdog is offline   Reply With Quote
Old 07-04-2019, 01:53 PM   #27
Senior Member
 
153stars's Avatar
 
Join Date: Mar 2019
Location: Braidwood Il.
Posts: 8,300
Just in case someone is searching later with bad neutral. That will read high one leg low other, but still 240v across hot legs,
like 100v + 140v or 80v + 160v ect. = 240v
__________________
95 Monaco Crown Royale
M11 400hp, 4060 trans.
Aquahot, Generac Guardian7.5k
153stars is offline   Reply With Quote
Reply

Tags
generator



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Change from 2 6 volts to 1 12 volts ron l Class A Motorhome Discussions 20 01-26-2013 09:20 PM
Inverter putting out too many volts? VACMAN Newmar Owner's Forum 7 07-29-2009 08:08 AM
Generator only putting out a few volts AC TallPaul RV Systems & Appliances 7 12-25-2007 02:57 PM
2-6 volts or 4-6 volts rick_od Boondocking 8 05-09-2007 06:37 PM
Genset putting out over 130 volts.. Houndog RV Systems & Appliances 5 10-29-2005 01:19 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 08:42 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.