Onan 5500 Generator question

Hello to all my fellow rv'rs out there. Quick question for those who know. I read in the owners manual that you are not supposed to start your generator with the 2/30 amp breakers in the on position, the same thing when shutting down. You are supposed to shut the breakers off first before shutting down. My question is, if there is no load on the generator what does it hurt leaving the breakers in the on position full time?
craigd853 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 02-02-2023, 06:23 PM   #2
Senior Member
 
Psneeld's Avatar
 
Join Date: May 2020
Location: Ft Pierce, Fl
Posts: 1,364
I could be wrong, but as long as there are only light loads or none at all, it doesn't seem to hurt generators. Have not been turning off the breakers EVER in the last 20+ years of using them commercially and recreationally.

Sensitive loads connected may not like the startup sequence, but if light loads, I don't think the generator seems to care.
__________________
Retired USCG Helo Pilot, Retired USCG Lic. Captain
2022 Entegra Vision 29s, 2021 Ford Ranger toad
Ft Pierce, Fl
Psneeld is online now   Reply With Quote
Old 02-02-2023, 06:35 PM   #3
Senior Member
 
Ford Super Duty Owner
Join Date: Dec 2009
Location: Mcdonough, Ga.
Posts: 5,931
Quote:
Originally Posted by craigd853 View Post
Hello to all my fellow rv'rs out there. Quick question for those who know. I read in the owners manual that you are not supposed to start your generator with the 2/30 amp breakers in the on position, the same thing when shutting down. You are supposed to shut the breakers off first before shutting down. My question is, if there is no load on the generator what does it hurt leaving the breakers in the on position full time?
Are you sure you are reading this right? I have never heard of this. I have owned motorhomes since 1974 and have never shut off the breakers. I was service manager for 15 years and went to the Onan factory school and again I never heard this.
__________________
1998 Pace Arrow 35 ft. F53 Ford V10 2014 Honda CRV toad
32 years mechanic at Delta Air Lines 15 year motorhome service manager. 3 popups....2 travel trailers....5 motorhomes....loved them all.
ga traveler is offline   Reply With Quote
Old 02-02-2023, 08:25 PM   #4
Senior Member
 
Join Date: Aug 2020
Location: Ohio
Posts: 2,353
I am not an electrician.. but I believe it is to save the caps inside the generator voltage regulator.. so it's to save the voltage regulator.. and they are expensive.. and a real pain to get at.. so I believe that is why.. also don't forget to let it cool down.. so take the load off and let run for about 5 to 10mins to let engine cool off..
Good luck and keep us posted
__________________
2000 southwind storm, workhorse custom chassis with 7.4l vortec
donr103 is offline   Reply With Quote
Old 02-02-2023, 08:29 PM   #5
Community Moderator
 
TonyDi's Avatar


 
Newmar Owners Club
Join Date: Feb 2011
Location: Point Pleasant Beach, NJ
Posts: 31,505
That doesn't sound right to me. That could be a major task for some people. What if it's raining? I've never done this.
__________________
Tony & Ruth........... FMCA#F416727
2016 London Aire 4519, Freightliner chassis, Cummins ISX, 2018 Jeep Wrangler Unlimited, Blue Ox Avail with AF1. TST 507 TPMS
No amount of money can buy you an extra second of time.
TonyDi is offline   Reply With Quote
Old 02-03-2023, 03:31 AM   #6
Senior Member
 
Join Date: Mar 2021
Posts: 513
Blog Entries: 1
Quote:
Originally Posted by TonyDi View Post
That doesn't sound right to me. That could be a major task for some people. What if it's raining? I've never done this.
Thanks for all who answered I didn’t think it was a big deal either as long as ur not shutting it off with a load on it. If I recall it states in the onan owners manual to turn the breakers on after starting and off before shutdown. Kind of negates the auto start button in the motorhome if u have to do this right? I have been shutting them off and turning them on for 2 years now. PIA Lol
craigd853 is offline   Reply With Quote
Old 02-03-2023, 04:01 AM   #7
Senior Member
 
Psneeld's Avatar
 
Join Date: May 2020
Location: Ft Pierce, Fl
Posts: 1,364
Just read all the pages (about 5) concerning starting and shutting down my 2022 Onan 5500.

Not one word about circuit breakers.

A couple pages later they discuss if they have tripped, it may be necessary to turn off fully before resetting.
__________________
Retired USCG Helo Pilot, Retired USCG Lic. Captain
2022 Entegra Vision 29s, 2021 Ford Ranger toad
Ft Pierce, Fl
Psneeld is online now   Reply With Quote
Old 02-03-2023, 05:28 AM   #8
Senior Member
 
Join Date: Jul 2014
Posts: 35,413
Your not starting the generator with power connected.

Any RV with an auto transfer switch will not switch to generator power until a 30 to 45 second timer runs out, after sensing generator voltage.
That's there to let the generator stabilize power.

You can see this delay yourself if you start your generator, without shore power, and then watch your microwave. It will not power on for at least 30 seconds.
twinboat is online now   Reply With Quote
Old 02-03-2023, 05:37 AM   #9
Senior Member
 
Join Date: Aug 2020
Posts: 590
[QUOTE=craigd853;6415363]If I recall it states in the onan owners manual to turn the breakers on after starting and off before shutdown. Correct.

Can you start the genny with the breakers ON...of course you can. But best practice is keep them OFF till the genny warms up and begins to warm up and smooth out the proper RPM.

As someone else said “it is to save the caps inside the generator voltage regulator.. so it's to save the voltage regulator.. and they are expensive.. and a real pain to get at and repair..” This delay is to allow the generator to stabilize power first.

Quote:
Originally Posted by craigd853 View Post
Kind of negates the auto start button in the motorhome if u have to do this right? Nope
I have been shutting them off and turning them on for 2 years now. PIA Lol
No it doesn’t negate it because most Jenny’s that have auto start there is a built in time delay before the genny starts to produce power to the RV. This is a built in safety protocol that I mentioned above. So if you have auto start and the built in time delay is long enough for the genny to warm up and smooth out to a nice even rpm, before power starts to be delivered to the RV, then it’s fine to leave the breakers ON.

I don’t have auto start and I personally manually turn ON breakers after the genny warms up. Before I shut the genny OFF I give it a 5-10 minute cool down period, then turn OFF breakers and then shut OFF the genny. My 5500 is 13yrs.old with approx 1200hrs. on it.
__________________
Traveling Full Timers
Gas Motorhome
Escapees, Maintenance Freak
mr.tommy is offline   Reply With Quote
Old 02-03-2023, 07:42 AM   #10
Senior Member
 
Join Date: May 2018
Posts: 890
Most RVers don't even know the breaker exists.

If you think about how the Automatic Generator Start (AGS) works with the air conditioner it turns off when the air conditioner turns off, so no big loads. For turning on it depends on the fact that the transfer switch takes about 30 seconds before it turns on, thus there isn't a load on the generator when it first starts up.

It's a good idea to unload the generator before starting or stopping it. Unloading it when you stop it is more important, assuming your transfer switch has a delay to put the load on the generator.

Are you sure you have two 30 amp breakers on your Onan 5500? That's about 7000 watts and what my QG7000 has. I thought that the QG5500 had a 20 and a 25 amp breaker.
dssl is offline   Reply With Quote
Old 02-03-2023, 11:26 AM   #11
Senior Member
 
National RV Owners Club
Join Date: Jul 2018
Location: Melbourne, FL
Posts: 468
Quote:
Originally Posted by dssl View Post
Most RVers don't even know the breaker exists.

If you think about how the Automatic Generator Start (AGS) works with the air conditioner it turns off when the air conditioner turns off, so no big loads. For turning on it depends on the fact that the transfer switch takes about 30 seconds before it turns on, thus there isn't a load on the generator when it first starts up.

It's a good idea to unload the generator before starting or stopping it. Unloading it when you stop it is more important, assuming your transfer switch has a delay to put the load on the generator.

Are you sure you have two 30 amp breakers on your Onan 5500? That's about 7000 watts and what my QG7000 has. I thought that the QG5500 had a 20 and a 25 amp breaker.
The 5500 has two 30A breakers, at least mine does, and the spec sheet shows 30A.

Al
__________________
SeaBreeze LX 8321
FLRosebud is offline   Reply With Quote
Old 02-03-2023, 12:30 PM   #12
Senior Member
 
astrnmrtom's Avatar
 
Join Date: Sep 2013
Location: Pacific Northwest and Arizona
Posts: 2,048
Ok, I've read the Op's post several times because I've never heard this. Then it dawned on me. I bet most readers are assuming he has a built in RV generator, not a portable. I can see this for a portable because they may not have a built in delay.
__________________
Tom and Pris M. along with Buddy the 18 year old Siamese cat
1998 Safari Serengeti 3706, 300HP Cat 3126 Allison 3060, 900 watts of Solar.
Dragging four telescopes around the US in search of dark skies.
astrnmrtom is offline   Reply With Quote
Old 02-03-2023, 01:05 PM   #13
Senior Member
 
hilgert's Avatar
 
Join Date: Nov 2014
Location: Somewhere
Posts: 827
I never turn on/off our breakers, either on the generator or in the coach, and have never heard of a need to do so. Generator is an Onan QD8000, and we use it often (exercise it monthly if not traveling).
__________________
2019 Fleetwood Discovery LXE 40D
2023 Ford Expedition Limited Stealth Edition Towed
Full-Timers since 2018
hilgert is offline   Reply With Quote
Old 02-03-2023, 01:07 PM   #14
Senior Member
 
hilgert's Avatar
 
Join Date: Nov 2014
Location: Somewhere
Posts: 827
Quote:
Originally Posted by astrnmrtom View Post
Ok, I've read the Op's post several times because I've never heard this. Then it dawned on me. I bet most readers are assuming he has a built in RV generator, not a portable. I can see this for a portable because they may not have a built in delay.
The OP's Onan 5500 is a built in RV generator.

Most ATS units (if not all ATS's?) have a 30 second delay when switching from shore power to generator power...that is where the delay is.
__________________
2019 Fleetwood Discovery LXE 40D
2023 Ford Expedition Limited Stealth Edition Towed
Full-Timers since 2018
hilgert is offline   Reply With Quote
Reply

Tags
generator, onan



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Onan 5500 generator voltage question bwanna2016 RV Systems & Appliances 21 11-30-2021 03:44 PM
Onan 5500 Generator Fuel Consumption Question DMacLeod RV Systems & Appliances 2 09-30-2021 05:16 PM
Replacing a 5500 Onan with a 7000 Onan dfwd RV Systems & Appliances 5 08-11-2021 08:00 AM
2003 Dolphin - Onan 5500 generator question... smithbill Workhorse and Chevrolet Chassis Motorhome Forum 3 07-25-2021 08:00 PM
5500 Onan vs 7000 Onan HUGHP MH-General Discussions & Problems 10 07-16-2016 07:09 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 05:05 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.