Old 07-30-2021, 08:59 PM   #1
Senior Member
 
Join Date: Jul 2012
Posts: 887
Onan 7500 Code 38 Won't Run with Circuit Breaker on any advice

Started a Florida to Iowa trip this afternoon. Got 35 miles from home and wanted to use roof air so turned on generator. It ran for a bit then shut off. Pulled off interstate and restarted gen. Ran fine while we sat there for about ten minutes. Started back to interstate the generator shut back off. The generator would crank but would immediately shut back off. Error code was 38.

Fuel was not low, fuel filter was changed in June, air filter is fine, coolant and oil levels are fine. Error code indicates an overload but there was no load on the generator when it was shutting off.

Checked and cleaned terminals on gen going to transfer switch and terminals at transfer switch. Went as far as disconnecting terminals from gen to transfer switch- same issue. Gen would still crank and immediately shut off. Turned the gen circuit breaker to the off position generator ran fine. Turn breaker on generator immediately shuts off.

Turned off all breakers inside coach turned on generator. It immediately shut off. Generator will run fine as long as gen circuit breaker is in off position.

Any advice?
__________________
Mark
2002 40 PWD Monaco Windsor
Flat Towing Honda CR-V
mlh2013 is online now   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 07-30-2021, 09:22 PM   #2
Senior Member
 
Mile Marker 42's Avatar
 
Join Date: May 2013
Location: S. California
Posts: 1,379
Quote:
Originally Posted by mlh2013 View Post
Started a Florida to Iowa trip this afternoon. Got 35 miles from home and wanted to use roof air so turned on generator. It ran for a bit then shut off. Pulled off interstate and restarted gen. Ran fine while we sat there for about ten minutes. Started back to interstate the generator shut back off. The generator would crank but would immediately shut back off. Error code was 38.

Fuel was not low, fuel filter was changed in June, air filter is fine, coolant and oil levels are fine. Error code indicates an overload but there was no load on the generator when it was shutting off.

Checked and cleaned terminals on gen going to transfer switch and terminals at transfer switch. Went as far as disconnecting terminals from gen to transfer switch- same issue. Gen would still crank and immediately shut off. Turned the gen circuit breaker to the off position generator ran fine. Turn breaker on generator immediately shuts off.

Turned off all breakers inside coach turned on generator. It immediately shut off. Generator will run fine as long as gen circuit breaker is in off position.

Any advice?
You said "I cleaned terminals on gen going to transfer switch". Do you mean in the front left of the generator where all your wires come out, you opened that up and checked all those connections for tightness and correctness? Do you have a junction box between generator and transfer switch? Have you ridden in the rain since you have been on this trip? Did you have your dash AC on when this happened or happens?
__________________
2003 Monaco Knight 36ft PST Triple Slide- 315 ISC
2007 Jeep Grand Cherokee 3.0 Diesel 4x4
2- 2013 Yamaha VXR's 70MPH+. 2019 Sun Tracker 18ft Pontoon w/ 75hp Mercury
Mile Marker 42 is offline   Reply With Quote
Old 07-30-2021, 09:29 PM   #3
Senior Member
 
Join Date: Jul 2012
Posts: 887
Quote:
Originally Posted by Mile Marker 42 View Post
You said "I cleaned terminals on gen going to transfer switch". Do you mean in the front left of the generator where all your wires come out, you opened that up and checked all those connections for tightness and correctness? Have you ridden in the rain since you have been on this trip? Did you have your dash AC on when this happened or happens?
Yes removed front left panel on top of gen and cleaned all those terminals. No coach has been inside barn out of weather. Yes my dash air was on when problem first started.
__________________
Mark
2002 40 PWD Monaco Windsor
Flat Towing Honda CR-V
mlh2013 is online now   Reply With Quote
Old 07-30-2021, 09:36 PM   #4
Senior Member
 
Mile Marker 42's Avatar
 
Join Date: May 2013
Location: S. California
Posts: 1,379
Quote:
Originally Posted by mlh2013 View Post
Yes removed front left panel on top of gen and cleaned all those terminals. No coach has been inside barn out of weather. Yes my dash air was on when problem first started.
The 7500's front mounted had water intrusion problems to that front left area where the wiring is. Many reported their dash AC was dripping in such a way that it ended up on the connectors in the front left area and was shorting to ground causing a 38 code. Is it possible that is happening on yours? Are there wire nuts for the house wiring in there on yours? Did you try tightening them or first loosening them to look at the wires, then re tightening? Many have said that fixed their 38 code.
__________________
2003 Monaco Knight 36ft PST Triple Slide- 315 ISC
2007 Jeep Grand Cherokee 3.0 Diesel 4x4
2- 2013 Yamaha VXR's 70MPH+. 2019 Sun Tracker 18ft Pontoon w/ 75hp Mercury
Mile Marker 42 is offline   Reply With Quote
Old 07-30-2021, 09:42 PM   #5
Senior Member
 
Join Date: Jul 2012
Posts: 887
Quote:
Originally Posted by Mile Marker 42 View Post
The 7500's front mounted had water intrusion problems to that front left area where the wiring is. Many reported their dash AC was dripping in such a way that it ended up on the connectors in the front left area and was shorting to ground causing a 38 code. Is it possible that is happening on yours? Are there wire nuts for the house wiring in there on yours? Did you try tightening them or first loosening them to look at the wires, then re tightening? Many have said that fixed their 38 code.
I didn't see any wire nuts in there. What I did was took each wire out and cleaned the terminal and then cut back the wire so fresh wire would be going back into the terminal.
__________________
Mark
2002 40 PWD Monaco Windsor
Flat Towing Honda CR-V
mlh2013 is online now   Reply With Quote
Old 07-30-2021, 10:04 PM   #6
Senior Member
 
Mile Marker 42's Avatar
 
Join Date: May 2013
Location: S. California
Posts: 1,379
Quote:
Originally Posted by mlh2013 View Post
I didn't see any wire nuts in there. What I did was took each wire out and cleaned the terminal and then cut back the wire so fresh wire would be going back into the terminal.
Strange, if it were me, I would be thinking of replacing the Onan circuit breaker first before giving up and taking it to a shop. Easy to replace and the part is under $100 online. Keep us posted what you find.
__________________
2003 Monaco Knight 36ft PST Triple Slide- 315 ISC
2007 Jeep Grand Cherokee 3.0 Diesel 4x4
2- 2013 Yamaha VXR's 70MPH+. 2019 Sun Tracker 18ft Pontoon w/ 75hp Mercury
Mile Marker 42 is offline   Reply With Quote
Old 07-31-2021, 08:24 AM   #7
Senior Member
 
Join Date: Jul 2012
Posts: 887
Okay I pulled circuit breaker and inspected found no eye catching issues reinstalled it. I then pulled all 3 fuses while in there, 1 seem to have some type of discoloration on it's legs, replaced it and reinstalled fuses fired it up turned on gen circuit breaker and it runs.

I turn on front ac to put load on gen no problem so far.
I turn on rear ac to increase load no problem.
I drive on 15 mile drive with gen on and ac's on no problem.
I come home park in front yard with gen and ac's running for over an hour no problem.
I shut down gen and leave off for a few minutes start back up put under load and all is well.

I don't know if it is just a coincident that now it's running fine or if removing breaker and checking fuses had something to do with it.
__________________
Mark
2002 40 PWD Monaco Windsor
Flat Towing Honda CR-V
mlh2013 is online now   Reply With Quote
Old 07-31-2021, 08:25 AM   #8
Senior Member
 
Join Date: Jul 2012
Posts: 887
Quote:
Originally Posted by Mile Marker 42 View Post
Strange, if it were me, I would be thinking of replacing the Onan circuit breaker first before giving up and taking it to a shop. Easy to replace and the part is under $100 online. Keep us posted what you find.
Yes I will order a new circuit breaker for sure, thanks for the suggestion.
__________________
Mark
2002 40 PWD Monaco Windsor
Flat Towing Honda CR-V
mlh2013 is online now   Reply With Quote
Old 07-31-2021, 01:19 PM   #9
Senior Member
 
Mile Marker 42's Avatar
 
Join Date: May 2013
Location: S. California
Posts: 1,379
Quote:
Originally Posted by mlh2013 View Post
Okay I pulled circuit breaker and inspected found no eye catching issues reinstalled it. I then pulled all 3 fuses while in there, 1 seem to have some type of discoloration on it's legs, replaced it and reinstalled fuses fired it up turned on gen circuit breaker and it runs.

I turn on front ac to put load on gen no problem so far.
I turn on rear ac to increase load no problem.
I drive on 15 mile drive with gen on and ac's on no problem.
I come home park in front yard with gen and ac's running for over an hour no problem.
I shut down gen and leave off for a few minutes start back up put under load and all is well.

I don't know if it is just a coincident that now it's running fine or if removing breaker and checking fuses had something to do with it.
Wow, certainly good news for sure. These things seem to have lots of strange issues or odd fixes.
__________________
2003 Monaco Knight 36ft PST Triple Slide- 315 ISC
2007 Jeep Grand Cherokee 3.0 Diesel 4x4
2- 2013 Yamaha VXR's 70MPH+. 2019 Sun Tracker 18ft Pontoon w/ 75hp Mercury
Mile Marker 42 is offline   Reply With Quote
Old 07-31-2021, 01:22 PM   #10
Senior Member
 
PJStough's Avatar
 
Winnebago Owners Club
Workhorse Chassis Owner
Join Date: Oct 2015
Posts: 1,718
Quote:
Originally Posted by mlh2013 View Post
Yes removed front left panel on top of gen and cleaned all those terminals. No coach has been inside barn out of weather. Yes my dash air was on when problem first started.
Any chance rodents could have gotten into the wiring while stored inside the barn?
__________________
Paul J Stough Iowa
2005 Winnebago Voyage 38J
PJStough is offline   Reply With Quote
Old 07-31-2021, 01:42 PM   #11
Senior Member
 
Join Date: Apr 2018
Posts: 3,441
Anytime you shut these down under a load it seems to scramble the boards proccessor. Always disconnect the 12v cables into the back of the gen and wait 10 minutes. Reconnect and try again. That resets the chips in the control board. Mine would start and die, then went to crank only, then went to nothing. Resetting the board fixed it. I created the problem by shutting it down with the ACs running.
shootist is offline   Reply With Quote
Old 07-31-2021, 07:45 PM   #12
Senior Member
 
Join Date: Jul 2012
Posts: 887
Quote:
Originally Posted by PJStough View Post
Any chance rodents could have gotten into the wiring while stored inside the barn?
I don't think so I didn't see any evidence of rodents while lid was off.
__________________
Mark
2002 40 PWD Monaco Windsor
Flat Towing Honda CR-V
mlh2013 is online now   Reply With Quote
Old 07-31-2021, 07:46 PM   #13
Senior Member
 
Join Date: Jul 2012
Posts: 887
Quote:
Originally Posted by shootist View Post
Anytime you shut these down under a load it seems to scramble the boards proccessor. Always disconnect the 12v cables into the back of the gen and wait 10 minutes. Reconnect and try again. That resets the chips in the control board. Mine would start and die, then went to crank only, then went to nothing. Resetting the board fixed it. I created the problem by shutting it down with the ACs running.
Thank you for that tip
__________________
Mark
2002 40 PWD Monaco Windsor
Flat Towing Honda CR-V
mlh2013 is online now   Reply With Quote
Old 07-31-2021, 10:43 PM   #14
Senior Member
 
Mile Marker 42's Avatar
 
Join Date: May 2013
Location: S. California
Posts: 1,379
Quote:
Originally Posted by shootist View Post
Anytime you shut these down under a load it seems to scramble the boards proccessor. Always disconnect the 12v cables into the back of the gen and wait 10 minutes. Reconnect and try again. That resets the chips in the control board. Mine would start and die, then went to crank only, then went to nothing. Resetting the board fixed it. I created the problem by shutting it down with the ACs running.
I had a strange issue on my 7500 QD last year. It's a 2003 with 755+ hours. Less than 25 of those are mine and I have had it 7 years. The only run time it gets is exercising. 1 time it would shut off after 10 mins of running. Did this 3 times. Never had done this before. Threw a 24 coolant sensor issue. I came here to IRV2 and created a post on it asking if anyone knew a trick to clear codes or get the 24 to turn off. Otherwise, I would have had to pull the generator out the front door. Mine won't drop down. Anyway, an air plane mechanic in Denver said to disconnect the 12 volt positive and negative cable that come in to the generator underneath. He said wire brush the cable ends and mounting studs and leave disconnected for an hour. He said this is how they clear codes in jets. He then suggested once I had assembled the cables back on to the generator, hold down start button for 60 seconds before attempting to start it. I'll be darned if this didn't work for me and fix that code 24. Granted I don't heavily use my generator, it works fine. So Shootist, What you are saying jives with me:-)
__________________
2003 Monaco Knight 36ft PST Triple Slide- 315 ISC
2007 Jeep Grand Cherokee 3.0 Diesel 4x4
2- 2013 Yamaha VXR's 70MPH+. 2019 Sun Tracker 18ft Pontoon w/ 75hp Mercury
Mile Marker 42 is offline   Reply With Quote
Reply

Tags
advice, breaker, circuit breaker, onan



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
"lights" circuit breaker on breaker panel...help sinjineer Newmar Owner's Forum 12 12-08-2018 05:11 PM
Onan QD 8000 Code 36 & Circuit Breaker f15epilot Travel Supreme Owner's Forum 4 11-06-2016 10:02 AM
Onan 7500 won't run - replacing fuel filter & pump - Help! randomhero Class A Motorhome Discussions 3 04-26-2016 09:07 PM
Replacing circuit breaker on a Onan 7500 generator steved44 Class A Motorhome Discussions 2 02-21-2014 12:05 PM
Replacing the circuit breaker on an Onan 7500 Quiet Diesel Denali Monaco Owner's Forum 9 06-17-2010 10:27 AM