Plug In 30A Electrical Question and Issue

We have a 'campsite' at a new (for us) home we purchased. Home was built in 2008 so everything is modern and current.

The campsite has its own subpanel. See attached photo of the interior of the panel. The campsite is fed via a 30A 240v breaker in the main panel in the main house. I'm guessing because the subpanel at the site doesn't have a 'main,' it has a 30A 240v breaker which is really the breaker at the panel for the incoming power. It is marked as Main In in the picture.

There is a 30A breaker for the 30A RV outlet at the campsite marked as Campsite in the photo. The campsite also has other two 20A/120v outlets mounted on the post, each with its own breaker. There are ultimately two extra 20A breakers and I'm not sure why.

Now that the groundwork is laid, here is the issue:

Our friends have a diesel Class A Winnebago with 50A service. He utilizes the same surge protector I do (Progressive Industries but he has an older model) and his showed a bad ground (two green lights and two #1 red lights) at the campsite. When I plugged in mine later, as shown in the pic, it shows fine.

When he plugged in his rig, things were fine until he turned on the AC. Then after about 20 seconds, the microwave popped (like it had blown a fuse or a GFCI popped) and then the refrigerator beeped showing an issue. In checking, Inverter showed 'overload.' We moved the rig to our driveway 50A outlet.

To condense the story, we found that the PC board on the refer had fried. Replaced that and it worked. We couldn't even find where the microwave plugged in to see if it had a GFCI. The microwave has its own breaker, did not trip and yes, I have never seen a GFCI on a microwave, but we wanted to see anyway.

So, the question here is why did this happen? Everything on the campsite panel checked out ok, 120-122v. It's grounded, etc.

Anyone have any ideas?
rdibbxsh is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 10-18-2022, 10:11 AM   #2
Senior Member
 
Arch Hoagland's Avatar
 
Monaco Owners Club
Workhorse Chassis Owner
Join Date: Aug 2002
Location: Clovis, CA, USA
Posts: 13,149
No picture has showed up yet.
__________________
2004 Monaco La Palma 36DBD, W22, 8.1, 7.1 MPG
2000 LEXUS RX300 FWD 22MPG 4020 LBS
Criticism is easier than Craftsmanship
Arch Hoagland is offline   Reply With Quote
Old 10-18-2022, 10:12 AM   #3
Senior Member
 
Join Date: Oct 2014
Posts: 7,882
Quote:
Originally Posted by rdibbxsh View Post
The campsite is fed via a 30A 240v breaker in the main panel in the main house. I'm guessing because the subpanel at the site doesn't have a 'main,' it has a 30A 240v breaker which is really the breaker at the panel for the incoming power.

So, your 30 amp is fed from a 30 amp duplex breaker (two hots)???


If so, that will let the smoke out of a lot of your electronics.


30 amp RV is ONE hot, one neutral and one ground. NOT the same as house-style 30 amp 240 VAC.
__________________
Brett Wolfe
Ex: 2003 Alpine 38FDDS. Ex: 1997 Safari Sahara. Ex: 1993 Foretravel U240
wolfe10 is offline   Reply With Quote
Old 10-18-2022, 10:14 AM   #4
Senior Member
 
Old-Biscuit's Avatar
 
Join Date: Nov 2015
Posts: 26,843
No pictures!!!


Is the 30A outlet 3 prong or 4 prong?

So you have TWO 30A circuit breakers feeding the 'subpanel' and TWO 30A CBs for the 30A outlet?
If so ...the 30A is 240V. Not 120VAC
__________________
I took my Medication today. HAVE YOU?
Dodge 3500 w/Tractor Motor
US NAVY---USS Decatur DDG-31
Old-Biscuit is online now   Reply With Quote
Old 10-18-2022, 12:23 PM   #5
Member
 
Join Date: Apr 2011
Location: Jonesborough
Posts: 63
OK, I uploaded four pics and it shows them uploaded. Never having posted a pic, is there something else I need to do?
rdibbxsh is offline   Reply With Quote
Old 10-18-2022, 12:26 PM   #6
Member
 
Join Date: Apr 2011
Location: Jonesborough
Posts: 63
I'm not sure why the pics are not posting. The 30A is wired to a single 30A breaker, all 10 ga wire (maybe one foot total length), black to breaker, white to neutral bar, green and box to ground bar
rdibbxsh is offline   Reply With Quote
Old 10-18-2022, 12:29 PM   #7
Member
 
Join Date: Apr 2011
Location: Jonesborough
Posts: 63
It is 3 prong, typical 30A outlet. Not sure why the pics won't post. They did upload with the post. It also duplicated my post do there is another new thread I can't seem to delete.
rdibbxsh is offline   Reply With Quote
Old 10-18-2022, 12:38 PM   #8
Senior Member
 
Join Date: Oct 2014
Posts: 7,882
Quote:
Originally Posted by rdibbxsh View Post
The 30A is wired to a single 30A breaker, all 10 ga wire (maybe one foot total length), black to breaker, white to neutral bar, green and box to ground bar

This is very different from your original post and, assuming the wires go to the correct position in the outlet is correct (one hot, one neutral and one ground):

Originally Posted by rdibbxsh
The campsite is fed via a 30A 240v breaker in the main panel in the main house. I'm guessing because the subpanel at the site doesn't have a 'main,' it has a 30A 240v breaker which is really the breaker at the panel for the incoming power.
__________________
Brett Wolfe
Ex: 2003 Alpine 38FDDS. Ex: 1997 Safari Sahara. Ex: 1993 Foretravel U240
wolfe10 is offline   Reply With Quote
Old 10-18-2022, 01:03 PM   #9
Senior Member
 
Join Date: Jul 2018
Posts: 4,925
Quote:
Originally Posted by rdibbxsh View Post
I'm not sure why the pics are not posting. The 30A is wired to a single 30A breaker, all 10 ga wire (maybe one foot total length), black to breaker, white to neutral bar, green and box to ground bar
You uploaded your pictures to your Photos, not as an attachment to the post.

That said: if the "campsite" is fed from a 2 pole breaker and ONE outlet is the only receptacle at the site and it is a TT-30 receptacle, the outlet is *likely* mis-wired for 240V use (like a clothes dryer).

It's been said elsewhere but the voltage on a TT-30 is the same as a regular household (Edison) outlet, only the TT-30 is capable of greater current capacity (30 amps).

Go to Harbor Freight and buy a $20 volt meter. Read the directions for measuring AC voltage. If your site outlet has only 3 pins (or sockets for only 3 pins), you should not read any voltage between ground and neutral (the widest of the flat pins), and nominally 120V between neutral and Line. If you have 4 pin sockets or find 240V between any combination of pins, DO NOT CONNECT YOUR RV to the outlet until you consult an electrician who understands RV power, or at least is aware of NEC Article 551.
__________________
2005 Four Winds Majestic 23A
“To the world you may be one person; but to one person you may be the world.” - Dr Suess
Solo_RV_Guy is offline   Reply With Quote
Old 10-18-2022, 03:24 PM   #10
Member
 
Join Date: Apr 2011
Location: Jonesborough
Posts: 63
Agreed. It should have said the entire campsite panel (actually a small box for about 8 breakers) is fed with a 30A, 240v and breaker. The actual panel has a 30A breaker for the campsite plug and other 20A breakers for the GFCI outlets there.

I still don't know why the pic will not or have not uploaded.
Attached Thumbnails
Click image for larger version

Name:	2022-10-16 15.27.18.jpg
Views:	42
Size:	67.8 KB
ID:	379043   Click image for larger version

Name:	2022-10-15 16.15.00.jpg
Views:	27
Size:	70.7 KB
ID:	379044  

Click image for larger version

Name:	2022-10-15 16.14.35.jpg
Views:	29
Size:	4.91 MB
ID:	379045   Click image for larger version

Name:	2022-10-15 16.13.50.jpg
Views:	28
Size:	64.9 KB
ID:	379046  

rdibbxsh is offline   Reply With Quote
Old 10-18-2022, 03:25 PM   #11
Member
 
Join Date: Apr 2011
Location: Jonesborough
Posts: 63
Sorry, although I had resized them, I made them into thumbnails and it worked.
rdibbxsh is offline   Reply With Quote
Old 10-19-2022, 07:24 AM   #12
Member
 
Join Date: Apr 2011
Location: Jonesborough
Posts: 63
Yes, nomenclature can get confusing here, sorry.

The entire campsite box, shown in the picture, is fed from a 30A, 2 pole breaker in the house's basement. So in the US fashion, I have two 120v legs coming to the box.

Yes, it is a standard 30A RV outlet, although I didn't know the true name, it is a TT-30. Yes, I would say it is just a standard higher amperage outlet versus an Edison outlet which is either 15A or 20A.

No disrespect, but I have several full function multimeters, even a Fluke, and can operate them for AC voltage, DC voltage Ohms, Amps, etc.

From the pic, on the 30A breaker shown as Main In, I get 244v across both poles on the breaker. For all the other 120v breakers, I get 122v breaker pole to neutral. On the TT-30 outlet, I get 122v across the two prongs (hot and neutral). I get zero volts neutral to ground (round prong). I get 122v hot to ground.

So I think we're talking the same thing. How or why this occurred is beyond my understanding, thus why I posted it. And why was turning on the basement AC the triggering factor?

I tried reattaching the box pic for clarification. It shows uploaded.

Thank you



**[That said: if the "campsite" is fed from a 2 pole breaker and ONE outlet is the only receptacle at the site and it is a TT-30 receptacle, the outlet is *likely* mis-wired for 240V use (like a clothes dryer).

**[It's been said elsewhere but the voltage on a TT-30 is the same as a regular household (Edison) outlet, only the TT-30 is capable of greater current capacity (30 amps).

**[Go to Harbor Freight and buy a $20 volt meter. Read the directions for measuring AC voltage. If your site outlet has only 3 pins (or sockets for only 3 pins), you should not read any voltage between ground and neutral (the widest of the flat pins), and nominally 120V between neutral and Line. If you have 4 pin sockets or find 240V between any combination of pins, DO NOT CONNECT YOUR RV to the outlet until you consult an electrician who understands RV power, or at least is aware of NEC Article 551.[/QUOTE]
Attached Thumbnails
Click image for larger version

Name:	2022-10-16 15.27.18.jpg
Views:	29
Size:	67.8 KB
ID:	379120  
rdibbxsh is offline   Reply With Quote
Old 10-19-2022, 08:15 AM   #13
Senior Member
 
Join Date: Jul 2005
Posts: 5,996
What seems curious to me is the grounding lug in the panel appears to have a #12 White wire that goes to a yellow/red twister. Can't see what else is in the yellow/red twister. Are you sure the Campsite panel has it's own secure, adequately sized ground?
__________________
TandW
TandW is offline   Reply With Quote
Old 10-19-2022, 09:12 AM   #14
Senior Member
 
Sweetbriar's Avatar
 
Thor Owners Club
Ford Super Duty Owner
Join Date: Jul 2011
Posts: 3,796
I would be looking deeper into the Winnebago for a problem. It almost reads like the Winni had a hot neutral at the 30 amp outlet but the surge protector would have caught it and would have never passed power to the coach and your meter checks didn't show a problem either.

Have you checked his 30 to 50 amp adaptor with a meter? It's the one thing that would be different with his configuration when using the 30 amp outlet as compared to the 50 amp.

And just to confirm, everything was OK with his rig other than the listed problems once he moved to the 50 amp circuit? Is the inverter functional including the converter side keep the batteries up when plugged in?
__________________
2006 Hurricane 31D built on a 2006 Ford F53
Sweetbriar is offline   Reply With Quote
Reply

Tags
electric, electrical



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
30a fixed umbilical to 30a twist lock Pdx camper RV Systems & Appliances 0 04-14-2022 11:29 PM
Can A 30A MH Plug Into A 50A Outlet (with a plug converter of course) Ceratto's Grotto MH-General Discussions & Problems 15 06-13-2017 11:14 PM
Use of 50A Surge Protector with 30A Pigtail for 30A Shore Power hugh37 Newmar Owner's Forum 9 07-08-2016 01:14 PM
220 dryer plug to 30A? monkey MH-General Discussions & Problems 109 05-23-2012 02:49 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 09:56 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.