12-05-2018, 01:11 PM
|
#1
|
Senior Member
Join Date: Nov 2017
Location: Tampa FL
Posts: 502
|
Safe to use an extension cord with a ceramic heater?
My wife is concerned about one of the space heaters that I'm using since I have that one plugged into an extension cord. It's a quality extension cord, but nevertheless it is an extension cord and most if not all space heater manufacturers warn of using their heaters with extension cords.
Most cords on space heaters are rather short, and I'm guessing that's by design.
__________________
2018 Coachmen Sportscoach 408DB
41 foot DP
2018 Jeep Wrangler JL -Alpha Blue Ox and RVI3
It's never too late to do the right thing!
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
12-05-2018, 01:31 PM
|
#2
|
Senior Member
Join Date: Sep 2012
Posts: 8,055
|
Feel the extension cord. If it is warm to the touch consider a larger gauge cord. Other than that the only other issue is reduced heat output.
|
|
|
12-05-2018, 01:42 PM
|
#3
|
Community Moderator
Join Date: Sep 2011
Location: Between the Oceans
Posts: 8,034
|
Assuming your space heater is 1500w or less. As only as the extension cord is labeled 15a or higher, you are fine. But I have seen some of that in 6ft or so are for computer or Christmas lights, that shouldn't be used.
As above said, feel it while using it; if it's warm and soft, stop using it.
__________________
Steven & Polly
2000 Country Coach Intrigue 40' ISC 350
2018 Ford Explorer 4WD
|
|
|
12-05-2018, 02:27 PM
|
#4
|
Senior Member
Join Date: Nov 2017
Location: Tampa FL
Posts: 502
|
Quote:
Originally Posted by nothermark
Feel the extension cord. If it is warm to the touch consider a larger gauge cord. Other than that the only other issue is reduced heat output.
|
Thanks
__________________
2018 Coachmen Sportscoach 408DB
41 foot DP
2018 Jeep Wrangler JL -Alpha Blue Ox and RVI3
It's never too late to do the right thing!
|
|
|
12-05-2018, 02:33 PM
|
#5
|
Senior Member
Join Date: Nov 2017
Location: Tampa FL
Posts: 502
|
Quote:
Originally Posted by CountryFit
Assuming your space heater is 1500w or less. As only as the extension cord is labeled 15a or higher, you are fine. But I have seen some of that in 6ft or so are for computer or Christmas lights, that shouldn't be used.
As above said, feel it while using it; if it's warm and soft, stop using it.
|
Thanks, I'm hoping some of these responses will put my wife's mind at ease.
We had a very large tree branch come down where we live in Denver that just missed our coach, after that I was sleeping with one eye open, so to speak. I finally convinced the RV park to cut it down, since there were obvious signs the tree was dying (hollow in many areas). I feel much better now that the tree is gone.
My wife said to me the other night that the space heater with the extension cord was her "tree".
__________________
2018 Coachmen Sportscoach 408DB
41 foot DP
2018 Jeep Wrangler JL -Alpha Blue Ox and RVI3
It's never too late to do the right thing!
|
|
|
12-05-2018, 02:58 PM
|
#6
|
Senior Member
Join Date: Jul 2018
Posts: 4,922
|
Quote:
Originally Posted by larliebler
Thanks, I'm hoping some of these responses will put my wife's mind at ease.
We had a very large tree branch come down where we live in Denver that just missed our coach, after that I was sleeping with one eye open, so to speak. I finally convinced the RV park to cut it down, since there were obvious signs the tree was dying (hollow in many areas). I feel much better now that the tree is gone.
My wife said to me the other night that the space heater with the extension cord was her "tree".
|
There are classes of "portable cord" designated for space heaters and other appliances that generate heat as their primary mission (toasters, waffle irons, hot plates) and those classes are used to make extension cords. A quick search of the "A" company for heater extension cords brought up too many poor choices, you might try "iron" in your search terms. You want a cord that is labeled in a way to reduce Darling Wife's anxiety. Showing it's made for the use and is U.L. Listed for that use should help.
Space heaters have shorter cords for several reasons (most of them liability related) but what the fire department really, really, really wants us to NOT do is use "power strips" with space heaters and adding an extension cord to the power strip is a big no-no, too.
If this doesn't work you might try to find a space heater with a longer cord and eliminate the extension objection.
Have fun and safe travels always.
__________________
2005 Four Winds Majestic 23A
“To the world you may be one person; but to one person you may be the world.” - Dr Suess
|
|
|
12-05-2018, 03:55 PM
|
#7
|
Senior Member
Tiffin Owners Club
Join Date: Feb 2017
Location: Frankfort, KY
Posts: 1,906
|
One other option is to re-wire it yourself with the same gage wire or heavier to the length you need, no more, no less. Just a thought.
__________________
Scott and Deanna
2014 Tiffin Allegro Bus 45LP
Home base - Polk City, FL
|
|
|
12-05-2018, 04:33 PM
|
#8
|
Moderator Emeritus
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 27,678
|
1500 watts is 1500 watts, whether a space heater, hair dryer or water heater. That's 12.5 amps @ 120v, so you need an extension cord rated for that much amperage. That means 14 gauge wire or higher. Shorter cords with that capacity are often labeled "appliance cords", but longer ones (25 ft or more) are usually just labeled with the wire gauge size.
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is West Palm Beach, FL
|
|
|
12-05-2018, 05:27 PM
|
#9
|
Senior Member
Join Date: Aug 2017
Posts: 698
|
Safe to use an extension cord with a ceramic heater?
Just a clarification on Gary’s post. By “higher” he actually means a LOWER gauge number for a HIGHER current capacity.
12 gauge wire is larger than 14 gauge.
10 gauge is larger than 12.
Etc.
Buy a good, 10 gauge extension cord and you can run any 1,500 watt device with it. Like this one...
https://www.homedepot.com/p/Duromax-...050A/302770085
|
|
|
12-06-2018, 11:45 AM
|
#10
|
Senior Member
Join Date: Nov 2017
Location: Tampa FL
Posts: 502
|
Quote:
Originally Posted by A Traveler
Just a clarification on Gary’s post. By “higher” he actually means a LOWER gauge number for a HIGHER current capacity.
12 gauge wire is larger than 14 gauge.
10 gauge is larger than 12.
Etc.
Buy a good, 10 gauge extension cord and you can run any 1,500 watt device with it. Like this one...
https://www.homedepot.com/p/Duromax-...050A/302770085
|
I did know what he meant, but it's always good to check, and thanks for the link. I think I'll go ahead and purchase it for no reason other than peace of mind.
__________________
2018 Coachmen Sportscoach 408DB
41 foot DP
2018 Jeep Wrangler JL -Alpha Blue Ox and RVI3
It's never too late to do the right thing!
|
|
|
12-06-2018, 12:23 PM
|
#11
|
Senior Member
Workhorse Chassis Owner
Join Date: Dec 2004
Location: Baraboo, Wisconsin
Posts: 1,728
|
I looked at the link and see it's for a 50' cord, which is pretty long to use inside a motorhome. I did a little search and Home Depot also has a 25' cord. I'd want it even shorter for inside, maybe in the 10' range, you may be able to find one with a little research.
__________________
Steve & Nancy
2005 Itasca Sunrise 33', W20 Chassis, Ultrapower, Henderson Trac Bar
2012 Chevy Captiva Sport AWD, ReadyBrute Elite Tow Bar, Blue Ox Base Plate, Protect-A-Tow
|
|
|
12-06-2018, 12:39 PM
|
#12
|
Senior Member
Join Date: Nov 2017
Location: Tampa FL
Posts: 502
|
Quote:
Originally Posted by Easyrider
I looked at the link and see it's for a 50' cord, which is pretty long to use inside a motorhome. I did a little search and Home Depot also has a 25' cord. I'd want it even shorter for inside, maybe in the 10' range, you may be able to find one with a little research.
|
Yeah, 50 feet is a bit long, but I'm sure I can find a comparable one with same specs. Thanks
__________________
2018 Coachmen Sportscoach 408DB
41 foot DP
2018 Jeep Wrangler JL -Alpha Blue Ox and RVI3
It's never too late to do the right thing!
|
|
|
12-06-2018, 02:22 PM
|
#13
|
Registered User
Join Date: Apr 2018
Posts: 1,459
|
My normal house warming gift when somebody buys their first house. Buy a 100 ft 12 gauge extension cord. Starting at the plug end, cut at 25 ft, and put a weather proof box/duplex outlet on the end. Cut again at 15 feet, ad plug and weather proof box/duplex outlet. Put a plug on what is left over, they got 3 cords in useful lengths...
|
|
|
12-07-2018, 08:07 AM
|
#14
|
Moderator Emeritus
Join Date: Jan 2000
Location: West Palm Beach, FL. USA
Posts: 27,678
|
You can easily get "appliance" grade extension cords in lengths as short as 3 ft and wire gauges in the 14, 12, and 10 gauge sizes. 14 gauge wire will handle 1500 watts at distances up to 25 ft, so 10 gauge is really overkill on a shorter cord.
Here's a 12 gauge, 9 ft long cord at Walmart for about $10.
https://www.walmart.com/ip/Coleman-C...hcpid=21309876
Or this one At Amazon (and Walmart too): 8 ft and rated for 1625 watts
https://www.amazon.com/Woods-2611-3-.../dp/B003RRWWCW
__________________
Gary Brinck
Former owner of 2004 American Tradition and several other RVs
Home is West Palm Beach, FL
|
|
|
|
|