Transfer Switch Failure
The other day, out of the blue, my MH tripped the 50A pedestal breaker. A quick analysis of the problem showed power as far down the circuit as my Progressive EMS but the pedestal breaker would trip unless the generator had been started.
Thinking the problem through, I reasoned that the fact that the breaker didn't trip when the generator was on and that the EMS showed power behind the transfer switch meant that the short wasn't in the power cable or the cable reel.
Eventually I convinced myself that the short was had to be in the transfer switch itself although this isn't a common failure mode for these switches. I opened the transfer switch case but didn't see any evidence of arcing.
Today, I bypassed the switch so that shore power was directly connected to
he coach while we wait for a new switch to be delivered. Sure enough, with the switch bypassed everything was fine.
My wife, who was in the coach when the power failed, says that she saw the 120V lights flickering just before power was lost. I had noticed a little flickering the last couple of evenings, but I attributed it to the power company.
My expectation is that when I tear apart the old switch I'll find a hairline crack in the contactor insulation structure. I'm posting this so people will know that this is a possible failure mode in a (20 year old) transfer switch.
Joel (AKA docj)
__________________
Joel (AKA docj)--
RV Technology Specialist
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
11-11-2019, 10:37 PM
|
#2
|
Senior Member
Join Date: Jul 2014
Posts: 35,446
|
Not sure why a hairline crack would create a 50 amp short, unless the contacts are hanging free and contacting each other in the enclosure.
Following.
|
|
|
11-11-2019, 11:19 PM
|
#3
|
Senior Member
Join Date: Dec 2015
Location: Dittmer, MO 63023
Posts: 1,123
|
Quote:
Originally Posted by docj
The other day, out of the blue, my MH tripped the 50A pedestal breaker. A quick analysis of the problem showed power as far down the circuit as my Progressive EMS but the pedestal breaker would trip unless the generator had been started.
Thinking the problem through, I reasoned that the fact that the breaker didn't trip when the generator was on and that the EMS showed power behind the transfer switch meant that the short wasn't in the power cable or the cable reel.
Eventually I convinced myself that the short was had to be in the transfer switch itself although this isn't a common failure mode for these switches. I opened the transfer switch case but didn't see any evidence of arcing.
Today, I bypassed the switch so that shore power was directly connected to
he coach while we wait for a new switch to be delivered. Sure enough, with the switch bypassed everything was fine.
My wife, who was in the coach when the power failed, says that she saw the 120V lights flickering just before power was lost. I had noticed a little flickering the last couple of evenings, but I attributed it to the power company.
My expectation is that when I tear apart the old switch I'll find a hairline crack in the contactor insulation structure. I'm posting this so people will know that this is a possible failure mode in a (20 year old) transfer switch.
Joel (AKA docj)
|
Not sure if the crack is causing the short but could be causing magnetic coil to not move the switch and properly transfer power through the switch. Not sure what is causing the short unless the coil has a dead short. Strange things do happen at times. I encourage you to post your findings.
__________________
2005 CC Affinity 770, 2006 Jeep TJ
2015 Newmar Essex 4553 2022 Jeep Gladiator.
|
|
|
11-12-2019, 04:27 AM
|
#4
|
Senior Member
Join Date: Jul 2014
Posts: 35,446
|
One other thought, was the 50 amp outlet a GFCI protected type ?
I know they are not common, but are out there, and can trip with the slightest ground fault or current imbalance.
|
|
|
11-12-2019, 05:04 AM
|
#5
|
Senior Member
Join Date: Jul 2018
Posts: 3,165
|
Quote:
Originally Posted by twinboat
One other thought, was the 50 amp outlet a GFCI protected type ?
I know they are not common, but are out there, and can trip with the slightest ground fault or current imbalance.
|
Yes they can and already do at new Marinas with older boats. Not long before we see them in campgrounds. I have seen Marinas put them in for inspection then remove them after they get a CO.
__________________
2011 Keystone Sprinter 323 BHS. Port Charlotte Fl/Hinsdale MA. Retired Master Electrician. All Motor homes are RV's. All RV's are not Motor homes.
|
|
|
11-12-2019, 06:31 AM
|
#6
|
Senior Member
Join Date: Sep 2018
Location: Fort Myers, FL
Posts: 1,694
|
Sounds as if a contact blew off (due to cracked plastic as OP suggests) and is now shorted on the shore side of the contacts. Would be easy to verify with a meter once it's on a table... I'd guess.
It will be good hear what Joel actually finds as the failure point in his 20 year old transfer switch
__________________
2008 Phaeton 36QSH, Safe-t-Plus, Quadra Bigfoot
2017 Jeep Cherokee Trailhawk w/ flat tow wiring mod.
Blue ox, BrakeMaster + BrakeAway, diode lights and charge.
|
|
|
11-12-2019, 12:44 PM
|
#7
|
Senior Member
Official iRV2 Sponsor
Join Date: May 2011
Posts: 8,305
|
Quote:
Originally Posted by twinboat
One other thought, was the 50 amp outlet a GFCI protected type ?
|
No, it isn't
__________________
Joel (AKA docj)--
RV Technology Specialist
|
|
|
11-12-2019, 01:14 PM
|
#8
|
Senior Member
Monaco Owners Club Vintage RV Owners Club Holiday Rambler Owners Club
Join Date: Jul 2012
Location: Lexington, SC
Posts: 2,820
|
What is he brand/model number of your old unit, and what are you replacing it with?
__________________
Vera & Ken
1998 Holiday Rambler Imperial, RR8S Chassis
Cummins 6C8.3 mechanical engine, 325HP, 3060 Allison
Towing 2014 Ford Explorer
|
|
|
11-12-2019, 04:46 PM
|
#9
|
Senior Member
Official iRV2 Sponsor
Join Date: May 2011
Posts: 8,305
|
Quote:
Originally Posted by veraken
What is he brand/model number of your old unit, and what are you replacing it with?
|
It's an ESCO ES50M-65N and I'm replacing it with the same exact model
__________________
Joel (AKA docj)--
RV Technology Specialist
|
|
|
11-12-2019, 06:10 PM
|
#10
|
Senior Member
Join Date: Oct 2015
Posts: 862
|
Quote:
Originally Posted by docj
It's an ESCO ES50M-65N and I'm replacing it with the same exact model
|
Would love to see pictures, before, after, during. I know what a transfer is but don’t know exactly where it is, what it looks like, and what it takes to replace one.
__________________
2013 Fleetwood Excursion 33A
Cummins ISB 6.7L (ISB 10)/Allison 2100 Transmission
Freightliner XCS chassis
|
|
|
11-13-2019, 05:49 AM
|
#11
|
Junior Member
Join Date: May 2018
Posts: 3
|
I had a five year old transfer switch fail for a different reason. One of the stranded power wires wasn’t caped and the lug screw separated the wires causing arcing. This burned out the switch.
|
|
|
11-13-2019, 08:45 AM
|
#12
|
Senior Member
Official iRV2 Sponsor
Join Date: May 2011
Posts: 8,305
|
Quote:
Originally Posted by ualdriver
Would love to see pictures, before, after, during. I know what a transfer is but don’t know exactly where it is, what it looks like, and what it takes to replace one.
|
This is what the transfer switch looked like prior to my opening it up and disconnecting it. On the left is the Progressive EMS system.
__________________
Joel (AKA docj)--
RV Technology Specialist
|
|
|
11-13-2019, 04:28 PM
|
#13
|
Senior Member
Join Date: Oct 2015
Posts: 862
|
Quote:
Originally Posted by docj
This is what the transfer switch looked like prior to my opening it up and disconnecting it. On the left is the Progressive EMS system.
|
OK that is helpful. I thought the transfer switch was some sort of solenoid inside one of the boxes in my electrical compartment. So if my transfer switch ever fails, you replace the whole box?
__________________
2013 Fleetwood Excursion 33A
Cummins ISB 6.7L (ISB 10)/Allison 2100 Transmission
Freightliner XCS chassis
|
|
|
11-13-2019, 05:53 PM
|
#14
|
Senior Member
Monaco Owners Club
Join Date: Oct 2009
Location: Tucson, AZ
Posts: 6,579
|
Ours is also an Esco ES50-65N. It can get noisy at times.
Esco technician recommended a new LPT50BRD replacement. It's a new design and supposed to be very quiet.
__________________
97 Monaco Windsor- Sold
07 Monaco Executive McKinley- Sold
04 Monaco Signature Chateau IV
|
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|