Ok, sometimes you have to go back to “what was the last thing I did!”.
I bought a new capacitor and put it in and still the fan did not come on. Last fall I had replaced the old Dometic thermostat with a Honeywell Digital thermostat and I thought everything was fine.
Come to find out a couple of things:
1. The furnace DOES NOT require the fan to be wired as the furnace fan runs based upon the temperature of the furnace, not on the setting of the thermostat.
2. In this unit the furnace and the A/C are totally separate and all the thermostat does is enable the furnace or enable the furnace or the A/C, HOWEVER the thermostat does control the fan on the A/C unit independently.
3. I also found out that my old Dometic thermostat is bad and never operated correctly (hence me wiring the A/C fan switch incorrectly!), so when I was testing I was trying to duplicate the way the original Dometic thermostat (so basically I duplicated a broken switch
Does that mean I was successful?
)
4. My first High/Low Fan switch had a broken wire which stopped the fan from running at all!
5. The way the High/Low switch works is that it is a cascading connection, NOT an either or! What that means is in order for the low speed fan setting to work there must be a connection from the FAN terminal to the LOW Speed wire. In order to make the fan work in high speed you must have a connection from the FAN terminal to the LOW speed wire AND to the HIGH speed wire as well.
So bottom line is that my first attempt at a HIGH/LOW fan switch failed but the second one is working great! (And I have a spare capacitor!)