Xantrex (maybe Magnum) Charge Rate setting - question

My Coach has the Xantrex-Trace 2512RV Inverter-Charger with the RC7 remote display.

In the configuration settings there is an option to select the "max charge rate".

What is the purpose of this setting - why would anyone want to choose less than a 100% Charge Rate?
Attached Thumbnails
Click image for larger version

Name:	Xantrex Inverter - Max Charge Rate.jpg
Views:	3
Size:	55.9 KB
ID:	308686  
__________________
Mike ----- 2005 Beaver Patriot Thunder CAT C13 525HP, 42-ft Tag, with HydraLift -----
*SMC-Bvr-Mnco History/Chassis Info https://1drv.ms/f/s!AtvAXw_lfqbToxXYREK9YdBP08Jn
*SMC-Bvr-Mnco Wiring Diagrams https://1drv.ms/f/s!AtvAXw_lfqbTm0WTuuNqpn9a8hCh
CountryB is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 11-20-2020, 01:12 PM   #2
Member
 
Join Date: Sep 2018
Posts: 73
In the rare circumstance that you may wish to reduce the current output because you have a small battery bank and don't want to charge above the recommended rate, OR you wish to impart a slow tricke charge in an attempt to revive dead batteries, OR the 110V power supply is limited and you wish to limit the drain going to the charger.

The latter could also be handled by setting the maximum AC power input.
__________________
Richard Entrekin
99 Newell,Subie Outback toad
Inverness, Fl
RichardE is offline   Reply With Quote
Old 11-20-2020, 01:31 PM   #3
Senior Member
 
CountryB's Avatar
 
Monaco Owners Club
Join Date: Aug 2017
Location: Orlando, Florida
Posts: 5,270
Thanks Richard.
__________________
Mike ----- 2005 Beaver Patriot Thunder CAT C13 525HP, 42-ft Tag, with HydraLift -----
*SMC-Bvr-Mnco History/Chassis Info https://1drv.ms/f/s!AtvAXw_lfqbToxXYREK9YdBP08Jn
*SMC-Bvr-Mnco Wiring Diagrams https://1drv.ms/f/s!AtvAXw_lfqbTm0WTuuNqpn9a8hCh
CountryB is offline   Reply With Quote
Old 11-20-2020, 01:55 PM   #4
Senior Member
 
757driver's Avatar


 
Entegra Owners Club
Join Date: Jun 2004
Location: Cambridge, Ontario
Posts: 4,260
Practical example. Typical motorhome has four 6v GC2 flooded batteries with a total of 440AH capacity. Recommended charge rate for most flooded batteries is between 10-15% of the C rating. A typical inverter/charger has a 100 amp charger. For the above example to be within the recommended charge rate of 44-66 amps need to set the charger to between 50-70% of its total output.
__________________
Don & Gerri
2014 Entegra Anthem 44B
2014 Honda CRV Touring

1300W Solar, 1200AH LiFePO4 FMCA F443497
757driver is offline   Reply With Quote
Old 11-21-2020, 10:24 PM   #5
Senior Member
 
Join Date: Apr 2018
Posts: 1,013
Has to do with how much ac power you have available. If you're on the gennie and running ac's , micro etc.. Or plugged into 30 amp the charger can easily draw enough power to start popping breakers from low voltage .
shootist is offline   Reply With Quote
Old 11-21-2020, 11:37 PM   #6
Senior Member
 
96 Wideglide's Avatar
 
Holiday Rambler Owners Club
Join Date: Aug 2010
Posts: 6,803
Quote:
Originally Posted by 757driver View Post
Practical example. Typical motorhome has four 6v GC2 flooded batteries with a total of 440AH capacity. Recommended charge rate for most flooded batteries is between 10-15% of the C rating. A typical inverter/charger has a 100 amp charger. For the above example to be within the recommended charge rate of 44-66 amps need to set the charger to between 50-70% of its total output.
This ^^

It's adjustable for use on different size battery banks.
I have my 100A Magnum charger set at 60% to charge the 4 6V batteries (460 AH total). If I were to add another pair, I would turn it up to 80%.
__________________
Ben & Sharon
2008 43' Holiday Rambler Scepter PDQ
96 Wideglide is online now   Reply With Quote
Old 11-22-2020, 01:25 AM   #7
Senior Member
 
Join Date: Jul 2014
Posts: 24,660
Quote:
Originally Posted by shootist View Post
Has to do with how much ac power you have available. If you're on the gennie and running ac's , micro etc.. Or plugged into 30 amp the charger can easily draw enough power to start popping breakers from low voltage .
It's the " Shore Max " setting, that you change when on limited shore or generator power, to prevent breaker tripping.

Charge rate is a configuration setting depending on battery bank size, while Shore Max is a temporary setting.
twinboat is online now   Reply With Quote
Old 11-22-2020, 07:17 AM   #8
Senior Member
 
CountryB's Avatar
 
Monaco Owners Club
Join Date: Aug 2017
Location: Orlando, Florida
Posts: 5,270
My Xantrex has a setting for "Battery Capacity in Ah" that sets the length of Time for absorption charging before it switches to Float mode.
According to the manual, in Auto, it charges in this mode for 1.8 hrs. If set to 500Ah this charge time would be 2.5 hrs. I left the setting in Auto. My House batteries are 450 Ah (four 225Ah GC2).

Then there is the "Max Charge Rate" setting that I'm asking about here.

And there is a setting for "Shore Power" - which I have set to 20A since I'm plugged into a 20A outlet while in storage.


Thanks for your help understanding this.
Attached Thumbnails
Click image for larger version

Name:	Xantrex 2512RV setup choices.jpg
Views:	3
Size:	101.2 KB
ID:	308898  
__________________
Mike ----- 2005 Beaver Patriot Thunder CAT C13 525HP, 42-ft Tag, with HydraLift -----
*SMC-Bvr-Mnco History/Chassis Info https://1drv.ms/f/s!AtvAXw_lfqbToxXYREK9YdBP08Jn
*SMC-Bvr-Mnco Wiring Diagrams https://1drv.ms/f/s!AtvAXw_lfqbTm0WTuuNqpn9a8hCh
CountryB is offline   Reply With Quote
Old 11-22-2020, 07:28 AM   #9
Senior Member
 
CountryB's Avatar
 
Monaco Owners Club
Join Date: Aug 2017
Location: Orlando, Florida
Posts: 5,270
Quote:
Originally Posted by 757driver View Post
Practical example. Typical motorhome has four 6v GC2 flooded batteries with a total of 440AH capacity. Recommended charge rate for most flooded batteries is between 10-15% of the C rating. A typical inverter/charger has a 100 amp charger. For the above example to be within the recommended charge rate of 44-66 amps need to set the charger to between 50-70% of its total output.
The specs on my Xantrex 2512RV unit says the maximum charge rate is 120A.

My batteries are four deep cycle GC2 (225Ah each) - so 450Ah for the House bank. And for the Chassis batteries there are two Group 31 (950CCA). At some point (when the House batteries are fully charged) the "Big Boy - BIRD" setup will combine the House and Chassis to keep both sets charged.

What should the Max Charge rate be on my setup? 50% (which would be 60A charge rate)? I left it in default mode for now.

The shore Power setting drops the charging amperage - so I think the Shore Power setting overrides the Max Charge rate setting (i.e. In Shore Power 20A, the charge amperage is limited to 20A), but when plugged into 50A Shore Power (with the Shore Power setting at "30A or More" - then the Max Charge Rate setting is used. Does this sound correct?
__________________
Mike ----- 2005 Beaver Patriot Thunder CAT C13 525HP, 42-ft Tag, with HydraLift -----
*SMC-Bvr-Mnco History/Chassis Info https://1drv.ms/f/s!AtvAXw_lfqbToxXYREK9YdBP08Jn
*SMC-Bvr-Mnco Wiring Diagrams https://1drv.ms/f/s!AtvAXw_lfqbTm0WTuuNqpn9a8hCh
CountryB is offline   Reply With Quote
Old 11-22-2020, 02:39 PM   #10
Senior Member
 
757driver's Avatar


 
Entegra Owners Club
Join Date: Jun 2004
Location: Cambridge, Ontario
Posts: 4,260
Quote:
Originally Posted by CountryB View Post
The specs on my Xantrex 2512RV unit says the maximum charge rate is 120A.

My batteries are four deep cycle GC2 (225Ah each) - so 450Ah for the House bank. And for the Chassis batteries there are two Group 31 (950CCA). At some point (when the House batteries are fully charged) the "Big Boy - BIRD" setup will combine the House and Chassis to keep both sets charged.

What should the Max Charge rate be on my setup? 50% (which would be 60A charge rate)? I left it in default mode for now.

The shore Power setting drops the charging amperage - so I think the Shore Power setting overrides the Max Charge rate setting (i.e. In Shore Power 20A, the charge amperage is limited to 20A), but when plugged into 50A Shore Power (with the Shore Power setting at "30A or More" - then the Max Charge Rate setting is used. Does this sound correct?
Yes, I would set the max. charge rate to 50% (assuming you have flooded batteries). It will be better for the batteries in the long run and you will get less off gassing and less corrosion around your battery posts and battery compartment.

If your charge amps is indeed limited to 20A when shore power is dialed back to 20A keep in mind that this is 20A AC power which is roughly 180 amps of DC charge (something your charger is not capable of). If you are seeing a reduction in your charge amps while on 20A shore power it could be one of two things either your batteries are getting full and the amps are reducing or other AC loads are being run and it is reducing what the charger gets to stay within the 20A shore power setting.
__________________
Don & Gerri
2014 Entegra Anthem 44B
2014 Honda CRV Touring

1300W Solar, 1200AH LiFePO4 FMCA F443497
757driver is offline   Reply With Quote
Old 11-22-2020, 02:42 PM   #11
Senior Member
 
757driver's Avatar


 
Entegra Owners Club
Join Date: Jun 2004
Location: Cambridge, Ontario
Posts: 4,260
I see in your previous post that you circled AGM batteries. Do you have AGM batteries? If so what brand are they? You may be able to have a slightly higher charge rate setting.
__________________
Don & Gerri
2014 Entegra Anthem 44B
2014 Honda CRV Touring

1300W Solar, 1200AH LiFePO4 FMCA F443497
757driver is offline   Reply With Quote
Old 11-22-2020, 04:00 PM   #12
Senior Member
 
CountryB's Avatar
 
Monaco Owners Club
Join Date: Aug 2017
Location: Orlando, Florida
Posts: 5,270
I have new AGM batteries. Just installed last week.
They are made by Crown Batteries. 220Ah @ 20Hr. "GC2 6V Deep Cycle Sealed".

Thanks for your reply. I'm just looking for the best charge rate - whatever will provide the best battery longevity.

These batteries are expensive. I want them to last.

https://www.crownbattery.com/hubfs/D...Deep-Cycle.pdf
__________________
Mike ----- 2005 Beaver Patriot Thunder CAT C13 525HP, 42-ft Tag, with HydraLift -----
*SMC-Bvr-Mnco History/Chassis Info https://1drv.ms/f/s!AtvAXw_lfqbToxXYREK9YdBP08Jn
*SMC-Bvr-Mnco Wiring Diagrams https://1drv.ms/f/s!AtvAXw_lfqbTm0WTuuNqpn9a8hCh
CountryB is offline   Reply With Quote
Old 11-22-2020, 09:16 PM   #13
Senior Member
 
757driver's Avatar


 
Entegra Owners Club
Join Date: Jun 2004
Location: Cambridge, Ontario
Posts: 4,260
Quote:
Originally Posted by CountryB View Post
I have new AGM batteries. Just installed last week.
They are made by Crown Batteries. 220Ah @ 20Hr. "GC2 6V Deep Cycle Sealed".

Thanks for your reply. I'm just looking for the best charge rate - whatever will provide the best battery longevity.

These batteries are expensive. I want them to last.

https://www.crownbattery.com/hubfs/D...Deep-Cycle.pdf
Crown recommends 10% of the C rating up to a maximum of 25% of C. I would set it at 50-60% charge rate. For battery capacity I would set it to 500 amp (just slightly over what you have) which will give a 2.5 hour Absorb phase. Battery type set to AGM will give the closest to what Crown recommends for Bulk/Absorb/Float.
__________________
Don & Gerri
2014 Entegra Anthem 44B
2014 Honda CRV Touring

1300W Solar, 1200AH LiFePO4 FMCA F443497
757driver is offline   Reply With Quote
Reply

Tags
xantrex



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
ME-ARC "Max Charge Amps" vs "Max Charge Rate" tankcj RV Systems & Appliances 2 01-21-2020 11:27 AM
Charge rate setting on Magnum Energy system Dean n Mike Fleetwood Owner's Forum 11 05-07-2018 12:34 PM
Sumo springs----maybe, maybe not MoCoTom Workhorse and Chevrolet Chassis Motorhome Forum 25 01-28-2018 09:31 PM
Magnum Inverter "Final Charge" Setting 757driver Entegra Owner's Forum 19 11-01-2016 08:48 PM
Battery charge rate & absorb charge time loisjop Entegra Owner's Forum 0 11-01-2014 02:15 PM


All times are GMT -6. The time now is 11:46 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2020, vBulletin Solutions, Inc.