#2 air conditioner

I’m still having problems with my number 2 air conditioner. I checked the balesters and they aren’t burnt as some have suggested. Today I called the Coleman service center and he suggested putting a jumper across the “freeze” line. No joy

No oil residues at all and the unit looks clean. The compressor cycles every 40 seconds for about 2 seconds. When it does I can feel coolness on the coils. Unfortunately I’m not much of an a/c mechanic. And the Coleman service center seemed a bit annoid since I’m not a technician. Any ideas what to check next?
__________________
2023 Ram 3500 H.O.
2020 DRV
2015 Entegra Aspire RBQ SOLD
dave&ginny is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-29-2018, 05:41 AM   #2
Registered User
 
Join Date: May 2017
Posts: 2,582
Sure sounds like the start capacitor. Sometimes you can tell if they're bad by looking at them, sometimes not. I would replace it.
Rollin101 is offline   Reply With Quote
Old 06-29-2018, 05:54 AM   #3
Senior Member
 
brobox's Avatar
 
Entegra Owners Club
Join Date: Apr 2007
Location: SW FL
Posts: 31,717
Dave, it sounds like it is a bad run capacitor? They are easy to change less and than $10. at a supply house If you do get one go to an A/C supply house in town, not an RV parts store, which would probably have to order it anyhow. Also an A/C supply house can give you excellent trouble shooting advice. These are pretty simple units. If you replace one, I would replace both the start and the run capacitors at the same time, they are located next to each other. IIRC, the capacitors are inside of a black box on the Mach 8.
__________________
Chuck in SW FL
Digital 2021 Cornerstone "B"
A "Digital" 2019 Cornerstone "B" Traded
A "Classic" 2014 Anthem 42 RBQ---Sold
brobox is offline   Reply With Quote
Old 06-29-2018, 10:36 AM   #4
Senior Member
 
dave&ginny's Avatar
 
Join Date: Feb 2012
Location: Peoria IL
Posts: 2,085
Thanks guys I’ll try that as well. I just got off the phone again with the service people and they suggested to pull the white wire off the high pressure limit switch. I’ll try that tonight when I get home and if that doesn’t work I’ll get the capacitors
__________________
2023 Ram 3500 H.O.
2020 DRV
2015 Entegra Aspire RBQ SOLD
dave&ginny is offline   Reply With Quote
Old 06-29-2018, 10:56 AM   #5
Senior Member
 
gswindle's Avatar


 
Entegra Owners Club
Join Date: Apr 2018
Location: Larue, Texas
Posts: 192
I pulled the white wire going to the pressure switch on my unit and it has worked great every since. It was only blowing air. it started working immediately. You need to make sure you turn off the breaker before you do it.



Gary
__________________
Gary & Linda
2019 Entegra Anthem 44F
2016 Tiffin Phaeton 40 QBH (Traded)
2017 Chevrolet Tahoe, M&G Braking, Blue Ox Avail
gswindle is offline   Reply With Quote
Old 06-30-2018, 06:25 AM   #6
Senior Member
 
mymyst's Avatar
 
Entegra Owners Club
Join Date: Jun 2013
Location: Central Florida
Posts: 574
if you have and know how to use a multimeter, it is easy to test the capacitors. Once power is turned off, remove the leads from the subject capacitor. Discharge the capacitor by applying a screw driver acorss the capacitor terminals. Set your multimeter for checking conitnuity. Apple meter leads across the capacitor terminals. If the capacitor is good, you should see a positive needle (or immediate positive continuity indication, if meter is digital) movement on the meter, followed by an immediate drop to zero. If needle doesn't move, or goes positive and stays there, the capacitor is bad. If bad, they are cheap at an ac supply house.
Sounds like a bad run capacitor from your description. Also, if a defective high pressure switch is found to be the culprit such as in prevpost, it should really be replaced with new, or if it is tripping aaaaand not defective, look for the cause, ie; dirty condenser coil, or possibly smashed condenser fins. Good luck!!
__________________
Ernie and Dianna Northern
2015 Entegra Anthem 44 DLQ2017 Entegra Cornerstone 45B
2013 Equinox toad/
2014 Jeep GC diesel - 2024 Renegade Verona 36VSB
mymyst is offline   Reply With Quote
Old 06-30-2018, 06:48 PM   #7
Senior Member
 
dave&ginny's Avatar
 
Join Date: Feb 2012
Location: Peoria IL
Posts: 2,085
I crawled up on the roof last night in 96 degree temps and pulled the white wire off and it didn't help. Today I called Camping World in Davenport Iowa and they had 2 start capacitors in stock so off we went for a 1.5 hour drive and picked them up. I figured if one a/c unit went down because of the capacitor the others might as well, and I like to carry spare parts.

So in the blistering heat, up the ladder I went. I believe I broke a sweat as I left the inside of the RV. I changed out the capacitor and .....No luck.

I think I've tried about everything a shade tree mechanic can do. After our trip to the A.I.M. rally, I'll get it into the shop. I really don't need the 2nd a/c unit because our coach maintains 68 degrees with just 2 but if one of those go out on this trip I might be a bit upset.

I was told a new unit will cost about $950 and I might just buy a new one and save this one for parts.
__________________
2023 Ram 3500 H.O.
2020 DRV
2015 Entegra Aspire RBQ SOLD
dave&ginny is offline   Reply With Quote
Old 06-30-2018, 07:20 PM   #8
Senior Member
 
LWBAZ's Avatar


 
Join Date: Aug 2016
Location: Scottsdale, AZ
Posts: 3,122
Quote:
Originally Posted by brobox View Post
Dave, it sounds like it is a bad run capacitor? They are easy to change less and than $10. at a supply house If you do get one go to an A/C supply house in town, not an RV parts store, which would probably have to order it anyhow. Also an A/C supply house can give you excellent trouble shooting advice. These are pretty simple units. If you replace one, I would replace both the start and the run capacitors at the same time, they are located next to each other. IIRC, the capacitors are inside of a black box on the Mach 8.
Dave, my reading of Chuck's post quoted above suggests there are two capacitors per AC unit.

Did you replace both of them or just one?
__________________
Larry & Amy Beckner
Scottsdale, AZ
2022 Newmar Super Star 4061
LWBAZ is offline   Reply With Quote
Old 07-01-2018, 06:31 AM   #9
Senior Member
 
brobox's Avatar
 
Entegra Owners Club
Join Date: Apr 2007
Location: SW FL
Posts: 31,717
Dave, there is also a difference in the start and run capacitors. You mentioned yours started, but quit in a few seconds.....run capacitor suspicion.

mymyst is correct about testing the capacitors for continuity. Lot's of photo post on the internet of how to's. Let us know what you find.
Check for an AC supply house closer than CW and explain what you have done, the counter guys at those places are sharp, they deal with those problems everyday, most use to be AC techs. The guys at CW were selling tents yesterday.

It was explained to me once that an RV A/C is nothing more than a window A/C unit made to mount on the roof.
__________________
Chuck in SW FL
Digital 2021 Cornerstone "B"
A "Digital" 2019 Cornerstone "B" Traded
A "Classic" 2014 Anthem 42 RBQ---Sold
brobox is offline   Reply With Quote
Old 07-01-2018, 06:42 AM   #10
Senior Member
 
dave&ginny's Avatar
 
Join Date: Feb 2012
Location: Peoria IL
Posts: 2,085
Quote:
Originally Posted by LWBAZ View Post
Dave, my reading of Chuck's post quoted above suggests there are two capacitors per AC unit.

Did you replace both of them or just one?
You’re right there are 2 capacitors. One is for the fan which is working great and the other is for the compressor.
__________________
2023 Ram 3500 H.O.
2020 DRV
2015 Entegra Aspire RBQ SOLD
dave&ginny is offline   Reply With Quote
Old 07-01-2018, 06:44 AM   #11
Senior Member
 
dave&ginny's Avatar
 
Join Date: Feb 2012
Location: Peoria IL
Posts: 2,085
Quote:
Originally Posted by brobox View Post
Dave, there is also a difference in the start and run capacitors. You mentioned yours started, but quit in a few seconds.....run capacitor suspicion.

mymyst is correct about testing the capacitors for continuity. Lot's of photo post on the internet of how to's. Let us know what you find.
Check for an AC supply house closer than CW and explain what you have done, the counter guys at those places are sharp, they deal with those problems everyday, most use to be AC techs. The guys at CW were selling tents yesterday.

It was explained to me once that an RV A/C is nothing more than a window A/C unit made to mount on the roof.
I gree about CW! I’ll call one of those shops and see what they say. The schematic shows both capacitors, with one for the fan and the other for the compressor. Since the fans start right up I don’t see how the second capacitor can be the problem.

When I spoke with one of the techs he said either a stuck compressor, circuit board issue or a bad thermostat
__________________
2023 Ram 3500 H.O.
2020 DRV
2015 Entegra Aspire RBQ SOLD
dave&ginny is offline   Reply With Quote
Old 07-01-2018, 07:06 AM   #12
Senior Member
 
brobox's Avatar
 
Entegra Owners Club
Join Date: Apr 2007
Location: SW FL
Posts: 31,717
Quote:
Originally Posted by dave&ginny View Post
When I spoke with one of the techs he said either a stuck compressor, circuit board issue or a bad thermostat
When one of my AC's went out in SD, closest one was in Denver, I found how to test all of those units on the internet. When I got up on the roof to run the test, found the front of the unit was soaked with Freon. Had to go to Denver for the new unit
__________________
Chuck in SW FL
Digital 2021 Cornerstone "B"
A "Digital" 2019 Cornerstone "B" Traded
A "Classic" 2014 Anthem 42 RBQ---Sold
brobox is offline   Reply With Quote
Reply

Tags
air, air conditioner



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
What is correct direction of air flow on air conditioner Biggee RV Systems & Appliances 10 08-21-2013 07:44 PM
Basement air conditioner air flow azloafer Winnebago Industries Owner's Forum 63 09-07-2010 05:57 PM
Cold Air from Dash Air Conditioner ??? Barrow Bay Monaco Owner's Forum 11 06-10-2010 08:32 AM
Manual for True Air Air Conditioner? #2 Compressor Inop? FlyingW Winnebago Industries Owner's Forum 32 09-05-2007 09:05 AM
Loss of Air - Basement Air Conditioner Ducts j griff Winnebago Industries Owner's Forum 8 07-14-2007 09:18 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 02:24 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.