2 Circuit Breakers trip every power is transferred

I'll preface this post by saying I'm as dumb as the day is long when talking about electricity (my wife says that applies whenever I talk...). Anyway, 2 CBs under the bed in my 2019 Reatta trip off every I transfer power from shore to coach or generator to shore. One is to the kitchen, the other to LR and bathroom. They both trip at the same time. I reset them and everything works fine until the next power transfer. Entegra sent me a schematic and nothing downstream of the breakers are in use when they trip. NIRVC in Lewisville, TX said they could not duplicate the problem (interesting because when I picked my coach up, the breakers were tripped). Any ideas on what could cause this? I've read other threads about loose wires, etc., but to me it seems odd that 2 independent circuits always trip at the same time and not when I am actually using one of the outlets on one of the circuits. They always trip when power is switched. It seems to me the problem would be upstream, not downstream. Any advice is appreciated. Attached is a pic of the underbed CBs.
Attached Thumbnails
Click image for larger version

Name:	CBs.jpg
Views:	14
Size:	85.7 KB
ID:	332112  
__________________
Hank, Kristin & Harley (Golden Retriever)
Dallas, TX
'19 Reatta
fallmeadow is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-14-2021, 10:56 AM   #2
Senior Member
 
Join Date: Oct 2014
Posts: 2,935
From your picture, both those breakers appear to be not just breakers, but GFI breakers.


Is the GFI part tripping.
__________________
Brett Wolfe
Ex: 2003 Alpine 38FDDS. Ex: 1997 Safari Sahara. Ex: 1993 Foretravel U240
wolfe10 is online now   Reply With Quote
Old 06-14-2021, 12:12 PM   #3
Senior Member
 
LWBAZ's Avatar


 
Join Date: Aug 2016
Location: Scottsdale, AZ
Posts: 2,096
In our 2018 Cornerstone we have one breaker that does that from time to time - tripping when we connect to shore power. And like you, we can reset the breaker and all is well until then next time it decides to trip.

I suspect the solution is to replace the breaker, but in our case it doesn't happen often enough to motivate me to do the replacement. In your case, I would replace the two offending breakers (yourself or have an electrician do it for you) and see if that solves the problem. My guess is that it will, but if not you'll have a couple of spare breakers.
__________________
Larry & Amy Beckner
Scottsdale, AZ
2018 Entegra Cornerstone 45B
LWBAZ is online now   Reply With Quote
Old 06-14-2021, 12:29 PM   #4
Senior Member
 
J Birder's Avatar
 
Join Date: Feb 2012
Location: Lake County, IL
Posts: 1,509
The fact that the only GFCI/breakers are those that trip, suggest that at some point while the power is being transferred, the ground and neutral may briefly be getting connected. Try monitoring the ground - neutral voltage while having somebody do the transfer. That voltage is usually only a few volts, but if it suddenly drops to zero, then that is the problem.

Note that the sudden voltage drop will be only a very short duration. It will be easier to detect with an analog meter.

Joel
__________________
Retired electronics engineer. Avid paddler & birder.
2011 Silverado 2500HD, diesel, 4x4,crew cab, 8' bed
Palomino Puma 253FBS (27' 5er) & '94 19' Class B
J Birder is online now   Reply With Quote
Old 06-14-2021, 01:05 PM   #5
Junior Member
 
Entegra Owners Club
Join Date: Jul 2020
Location: Dallas
Posts: 23
No. Just the breakers.
__________________
Hank, Kristin & Harley (Golden Retriever)
Dallas, TX
'19 Reatta
fallmeadow is offline   Reply With Quote
Old 06-14-2021, 02:40 PM   #6
Senior Member
 
J Birder's Avatar
 
Join Date: Feb 2012
Location: Lake County, IL
Posts: 1,509
Quote:
Originally Posted by fallmeadow View Post
No. Just the breakers.
I don't understand what you're saying.


The 2nrx and 3rd breakers from the top are combination circuit breaker and ground fault circuit interrupter.


Joel
__________________
Retired electronics engineer. Avid paddler & birder.
2011 Silverado 2500HD, diesel, 4x4,crew cab, 8' bed
Palomino Puma 253FBS (27' 5er) & '94 19' Class B
J Birder is online now   Reply With Quote
Old 06-14-2021, 03:23 PM   #7
Senior Member
 
andy29847's Avatar
 
Join Date: Oct 2013
Posts: 843
I'm betting you have a loose connection on the neutral buss in the panel. All the grounds and neutrals should be checked to see if they are tight. You can do this safely if you disconnect form all power including the batteries before opening the panels.
__________________
2001 Alpine Coach 38/8
ACA 2018006
Andy
andy29847 is offline   Reply With Quote
Old 06-14-2021, 03:38 PM   #8
Senior Member
 
Jayco Owners Club
Join Date: May 2016
Location: North Texas
Posts: 360
What is happening (most likely) is that the RV power (generator or inverter) has a neutral to ground bond (as it should) and when transferring power there is a moment that the GFCI senses the change in the transfer switch in particular with the neutral connection being bonded (when on shore power the neutral to ground bond is not bonded in the RV but on inverter or generator it is). Some inverter companies have written tech notes on this happening (basically explaining it without any resolution). One thing you could try is to disconnect from the shore power completely and then turn on the inverter or generator and see if they still trip (don't have the inverter or generator on when disconnecting from shore power). If that works then you have a choice of disconnecting power first and then turning on the inverter or generator, or resetting the gfci breakers everytime this occurs. There isn't a lot you can do about this, although some gfci breakers are more sensitive to this happening, you could try another brand breaker that is compatible with your panel or even a different transfer switch, although even with doing that the problem certainly could continue. ~CA

BTW, I suspect this has always occurred and not a recent change?
__________________
2010 Jayco GreyHawk 31SS
craigav is online now   Reply With Quote
Old 06-14-2021, 05:08 PM   #9
Senior Member
 
Join Date: Jan 2018
Posts: 1,026
Mine did just that!
When connecting or disconnecting shore power...

It started where I'd have to reset all the clocks that plugged into anything on the inverter panel.

Then the 2 gfi breakers would pop and I'd reset them.

Then they would not reset, popped immediately.

Then one day I got a DC overload lite on the magnum panel.

I removed the inverter and took it apart, the MOSFET board had let the magic smoke out!

The good news is Magnum's warranty wins at 5 years, and they agreed to cross ship a warranty replacement inverter.

Sent from my moto z3 using iRV2 - RV Forum mobile app
__________________
Jim and Carol, plus furrballs Riley, Nikko, and Kobi

2017 Entegra Aspire, 2008 Monaco Knight, 2000 Fleetwood Pace Arrow
oneknight is offline   Reply With Quote
Old 06-14-2021, 05:36 PM   #10
Senior Member
 
hdgoldie's Avatar


 
Entegra Owners Club
Join Date: Apr 2012
Location: South Gulf Cove, FL
Posts: 1,514
Iím just as dumb about anything electrical so this probably will not help, but we were always told to make sure we did the shore/generator or generator/shore transfer with as little load as possible. Weíve always turned off the A/C and the generator before plugging into shore power and reversed the process when going back to generator. The only time we do not follow that procedure is when we are using the gen auto set. We havenít had any issues with the transfer on the rare occasions when the shore power has gone out and the generator kicks in and never when using the auto set when boondocking for a night. Do you still throw the circuit breakers if you are using the gen auto start or is it only when you are going from shore to gen or back?
__________________
Goldie & Rick
2019 Entegra Aspire 44B, 2014 G/C Summit
Dixie & Scruffy (furkids)
hdgoldie is offline   Reply With Quote
Old 06-14-2021, 06:41 PM   #11
Senior Member
 
Gary.Jones's Avatar


 
Join Date: Oct 2012
Location: Louisiana
Posts: 8,994
Blog Entries: 1
A Ground Fault Interrupter Circuit breaker (GFCI) is designed to minimize the chances that there may be an accidental potential difference (voltage) between earth ground and the ground/neutral of your electrical system and appliances which could produce electrocution or shock to users of the appliances or some appliance plugged into a power circuit. This is particularly critical on kitchen and bathroom circuits, A GCFI senses any potential difference (Voltage) that exists between the two "grounds" and the GFCI "trips" to prevent shock or electrocution.

I believe that J Birder and others are exactly correct. You have a failed ground or neutral in your buss wiring. Now the problem is to find out where that failed ground/neutral is located.

Gary
__________________
Gary and Dee, Zowie and Bowie (traveling cat sibs)
2019 Cornerstone 45B, X15-605hp, Imperial, Spartan K3,
2013 Honda CR-V toad, Demco Excali-Bar II,
Demco Baseplate, Demco Toad Light system, 73 de W5FI
Gary.Jones is offline   Reply With Quote
Old 06-15-2021, 05:31 AM   #12
Senior Member
 
Butte64's Avatar
 
Entegra Owners Club
Spartan Chassis
Join Date: Jul 2012
Location: Mount Olive Shores North, FL
Posts: 2,291
Quote:
Originally Posted by fallmeadow View Post
I'll preface this post by saying I'm as dumb as the day is long when talking about electricity (my wife says that applies whenever I talk...). Anyway, 2 CBs under the bed in my 2019 Reatta trip off every I transfer power from shore to coach or generator to shore. One is to the kitchen, the other to LR and bathroom. They both trip at the same time. I reset them and everything works fine until the next power transfer. Entegra sent me a schematic and nothing downstream of the breakers are in use when they trip. NIRVC in Lewisville, TX said they could not duplicate the problem (interesting because when I picked my coach up, the breakers were tripped). Any ideas on what could cause this? I've read other threads about loose wires, etc., but to me it seems odd that 2 independent circuits always trip at the same time and not when I am actually using one of the outlets on one of the circuits. They always trip when power is switched. It seems to me the problem would be upstream, not downstream. Any advice is appreciated. Attached is a pic of the underbed CBs.


From your description it sounds like you are switching between generator and shore while generator is running. Yes, the transfer switch is supposed to handle that but it does put more stress on the system. Have you tried turning off everything that is not on inverter, shutting down generator, then connect shore power? Then do in reverse going from shore to generator.
__________________
Jerry - 2021 Entegra Anthem 44F
2017 Grand Cherokee
sold 2018 Entegra Aspire 42DEQ Sweet Victory
Butte64 is online now   Reply With Quote
Old 06-15-2021, 06:43 AM   #13
Senior Member
 
brobox's Avatar
 
Entegra Owners Club
Join Date: Apr 2007
Location: SW FL
Posts: 25,478
Quote:
Originally Posted by Butte64 View Post
From your description it sounds like you are switching between generator and shore while generator is running. Yes, the transfer switch is supposed to handle that but it does put more stress on the system. Have you tried turning off everything that is not on inverter, shutting down generator, then connect shore power? Then do in reverse going from shore to generator.
X2 and as hdgoldie said. There is a lot of voltage when switching power if both gen and shore power are on at the same time. Very taxing on our small RV switching stations. Next would be to check the connections in the circuit panel.
__________________
Chuck in SW FL
Digital 2021 Cornerstone "B"
A "Digital" 2019 Cornerstone "B" Traded
A "Classic" 2014 Anthem 42 RBQ---Sold
brobox is online now   Reply With Quote
Old 06-15-2021, 11:14 AM   #14
Senior Member
 
Mwoodofd's Avatar


 
Entegra Owners Club
Join Date: Apr 2013
Location: Las Colinas, Texas
Posts: 1,557
No expert on electricity either, but when we built our house, electrical contractor put some of those breakers with the GFCI on them for some circuits in the main breaker box.. One of these controlled our kitchen plugs above the counters we use for coffee makers etc, and we kept tripping the breaker in the box in the garage. These plugs in the kitchen also had the built in GFCI controls on them too. Electrician said there should not be 2 on one circuit. Removed and replaced the breakers from the main breaker box in the garage with non GFCI, problem solved. I would see if any of the other GFCI plugs in your rig don't work when the breaker box trips and see if a circuit has 2 on them. (If that makes sense)
__________________
Mark & Debra Wood, Las Colinas, TX.
2013 Entegra Aspire 42RBQ
2014 Jeep Wrangler Sahara
Mwoodofd is offline   Reply With Quote
Reply

Tags
power, circuit breaker, breaker



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Power Components circuit breakers hepkess RV Systems & Appliances 3 01-25-2021 05:09 PM
Circuit breakers trip Daryl molly Newmar Owner's Forum 4 07-26-2020 06:42 PM
Roof A/C Circuit Breakers Trip During Travel rdpricejr Tiffin Owner's Forum 4 07-24-2020 08:32 AM
Why DO our AC units trip circuit breakers ?? Gary.Jones Entegra Owner's Forum 38 08-29-2016 10:14 AM
110 electric power...15 amp circuit breakers Cocoa Loco RV Systems & Appliances 4 01-03-2007 05:48 AM


All times are GMT -6. The time now is 11:11 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2021, vBulletin Solutions, Inc.