Aqua Hot Shuts Off

I continue to have issues with our Aqua Hot. It has been to certified Aqua Hot Dealer twice but we still have a problem. It has had two circuit boards replaced. The latest issue is it will fire and run for about 45 minutes and then the green light on the burner switch turns off and it shuts down. If I cycle the switch it will run again but about every 30 to 45 minutes will shut down. Fuel level is fine. No red lights on panel. Fluid level is good. Frustrated with our unit. Thanks in advance for any suggestions.
__________________
Chad and Nanci
2014 Entegra Anthem 44SL
Chad K is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 02-04-2018, 03:29 PM   #2
Senior Member
 
Join Date: Jan 2015
Location: Prescott, Arizona
Posts: 3,564
Blog Entries: 6
Professional Help is Free w/ Roger Berke. Hydro-/Aqua- Hot
Roger Berke: RV Hydronic Heater Repair - Home (RV Hydronic Heater Repair - Home)
__________________
'04 Newmar MADP, 1100w of solar, Rubicon toad
ByeTheWay is offline   Reply With Quote
Old 02-04-2018, 03:53 PM   #3
Senior Member
 
brobox's Avatar
 
Entegra Owners Club
Join Date: Apr 2007
Location: SW FL
Posts: 31,735
Have you called Aqua Hot and run through the troubleshooting over the phone? They are good at troubleshooting problems with their units.
__________________
Chuck in SW FL
Digital 2021 Cornerstone "B"
A "Digital" 2019 Cornerstone "B" Traded
A "Classic" 2014 Anthem 42 RBQ---Sold
brobox is offline   Reply With Quote
Old 02-04-2018, 04:26 PM   #4
Member
 
Chad K's Avatar
 
Join Date: Nov 2012
Location: Kansas
Posts: 72
Will call Aqua Hot tomorrow and hope to get some direction. Thanks
__________________
Chad and Nanci
2014 Entegra Anthem 44SL
Chad K is offline   Reply With Quote
Old 02-04-2018, 04:37 PM   #5
Senior Member
 
saddlesore's Avatar


 
Foretravel Owners Club
Join Date: Apr 2016
Location: Home is Where WE PARK IT...
Posts: 6,058
Sounds like the coil is going kaputski....
Ours does that, fails to re-fire, light goes out on rocker switch,flip off and back on and it fires off again..Looking for a qualified AH mobile service as we speak
__________________
Retired truckdriver,
'02 Foretravel... "This Shack will do"
being pushed by an '06 Scion xB
SKP's of Box Elder, South Dakota
saddlesore is online now   Reply With Quote
Old 02-05-2018, 06:16 AM   #6
Senior Member
 
Join Date: Jan 2016
Location: Montgomery, TX (Home Sweet Home)
Posts: 2,501
Chad, when is the last time you had a routine service? The reason I ask is the symptom you describe is “lockout”. Basically, the unit needs a fuel filter, burner scrub, and fuel nozzle.

This job isn’t hard, it takes (2) fuel line clamp pliers, and a few small hand tools, and the parts. You can get the fuel filter at NAPA and you will need a nozzle and burner gasket.

The big caution is to not overtorque the 2 ear bolts holding the burner in place. The ears the bolts attach to can be pretty easily broken.

The Aquahot owners manual has a very good Go-By for this service.

-Matt

P.S. Aquahot says do the routine service every year. We got 10 months out our new unit. My personal interval is now 6 months.
__________________
Currently Motorhomeless
2017 Entegra Aspire 44R (bunks) towing 2019 F-350 LB (Sold)
2012 Tiffin Phaeton 40QKH (Our Phaeton was so nice, we bought it twice)
2016 Open Range RF376FBH (Sold)
Matt D is offline   Reply With Quote
Old 02-05-2018, 06:26 AM   #7
Senior Member
 
Newmar Owners Club
Spartan Chassis
Join Date: Nov 2012
Posts: 221
AquaHot Shuts Off

Quote:
Originally Posted by Chad K View Post
I continue to have issues with our Aqua Hot. It has been to certified Aqua Hot Dealer twice but we still have a problem. It has had two circuit boards replaced. The latest issue is it will fire and run for about 45 minutes and then the green light on the burner switch turns off and it shuts down. If I cycle the switch it will run again but about every 30 to 45 minutes will shut down. Fuel level is fine. No red lights on panel. Fluid level is good. Frustrated with our unit. Thanks in advance for any suggestions.
I hope this may be helpful. I had the same symptoms on my AquaHot, and was very frustrating. Cutting to the chase, the ignition electrodes were too close to the swirler. So, after the first cycle, I would get no ignition the second time. The swirler does move a little when you reinstall the burner, until everything is tightened up. That movement was enough to shift the swirler too close to the electrodes. You could actually see two marks on the swirler. Check the swirler for marks, check everything with the gapping tool.
Car1 is offline   Reply With Quote
Old 02-05-2018, 06:27 AM   #8
Member
 
Chad K's Avatar
 
Join Date: Nov 2012
Location: Kansas
Posts: 72
It was serviced Feb 2017 so one year ago. May not matter but very few hours on the AH since then. I will service it. Thanks Matt.
__________________
Chad and Nanci
2014 Entegra Anthem 44SL
Chad K is offline   Reply With Quote
Old 02-05-2018, 09:35 AM   #9
Senior Member
 
DoggieDaddy's Avatar
 
Join Date: Jul 2013
Location: Where ever we park it
Posts: 1,295
Ours is doing the same but only once a week or so at night when it's working hard to heat. We had the unit serviced at the end of November and a blower motor replaced in January. it's always something with this piece of junk. It is the weakest part of this coach. I wished there was a more reliable product to replace it with.

I'll be very interested in whatever the resolution is for this issue.
__________________
Robert & Holly - "Fulltimers" 8+ years
Schnauzers Augie Doggie and Monty Puppy
2014 Anthem 44B Rad Copper ----- SOLD
DoggieDaddy is offline   Reply With Quote
Old 02-05-2018, 11:20 AM   #10
Senior Member
 
pointrow's Avatar
 
Join Date: Dec 2014
Location: Cen Il.
Posts: 710
there are 1 or 2 thermostats on your unit located toward the top of the tank.
You should find a small white reset button. Reset them with a pencil and see if unit comes to life.
If so they are probably faulty. When the unit runs several cycles the heat builds and trips them. Replacing isn’t hard just requires draining off some of the boiler fluid.
If you have 2 you can unhook the bad one and run on one. The older units only have one to begin with.

Good luck
Pointrow
__________________
2014 Fleetwood Providence 42p
pointrow is offline   Reply With Quote
Old 02-05-2018, 11:25 AM   #11
Senior Member
 
pointrow's Avatar
 
Join Date: Dec 2014
Location: Cen Il.
Posts: 710
Quote:
Originally Posted by DoggieDaddy View Post
Ours is doing the same but only once a week or so at night when it's working hard to heat. We had the unit serviced at the end of November and a blower motor replaced in January. it's always something with this piece of junk. It is the weakest part of this coach. I wished there was a more reliable product to replace it with.

I'll be very interested in whatever the resolution is for this issue.
I can’t imagine why a moter would need replaced on 2014 unit. They can be rebuilt pretty reasonably unless shorted out.
__________________
2014 Fleetwood Providence 42p
pointrow is offline   Reply With Quote
Old 02-05-2018, 08:23 PM   #12
Member
 
Chad K's Avatar
 
Join Date: Nov 2012
Location: Kansas
Posts: 72
Thanks for the responses. I will do some more checks this weekend. Agree with DoggieDaddy the AH is the weakest part of the RV. We have had numerous issues with our AH.
__________________
Chad and Nanci
2014 Entegra Anthem 44SL
Chad K is offline   Reply With Quote
Old 02-05-2018, 09:13 PM   #13
Senior Member
 
Franko Foto's Avatar
 
Join Date: Jun 2015
Location: Wilmington NC
Posts: 157
I had intermittent AquaHot - it would just stop running for no apparent reason. It was traced to the switch at the door which was failing at various times.

Remove the switch and attach a multimeter set to continuity. Each time the switch is compressed it should produce a reaction on the meter - mine is a tone. I connected the switch to my meter and compressed the switch a dozen times and then one time it did not close the circuit and I had the culprit.

If you disconnect the switch and override with a standard fuse (photo) - connect a spade receiver on each side of the switch via the fuse, that will at least eliminate the switch as a source.

Frank
Attached Thumbnails
Click image for larger version

Name:	fuse-20a-ato.jpg
Views:	156
Size:	96.6 KB
ID:	191327  
__________________
Frank and Ruth
2017 Cornerstone
Franko Foto is offline   Reply With Quote
Old 02-06-2018, 04:28 AM   #14
Senior Member
 
DoggieDaddy's Avatar
 
Join Date: Jul 2013
Location: Where ever we park it
Posts: 1,295
Quote:
Originally Posted by pointrow View Post
I can’t imagine why a moter would need replaced on 2014 unit. They can be rebuilt pretty reasonably unless shorted out.
When you are full timing the AH is running every day. I don't think any of the parts used in the AH are built for that. It's not a "residential grade" unit I guess.
__________________
Robert & Holly - "Fulltimers" 8+ years
Schnauzers Augie Doggie and Monty Puppy
2014 Anthem 44B Rad Copper ----- SOLD
DoggieDaddy is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Aqua Hot solution to my hot, cold, hot water problem JeffK Entegra Owner's Forum 38 06-25-2017 03:54 PM
Front TV Shuts Off When Engine Starts DonBaja Monaco Owner's Forum 20 04-08-2010 09:49 AM
Refrigerator shuts off on propane glenda1908 Winnebago Industries Owner's Forum 4 09-30-2009 04:59 PM
Problem with heater, shuts off after 30 secs EAB 5th Wheel Discussion 8 10-18-2006 04:08 AM
Generac starts then shuts off royis RV Systems & Appliances 5 07-02-2005 06:19 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 10:43 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.