Colman Mach heat pumps - entegra cornerstone 2018

Hi everyone

On my zone one or heat pump one the fan seems to kick on properly but the compressor never kicks on completely. When I set heat or cold. I see the digital breaker panel turn on for a second (for the compressor) and I can hear the compressor kick on for half a second but it shuts off right away. The fan keeps running continuously though on high.

Could anyone provide troubleshooting or ideas as to what is happening and what I can do to fix it thank you
ChuckGirard is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 04-01-2023, 11:18 AM   #2
Senior Member
 
Join Date: Jul 2022
Posts: 220
Quote:
Originally Posted by ChuckGirard View Post
Hi everyone

On my zone one or heat pump one the fan seems to kick on properly but the compressor never kicks on completely. When I set heat or cold. I see the digital breaker panel turn on for a second (for the compressor) and I can hear the compressor kick on for half a second but it shuts off right away. The fan keeps running continuously though on high.

Could anyone provide troubleshooting or ideas as to what is happening and what I can do to fix it thank you
Start capacitor most likely problem. Pull air conditioner cover and it’s in the small metal box.
__________________
2020 Cornerstone
Ambetter is offline   Reply With Quote
Old 04-01-2023, 03:00 PM   #3
Senior Member
 
Join Date: May 2016
Location: Highland NY
Posts: 3,763
Quote:
Originally Posted by ChuckGirard View Post
Hi everyone

On my zone one or heat pump one the fan seems to kick on properly but the compressor never kicks on completely. When I set heat or cold. I see the digital breaker panel turn on for a second (for the compressor) and I can hear the compressor kick on for half a second but it shuts off right away. The fan keeps running continuously though on high.

Could anyone provide troubleshooting or ideas as to what is happening and what I can do to fix it thank you
Quote:
Originally Posted by Ambetter View Post
Start capacitor most likely problem. Pull air conditioner cover and it’s in the small metal box.
I though the same thing with my 21. Turned out needed a new HP
__________________
Bruce, Lisa and the pups, Charlie, Opie and Rebel
2021 Cornerstone Y Azure
2018 Anthem, Victory Blue Sold, 2019 Ram Laramie 1500
buddy110 is offline   Reply With Quote
Old 04-01-2023, 10:14 PM   #4
Senior Member
 
bevandtomH's Avatar
 
Join Date: Feb 2013
Posts: 2,613
Chuck, what temp demand are you asking for?

I am surmising the exterior temp is above 40°

Reason for asking is this; if the coach inside temp is 68°, and I ask for the heat pump to come on at say, 70°, the compressor doesn’t necessarily fire, only the fan.
I think there has to be a greater delta to get the compressor to fire.
At least, that is what happens with ours.
You might want to play with various deltas before you look at repair/replace.
__________________
___________
Tom & Bev, Riley 6yo Lab
2014 Entegra Aspire 44b, 2017 Jeep JKU
bevandtomH is offline   Reply With Quote
Old 04-02-2023, 08:11 AM   #5
Registered User
 
Join Date: Feb 2021
Posts: 1,337
You can try unplug the freeze sensor and see if the unit keeps running. If it’s does, then you just need to swap that out. If not, would need to get into the shop for a proper diagnosis. Contact your selling dealer or any NIRVC service center.
Bobby Dowdle is offline   Reply With Quote
Old 04-02-2023, 09:04 PM   #6
Senior Member
 
TerryO's Avatar
 
Entegra Owners Club
Join Date: Feb 2012
Location: Midland, Texas
Posts: 605
Sounds like your compressor is trying to start but not. It could be a bad capacitor or a locked compressor. I’ve just had the same problem. Checked capacitor microfarad rate first, found it good. Checked amp draw on compressor during start attempt found it drawing locked rotor amps. I was going to order a new compressor until I noticed oil on the vapor line comping out of the evap coil. Obviously a refrigerant leak. The 15,000 btu unit only has 22 oz of R410a. With such a small amount of refrigerant any leak will be the end of the compressor. Time for a new unit.
__________________
Terry & Gloria O, Midland, Texas
2020 Entegra Aspire 44W, 2022 F250 King Ranch
2012 Entegra Aspire 42RBQ Traded
TerryO is offline   Reply With Quote
Old 04-03-2023, 04:17 AM   #7
Senior Member
 
Join Date: May 2016
Location: Highland NY
Posts: 3,763
Quote:
Originally Posted by TerryO View Post
Sounds like your compressor is trying to start but not. It could be a bad capacitor or a locked compressor. I’ve just had the same problem. Checked capacitor microfarad rate first, found it good. Checked amp draw on compressor during start attempt found it drawing locked rotor amps. I was going to order a new compressor until I noticed oil on the vapor line comping out of the evap coil. Obviously a refrigerant leak. The 15,000 btu unit only has 22 oz of R410a. With such a small amount of refrigerant any leak will be the end of the compressor. Time for a new unit.
That's [retty much what I found also. Similar symptoms, diagnosis and outcome. In my case it took 16 weeks during covid to get a replacement
__________________
Bruce, Lisa and the pups, Charlie, Opie and Rebel
2021 Cornerstone Y Azure
2018 Anthem, Victory Blue Sold, 2019 Ram Laramie 1500
buddy110 is offline   Reply With Quote
Old 04-03-2023, 05:19 AM   #8
Senior Member
 
RVFunlovers's Avatar


 
Entegra Owners Club
Spartan Chassis
Join Date: Oct 2017
Posts: 1,662
Terry or Bruce, I have never had to replace a HVAC.
What is a ballpark cost for getting a unit replaced?
The HVAC unit? Labor?
__________________
Hal and Pam
2022 Entegra Cornerstone W
2020 Ford Edge ST
Sold 2017 Entegra Cornerstone B
RVFunlovers is offline   Reply With Quote
Old 04-03-2023, 05:23 AM   #9
Senior Member
 
Join Date: May 2016
Location: Highland NY
Posts: 3,763
Quote:
Originally Posted by RVFunlovers View Post
Terry or Bruce, I have never had to replace a HVAC.
What is a ballpark cost for getting a unit replaced?
The HVAC unit? Labor?
My guess is over 2k, but mine was replaced under warranty. Call service, they will quote you a price. Or DIY if you have the expertise
__________________
Bruce, Lisa and the pups, Charlie, Opie and Rebel
2021 Cornerstone Y Azure
2018 Anthem, Victory Blue Sold, 2019 Ram Laramie 1500
buddy110 is offline   Reply With Quote
Old 04-04-2023, 09:00 PM   #10
Senior Member
 
TerryO's Avatar
 
Entegra Owners Club
Join Date: Feb 2012
Location: Midland, Texas
Posts: 605
Replacing Coleman Mach 8

Quote:
Originally Posted by RVFunlovers View Post
Terry or Bruce, I have never had to replace a HVAC.
What is a ballpark cost for getting a unit replaced?
The HVAC unit? Labor?
Mine just came in yesterday. RV Products Shop in Wichita was $1964 with shipping. Originally their site said 6-8 weeks but mine came in 10 days. I’ll replace it myself so I’m not sure what labor would be to have it done.

It’s not my first one. Our 2012 had the rear unit go out. The solenoid came off the reversing valve and rubbed a hole in the valve body. I couldn’t source the reversing valve (Chinese) so it was a replacement.

They are not hard to replace IF you have a forklift and scissor lift
__________________
Terry & Gloria O, Midland, Texas
2020 Entegra Aspire 44W, 2022 F250 King Ranch
2012 Entegra Aspire 42RBQ Traded
TerryO is offline   Reply With Quote
Old 04-05-2023, 12:53 PM   #11
Senior Member
 
Marcosdad's Avatar
 
Entegra Owners Club
Join Date: Apr 2012
Location: Green Valley, AZ
Posts: 1,731
I've had to replace two A/C's. North of $2K each. Glad I have the extended warranty
__________________
Stew and Diane (and Marco)
2018 Entegra Cornerstone 45X
Formerly: 2015 Entegra Cornerstone 45B, 2013 Entegra Aspire DEQ IFS, 2004 DSDP; all sold
Marcosdad is offline   Reply With Quote
Reply

Tags
entegra, heat, heat pump, pump



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Entegra Cornerstone :: 2018 Entegra Cornerstone 45B mwmeier iRV2 Owners Registry 0 01-13-2022 12:04 PM
Colman Mach Air Conditioner mod Johndale RV Systems & Appliances 2 06-19-2021 04:03 PM
2007 Allegro bus no heat from Colman heat pump Veloce007 Tiffin Owner's Forum 1 02-22-2020 05:56 AM
Winnebago 2004 Adventurer Basement AC/Heat, Colman Mac Model 6535 and 6536 Heat Pump CarlJudy Class A Motorhome Discussions 3 11-05-2012 05:19 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 05:36 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2023, vBulletin Solutions, Inc.