Dual Inverter Question

To all the Anthem and Cornerstone owners who have two inverters, I have a question for you. The Magnum inverters have the ability to configure the amount of current to pull from shore power. If the AC load exceeds this limit, the inverter will try to meet this demand by utilizing the batteries. How do you configure the two inverters so as not to overwhelm one shore circuit and blow the breaker at the pedestal? For example, if the pedastal supplies 30A, then do you configure both inverter shore power to 30A or some combination 20/10, 15/15 on the two inverters to avoid exceeding 30A? It seems that to do this correctly, the best solution would be for the two inverters to talk to each other and to know what each inverter is drawing from the shore power. I haven't heard or seen anything about that and wonder how it all works together.
SteveUpp is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 11-22-2013, 09:57 PM   #2
Senior Member
 
Scottybdivin's Avatar


 
Newmar Owners Club
Join Date: Jun 2012
Location: Spicewood Texas (West of Austin)
Posts: 4,574
Quote:
Originally Posted by SteveUpp View Post
To all the Anthem and Cornerstone owners who have two inverters, I have a question for you. The Magnum inverters have the ability to configure the amount of current to pull from shore power. If the AC load exceeds this limit, the inverter will try to meet this demand by utilizing the batteries. How do you configure the two inverters so as not to overwhelm one shore circuit and blow the breaker at the pedestal? For example, if the pedastal supplies 30A, then do you configure both inverter shore power to 30A or some combination 20/10, 15/15 on the two inverters to avoid exceeding 30A? It seems that to do this correctly, the best solution would be for the two inverters to talk to each other and to know what each inverter is drawing from the shore power. I haven't heard or seen anything about that and wonder how it all works together.
My understanding is that the the Magnum inverters can only pass through 30 A / leg, therefore a 2 in 2 out configuration would only yield a Max of 30A to either leg. My assumption is that 1 leg would go to one inverter and the 2nd to the other, in a 1 in 1 out configuration Neither should pass more than 30A. I would like to hear explanations from others as well.
__________________
Scotty and Kristen, Airedales Wyatt and Belle Starr
2007 Newmar Mountain Aire 4528, 450 HP ISM, Allison
2024 Brinkley G4000
2022 F350 DRW King Ranch 4 x 4
Scottybdivin is offline   Reply With Quote
Old 11-22-2013, 10:14 PM   #3
Senior Member
 
SteveUpp's Avatar
 
Join Date: Nov 2013
Location: Fulltime Nomads
Posts: 250
I have looked at the Magnum manual available here: http://www.magnumenergy.com/Literatu...eries)_Web.pdf and the inverter can clearly handle 50A.

Your comment however triggered a new thought. These coaches have 8 6-Volt batteries. I assumed that these batteries were wired with 2 6-Volt batteries in series and then each pair was wired in parallel. Is the battery bank in fact wired in parallel where there are 4 x 2 - 6Volt batteries shared between the two inverters? Or does each Inverter have its own independent battery bank consisting of 2 x 2 6-Volt batteries? Having two independent banks of batteries would make energy management more challenging I would think.
SteveUpp is offline   Reply With Quote
Old 11-22-2013, 10:26 PM   #4
Senior Member
 
redbaron73's Avatar
 
Newmar Owners Club
Freightliner Owners Club
Join Date: Jun 2011
Location: Texas
Posts: 6,597
Blog Entries: 4
These are Magnum Energy inverters that are designed to Parallel. This means that the two will communicate with each other and automatically adjust the power draw. The two also read the same battery bank, and adjust accordingly. Basically 2 inverters function as 1 larger unit.
__________________
2022 London Aire 4551 * 2022 GD Imagine 2800BH * 2021 RAM 3500 DRW * 2020 Wrangler
NHSO (Newmar Hoot, Sevierville Original)
Kindness Matters
redbaron73 is online now   Reply With Quote
Old 11-22-2013, 10:49 PM   #5
Senior Member
 
MRUSA14's Avatar
 
Entegra Owners Club
Join Date: Nov 2012
Posts: 8,306
I question whether the inverters will augment power by drawing on the batteries when the 30A shore power is exceeded. I have never seen anything in the manuals to that effect. I think people may have been confused about the shore poer max setting. The Magnum manual says "Shore Max/Input Amps: This setting ensures the inverter AC loads receive the maximum current available from the utility or generator power. When the total current used to power the AC loads and charge the batteries begins to approach the Shore Max setting, the current that was used for charging the batteries will automatically be reduced."

That speaks for itself. I think that the coach will draw as much power as it can from the shore connection, and if the shore power capacity is exceeded, the shore outlet circuit breaker will (hopefully) pop. Only then will the inverter draw battery power to service the coach.
__________________
Marc and Jill, Wellington FL
2013 Entegra Anthem 44SL
2018 Lincoln MKX
MRUSA14 is offline   Reply With Quote
Old 11-23-2013, 07:13 AM   #6
Senior Member
 
Scottybdivin's Avatar


 
Newmar Owners Club
Join Date: Jun 2012
Location: Spicewood Texas (West of Austin)
Posts: 4,574
Quote:
I have looked at the Magnum manual available here: http://www.magnumenergy.com/Literatu...eries)_Web.pdf and the inverter can clearly handle 50A.
Transfer Relay Capability
MS2000: 30 A single input
MS2012, MS2812, MS4024: 2 legs at 30 A for 120 V/30 A or 240 V/60 A service

MS Series Data Sheet
__________________
Scotty and Kristen, Airedales Wyatt and Belle Starr
2007 Newmar Mountain Aire 4528, 450 HP ISM, Allison
2024 Brinkley G4000
2022 F350 DRW King Ranch 4 x 4
Scottybdivin is offline   Reply With Quote
Old 11-23-2013, 08:01 AM   #7
Senior Member
 
SteveUpp's Avatar
 
Join Date: Nov 2013
Location: Fulltime Nomads
Posts: 250
Quote:
Originally Posted by Scottybdivin View Post
Transfer Relay Capability MS2000: 30 A single input MS2012, MS2812, MS4024: 2 legs at 30 A for 120 V/30 A or 240 V/60 A service MS Series Data Sheet
The model I was referring to was the MSH model where the hybrid part is where the inverter combines AC with battery to handle high loads. But that is not the model used in the Entegra. What is actually used? Is it the MS2012 and Ms2812? Does each inverter have it's own battery bank?
__________________
Steve & Karen Upp
2019 Newmar New Aire 3341 (1620W solar, 1200AH Lithionics LiFePO4 Batteries)
2021 Ford F150 PowerBoost
SteveUpp is offline   Reply With Quote
Old 11-23-2013, 08:19 AM   #8
Senior Member
 
DSL417's Avatar
 
Entegra Owners Club
Join Date: Sep 2012
Posts: 6,730
Blog Entries: 2
I don't believe each operates its own battery bank. they are programmed to work together as MRUSA said.
__________________
Dave and Beth
2015 Cornerstone 45J
2020 Ford F-150 Lariat
DSL417 is offline   Reply With Quote
Old 11-23-2013, 09:04 AM   #9
Senior Member
 
SteveUpp's Avatar
 
Join Date: Nov 2013
Location: Fulltime Nomads
Posts: 250
In looking at the manuals for the MS2012 and MS2812 (the two inverters I think are included in the Entegra coaches) I don't see any reference to how the two inverters are tied together.

I see that model MS4024 supports Series Stacking for 120/240 VAC, but neither the MS2012 nor MS2812 support stacking.

Perhaps someone with one of these coaches could trace their battery cables and see if they can tell if all the batteries are in the same bank or are in different banks for each inverter.
SteveUpp is offline   Reply With Quote
Old 11-23-2013, 09:13 AM   #10
Senior Member
 
SteveUpp's Avatar
 
Join Date: Nov 2013
Location: Fulltime Nomads
Posts: 250
MRUSA14 - I see that the MS2012 and MS2812 do not do support the hybrid behavior that the MSH models support... I started off by reading the MSH manual and I didn't realize it was unique to the MSH series.
SteveUpp is offline   Reply With Quote
Old 11-23-2013, 09:32 AM   #11
Senior Member
 
Join Date: Jan 2011
Posts: 288
Quote:
Originally Posted by SteveUpp View Post
To all the Anthem and Cornerstone owners who have two inverters, I have a question for you. The Magnum inverters have the ability to configure the amount of current to pull from shore power. If the AC load exceeds this limit, the inverter will try to meet this demand by utilizing the batteries. How do you configure the two inverters so as not to overwhelm one shore circuit and blow the breaker at the pedestal? For example, if the pedastal supplies 30A, then do you configure both inverter shore power to 30A or some combination 20/10, 15/15 on the two inverters to avoid exceeding 30A? It seems that to do this correctly, the best solution would be for the two inverters to talk to each other and to know what each inverter is drawing from the shore power. I haven't heard or seen anything about that and wonder how it all works together.
I found this interesting.

I wrote Magnum about the load carrying feature because I wanted to set my input amps at 13 yet be able to start and run an AC unit off a regular house 15 amp breaker- or off a Honda 2K plumbed into propane.

Their rep replied that they do not guarantee the load carrying feature will work fast enough to start a "motor" like an AC unit without tripping.

Uncle Dave
Uncle Dave is offline   Reply With Quote
Old 11-23-2013, 09:44 AM   #12
Senior Member
 
SteveUpp's Avatar
 
Join Date: Nov 2013
Location: Fulltime Nomads
Posts: 250
Uncle Dave - turns out I think I was wrong about the load sharing capability because I don't think the Magnum inverters used in the Entegra coaches have that capability... The load sharing feature is an MSH series feature not the MS.
SteveUpp is offline   Reply With Quote
Old 11-23-2013, 11:12 AM   #13
Registered User
 
Entegra Owners Club
Join Date: Mar 2013
Posts: 2,516
A couple days ago while talking to CS I noticed one of my inverters was dark, the other had several green lights. I asked about it and he said the batteries assigned to one inverter were fully charged while the rest were still being charged by the other inverter. So looks like they do charge specific batteries and not cooperatively.
TXBart is offline   Reply With Quote
Old 11-23-2013, 01:17 PM   #14
Senior Member
 
rogelling's Avatar
 
Join Date: Oct 2013
Location: Blanchard, Idaho
Posts: 813
I believe my coach was built in August this year and according to the manuals provided, I have the MS 2812 and a series ME modified sine wave for the second inverter.

There is a review written by Mark "Cruzer" that covers the new MSH hybrid posted on FMCA.

Probably the single disappointment with our Anthem vs the Allegro Bus was the lack of EMS. The bus comes with the PCI system and remote display which I really miss. That is going to be one of my priorities for upgrade but it is something I don't feel I can tackle based on the PCI installation manual.

I can't really understand why Entegra misses out on this feature.

2014 Anthem 42RBQ
rogelling is offline   Reply With Quote
Reply

Tags
inverter



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 03:11 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2025, vBulletin Solutions, Inc.