Eaton GFCI failure and search for replacement

I’m embarrassed to post this thread because it took me approximately two full days to finally get this problem resolved and it should have taken an hour or two and a trip to a Lowes and fini !! For no discernable reason, one day Dee wanted to wash some clothes and she said that the washer was not working. Of course, the most likely culprit was the circuit breaker. On my Cornerstone, there are two Circuit breaker boxes above the driver’s seat. The left box is composed of all loads that are run directly and exclusively off of shore/commercial power. The right box is composed of loads and circuits that are powered by the Magnum inverters and are powered off the house batteries or the Magnum inverter bypass. The circuit I was looking for was then in the left box for commercial power only and marked “washer”. There are twelve circuits in that box, and 9 separate breakers. Three of the breakers are GFCI circuits with test buttons to provide additional protection from bad grounds and potential shock or electrocution. The Washer GFCI was thrown. I tried to reset and it immediately kicked right back off. Obviously, a problem in that circuit or appliance. I first accessed the duplex plugs in the rear of the coach behind the temporary panel in the closet. The top duplex had the dryer power cord and the bottom duplex had the washer power. I first unplugged the washer and swapped it with the dryer and this time the dryer GFCI did not trip. Then I plugged the dryer into the washer duplex and the circuit kicked off.. That told me conclusively that the problem was the Eaton GFCI. Easy!!

So, off to Lowes in State College to buy an Eaton GFCI 20 amp breaker, exact replacement. . Problem was that they didn’t have any!?! Lots of Eaton regular breakers but no GFCI. So off to Home Depot and again, no Eaton 20 amp GFCI. So, then off to an electrical supply company to buy a breaker and they didn’t have any either. So I powered the washer through an extension cord and waited until we arrived in Allentown to hit the bigger, better stocked Lowes. Guess what? NO 20 amp Eaton GFCI there either. Then I noticed some Eaton breakers all by themselves hanging in blister packages. They were about $70, and reading through the packaging I discovered that now they are a three of four function circuit-breaker that does ground fault plus detection of sparks, and at least one other function. Maybe those would work, but I wasn’t sure. Decided to wait until I could call Middlebury. Called Middlebury parts and explained that Eaton apparently did not make a GFCI breaker any more and the parts lady said “No problem, look for a 20 amp Siemen’s GFCI breaker, Model QF-120A”. So off to Lowes once again and they had it, but it was again around $60 and that seemed high. So checked Amazon, and they had the Siemens QF-120A and they were about $45 each, so bought two with Prime and had in two days.

Now, here is the most important part. Probably all Entegra coaches through 2019 and I would bet through 20 or 21 have a bunch of those Eaton GFCI breakers in the boxes. On my coach, there are 6 of them total. In the left commercial power box there are three and in the right inverter box there are three more. As of this fiasco, I now carry an extra spare circuit breaker to replace every type of circuit breaker that is in the bus…. Every size and type. And if you ever have a 20 amp Eaton GFCI fail, it would behoove you to have at least one Siemens QF-120A GFCI in your basement if you don’t want to go through the problems I had to find a replacement. Mark that down my friends…… Siemens QF-120A. In hindsight I probably could have gotten the sophisticated Eaton in the blister pack and been fixed a few days earlier but it was expensive and I believe it had an extra push-on connector on the back that would have prevented it from it being installed in our boxes. I didn’t buy it so don’t really know. One final comment, the correct Siemens come with a curled/coiled solid conductor (not stranded wire) coiled nicely behind the breaker. That bothered me as the OEM Eaton did not seem to have it, however, I realize that you just nicely uncoil the pigtail and it is the wire that does go to the neutral. Don’t be afraid of the pigtail…. Just unwind and straighten and cut off what you don’t need..

Took way too long to simply replace a circuit breaker

Pix #1; OEM failed Eaton GFCI breaker to washer.
Pix #2: New Siemens QF-120A GFCI breaker.
Pix #3: left side, Line-Powered circuit breaker box. The new Siemens replacement is next to last far right.
Pix #4: right side, Interver-Powered circuit breaker box.

Gary
Attached Thumbnails
Click image for larger version

Name:	Cornerstone - Circuit breaker box - failed Eaton 20A GFCI - one of 6 of these.jpg
Views:	8
Size:	54.1 KB
ID:	332224   Click image for larger version

Name:	Cornerstone - Circuit breaker box - replacement Siemens QF-120A.jpg
Views:	7
Size:	51.0 KB
ID:	332225  

Click image for larger version

Name:	Cornerstone - Circuit breaker box - line -powered (Left).jpg
Views:	13
Size:	78.0 KB
ID:	332226   Click image for larger version

Name:	Cornerstone - Circuit breaker box - Inverter powered.jpg
Views:	9
Size:	97.0 KB
ID:	332227  

__________________
Gary and Dee, Zowie and Bowie (traveling cat sibs)
2019 Cornerstone 45B, X15-605hp, Imperial, Spartan K3,
2013 Honda CR-V toad, Demco Excali-Bar II,
Demco Baseplate, Demco Toad Light system, 73 de W5FI
Gary.Jones is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 06-15-2021, 10:47 AM   #2
Senior Member
 
garysfb's Avatar


 
Entegra Owners Club
Join Date: May 2019
Posts: 758
Gary, no need to be embarrassed! Great job going through the process of troubleshooting and tracking down the correct part. Now you may save one of us those two days in the future
__________________
Gary and Phyllis Small
2018 Anthem 44F
2019 Jeep Wrangler Unlimited - Sahara
2003 Alegro Bus (sold)
garysfb is offline   Reply With Quote
Old 06-15-2021, 10:56 AM   #3
Senior Member
 
Gary.Jones's Avatar


 
Join Date: Oct 2012
Location: Louisiana
Posts: 8,984
Blog Entries: 1
One more thing. I found that this bad breaker (and it was not the cause of the problem) had a problem that I first saw within a day or two after I left NIRVC when I picked up the coach and it absolutely drove me nuts trying to figure out what the problem was. I have included a picture of the two white wires coming out of the old Eaton circuit breaker. Notice the amount of insulation that was stripped off the wires. The one on the bottom is pretty good. Remember, that wire is going to be pushed into one of the grounds or neutrals of the Eaton GFCI or the buss. The wire on the top in the picture has approximately half of the insulation stripped off of it that it should have stripped off, and if it was installed quickly, that wire might never make an electrical connection with the grounding buss. Now, this circuit worked for three years so I dont think that it was what caused the GFCI to keep kicking off, but it is the exact same problem that drove me nuts when I first bought the coach with a wire that had even less insulation stripped off the solid copper center conductor and in that case, the wire was definitely NOT making any electrical connection. Whoever did the electrical assembly and installation work on this coach simply did it so quickly that they never looked at how much insulation they were removing from the wire and in the earlier case I am discussing, there was so much insulation still on the wire, that the wire never made contact with the circuit breaker it was inserted into. Easy mistake, but just indicates sloppy, quick work.

Gary
Attached Thumbnails
Click image for larger version

Name:	Cornerstone  - electrical - wire stripping problem.jpg
Views:	10
Size:	30.4 KB
ID:	332232  
__________________
Gary and Dee, Zowie and Bowie (traveling cat sibs)
2019 Cornerstone 45B, X15-605hp, Imperial, Spartan K3,
2013 Honda CR-V toad, Demco Excali-Bar II,
Demco Baseplate, Demco Toad Light system, 73 de W5FI
Gary.Jones is offline   Reply With Quote
Old 06-15-2021, 02:33 PM   #4
Senior Member
 
Gary.Jones's Avatar


 
Join Date: Oct 2012
Location: Louisiana
Posts: 8,984
Blog Entries: 1
All the OEM Eaton GFCI breakers in both boxes except for the new Siemens Washer breaker have the white. "test" button near the bottom. The new Siemens, (second from right-most in the third picture) has that white test button replaced with a small, circular test button in the lower left of the breaker. There is an LED in that button that also tells you the main reason that the breaker has tripped.

This wording is from the Lowes web page for this product. It also explains to me for the first time why the breaker has been forced to change to this Siemens' type
-------------------------------------------

"The dual function circuit breaker combines GFCI and AFCI, protecting against both arc faults and ground faults. This, along with the new self-test and lockout feature, makes it the first in class in electrical safety for homeowners. The 2014 national electrical code (NEC) now requires both arc fault and ground fault protection on kitchen and laundry circuits. Dual function circuit breakers combines GFCI and AFCI protecting against both arc faults and ground faults

The 2014 national electrical code (NEC) now requires both arc fault and ground fault protection on kitchen and laundry circuits

Exclusive LED trip indicator pinpoints cause of trip

Wire range: #14-#8 AWG copper or #12-#8 AWG aluminum"

Gary
__________________
Gary and Dee, Zowie and Bowie (traveling cat sibs)
2019 Cornerstone 45B, X15-605hp, Imperial, Spartan K3,
2013 Honda CR-V toad, Demco Excali-Bar II,
Demco Baseplate, Demco Toad Light system, 73 de W5FI
Gary.Jones is offline   Reply With Quote
Old 06-15-2021, 02:55 PM   #5
Senior Member
 
garysfb's Avatar


 
Entegra Owners Club
Join Date: May 2019
Posts: 758
If the code changed in 2014 why were they installing the older ones in a coach probably built in 2018? Inventory grandfathered in?
__________________
Gary and Phyllis Small
2018 Anthem 44F
2019 Jeep Wrangler Unlimited - Sahara
2003 Alegro Bus (sold)
garysfb is offline   Reply With Quote
Old 06-15-2021, 03:15 PM   #6
Senior Member
 
Gary.Jones's Avatar


 
Join Date: Oct 2012
Location: Louisiana
Posts: 8,984
Blog Entries: 1
Good Question

Maybe the Eatons were dual function also, but I have never seen it referred to that way.... Eaton dumping old stock...... lots of possibilities.
__________________
Gary and Dee, Zowie and Bowie (traveling cat sibs)
2019 Cornerstone 45B, X15-605hp, Imperial, Spartan K3,
2013 Honda CR-V toad, Demco Excali-Bar II,
Demco Baseplate, Demco Toad Light system, 73 de W5FI
Gary.Jones is offline   Reply With Quote
Old 06-15-2021, 05:07 PM   #7
Senior Member
 
Dr. Mike's Avatar


 
Entegra Owners Club
Join Date: Sep 2020
Posts: 200
"And if you ever have a 20 amp Eaton GFCI fail, it would behoove you to have at least one Siemens QF-120A GFCI in your basement if you don’t want to go through the problems I had to find a replacement. Mark that down my friends…… Siemens QF-120A."


Question: Should this be added to the "sticky" for all the spare parts, belts and filters on the Entegra home page?

Best

Dr. Mike
__________________
Dr. Mike and Barb
2014 Entegra Anthem
FMCA F519406
Dr. Mike is offline   Reply With Quote
Old 06-15-2021, 05:33 PM   #8
Senior Member


 
Winnebago Owners Club
Join Date: Sep 2015
Posts: 774
There are really only three styles of breakers. Eaton and Cutler Hammer are interchangeable. There is the GE style and then Square D. If you have a breaker go, take it out and take it with you. The big box stores handle them all. I blew a Eaton while I was in Mexico. Only one style there. GE. Got to Tucson and walked in with the Eaton and not an Eaton in the store Cutler Hammer is the DIY version. Plenty of them. I carry 3 different 50 amp and 3 different 20 amp with me. I would have had one, but it would not have been GFCI. You'd have to risk it until you got the right one.
__________________
2006 Winnebago Journey
39K
Cat C7
amosnandy is offline   Reply With Quote
Old 06-15-2021, 08:27 PM   #9
Senior Member
 
Gary.Jones's Avatar


 
Join Date: Oct 2012
Location: Louisiana
Posts: 8,984
Blog Entries: 1
Mike

There is so much outdated and inaccurate information in that sticky that I am not inclined to add it to that list. Maybe people will find the information by searching for GFCI or similar.

Gary
__________________
Gary and Dee, Zowie and Bowie (traveling cat sibs)
2019 Cornerstone 45B, X15-605hp, Imperial, Spartan K3,
2013 Honda CR-V toad, Demco Excali-Bar II,
Demco Baseplate, Demco Toad Light system, 73 de W5FI
Gary.Jones is offline   Reply With Quote
Old 06-16-2021, 09:06 AM   #10
Senior Member
 
Join Date: Mar 2020
Posts: 156
Quote:
Originally Posted by garysfb View Post
If the code changed in 2014 why were they installing the older ones in a coach probably built in 2018? Inventory grandfathered in?



My bet is a national code adopted for S&B is not necessarily used as an oversight/check when dealing with a motorcoach build. I am sure Entegra doesn't schedule a framing/plumbing/electrical inspection with the city for each coach. So Entegra gets a good deal to help the Eaton's of the world work through (in this case) breakers that can't be used in residential building any longer.
__________________
Jeff and Kathy (Molly, Bella and Butterscotch fur kids)
2020 Entegra Reatta XL 40Q2
2019 Cherokee Trailhawk RViBrake3 +TPMS
jeff.herren is offline   Reply With Quote
Old 06-16-2021, 10:08 AM   #11
Senior Member
 
Gary.Jones's Avatar


 
Join Date: Oct 2012
Location: Louisiana
Posts: 8,984
Blog Entries: 1
Might as well complete every aspect of this thread.

I did pay about $60 for a Eaton GFCI at an electrical supply store that I am not using and pretty sure that it will not work at all in the box that is mounted above the driver seat.

The first picture shows the circuit breaker from the front. It appears to be a general match to the one that I took out except for the small round test button at the bottom rather than the big white test button on the ones in the panels in the coach.

However, in the side view of this same breaker, notice the additional clamp sort of connection on the back. The connection appears to be designed to slide into a bar that would be located on the back of the box. Never seen this before and dont really understand it, but that is my guess.

Also, there is no coiled pigtail or even pre-soldered wire out the back of the breaker.

I'm pretty sure that I am now stuck with a $60 Eaton breaker that I will never use and probably give to Goodwill....

Any real electrician, what do I have here?

Gary
Attached Thumbnails
Click image for larger version

Name:	Cornerstone  - Eaton Circuit Breaker with additional friction connection on back.jpg
Views:	8
Size:	38.0 KB
ID:	332368   Click image for larger version

Name:	Cornerstone  - Eaton Circuit Breaker with additional friction connection on back - side view .jpg
Views:	8
Size:	41.9 KB
ID:	332369  

__________________
Gary and Dee, Zowie and Bowie (traveling cat sibs)
2019 Cornerstone 45B, X15-605hp, Imperial, Spartan K3,
2013 Honda CR-V toad, Demco Excali-Bar II,
Demco Baseplate, Demco Toad Light system, 73 de W5FI
Gary.Jones is offline   Reply With Quote
Old 06-16-2021, 02:30 PM   #12
Senior Member
 
Join Date: Jul 2017
Location: Cypress, Tx.
Posts: 441
Quote:
Originally Posted by Gary.Jones View Post
Might as well complete every aspect of this thread.

I did pay about $60 for a Eaton GFCI at an electrical supply store that I am not using and pretty sure that it will not work at all in the box that is mounted above the driver seat.

The first picture shows the circuit breaker from the front. It appears to be a general match to the one that I took out except for the small round test button at the bottom rather than the big white test button on the ones in the panels in the coach.

However, in the side view of this same breaker, notice the additional clamp sort of connection on the back. The connection appears to be designed to slide into a bar that would be located on the back of the box. Never seen this before and dont really understand it, but that is my guess.

Also, there is no coiled pigtail or even pre-soldered wire out the back of the breaker.

I'm pretty sure that I am now stuck with a $60 Eaton breaker that I will never use and probably give to Goodwill....

Any real electrician, what do I have here?

Gary
I am not sure about Eaton but if like Square D they make two types of breakers Ones that have a buss bar for the neutral so when you plug the breaker in the panel it gets it hot from the phase buss bar and the neutral from the neutral buss bar in the panel. This panel has only been out for a few years now.

The other breaker with the pig tail is made for panels that do not have the the neutral buss and only have a neutral bar with screws that the pigtail is attached to.
__________________
2014 Foretravel IH45
Houston (Cypress), TX.
Turbojack is offline   Reply With Quote
Old 06-17-2021, 08:04 AM   #13
Senior Member
 
Props2's Avatar
 
Tiffin Owners Club
Join Date: Apr 2018
Location: McHenry, Illinois
Posts: 272
^^ Correct. All the primary manufactures of load centers are building these new style panels for convenience to installers and provide a cleaner installation. Then new electrical codes being adopted by many municipality's require afci in all areas of the home along with gfi"s as required. The early requirements of afci were bedrooms. So, yes, be careful what you buy.
__________________
2015 Tiffin Phaeton 40QKH All Electric
2015 Dodge Ram Laramie 4x4
Mark and Lori
Props2 is online now   Reply With Quote
Old 06-19-2021, 08:42 AM   #14
Senior Member
 
Gary.Jones's Avatar


 
Join Date: Oct 2012
Location: Louisiana
Posts: 8,984
Blog Entries: 1
Alternately, Entegra will be happy to sell you just one of these little gems for $119 including shipping.

Gary
__________________
Gary and Dee, Zowie and Bowie (traveling cat sibs)
2019 Cornerstone 45B, X15-605hp, Imperial, Spartan K3,
2013 Honda CR-V toad, Demco Excali-Bar II,
Demco Baseplate, Demco Toad Light system, 73 de W5FI
Gary.Jones is offline   Reply With Quote
Reply

Tags
ace, replace, replacement



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Where is master GFCI for bedroom GFCI circuits? cletesingler 5th Wheel Discussion 16 06-17-2021 04:30 AM
Multi topic: Sheppard M80 pump, Eaton diff oil, and dash gauges ground JerryLook Monaco Owner's Forum 30 01-23-2021 10:00 AM
No AC to GFCI outlet string, but GFCI is good Eric1959 RV Systems & Appliances 12 03-21-2019 08:38 PM
Bounder: 2016 Bounder 33C - GFCI keeps tripping (Internal to RV, not house GFCI) nehmia Fleetwood Owner's Forum 8 10-22-2016 07:34 AM


All times are GMT -6. The time now is 09:52 PM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2021, vBulletin Solutions, Inc.