Old 12-09-2017, 03:38 PM   #43
Senior Member
 
John Grant's Avatar
 
Entegra Owners Club
Spartan Chassis
Join Date: Oct 2017
Location: Kissimmee, Central Florida
Posts: 186
Larry, I did find a pump in that compartment. But, it only runs when Zone 1 is set to Gas and the thermostat is calling for heat. I have not been able to find any other circulation pumps yet.
__________________
JGrant
2013 Entegra Aspire
42 DEQ
John Grant is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 12-09-2017, 04:57 PM   #44
Senior Member
 
Thor 37GT's Avatar
 
Entegra Owners Club
Join Date: Jan 2014
Posts: 386
Just thought I would throw this out there. Not all aspires have in floor heat.
__________________
2021 Dynamax 30FW Xplorer , Blue OX Tow bar, '14 Jeep Grand Cherokee
Thor 37GT is offline   Reply With Quote
Old 12-09-2017, 05:01 PM   #45
Senior Member
 
John Grant's Avatar
 
Entegra Owners Club
Spartan Chassis
Join Date: Oct 2017
Location: Kissimmee, Central Florida
Posts: 186
Quote:
Originally Posted by Thor 37GT View Post
Just thought I would throw this out there. Not all aspires have in floor heat.
This is true, original owner I spoke with says yes and it worked awesome. That thought had crossed my mind [emoji23]
__________________
JGrant
2013 Entegra Aspire
42 DEQ
John Grant is offline   Reply With Quote
Old 12-09-2017, 05:07 PM   #46
Senior Member
 
Thor 37GT's Avatar
 
Entegra Owners Club
Join Date: Jan 2014
Posts: 386
Do you have a white thermostat on the wall behind the toilet?
__________________
2021 Dynamax 30FW Xplorer , Blue OX Tow bar, '14 Jeep Grand Cherokee
Thor 37GT is offline   Reply With Quote
Old 12-09-2017, 05:52 PM   #47
Senior Member
 
John Grant's Avatar
 
Entegra Owners Club
Spartan Chassis
Join Date: Oct 2017
Location: Kissimmee, Central Florida
Posts: 186
Frustrated to no end...Basement and Hydronic Floor Heat

Quote:
Originally Posted by Thor 37GT View Post
Do you have a white thermostat on the wall behind the toilet?


No it’s this thermostat, there was a white thermostat in the basement though.

Click image for larger version

Name:	IMG_1080.JPG
Views:	154
Size:	363.9 KB
ID:	185282


This is the thermostat that was in the basement. I replaced it with an entry level digital Honeywell Thermostat.
Click image for larger version

Name:	IMG_0859.JPG
Views:	150
Size:	378.3 KB
ID:	185283
__________________
JGrant
2013 Entegra Aspire
42 DEQ
John Grant is offline   Reply With Quote
Old 12-09-2017, 06:17 PM   #48
Senior Member
 
Thor 37GT's Avatar
 
Entegra Owners Club
Join Date: Jan 2014
Posts: 386
I have a thermostat like what is in your basement on the wall behind my toilet that controls the floor heat and my thermostat in the cabinet is different than yours so I don’t think I will be much help to you. Sorry
__________________
2021 Dynamax 30FW Xplorer , Blue OX Tow bar, '14 Jeep Grand Cherokee
Thor 37GT is offline   Reply With Quote
Old 12-10-2017, 06:06 AM   #49
Senior Member
 
Mwoodofd's Avatar


 
Entegra Owners Club
Join Date: Apr 2013
Location: Las Colinas, Texas
Posts: 2,040
Sounds like that circulation pump may be connected to the wrong zone. If it comes on when zone one is turned, that would be my next place to try. Not sure if it is something connected to the back of the thermostat that could be easily switched to try.

The floor is not getting enough circulation if it is connected to zone 1 - would only run when zone 1 heat registers are running. When I turn on zone 2 gas, and the thermostat is calling for heat, I can hear that pump turn on, and it will run until the coach reaches the temp set. I believe sure the rest of the pumps on on the AH unit.
__________________
Mark & Debra Wood, Las Colinas, TX.
2013 Entegra Aspire 42RBQ
2023 Jeep Wrangler Sahara 4XE
2013 Thor Challenger 37DT - Sold
Mwoodofd is offline   Reply With Quote
Old 12-10-2017, 08:01 AM   #50
Senior Member
 
Entegra Owners Club
Join Date: Mar 2012
Posts: 237
Here is some information that I copied from this forum about how the aquahot zones work that might shed light on your problem. I apologize but I forgot who posted it, but it is good info and has helped me alot.


Another thing to keep in mind is that Zone 2 and Zone 1 use the exact same plumbing loop. Zone 2 is really just sort of a "virtual" zone. The only difference between Zone 1 and 2 is that Zone 1 turns on the fans in the 3 heat exchangers. Actually, I think this is very clever.

Point is when you run Zone 1 you are also heating your floors to a certain extent because the hot water is flowing thru all the same pipe as "virtual" Zone 2.

When Zone 1 is on, the fans in the 3 heat exchangers are on and of course extract more of that heat into the air inside the coach and let less of it go to heating the floor. When Zone 2 is on the hot water runs thru the same pipe and all three heat exchangers but the fans in the three heat exchangers remain off and more of the heat goes into the floor.

I know this because we had a kink in the PEX pipe inside our floor which was not accessible to repair without surgery. During the troubleshooting process and working with Joyce and team I got very familiar with the pipe and zone layout. Entegra of course stepped up and made it right after a trip back to Middlebury - fortunately no tiles needed to be ripped out.

Also FYI, remember the Aquahot (all models as far as I know) have only two circulator pumps. So where do the four zones come from? One of those pumps is for Zone 1 & 2 (salon) and the other is for the Zone 3 (bedroom) and basement.

Same "virtual zone" deal with the Zone 3/basement - when heat is called for on Zone 3 (bedroom) hot water flows thru the bedroom and basement heat exchangers but only the fans on the two bed/bath heat exchangers turn on. If the basement thermostat is on and calls for heat, hot water still flows thru the same bedroom and basement heat exchangers but only the fan on the basement heat exchanger turns on.

You would know right away if you have a kink - for example if you set Zone 1 to come on, you should feel heat at all three heat exchangers (mid coach, under kitchen sink, under dash) after several minutes (gas/diesel burner should be on). If you do have a kink, Zone 2 won't work either.
__________________
James and Diana
2014 Entegra Coach Aspire 44B
jherrin99 is offline   Reply With Quote
Old 12-10-2017, 08:40 AM   #51
Moderator Emeritus
 
Country Coach Owners Club
Freightliner Owners Club
Join Date: Sep 2004
Location: Glen Allen, VA
Posts: 7,902
Blog Entries: 1
Quote:
Originally Posted by John Grant View Post
No it’s this thermostat, there was a white thermostat in the basement though.

Attachment 185282


This is the thermostat that was in the basement. I replaced it with an entry level digital Honeywell Thermostat.
Attachment 185283
That looks like a millivolt t stat. Not sure a digital t stat that usually needs a DC voltage to work can replace a millivolt. Just something to consider.
__________________
2007 Country Coach Allure Siskiyou Summit, sold/traded Nov. 2018.
2019 Grand Designs 384GK-R 5th wheel. Glen Allen, VA
smlranger is offline   Reply With Quote
Old 12-10-2017, 08:44 AM   #52
Senior Member
 
Armye7's Avatar
 
Join Date: May 2015
Posts: 289
I was just thinking the same thing. Jherrin99 post makes sense to me. When mine zone 1 runs a lot my floor temps drop. Soon as zone 1 shuts down my floor reheats.
__________________
Larry & Vickie Carman
2019 Aspire 44W
Springboro Ohio
Armye7 is offline   Reply With Quote
Old 12-10-2017, 08:54 AM   #53
Senior Member
 
hawgguy's Avatar
 
Join Date: Jun 2011
Location: College Station, Texas
Posts: 2,841
Quote:
Originally Posted by smlranger View Post
That looks like a millivolt t stat. Not sure a digital t stat that usually needs a DC voltage to work can replace a millivolt. Just something to consider.
This one works with a triple A that lasts a year or so.
Much nicer and the switch doesn't stick like the stock Tstat
__________________
Bob in College Station, TX
2015 Entegra Cornerstone 45K
2012 Jeep Rubicon, 1994 FXLR
hawgguy is offline   Reply With Quote
Old 12-10-2017, 09:09 AM   #54
Senior Member
 
John Grant's Avatar
 
Entegra Owners Club
Spartan Chassis
Join Date: Oct 2017
Location: Kissimmee, Central Florida
Posts: 186
Folks, you’ve all been so helpful and also you have educated me a lot. I’m understanding this setup much more now than I was prior to this.
So this is what I have come up with and where I’m at.

All interior registers blow hot air when Thermostat is set to gas.

Located a circulation pump in the rear compartment behind the rear axles. This pump only runs when I set my thermostat to zone 1 heat. No other combination of settings will turn on that rear circulation pump.

Basement heat stopped working a month ago, replaced thermostat and still no basement heat.

I’ve checked every single fuse and breaker I can located throughout the entire coach. All are good.

All temps on interior thermostat are set accordingly to Entegra CS recommendations.

I am told I indeed do have hydronic floor heating and that it has worked fantastic in the past.

Zone 2 Heat should call for warm floors, it does not.

I’ve had a certified aquahot tech onsite and quite frankly, jr didn’t know how everything was supposed to work, only that the aquahot was in good working order.

Any thoughts on next steps good people?
__________________
JGrant
2013 Entegra Aspire
42 DEQ
John Grant is offline   Reply With Quote
Old 12-10-2017, 09:12 AM   #55
Community Moderator


 
Join Date: Aug 2011
Posts: 6,201
Quote:
Originally Posted by John Grant View Post
Folks, you’ve all been so helpful and also you have educated me a lot. I’m understanding this setup much more now than I was prior to this.
So this is what I have come up with and where I’m at.

All interior registers blow hot air when Thermostat is set to gas.

Located a circulation pump in the rear compartment behind the rear axles. This pump only runs when I set my thermostat to zone 1 heat. No other combination of settings will turn on that rear circulation pump.

Basement heat stopped working a month ago, replaced thermostat and still no basement heat.

I’ve checked every single fuse and breaker I can located throughout the entire coach. All are good.

All temps on interior thermostat are set accordingly to Entegra CS recommendations.

I am told I indeed do have hydronic floor heating and that it has worked fantastic in the past.

Zone 2 Heat should call for warm floors, it does not.

I’ve had a certified aquahot tech onsite and quite frankly, jr didn’t know how everything was supposed to work, only that the aquahot was in good working order.

Any thoughts on next steps good people?


Maybe call Entegra and truly verify that your coach was built with floor heat.....not just take the word of previous owner.....
pasdad1 is offline   Reply With Quote
Old 12-10-2017, 09:14 AM   #56
Senior Member
 
John Grant's Avatar
 
Entegra Owners Club
Spartan Chassis
Join Date: Oct 2017
Location: Kissimmee, Central Florida
Posts: 186
Quote:
Originally Posted by pasdad1 View Post
Maybe call Entegra and truly verify that your coach was built with floor heat.....not just take the word of previous owner.....


Entegra CS says it has floor heat
__________________
JGrant
2013 Entegra Aspire
42 DEQ
John Grant is offline   Reply With Quote
Reply

Tags
floor, heat, rust



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
How do you search for 'floor heat'... not 'floor' or 'heat' 99phantoms iRV2.com General Discussion 5 06-08-2016 03:46 AM
Frustrated with floor plans! Jerry M Travel Trailer Discussion 17 06-01-2015 10:14 PM
Winnebago 2004 Adventurer Basement AC/Heat, Colman Mac Model 6535 and 6536 Heat Pump CarlJudy Class A Motorhome Discussions 3 11-05-2012 05:19 PM
Hydro Hot Hydronic Heat system Renipladlo Class A Motorhome Discussions 26 09-07-2008 09:20 AM
Hurricane (Hydronic) Heat Question craigt MH-General Discussions & Problems 4 08-21-2007 04:40 AM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 04:31 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.