03-23-2016, 06:22 AM
|
#1
|
Senior Member
Join Date: Dec 2011
Posts: 151
|
How to reset the Magnum charger inverter
Boondocked at a rest area last night and turned the generator off around 10pm and woke up around 6am. The house batteries were low. To low to start the generator so I linked the two sets of batteries and the generator fired right up. However, I couldn't get the house to "switch" over to the generator or the inverters to switch to charging mode. I'm guessing I need to "reset" the inverters. How do I do that?
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
03-23-2016, 06:24 AM
|
#2
|
Senior Member
Join Date: Dec 2011
Posts: 151
|
FYI its a 14 cornerstone.
I sure wish the batteries would last more than 6-7 hours with the only load being the fridge and aqua hot!
What have folks changed our their factory batteries with to give more ampacity? You would think they'd give these things enough battery to comfortably last through the night.
|
|
|
03-23-2016, 06:43 AM
|
#3
|
Senior Member
Nor'easters Club
Join Date: Feb 2009
Posts: 795
|
Did you check circuit breaker on the generator? Gen would run but no power to coach if disengaged.
__________________
2020 Anthem 44F
23 Jeep Cherokee Summit Reserve
BAILEY and BUSTAH,our Boston Terriers!
|
|
|
03-23-2016, 07:24 AM
|
#4
|
Senior Member
Entegra Owners Club
Join Date: Apr 2007
Location: SW FL
Posts: 31,622
|
The inverter resets should be on the inverters mounted to the ceiling of the rear P/S basement compartment.
On the batteries....the charging settings have to be set correctly if this has not been done since delivery. Mine were set from the factory to only charge the batteries at 65% instead of the required 80 to 90% depending on who you talk to.
Also setting the AGS to auto will start the generator before the batteries go dead. The Mag 30 also has to be setup to start before the batteries go dead. There was a post regarding this the other day. I have mine set to 12.1 V other set there lower but risk the generator not starting when needed.
Here is a link to that post that may help your situation. http://www.irv2.com/forums/f278/ags-issue-282560.html
__________________
Chuck in SW FL
Digital 2021 Cornerstone "B"
A "Digital" 2019 Cornerstone "B" Traded
A "Classic" 2014 Anthem 42 RBQ---Sold
|
|
|
03-23-2016, 07:53 AM
|
#5
|
Moderator Emeritus
Join Date: Oct 2002
Location: Sheboygan, WI
Posts: 5,642
|
We boondock at rest areas like you did and have no problem maintaining battery voltage over that time frame. That's running the fridge and Aqua-Hot in fairly cold weather. Your batteries should last longer than that. I would take a good look at your battery condition. They may not be performing as well as they used to.
__________________
Mark & Leann Quasius
2016 Cornerstone 45A
2020 Jeep Gladiator Rubicon
2021 Jeep Wrangler Rubicon
|
|
|
03-23-2016, 02:18 PM
|
#6
|
Senior Member
Newmar Owners Club Entegra Owners Club
Join Date: Feb 2014
Location: Birmingham, Alabama
Posts: 169
|
I had the same problem with the magnum inverter on the Aspire. It is mounted on the ceiling of the basement compartment. There is a small white reset button on the side of the inverter. When I reset this, everything worked. Hope you have figured this out since your post was 7 hours ago
John
2015 Newmar Mountain Aire 4503
2013 Jeep Wrangler Moab Edition
__________________
John
2018 Tiffin Zephyr PZ
2013 Jeep Wrangler Moab Edition
|
|
|
03-23-2016, 02:59 PM
|
#7
|
Senior Member
Tiffin Owners Club Freightliner Owners Club
Join Date: Aug 2014
Posts: 1,899
|
Is this a Magnum MS series inverter.
On this model, you hold power button on the inverter for 15 seconds until the light starts flashing, this resets everything to default values.
Dan
__________________
2014 40QBH Phaeton DP Cummins 380HP ISL, Freightliner XC, 2019 Jeep Grand Cherokee Trailhawk TOAD
Blue Ox Aventa tow bar, SMI Air Force One -Cave Creek, AZ.
|
|
|
03-23-2016, 03:39 PM
|
#8
|
Senior Member
Join Date: Dec 2011
Posts: 151
|
All that was needed was a reset of the inverter and everything is back to normal. However, I would think that the batteries would last longer. I am on my way home from the factory where they load tested the batteries and I was told they were fine.
|
|
|
03-23-2016, 04:03 PM
|
#9
|
Senior Member
Tiffin Owners Club Freightliner Owners Club
Join Date: Aug 2014
Posts: 1,899
|
Have you done the math?
how much load are you drawinv overnight?
What is your LBCO set to?
I think a lot of folks set it betweenn 11.8 and 12v.
And finally, are you sure your batteries are getting to full charge?
What is your battery configuration?
Might try equalizing the batteries.
Regards,
Dan
__________________
2014 40QBH Phaeton DP Cummins 380HP ISL, Freightliner XC, 2019 Jeep Grand Cherokee Trailhawk TOAD
Blue Ox Aventa tow bar, SMI Air Force One -Cave Creek, AZ.
|
|
|
03-23-2016, 05:44 PM
|
#10
|
Senior Member
Join Date: Aug 2010
Location: Wilmington,NC
Posts: 129
|
I am fighting the same battle, been posting some of same issue since last week, first thing I might do would change AGS to start @ 12.3 until u have figured issue out. I plan to take my gen battery from house battery,( if they r low then gen want start). Plan to use separate battery if Onan says ok.
|
|
|
03-23-2016, 06:00 PM
|
#11
|
Senior Member
Entegra Owners Club
Join Date: Apr 2007
Location: SW FL
Posts: 31,622
|
Those of us that have "Taddless era" built coaches have haphazard set charging setups on the inverter/charges and the mag 30. Don, 757Driver has made some great posts on the proper settings for our units. He put a lot of time speaking directly with the vendors and battery manufacture. Just my experience, but mine were not set at the factory. Might help others to check those settings if you are have charging problems like I was.
__________________
Chuck in SW FL
Digital 2021 Cornerstone "B"
A "Digital" 2019 Cornerstone "B" Traded
A "Classic" 2014 Anthem 42 RBQ---Sold
|
|
|
03-23-2016, 07:42 PM
|
#12
|
Senior Member
Entegra Owners Club
Join Date: Nov 2012
Posts: 8,108
|
Quote:
Originally Posted by ikold
All that was needed was a reset of the inverter and everything is back to normal. However, I would think that the batteries would last longer. I am on my way home from the factory where they load tested the batteries and I was told they were fine.
|
Your batteries should last longer than that. Are you sure they are charging fully? Maybe your generator is shutting off too early. Test them after a good 24 hours of shore charge. That way they should be fully topped off. Another possibility is loose or dirty connections at the batteries. That would decrease your run time even if the batteries are good.
__________________
Marc and Jill, Wellington FL
2013 Entegra Anthem 44SL
2018 Lincoln MKX
|
|
|
03-24-2016, 09:40 AM
|
#13
|
Senior Member
Entegra Owners Club
Join Date: Jun 2004
Location: Bayfield, Ontario
Posts: 5,456
|
Do NOT equalize your AGM batteries they are not designed for that.
If your batteries are only lasting 6-8 hours then there is a problem somewhere. In a 24 hour period the average consumption for one of these coaches (without undue waste) is about 400 AH which is about 1/2 or 50% of your battery bank amps (828 installed).
Either the bank is not getting fully charged or you have a bad cell or cells in the battery bank. Check each individual batteries voltage with a DVM and compare all 8 to each other to see if one may be bad. My guess would be not fully charged as the suggested Magnum Inverter settings that the factory uses are not giving you a full charge.
__________________
Don & Gerri
2014 Entegra Anthem 44B
2014 Honda CRV Touring
1300W Solar, 1200AH LiFePO4 FMCA F443497
|
|
|
03-25-2016, 08:43 AM
|
#14
|
Senior Member
Join Date: Dec 2011
Posts: 151
|
That response begs the question. What is the correct / best setup for the magnum inverter and our AGM batteries. I would hope that I could go at least through the night without having to run the generator.
|
|
|
|
|