More Zone 2 info

Here is part of an email I sent CS this morning.

My Anthem is in my driveway. We are experiencing nighttime lows in the high teens to mid twenties to I set Zones 1 and 3 on "Gas" at 45 degrees and turned set basement heat about 25% from the bottom of the range. Zone 2 is off. Burner is on.

When I went out this morning outside temperature was still in the low 20s. Zone 1 and 3 temperatures were high 40s, basement was 56 (I have a remote temperature sensor) and Zone 2 (which is off) was 66.

We camped in the northwest last fall in temps to the mid teens and remained at one park for 3 weeks with heat on the entire time. We tried various settings to get the floors to feel warm, I would say the best they got was "not cold" even with Zone 2 set at 85 and could not say that about the entire floor.
TXBart is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 01-28-2014, 10:54 AM   #2
Senior Member
 
stevedenesha's Avatar
 
Join Date: Jul 2013
Location: Queen Creek AZ
Posts: 421
So what is the question you have for CS?
__________________
Steve, Judy and the Pups Tinker and Shortcut
2016 Entegra Anthem 44B Victory Blue
stevedenesha is offline   Reply With Quote
Old 01-28-2014, 01:08 PM   #3
Registered User
 
Entegra Owners Club
Join Date: Mar 2013
Posts: 2,516
Oops, kinda forgot that. The floor was icy cold. Obviously taking temps from an inappropriate spot. No wonder that it doesn't heat the floor very well even when it is set to 85; it gets to 85 at that spot but not the floor.

Asking them to offer a solution.
TXBart is offline   Reply With Quote
Old 01-28-2014, 01:30 PM   #4
Registered User
 
Join Date: Feb 2012
Location: Troy Mo
Posts: 1,951
Vance, are you sure you don't have a kinked hose like Dave and a couple of others have had for zone 2. Noel
loisjop is offline   Reply With Quote
Old 01-28-2014, 01:53 PM   #5
Registered User
 
Entegra Owners Club
Join Date: Mar 2013
Posts: 2,516
I'm not trying to heat Zone 2, I'm trying to prevent freezing. Zone 2 isn't turned on but is reading the highest temperature.

CS said a few coaches went out with the Zone 2 sensor too close to a Zone 1 register, it sounds like mine is one of those. I'm waiting to hear how to resolve it.
TXBart is offline   Reply With Quote
Old 01-28-2014, 02:24 PM   #6
Senior Member
 
rogelling's Avatar
 
Join Date: Oct 2013
Location: Blanchard, Idaho
Posts: 813
Quote:
Originally Posted by TXBart View Post
I'm not trying to heat Zone 2, I'm trying to prevent freezing. Zone 2 isn't turned on but is reading the highest temperature.

CS said a few coaches went out with the Zone 2 sensor too close to a Zone 1 register, it sounds like mine is one of those. I'm waiting to hear how to resolve it.
I have the same situation. Here is a pic I think of the zone 2 sensor in the bedroom.
Attached Thumbnails
Click image for larger version

Name:	IMAG0161.jpg
Views:	119
Size:	211.0 KB
ID:	54866  
rogelling is offline   Reply With Quote
Old 01-28-2014, 02:42 PM   #7
Registered User
 
Entegra Owners Club
Join Date: Mar 2013
Posts: 2,516
Someone, seems like Dave Ladwig, had a similar issue and his Zone 2 sensor was near the fireplace in his DEQ and had to be moved.
TXBart is offline   Reply With Quote
Old 01-28-2014, 03:14 PM   #8
Senior Member
 
DSL417's Avatar
 
Entegra Owners Club
Join Date: Sep 2012
Posts: 6,695
Blog Entries: 2
Yes I did, and kudos to Corey, who had similar issue and showed me where the kink was.

Vance, make sure that when you turn to heat, using diesel and with the slide out, that the front heat exchanger in the coach (below the dash drawer is pushing warm air. Give it 5 minutes after you turn on for the fluid to circulate). If you're getting warm air there, you're probably good. If there is a kink anywhere, this blower will blow cold air, because the boiler fluid is not circulating. If not blowing warm air, give me a call...think you have my number.

And BTW, my tiles now run from downright toasty to tepid, depending where the hose runs under the tile (including the bedroom)...after PJ showed me where the pipes run. AND, Joyce called me two days later, just to make sure my floors were warm...she's a sweetie!
__________________
Dave and Beth
2015 Cornerstone 45J
2020 Ford F-150 Lariat
DSL417 is offline   Reply With Quote
Old 01-28-2014, 03:37 PM   #9
Registered User
 
Entegra Owners Club
Join Date: Mar 2013
Posts: 2,516
My dash drawer gets so hot I get worried about the iPod I keep there.

I don't think my issue is flow in Zone 2, it is sensing for Zone 2. Which isn't to say I don't also have a kink or 2, maybe even in the coach.

Ray said some coaches left the factory with the Zone 2 sensor too close to a heat outlet which makes sense why our Zone 2 reads so much higher than it is set without really warming the floor, it's getting heat right out of an outlet where it is the hottest.
TXBart is offline   Reply With Quote
Old 01-28-2014, 03:39 PM   #10
Registered User
 
Entegra Owners Club
Join Date: Mar 2013
Posts: 2,516
From Ray:

More than likely, the zone 2 temperature sensor is getting heated by the register in the center of the unit. We had a few units that the temperature sensor for zone 2 was to close to the heat register and was registering that heat. I would suspect your unit is one of these units.


I have asked for the remedy. I'll post the reply.
TXBart is offline   Reply With Quote
Old 01-28-2014, 03:57 PM   #11
Senior Member
 
DSL417's Avatar
 
Entegra Owners Club
Join Date: Sep 2012
Posts: 6,695
Blog Entries: 2
FWIW, I set Zone 2 to 90...set the others to whatever I want. Thus far I have never seen the thermostat get to 90 in Zone 2, so the floor continues to get hot fluid. Using the electric heater on the AH boiler won't get the Zone 2 anywhere near 80, tough to get it to 70. But it does cause the boiler to operate, I think.
__________________
Dave and Beth
2015 Cornerstone 45J
2020 Ford F-150 Lariat
DSL417 is offline   Reply With Quote
Old 01-28-2014, 04:14 PM   #12
Senior Member
 
Join Date: Nov 2010
Posts: 123
Floor heat

My coach is currently inside my storage barn here in Michigan where we are seeing 10-15 below temps. I keep it plugged in with temps set at 50 in the coach and lowest setting in basement. I have diesel and electric switches set on .

Normal cold weather usage (when we are actually staying in it ) gets floor sort of warm when zone 2 temp is set 5-10 degrees higher than setting for zone 1 and 3,

While in my barn , not in use, This winter and last--My coach has been fine (not even close to freezing). This is a tribute to the insulation in the entegra.

All that said, my zone 2 would work much better if my coach was sitting in south Florida or Arizona right now!
tvolk is offline   Reply With Quote
Old 01-28-2014, 04:40 PM   #13
Senior Member
 
voltdoc's Avatar
 
Entegra Owners Club
Join Date: Oct 2010
Location: East Greenwich, RI
Posts: 2,303
Quote:
Originally Posted by rogelling View Post
I have the same situation. Here is a pic I think of the zone 2 sensor in the bedroom.
That looks like the mic for the alarm, the thermostat sensor has a diamond shape and if that's the rear bedroom, on my coach it's higher up on that same wall.
__________________
Rob & Linda https://MyQuantumDiscovery.com
2017 Entegra Aspire 44B - 2021 Jeep Grand Cherokee L Overland
2013 Entegra Aspire 42RBQ
voltdoc is offline   Reply With Quote
Old 01-28-2014, 05:18 PM   #14
Senior Member
 
voltdoc's Avatar
 
Entegra Owners Club
Join Date: Oct 2010
Location: East Greenwich, RI
Posts: 2,303
Another thing to keep in mind is that Zone 2 and Zone 1 use the exact same plumbing loop. Zone 2 is really just sort of a "virtual" zone. The only difference between Zone 1 and 2 is that Zone 1 turns on the fans in the 3 heat exchangers. Actually, I think this is very clever.

Point is when you run Zone 1 you are also heating your floors to a certain extent because the hot water is flowing thru all the same pipe as "virtual" Zone 2.

When Zone 1 is on, the fans in the 3 heat exchangers are on and of course extract more of that heat into the air inside the coach and let less of it go to heating the floor. When Zone 2 is on the hot water runs thru the same pipe and all three heat exchangers but the fans in the three heat exchangers remain off and more of the heat goes into the floor.

I know this because we had a kink in the PEX pipe inside our floor which was not accessible to repair without surgery. During the troubleshooting process and working with Joyce and team I got very familiar with the pipe and zone layout. Entegra of course stepped up and made it right after a trip back to Middlebury - fortunately no tiles needed to be ripped out.

Also FYI, remember the Aquahot (all models as far as I know) have only two circulator pumps. So where do the four zones come from? One of those pumps is for Zone 1 & 2 (salon) and the other is for the Zone 3 (bedroom) and basement.

Same "virtual zone" deal with the Zone 3/basement - when heat is called for on Zone 3 (bedroom) hot water flows thru the bedroom and basement heat exchangers but only the fans on the two bed/bath heat exchangers turn on. If the basement thermostat is on and calls for heat, hot water still flows thru the same bedroom and basement heat exchangers but only the fan on the basement heat exchanger turns on.

You would know right away if you have a kink - for example if you set Zone 1 to come on, you should feel heat at all three heat exchangers (mid coach, under kitchen sink, under dash) after several minutes (gas/diesel burner should be on). If you do have a kink, Zone 2 won't work either.

I have been having problems lately with the kitchen slide pinching the rubber hose for Zone 1/Zone 2 as it extends. I now have someone extend the slide while I guide the hose so it doesn't go where it shouldn't.

Just another observation. On our coach the bedroom floor has no heat in the floor. While you might think on casual observation that the salon and bath floors might just feel slightly warm to the touch, on a cold morning you will definitely appreciate how much warmer the heated part of the floors are compared to the unheated bedroom floor when you walk on them with bare feet.
__________________
Rob & Linda https://MyQuantumDiscovery.com
2017 Entegra Aspire 44B - 2021 Jeep Grand Cherokee L Overland
2013 Entegra Aspire 42RBQ
voltdoc is offline   Reply With Quote
Reply



Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Dealership info blntln iRV2.com General Discussion 3 12-30-2013 12:43 PM
Engine ID info bukzin Cummins Engines 12 11-28-2013 10:26 AM
HELP with engine and trans info 03BLACKBIRD Winnebago Industries Owner's Forum 5 10-27-2013 06:13 AM
Coachmen: need some info from coachmen owners! coach_quin Forest River Owners Forum 3 07-14-2013 05:03 PM

» Featured Campgrounds

Reviews provided by


All times are GMT -6. The time now is 12:46 AM.


Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.