Bigb56: I did answer your question. Current capacity depends on cable design and not wire gauge only.
The manufactures rating includes intended usage. It it intended to be put in a wall with restricted air flow? Is it is intended to be thrown loose on the floor or ground with free air flow around it. How is it rated when arranged in a cable tray? Again, current capacity is more than just wire gauge.
__________________
Coachman Leprechaun 311FS, 2018
|
|
|
|
Join the #1 RV Forum Today - It's Totally Free!
iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!
You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!
|
08-05-2022, 03:21 PM
|
#16
|
Senior Member
Join Date: Jul 2014
Posts: 35,444
|
If 10 gauge wire, used in 30 amp service, is safe to use, at what amperage is it actually going to fail.
Let's say you plunge an axe thru your 30 amp cable, which is plugged into a 50 amp service thru an adaptor.
Will the cable handle the 50 amps of dead short and trip the breaker OR will the cable overheat and burst into flames.
I would think if it can handle 30 amps all day, it can handle 50 amps for as long as it takes to trip the 50 amp breaker.
|
|
|
08-05-2022, 06:04 PM
|
#17
|
Senior Member
Join Date: May 2018
Posts: 3,223
|
Quote:
Originally Posted by twinboat
If 10 gauge wire, used in 30 amp service, is safe to use, at what amperage is it actually going to fail.
Let's say you plunge an axe thru your 30 amp cable, which is plugged into a 50 amp service thru an adaptor.
Will the cable handle the 50 amps of dead short and trip the breaker OR will the cable overheat and burst into flames.
I would think if it can handle 30 amps all day, it can handle 50 amps for as long as it takes to trip the 50 amp breaker.
|
Of course it can, and that's why NEC allows short circuit protection to be rated higher than overload protection.
__________________
Brian, 2011 Winnebago Via Class A on Sprinter Chassis
2000 Jeep TJ toad
Tucson, AZ
|
|
|
08-06-2022, 06:45 AM
|
#18
|
Senior Member
Join Date: May 2018
Posts: 3,223
|
Quote:
Originally Posted by MichaelBarb
Bigb56: I did answer your question. Current capacity depends on cable design and not wire gauge only.
The manufactures rating includes intended usage. It it intended to be put in a wall with restricted air flow? Is it is intended to be thrown loose on the floor or ground with free air flow around it. How is it rated when arranged in a cable tray? Again, current capacity is more than just wire gauge.
|
The reason we are allowed to plug smaller and lower ampacity rated cords, and connect smaller and lower ampacity conductors to higher ampacity circuits is because those loads are self limiting in current by design, or there is overcurrent protection provided at the load for things like motors which can't be self limiting. As far as the adapter and the trailer cord, the 30 amp main breaker in the trailer serves as the overcurrent protection for both and the 50 amp breaker serves as the short circuit protection.
One only has to look at 250.122 to see that the #10 grounding conductor in the adapter and in the trailer cord is rated to safely carry enough fault current to open an OCPD up to 60 amps without suffering damage.
I can feed a clothes dryer and an air conditioner both with the same #10 NM and for the clothes dryer I am limited to a 30 amp OCPD but with an air conditioner I can breaker it at 50 amps on the supply side and fuse it at 30 amps at the load per NEC and per the manufacturer's name plate instructions.
__________________
Brian, 2011 Winnebago Via Class A on Sprinter Chassis
2000 Jeep TJ toad
Tucson, AZ
|
|
|
08-06-2022, 12:28 PM
|
#19
|
Senior Member
Ford Super Duty Owner
Join Date: Apr 2022
Location: Wrentham, MA
Posts: 134
|
I have worked in cable manufacturing. A grounding conductor can be smaller than the hot and neutral conductors because it is uninsulated. An uninsulated conductor allows for more cooling than an insulated one. There is more to it than just wire gauge.
There are also all kinds of special exceptions that have been grandfathered in. When you do railroad work there are some things you can do that seem in violation of NEC code. These were covered by codes before NEC and are grandfathered in. Same when doing in work in the city of Chicago, Los Angelous, and other odd places. In general, the local codes are more stringent than NEC, but some odd things get grandfathered in.
Over time the grandfathered exceptions are being eliminated. Some will never be. The plugs we use in RV's are a good example. By rights they are not switch rated. In other words, they cannot be used to break power under load. There is no way to contain the arc flash. Twist locks are not switch rated but the older spade connectors we use are grandfathered in as switch rated. It is a topic of ongoing debate. Personally, I have found it almost humous over the years. The anti-arc flash movement has gotten radical in some ways but justified in most.
There is a fundamental law of safety rules and codes, "There will be no changes unless there is blood." A macabre statement but unfortunately it is true.
__________________
Coachman Leprechaun 311FS, 2018
|
|
|
08-06-2022, 04:58 PM
|
#20
|
Moderator Emeritus
Ford Super Duty Owner
Join Date: Aug 2000
Location: Bryan, TX when not traveling.
Posts: 22,948
|
It is simple. The RV is rated for 30 amps, and the cord is rated for 30 amps. The RV has a 30-amp breaker in the inlet panel and it will trip if the amperage exceeds wo amps. You are protected.
Ken
__________________
Amateur Radio Operator (KE5DFR)|No Longer Full-Time! - 2023 Cougar 22MLS toted by 2022 F150, 3.5L EcoBoost Tow Max FX4 Lariat Travel with one Standard Schnauzer and one small Timneh African Gray Parrot, retired mechanical engineer
|
|
|
08-06-2022, 06:12 PM
|
#21
|
Senior Member
Join Date: Apr 2017
Posts: 260
|
I Agree
Have tripped the RV camper breaker but very rare trip the campground service
__________________
2008 Carriage Carri-Lite 36 DFQ SOLD
2015 Chevy 3500HD High Country DRW
2015 Host Aspen 9.5 LB
|
|
|
|
|
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
|
|
Posting Rules
|
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts
HTML code is Off
|
|
|
|
» Recent Discussions |
|
|
|
|
|
|
|
|
|
|
|
|
|