240v from generator

Background: I am a commercial/industrial electrician, 21 yrs experience. I understand electricity but may not convey so that the unknowing will understand what I am explaining.

Problem: my generator, Onan qc 5500 puts out 120/120. Both legs out of the generator are the same phase, testing 0v from wire to wire, not 240v. There are two 30a breakers on the generator, not tied together. I thought that odd at first but now I understand this generator will not support 240v as is. If it was able to support 240v the breakers would have been tied together.

Now, knowing that, and having a 240v mini split already installed I can only use the mini split from shore power and not the generator, or can I? I guess my main question is, how can I get 240v out of a 120/120 generator? Is there a phase shifter that can handle a generator? Yes, this is my first time seeing a 2 pole generator. I assumed it would be able to output 240v.

Thanks in advance.
Fifthwheel10 is offline   Reply With Quote
Join the #1 RV Forum Today - It's Totally Free!

iRV2.com RV Community - Are you about to start a new improvement on your RV or need some help with some maintenance? Do you need advice on what products to buy? Or maybe you can give others some advice? No matter where you fit in you'll find that iRV2 is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with other RV owners, see fewer ads, upload photographs, create an RV blog, send private messages and so much, much more!

Old 12-29-2018, 07:27 PM   #2
Member
 
Mallie's Avatar
 
Join Date: Dec 2018
Location: Eufaula, OK
Posts: 75
Yes, it is easy to step AC up or down. Just look on Ebay.
https://www.zoro.com/square-d-transf...MaAnNnEALw_wcB

Course it is going to take twice the 240v amps from the 120v. If it is an inverter driven unit, should not be a surge on start.
__________________
1995 42' Bluebird Wanderlodge
Mallie is offline   Reply With Quote
Old 12-29-2018, 07:48 PM   #3
Senior Member
 
Join Date: Jul 2014
Posts: 33,194
Check the exact model #. It seems that some can be configured for 240 volts.

Problem is, you will only get 23 amps per leg, but with a 240 volt AC, it may be OK.

My 1999 Generac was able to be converted. The wiring diagram showed how.
twinboat is offline   Reply With Quote
Old 12-29-2018, 07:58 PM   #4
Senior Member
 
Old Scout's Avatar
 
Join Date: Nov 2005
Posts: 7,196
…..curious--true, 240v, phased power on two legs is rarely required in RV industry applications--what issue are you needing to solve by converting your generator to 240v, phased power?
__________________
Old Scout
2015 IH45 Foretravel
2003 Alpine 40' MDTS [Sold]
New Braunfels, Texas
Old Scout is online now   Reply With Quote
Old 12-29-2018, 08:02 PM   #5
Senior Member
 
Sweetbriar's Avatar
 
Thor Owners Club
Ford Super Duty Owner
Join Date: Jul 2011
Posts: 3,749
There are transformers that will produce 220 VAC split phase from a single phase 120 VAC input but as Mallie posted you'll need twice the amps. Might be easier to return the current mini split for a single phase model if possible.
__________________
2006 Hurricane 31D built on a 2006 Ford F53
Sweetbriar is offline   Reply With Quote
Old 12-29-2018, 08:11 PM   #6
Senior Member
 
Mr_D's Avatar
 
Country Coach Owners Club
Solo Rvers Club
iRV2 No Limits Club
Join Date: May 2011
Location: Vancouver, WA
Posts: 37,725
The 10 and 12.5K Onan Quiet Diesel liquid cooled gen will produce 220/240 without modification. But they weigh close to 800#'s too.
My dryer is a 220/240 volt unit with the QD 12.5k gen
__________________
2009 45' Magna 630 w/Cummins ISX 650 HP/1950 Lbs Ft, HWH Active Air
Charter Good Sam Lifetime Member, FMCA,
RV'ing since 1957, NRA Benefactor Life, towing '21 Jeep JLU Rubicon Ecodiesel
Mr_D is offline   Reply With Quote
Old 12-30-2018, 07:13 AM   #7
Senior Member
 
Join Date: Aug 2017
Posts: 1,863
Some of the generators can be rewired to 240 volt and some can't . You could get a 120 to 240 volt transformer and connect it directly to the mini split using your original 120volt breaker. That way there would be no modifications to the coach wiring and the A/C unit will work from genny and shore power.
__________________
1993 Tiffin Allegro Bay 32'
Soppy is offline   Reply With Quote
Old 12-30-2018, 07:35 AM   #8
Senior Member
 
Join Date: Jul 2014
Posts: 33,194
Quote:
Originally Posted by Old Scout View Post
…..curious--true, 240v, phased power on two legs is rarely required in RV industry applications--what issue are you needing to solve by converting your generator to 240v, phased power?
He installed a 240 volt mini-split AC unit.
twinboat is offline   Reply With Quote
Old 12-30-2018, 10:27 AM   #9
Senior Member
 
Join Date: Mar 2018
Posts: 1,644
I have a generator with a built in 240 outlet and two 120v receptacles.
__________________
Professional mechanic.
2018 Ram 2500 HD Mega cab.
mobilemike is offline   Reply With Quote
Old 12-30-2018, 11:58 AM   #10
Senior Member
 
glennwest's Avatar
 
Join Date: Mar 2009
Posts: 1,592
Quote:
Originally Posted by Sweetbriar View Post
There are transformers that will produce 220 VAC split phase from a single phase 120 VAC input but as Mallie posted you'll need twice the amps. Might be easier to return the current mini split for a single phase model if possible.
All the 110v mini splits are max of 12k output. Any more than that you need 220. One 12k mini split heats my entire Teton with the help of the fireplace. Now it needs help to cool this. I'm going 220 also for more output.
__________________
2003 Teton Grand Freedom. 2006 Freightliner Century 120 with Detroit 14L and Ultrashift.2016 Smartcar carry on deck. Full time going from job to job. Building and maintaining plants across the USA. Sold 2006 Mobile Suites 32TK3
glennwest is offline   Reply With Quote
Old 12-30-2018, 12:21 PM   #11
Senior Member
 
Join Date: Nov 2015
Posts: 1,111
I need some help from those with knowledge of generators. Question I have is ,,, does a 120/120 output have two seperate neuteral legs. And, can the two neuteral legs be bridged to produce 240 volts. If so the breakers must be mechanically be bridged with a pin or clip. Just asking

CLIFFORD
clifford j is offline   Reply With Quote
Old 12-31-2018, 02:23 AM   #12
Junior Member
 
Join Date: Dec 2018
Location: Phoenix, AZ
Posts: 2
Generator

Quote:
Originally Posted by Soppy View Post
Some of the generators can be rewired to 240 volt and some can't . You could get a 120 to 240 volt transformer and connect it directly to the mini split using your original 120volt breaker. That way there would be no modifications to the coach wiring and the A/C unit will work from genny and shore power.
Thank you soppy. This seems like the most sensible idea, hopefully temporary, as I am going to email the manufacturer to find out if a tap or two can be changed. I do know that the breaker handles will have to be tied together. Lol, just thought of more that would have to change if I changed tap, the nameplate sticker from single phase 120 to single phase 120/240. Not sure how the neutrals are configured, but I will look into that also if taps are changed.

Thanks again!
Fifthwheel10 is offline   Reply With Quote
Old 12-31-2018, 04:36 AM   #13
Senior Member
 
American Coach Owners Club
Join Date: Jun 2012
Posts: 344
240v from generator

Onan makes a small 5500 gas commercial generator with the same footprint as the RV style. It is a 120/240 generator. (Has a white case)Most of the green RV models cannot be reconfigured to 240.
mhudson is offline   Reply With Quote
Old 12-31-2018, 06:43 AM   #14
Senior Member
 
Join Date: Aug 2017
Posts: 1,863
Quote:
Originally Posted by Fifthwheel10 View Post
Thank you soppy. This seems like the most sensible idea, hopefully temporary, as I am going to email the manufacturer to find out if a tap or two can be changed. I do know that the breaker handles will have to be tied together. Lol, just thought of more that would have to change if I changed tap, the nameplate sticker from single phase 120 to single phase 120/240. Not sure how the neutrals are configured, but I will look into that also if taps are changed.

Thanks again!

Some generators have 2 separate windings connected in parallel to produce 120 volts. You will nave 2 neutrals and 2 hots. For 240 volts the windings are connected in series (one hot to one neutral) This connection will now be the new neutral . The voltage regulator will have to be changed for 240 volt operation. I have seen some just use a 120 volt regulator on a 240 volt generator . You will need the proper wiring diagram before you start, otherwise you could "smoke" the generator.

With a 240 volt generator , you may have a problem with appliances being on the same leg and overloading on side of the generator.
If you use a transformer , it will be rite at the mini-split and no changes to the coach wiring or breakers will have to be made.
__________________
1993 Tiffin Allegro Bay 32'
Soppy is offline   Reply With Quote
Reply

Tags
generator



Currently Active Users Viewing This Thread: 2 (0 members and 2 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Generator 120v or 240v Shawn6596 MH-General Discussions & Problems 68 05-27-2018 06:21 AM
50A 120V/240V distribution panel - what uses 240V? CountryB Monaco Owner's Forum 27 10-13-2017 07:53 PM
Converting Generator 110V to 240V Rod33 RV Systems & Appliances 7 04-16-2014 01:22 AM
Generator 240V outlet tap roadhogs Monaco Owner's Forum 2 06-04-2012 06:43 PM