Quote:
Originally Posted by mel s
Riverc
See the trouble shooting instructions in this pdf: http://www.bdub.net/manuals/Suburban_Service_Manual.pdf
BTW I very much doubt that the click you hear is the sail switch.
When the sail switch in my Suberban in my SF-42F furnace closes or opens it doesn't "click" loud enough for me to hear...(however I can hear the click of the "gas valve").
Mel
'96 Safari
|
Exactly^^^^^^^^^
Hot air blowing means main flame is lighting off........but then dropping out and locking out due to 'lack of flame proving' That is why you have to reset using the t-stat
Flame proving is done by 'flame ionization' ---a milivolt signal is generated and sent back to circuit board -----no signal board shuts down gas valve. Usually will make 3 attempts then lock out
Burner slots obstructed and flame isn't engulfing spark electrode
Spark electrode is not centered over burner slots
Spark gap is not correct---S/B 1/8"
High Tension wire from board to electrode connections are loose/dirty (doesn't take much resistance to stop milivolt)
Ceramic is cracked allowing milivolt signal to jump to ground
Which Suburban Model do you have??