Quote:
Originally Posted by tred
Persistant - I like your idea about a circuit breaker. What size would you recommend?
|
Isaac is correct.
For residential 120 volt AC wiring there is a national standard. There are two tables. The ampacity table lists the circuit breaker or fuse size for any given cable specs. There is another table that lists the cable to be used based on distance and maximum load. As Isaac said, it is to make sure appliances have enough power at the far end of the cable.
12 volt DC circuits do not have a national standard. The point is you do not want hot connectors or cables in the walls of a trailer you live and sleep in. You do want appliances at the end of the cable to work properly and efficiently.
Use the table listed above. The circuit breaker should be sized according the shortest listed length of wire. So use the top box for each column.
I use the ampacity table in the 120 volt National Standard. It has more than 100 years of validation behind it.
Example:
4 awg wire is rated to carry 90 or 100 amps at 6 feet. Choose a circuit breaker of no more than 100 amps to protect 4 awg wire.
For my personal safety, I tend to use a smaller breaker or a larger wire. Different 12 volt charts show different capacities for different purposes. I plan to be safe.
For battery charging I always choose a larger wire.
Some inverters need larger wire to prevent voltage drop that causes the inverter to disconnect. In this case length of wire and the number of connectors in the circuit matter as well.
First, determine the load the wire will carry.
Next, determine wire size to safely carry the load.
Next, choose a breaker or fuse that will not allow the wire or connectors to get hot. (ampacity)
Finally, up size the wire to get the power at the end of the wire high enough to meet the needs of the load.
The ultimate test is to put your hand on the wire and the connectors when the wire is carrying the maximum load. If it gets warm, you are loosing efficiency. If it gets hot, your safety may be at risk. (Yes if your hands are wet, or you are touching a ground, you may get a shock.)